I have a Coleman gas furnace model DGAA070BDTA, in mobile home.

Customer Question
The air pressure switch needs...
I have a Coleman gas furnace model DGAA070BDTA, in mobile home. The air pressure switch needs to be replaced (which is an easy fix)-- it took a digger last winter and I blew into one of the rubber hoses until it lit. My problem now is that the burners ignite but won;t stay lit... is this a bad ignitor, or another part?
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
10/1/2009
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,886
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
would you say the flame only last around a few seconds?
Ask Your Own HVAC Question
Customer reply replied 8 years ago
Exactly, and then it just goes out.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago
In the burner area ill be a rod with a white porcelin base. Find this rod and sand it off with emery cloth or sand paper then try it.
Ask Your Own HVAC Question
Customer reply replied 8 years ago

I did that just now, then waited for 3 failed ignitings, then the "indicator light"(green light) blinks once: "ignition failure". What now? Could it be the sensor rod? or Ignition switch?

Customer reply replied 8 years ago
Hello? Did Billy go offline?
Customer reply replied 8 years ago

The gas is flowing okay... I turned furnace on with gas off, waited until I could see the "element(?)" glow, and then turned gas on and it ignited and ran for close to 3 minutes then shut down.

 

HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago
Wow you have a strange one there. Doent sound like flame sense. Is the stack and vent clear to where you would not be faulting on pressure switch?
Ask Your Own HVAC Question
Customer reply replied 8 years ago
Sorry, don't know what you're talking about. Just a guy with a broken furnace.
Customer reply replied 8 years ago
I have to blow into the lower tube of pressure switch because it's broken, so that's a temporary fix and it should be working otherwise. I intend on ordering one, and then whatever part you think is causing my current problem with the ignition failure.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago
Sorry, On your furnace is a draft fan that starts up first. IT pulls air through a small tube that closes a air switch. This air switch is a pressure tube. Take tube off and clear and check ends where tube attaches to make sure they are clear.
Ask Your Own HVAC Question
Customer reply replied 8 years ago
All clear! Make sure to read what I wrote you just before you replied; about blowing thru tube...
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago

Ok, I see we are on the same page. To test the theory (and this is for test only)

remove the 2 wires from the pressure switch. Start the furnace, and after the draft fan is running connect the 2 wires together. This simulates the air switch holding the contacts closed. Remember though that to start, the wires cannot be touching. Start with them apart and join when draft fan runs.

Ask Your Own HVAC Question
Customer reply replied 8 years ago

Nothing happens, or I should say, the same problem.

When I am blowing thru end of tube of pressure switch, I can see thru little window when it begins to glow, then when the flames ignite, and then they go out; there's where the problem is. Sorry if I'm getting you messed up.

HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago
Ok I got ya now. As long as you continue blowing while the flame is lit and the pressure switch is still closed, and you sanded the sensor, it sounds as though it is the control board. The board decides if the flame stays on or not. As long as the items I mentioned were addressed it would be the board. Only other option is if you are on propane and the pressure is low. Then a low LP pressure switch would do the same thing.
Ask Your Own HVAC Question
Customer reply replied 8 years ago

Not on propane.

So does that mean a new control board?

HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago
Yes, IF the sensor is clean and IF the pressure switch is connected.
Ask Your Own HVAC Question
Customer reply replied 8 years ago
Dagnabbit! It would have to be expensive! Okay, I'll try sanding the sensor again just in case. Thanks for the help, I really appreciate it!
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago
I really appreciate your patience, I had some connection problems and I am not as good with computers as furnaces. Thank you.
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,886
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,886
22,886 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My 26000 btu heater began with it cutting off ocasionally
Second opinion] my 26000 btu heater began with it cutting off ocasionally now it wont light at all but the pilot will light @ when u release the button it goes out what is my problem. thanks … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Help me validate my plan to connect two EcoBee 3 Smart
Please help me validate my plan to connect two EcoBee 3 Smart Thermostats to a Honeywell EMM-3 Zone Controller.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Trying to connect a new ecobee4 thermostat to my gas
Trying to connect a new ecobee4 thermostat to my gas furnace/AC. The control board shows wires attached to W,R,T,G screws, and the thermostat has connectors to W,R,Y,G. Since I don't have a common wir… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Goodman furnace model B14933255. I have had issues
i have had issues lately with it. I have replaced both filters, cleaned the flame sensor with steel wool and vacuumed the area within the furnace. it lights up on the 2nd cycle and will stay on for a short while then cycles again and starts again after the 2nd cycle. Sometimes it cycles 3 times and shuts down for appx an hour and the light flashes once. What else should I check or do or replace? Oh by the way i replaced the motherboard about 3-4 years ago. That's not an issue. Please advise … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Airease nat gas furnace lights but shuts off about 10 sec
airease nat gas furnace lights but shuts off about 10 sec later, a vent blower keeps running and after a minute or so it lights again and keeps cycling in this manner. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Question is about the augar motor on a Quadrafire pellet
question is about the augar motor on a Quadrafire pellet stove insert … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
We have a 10 year old well water system with a Buderus
We have a 10 year old well water system with a Buderus indirect fired hot water tank Model S120. We have for some time been getting rust colored hot water. Our cold water was tested by the Penn State … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My boiler is running low on water every day or so. I see a
My boiler is running low on water every day or so. I see a good deal of steam escaping around the water-level indicator (a vertical glass tube), and I wonder if I have the valves adjusted wrong. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a Lennox lf24-150 that is giving me a 4 flash. It
Hi I have a Lennox lf24-150 that is giving me a 4 flash. It runs perfectly for 2-3 cycles then starts fires but the fan doesn't turn on. Then I get the 4 flash since it is overheating without the fan … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Sure. I need to reset my Trane Xe90 Furnace. It's on
Sure. I need to reset my Trane Xe90 Furnace. It's on external lockout after failing to light. Happened after I tried switching to a new thermostat. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Appreciate you helping me. I have a similar issue as to this
Hi, appreciate you helping me. I have a similar issue as to this post where it seems like my Control 4 thermostat is sourcing power from the battery instead of the main power source. If I told you the… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Xrv95 trane furnace. Power to unit, fuse ok, transformer ok,
xrv95 trane furnace. Power to unit, fuse ok, transformer ok, Circuit breaker ok. Power to furnace. Changed thermostat batteries. Problem is fan will not run even in on position. No heat. No codes, no … read more
Certified HVAC Service Technician
Certified HVAC Service Technician
Welder
Vocational, Technical or Trade School
2 satisfied customers
I have a zvc404-4 and a Honeywell perstige eim that controls
I have a zvc404-4 and a Honeywell perstige eim that controls my heat pump and electric forced air heat. I am trying to connect the taco zone one to the 3rd stage of backup heat on the eim… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a GCG-50 water heater in stalled 5 years ago, and the
Hi, I have a GCG-50 water heater in stalled 5 years ago, and the indicator light now flashes 4 times. Heater will not start. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I. Iam installing a service disconnect to my 240 volts water
iam installing a service disconnect to my 240 volts water hetaer where do i place the earth or ground wire and ther neutral wire,i … read more
David Bowden
David Bowden
Owner
467 satisfied customers
Have a Ac/Heater unit Model RGPS-10EBRJR made 03/2010, the
Have a Ac/Heater unit Model RGPS-10EBRJR made 03/2010, the heater will come on & light, as soon as the blower comes on the flame will go out. it will do this over & over, I can turn the heater off & l… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
It doesn't seem like my newly installed Aprilaire humidifier
It doesn't seem like my newly installed Aprilaire humidifier is working. Shouldn't I hear water draining out the condensation drain? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
My spa heater isn't working properly and I don't know how to
Hi my spa heater isn't working properly and I don't know how to interpret the codes … read more
David Bowden
David Bowden
Owner
467 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x