I have a Carrier Air Handler Model No. FC4BNF042 which is less than 7 years old and it has developed a leak. The a/c repairperson said he installed 25 lbs of R-22 freon in the compressor this AM saying it leaks at the Air Handler. He said the compressor is a 3 ton unit with the Air Handler being a 3 1/2 ton unit.

Question: (1) What is the maximum lbs of R-22 that can be installed?
(2) Don't air handlers typically carry a 10 year warranty for leaks?
Submitted: 8 years ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
9/26/2009
HVAC Technician: Kenton Guidry, HVAC Technician replied 8 years ago
Kenton Guidry
Kenton Guidry, HVAC Technician
Category: HVAC
Satisfied Customers: 966
Experience: 12 years install/service experience.
Verified

There is no maximum that an air conditioner can have of refrigerant.

 

The charge would have to do with the length of line set.

 

The minimum charge is listed on the condenser.

 

It is illegal to keep charging a system that is leaking.

 

That technician needs to find the leak.

 

The technician can use a few different ways to find the leak.

 

As a last resort, the coil can be removed and pressure tested.

 

The technician can also use an electric refrigerant leak detector as well.

 

It is not okay that the system has been charged multiple times without finding the leak.

 

It is against the rules that anyone with a refrigeration license must follow.

 

Depending on the efficiency of your condenser you can just replace the evaporator coil.

Ask Your Own HVAC Question
Customer reply replied 8 years ago

The minimum charge listed on the condenser - is that where it says Factory Charged 8 lbs?

 

You respond that "As a last resort, the coil can be removed and pressure tested." What to do before the last resort? I take that to mean I shouldn't replace the entire system. Is that what you are saying?

 

Customer reply replied 8 years ago

I appreciate your attempt to answer my questions. I thought you would answer the 2nd inquiry but I guess not and it is no longer desired that you do so.
I have been informed by a local a/c company that it is not illegal to keep charging a system that is leaking and as to the limit on the volume of maximum that an a/c can have...well there is a limit.

 

I do not accept your responses.

HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 8 years ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,767
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello, I have looked at your question and I am volunteering an opinion as to your situation.

 

1) to say recharging is not illegal is preposterous. The reason the cfc's were outlawed is beacuase of environmental concerns. To say it is not illegal means you could just keep refilling a unit over and over with no recourse. To fill a unit requires identification of a leak and the subsequent repair.

 

2) If you unit ships with 8 lbs of rerfigerant why are you paying for a company to put in 25 lbs. It is one of the more unethical service calls I have heard. You can plan on one ton of cooling taking around 2.75 - 3 lbs. You have been taken advantage of then given information that does not make sense.

 

3) If money is no object, replace the entire system. I am sure the contractor would like that. IF yoiur problem is the coil you can simply address the coil. And if you get information of equipment not available because of refrigerant phase out, ask your contractor about R417A. It is a direct replacement for R22 that no one wants to talk about. This information is at no cost. Your biggest concern is not a $15 dollar question here if you are dealing with a contractor who installs 25 lbs in a 3 ton unit.

Ask Your Own HVAC Question
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,767
22,767 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

966 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
travis webb
travis webb
tech.
2,153 satisfied customers
I have a Carrier 58SX gas fired condensing furnace that will
I have a Carrier 58SX gas fired condensing furnace that will not start. The pilot flame comes up upon the thermostat calling for heat but the flame is a bit lazy and it goes out after about 5-7 second… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
On our heat pump the evaporator blower runs constant even
On our heat pump the evaporator blower runs constant even when set to auto. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Question for you regarding wiring a carrier infinity with a
Question for you regarding wiring a carrier infinity with a Honeywell lyric. I have a gas furnace and an AC condenser. Today the terminal with the abcd wires connected in the furnace has 2 sets of wir… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am installing an Evaporator Control Limit switch on the
I am installing an Evaporator Control Limit switch on the outside heat exchanger for the upstairs central heat & air unit in my house. I know that it is just supposed to splice into the low voltage co… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My carrier evaporator keeps on blowing the 3 amp fuses. I
my carrier evaporator keeps on blowing the 3 amp fuses. I already replaced the capacitor, contactor and lastly the transformer. You think that I have wires sticking together? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set on hold, auto, cooling.75 dgr. A/C will run for a while and go dark.Cooling stops. eventually it will light up and cooling will begin and wi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I am looking for a evaporator coil assy model number
I am looking for a evaporator coil assy model number G/HC030SA FOR CENTRAL ENVIRONMENTAL SYSTEMS … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
New r410 condensing unit and new evaporator coil. gauges go
new r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am told I have a leaking evaporating pan in a Lennox Model
I am told I have a leaking evaporating pan in a Lennox Model #C16-46-1FF. Iwould like to find a replacement pan. Is this possible, or can I tape crack? … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I installed a carrier 38MGQF-36-6 mini split system for one
I installed a carrier 38MGQF-36-6 mini split system for one of my customers and he had all of the wiring done by an electrician who used solid romex wire, I know that's good for the feed but not betwe… read more
David Bowden
David Bowden
Owner
333 satisfied customers
I have a carrier condenser outside and the relay keeps on
I have a carrier condenser outside and the relay keeps on popping I want to know if I can bypass until I can get a new one … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has run without problem for the last two years. Lately, it has begun to shut down and then restart on its own after about an hour or more. The l… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
My Carrier is 4 years old. My problem is the condensate
Hi my name is Dave. My Carrier is 4 years old. My problem is the condensate drain is stopped up. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Carrier condenser Model#: 38HDC060321. Relay opens after
Carrier condenser Model#: 38HDC060321. Relay opens after about 1 minute of running. I've replaced the capacitor (usually burns out about every two years) and the main fuses (1 blew, replaced both). Go… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a carrier furnace (1990') with a Heil Condenser. The
I have a carrier furnace (1990') with a Heil Condenser. The furnace blower doesn't shut off and the thermostat appears to be inoperative meaning the controls don't seem to have any effect on the syste… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a Carrier Condenser Model 38CK036320 I need to know
I have a Carrier Condenser Model 38CK036320 I need to know how to connect the new type S1-DP130024 Contasctopr… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x