I have a YORK modulating furnace installed 8/07. The first

heating season was fine. In...
I have a YORK modulating furnace installed 8/07. The first heating season was fine. In early November 08 it would shut off. My installer came and based on the diagnostic lights replaced the pressure switch. Furnace worked fine for 2 months. On January 9 this year;failed again. Same problem; pressure switch. Replaced again. Furnace worked fine again until this morning. Same diagnostic code. None have been a immediate hard fail. Shutting power off and restarting would resulting in furnace working but would fail later in day. Also furnace always starts but shuts off about 5 minutes later. My technician has checked out other causes and seems very competent. Other than this problem, I love this furnace.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 minutes by:
4/29/2009
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,764
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Do you have a 2 pipe system?

 

one for exhaust and one for combustion air?

 

Billy

Ask Your Own HVAC Question
Customer reply replied 8 years ago
I have a 2 pipe system. Looks like 4 inch PVC. Every thing is within the mfg recomendation. My installer is a very reputable company. Been in business over 30 years and have a very good reputation.

Hello again,

 

It is good to hear that you have a great company servicing the unit.

 

I can really get into this more via any technical releases if you can get me the model number of the furnace with serial number.

 

This will enable me to examine engineering data as well as any technical updates or issues with the unit.

 

I have seen evrything from the pitch of the furnace off an inch, to condensation jelling and not draining properly resulting in sporadic nuisance lock outs.

 

If you can get me that info I can supply you with an analyisis of the unit.

 

Billy

Ask Your Own HVAC Question
Customer reply replied 8 years ago
Its a PM9 Affinity upfloe 100K BTU.

Model #PC36C3XN1A

Serial # XXXXX

Just to restate...this furnace ran fine for one complete heating season......the pressure sw has been replaced twice and the problem went away twice.

One other thing. The initial fail always occurs at night after the furnace has been turn down for the night. This morning it did come start on time, but when off shortly.

Also, my understanding is that this furnace fires and after about 5 minutes will increase the firing rate if more heat is required. Not positive, but I believe that at this is when the furnace shuts down. The fail code is aways 3 blinking red.

Ok,

 

here we go. You have a common denominator which is pressure related.

 

You have already changed pressure switches which rule a defective switch out of the mix. That means something either due to installation or something introduced into the system is responsible.

 

I feel if the piping for vent and intake were inadequate, too may elbows etc you would have experienced it from the beginning. So I discharge that option.

 

Likewise on draft fan, It would be a regular occurance if not daily if we lost rpm or volume.

 

What else can affect the switch? The condensate drain. Obstruction in vent or intake pipe. Now we are down to 2 fair possibilities. But the first thing techs check when a unit faults on pressure is the intake. Which brings my rambling to a interrmittant issue with the condensate removal.

 

When condensate builds up in the unit it can fault the switch....meanwhile it still slowly drains and then is not evident. I have found units that needed a water sterilizer tab put in the collector box to keep the water "thin". Hot air with moisture made a nice breeding ground to thicken the condensate which then would not drain or drain very slowly.

 

I have also found units slightly out of "pitch". The drains in these units drain back to front. When the unit is not pitched right it collects water instead of free flowing.

The unit is humming along on low speed when all of a sudden the draft fan ramps up and jerks that water a bit. All it takes is a microsecond to drop the pressure switch and start all over.

 

I know it sounds like I have already held court and decided what is wrong...but through process of elimination and what I have seen and experienced in the field, my bet is on the drain.

 

Check the trap, pitch, extra water in inducer housing, proper drain assembly for unit and the viscosity of the condensate itself.

 

I am available for follow up.

 

Billy

Ask Your Own HVAC Question
Customer reply replied 8 years ago
What you say makes since, and my local technician has checked the drain. The unit appears to be level. Some of the other things I am not qualified to check.

It still bothers me that this ran a complete heating season before the first fail. And it ran from January 9 until yesterday during the coldest part winter flawlessly.The first switch appeared to be the problem. It failed multiple times over several days and appeared to be getting worst. The second time I called my technician after two fails given it was a Friday on a cold winter day in northern New England. Since it failed yesterday, It has not re-occured. Furnace has come on about 10 times.

Do you have a theory why the initial fail is always at night after the temp has been turned down for the evening.

One other thing. I have an AC unit also on this furnace. Is it possible for AC water to get down into the furnace.

I think you have been quite thourough. Get back with be on the above and I will accept the charges.

Hello again,

 

Keep in mind this items I discuss are currently "possibilities". The best find I have had in my career involved a 90% furnace that had 3 contractors that between them had basically rebuilt the furnace. New exchanger, draft motor, pressure switch, reroute of pvc etc. This furnace had literally every part except the outer cabinet replaced.

 

I went out and found the code of pressure switch (which the unit had done for 2 years).

I pulled the drains and even the collector box to examine the unit and noticed the water moved slow. I then, through research and taking a sample found that bacteria, spores or other organic matter was being drawn into the intake pipe, through the heating process and took up comfortable residence in the warm, wet environment inside the furnace and started to "jell" the condensate.

 

I then found that the company that made the furnace was aware of this, but had not received the right amount of complaints to qualify for a "technical release".

I installed a sanitary pan strip and at the request of the manufacturer a pice of copper tube in the collector box inside the furnace.

 

The copper creates a reaction that prohibits the growth of the micro-organisms.

 

The good news is the furnace never faulted again and the customer was relieved to find out he did not need to replace his furnace.

 

I am making this assumption based on your information of the quality and credibility of your contractor,and feel comfortable that they have addressed design, piping, mechanical or installation flaws. We already what is faulting....the issue now is to find why.

 

My theory of why it faults after sitting dormant for a while is the thickening of the condensate while sitting inactive.

 

I certainly hope you rectify your issue and I am available for any follow up questions you may have.

 

Billy

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,764
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,764
22,764 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a electric furnace. The heating elements come on but
I have a coleman electric furnace. The heating elements come on but the fan does not run. The fan runs when you run it manually or with the A/C turned on. What sencer needs changed? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an Englander MDL 13-NCH 6" pipe. I have always been
I have an Englander MDL 13-NCH 6" pipe. I have always been confused about the connection on the top of the stove to the black pipe. It doesn't seem to fit tight inside it and I get some blow back smok… read more
Paul the Plumber
Paul the Plumber
Vocational, Technical or Trade Scho
21 satisfied customers
My Rodgers digital display thermostat does not display
My White Rodgers digital display thermostat does not display anything. The house is getting colder. The fan will turn on. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Thermostat will not shut off heat even though it is in the
thermostat will not shut off heat even though it is in the "off" position. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Our pellet stove model number 045086 keeps shutting off
our pellet stove model number 045086 keeps shutting off after 20 minutes to a half hour power just stops? … read more
Webb-Guy
Webb-Guy
tech.
73 satisfied customers
How do I unlock my Luxpro Thermostat?
How to unlock a Luxpro PSP511LC thermostat? The on-line manual says to use this key sequence: up, down, next, hold, rotary dial, and software reset. But it does not work. How do you key a rotary dial?… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,764 satisfied customers
Phi, I have a HW Vision PRO IAQ. We had a power outage a few
Phi, I have a HW Vision PRO IAQ. We had a power outage a few days ago. The screen on the Pro IAQ is blank. I changed the battery and the screen light up and was functioning. This morning the screen is… read more
Webb-Guy
Webb-Guy
tech.
73 satisfied customers
Tappan furnace isn't staying on. Red light on panel blinks
Tappan furnace isn't staying on. Red light on panel blinks four times. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My American standard freedom 80 two stage furnace is very
My American standard freedom 80 two stage furnace is very sporadic. I have changed ignitor, flame sensor, and filter. 50 percent of the time it will not reach set temperature and short cycles giving a… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,080 satisfied customers
I have a P3HMX12F08001 and it won't do anything all of a
I have a P3HMX12F08001 and it won't do anything all of a suddenI think the main control board went bad. I can run the blower from the tstat but even if I jump the fuel side it won't do anything… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,080 satisfied customers
Having a problem with our fireplace... looking for some
HI, having a problem with our fireplace... looking for some assistance in troubleshooting … read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
27 satisfied customers
I have a 10yr. old gas furnace. On heat up cold day, furnace
I have a 10yr. old miller gas furnace. On heat up cold day, furnace ends up with blower running continuously after raising temperature about 80& of range. Status light shows continuous blinking red. H… read more
Webb-Guy
Webb-Guy
tech.
73 satisfied customers
A brick fell off the side of my small cabin fireplace.
A brick fell off the side of my small cabin fireplace. Bricks have no mortor. Fire is burning...a eminent problem … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,080 satisfied customers
I purchased a RTH2300B thermostat I have only 2 wires coming
I purchased a RTH2300B thermostat I have only 2 wires coming from old thermostat blue and white not sure how to connect . don't trust colors … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,764 satisfied customers
This time of year should my air exchanger be running full
This time of year should my air exchanger be running full time or can it be on automatic in which case it turns on and off on its own? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,080 satisfied customers
I have a Goodman GMNT040-3the furnace comes on but the
Hello, I have a Goodman GMNT040-3(###) ###-####the furnace comes on but the fan/blower. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Im having trouble switching my thermostat to heat i have a
Hi, Im having trouble switching my thermostat to heat i have a hunter thermostat model 44860 … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,080 satisfied customers
The blower motor dose not always start with out giving it
the blower motor dose not always start with out giving it some help … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
343 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x