I need someone to optimize a solarvoltaic system. Our new
Our new solar power system is truncated at 54.0V as far as storage is concerned. How can we get more power into the batteries faster? Should we split the array to two charge controllers or should we have components with higher specs? Can you diagnose our problem? What changes or additions to its components would help? OFF-GRID POWER SYSTEM 1- Outback VFXR3524A Inverter - 3600 watt 48V sine wave inverter/charger OG/GT Compatible 1- Outback FLEXmax 60 MPPT, 60 amp, 150 VDC Solar Charge Controller 2 - SIMPLIPHI3.5 48v LiFePO,3.8 KWh batteries 34 amp. 69 ah, 48 v Amp deep-cycle Lithium Ferro Phosphate (LFP) batteries 2kw Solar array with (6) 340 watt Q Cell Duo PV Panels,. 340 watt Qcell DUO Combiner Box for PV, 3 circuit from MidNite Solar Breaker, DIN Rail,150VDC 20Amp for PV Combiner Outback MATE3s for Install Controller HUB-4 Outback, communication manager, allows interconnection of inverter and FM60 MPPT Charge controller to MATE3 MATE#s system controller/datalogger for internet connection OBDC 40 Breaker, DC, 40A, 150VDC, SPST, 3/4" wide, 1/4" stud PV in Breaker, 60 amp, 150VDC, Controller to Battery MNSPD-300 Surge Suppressor, 300V, w/LED indicator for AC circuits Thank you, Don Neely Donald J. Neely 48 ***** ***** Norwich. VT###-##-#### (###) ###-####Office(###) ###-####Home(###) ###-####Mobile … read more
Chris Parson
Chris Parson
Electrician
227 satisfied customers
I am working on a solar project and I'd like someone to
I am working on a solar project and I'd like someone to check the wiring diagram for me to make sure the wiring is compliant with the NEC code … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
6,877 satisfied customers
What happens if i hook up a battery to the pv inputs of my
what happens if i hook up a battery to the pv inputs of my solar benerator … read more
Sparkette
Sparkette
Electrical question answer provider
Vocational, Technical or Trade School
18 satisfied customers
I am trying to put together an off grid PV solar system and
I am trying to put together an off grid PV solar system and am receiving so information which is confusing me. They want to give me 36V panels with a 48V battery and a 96V charge controller and what t… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
6,877 satisfied customers
Installing a 6kw solar system on roof and have questions
installing a 6kw solar system on roof and have questions about wiring and racking. Do you have an expert? … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
6,877 satisfied customers
I need help building a solar converter that can convert
I need help building a solar converter that can convert input DC 30V-3.0A to DC 19V-5.5A how can I build this circuit? I have been trying to build a working circuit for 3 months already and have not g… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
6,877 satisfied customers
I have a question about solar. I am installing a off the
I have a question about solar. I am installing a off the grid solar system. I have a hybrid PV1800 inverter/battery charger, 8- 12v 125AmH batteries and REC solar panels. My question is this. What wou… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
6,877 satisfied customers
I have a Conext 4024 Inverter in an off grid application
I have a Conext 4024 Inverter in an off grid application connected to a generator for recharging. I recently added solar panel and a C60 60amp charge controller. I presently do not have the Inverter a… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
6,877 satisfied customers
One more question could i run the system without the battery
one more question could i run the system without the battery and just the charge controler… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
6,877 satisfied customers
I have 3K watt solar system, I've installed and would like
I have 3K watt solar system, I've installed and would like to power a dedicated line (15 AMP) from it. I want to use the Samlex EVO2224 off of my 600 AH 24 Volt Battery bank. The only thing that's con… read more
AssuredElectrical
AssuredElectrical
Electrical Contractor
High School or GED
3,844 satisfied customers
My solar system got drained when a visitor left several fans
My solar system got drained when a visitor left several fans run overnight. I am attempting to recharge my system with a generator, but noted that my xantrex C60 charge controller shows no indication … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
6,877 satisfied customers
Hello, I have the same issue. I would like to know if
Hello, I have the same issue. I would like to know if there is a solar ready panel that has an integrated line side tap that is 100A.… read more
Phil
Phil
Consultant to Engrs, Govt & Contractors
Degree, Mech Engr Technology
12,405 satisfied customers
I have a Goal Zero Yeti 400 battery that i want to be able
I have a Goal Zero Yeti 400 battery that i want to be able to charge from a renogy 100w solar panel. The Goal Zero battery has a proprietary 8mm charging input, and the Renogy panels have standard out… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
6,877 satisfied customers
I HAVE A SOLAR POWERED ,WIND TURBINE,GENERATOR CONECTED TO
I HAVE A SOLAR POWERED ,WIND TURBINE,GENERATOR CONECTED TO THIS CABIN I AM LIVING IN.THE PROWATT 800 INVERTER READS POWER OVERLOAD.I DISCONNECT ALL POWER AND TRY SWITCHING INVERTER ON AGAIN,BUT IT DOE… read more
Phil
Phil
Consultant to Engrs, Govt & Contractors
Degree, Mech Engr Technology
12,405 satisfied customers
I plan on installing 4 arrays of 6 solar panels for a total
I plan on installing 4 arrays of 6 solar panels for a total of 24 solar panels rated a 15 watts/panel or 360 watts. 1. Is it better to connect each array together in series or in parallel? 2. To keep … read more
HotWired
HotWired
Industrial Electrician
Associate Degree
155 satisfied customers
I am in the state of Virginia. Questions What size wire
I am in the state of Virginia. Questions: What size wire is required to transport DC electricity from a 2KW Solar PV Array (10 ea 200W modules) 100ft to the inverter? Will 10-2 AWG not in conduit and … read more
Sir Sparks
Sir Sparks
Owner
State & UK Certified Master electri
2,519 satisfied customers
Can I attach to the end of 3000w inverter of 230v a transformer
Can I attach to the end of 3000w inverter of 230v a transformer for a building site to convert the 230v to 110v to run the lights in my home.… read more
Craig
Craig
Electrical Director
Vocational, Technical
2,287 satisfied customers
I BUILT A WIND GENERATOR WITH AN INVERTER AND A BATTERY BANK.
I BUILT A WIND GENERATOR WITH AN INVERTER AND A BATTERY BANK. IT PUTS OUT ELECTRICITY WHEN ITS ISOLATED BUT I NEED TO KNOW HOW TO HOOK IT UP TO FEED MY FUSE BOX FOR MAX USE WITH OUT BLOWING MY INVERTE… read more
TX_Engineer
TX_Engineer
Software Engineer
Bachelor's Degree
24 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

4,922 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

9,751 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

6,877 satisfied customers

34 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Amateur & Commercial Radio Licenses

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

mrromex

mrromex

Electrical Technician

281 satisfied customers

over 40 years of all phases related to residential wiring and remodeling

< Previous | Next >

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.