A electric kiln rated 208 8.4 KW single phase is supplied by a 60 ampre rated branch circuit the branch circuit it is extended using 6 AWG 2 type MC cable the conductors in the cable are copper the total length of the branch circuit is 80 feet what is the approximate percentage voltage drop in the branch circuits assume k=12.8
Show More
Show Less
Ask Your Own Electrical Question
Answered in 4 minutes by:
3/26/2018
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,419
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

Please be patient as it takes time to type and provide links. Also note that the website may be sending you a telephone offer, the offer is not originating from me.

1) A 208 supply voltage on an 80 foot run using 6 AWG copper conductors with a 60 amp breaker results in a voltage drop percentage of 1.9% or a loss of 4 volts at the end of the 80 foot run.

Ask Your Own Electrical Question
Customer reply replied 3 months ago
The options are
A. 1.5%
B.3%
C.3.5%
D4%

1) 1.5% would be the closest choice

Ask Your Own Electrical Question

1) 2/0 AWG copper. The total motor loads = 200 amps. 2/0 AWG copper is rated @ 200 amps.

Ask Your Own Electrical Question
Customer reply replied 3 months ago
B. 2/0 AWG?

Yes

Ask Your Own Electrical Question

1) This is a trick question since 350 kcm type THHN conductors are not included in table 310.15(B)(16). THHN conductors are rated using 90 degrees and not rated at 75 degrees. If using the 75 degree rating, a 350 kcm conductor is rated at 310 amps. Multiply 310 amps x 3 = 930 amps. I would say the answer is (D) 1000 amps.

Ask Your Own Electrical Question

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks.................Kevin:)

Ask Your Own Electrical Question
Customer reply replied 3 months ago
I have a lot more Togo how long can you help me tonight?

Sorry, I'm not going to be able to stay on the web site. I need to get to bed as I need to wake up early (4:00am) in the morning for work.

Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,419
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified
Kevin and 87 other Electrical Specialists are ready to help you
Ask your own question now
Customer reply replied 3 months ago
Ok can we do more tomorrow sorry I’m just not able to study easily right now my son is in the hospital sick and my teacher let me take home my test
Customer reply replied 3 months ago
Can you help on some more questions

Unfortunately I am not able to assist during the week. If you have some additional questions over the weekend, I can help out.

School started last week where I teach an electrical class at a local college and I am busy with school during the afternoon and evening hours.

Take care for now............Thanks.............Kevin:)

Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,419
4,419 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,196 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,419 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
Which of the following applies to the disconnecting means
Which of the following applies to the disconnecting means for a branch circuit or feeder to a separate structure? A. It shall be located as close as practicable to the entrance door B.It shall be rate… read more
Sam I
Sam I
Electrician
B.S.
821 satisfied customers
I have a question about voltage drop. We are installing 7-25
I have a question about voltage drop. We are installing 7-25 foot parking lot poles with one LED head each. about 1.5 A each at 208 volts. The lights are approximately 100 feet apart. The last light i… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
Match welder circuit install... Outlet is going to be 520
Miller match welder circuit install... Outlet is going to be 520 feet away from main feeder panel...My thoughts.... 50amp double pull breaker 60 -75°c termination #2 awg THHN copper.Will this work? Tr… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
I have a range that is 30 kw, 3 phase 380 volts. The range
Hello,I have a range that is 30 kw, 3 phase 380 volts.The range itselt has a 5 core cables. The cable is awg 10. Should I connect it to an awg 8 cable? Or do I need a bigger cable?The length is about … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
I want to install a 100A subpanel that's 150 feet away from
I want to install a 100A subpanel that's 150 feet away from the main panel? What wire size do I use? Does the voltage drop because of the distance? … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
I'm installing power and wiring to a new 24'x64' building.
I'm installing power and wiring to a new 24'x64' building. The longest run of new wiring will be to a workshop area which is about 85 feet from the service panel. A wiring calculator says I need #10 w… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
What is maximum advisable appliance wattage and distance 12
What is maximum advisable appliance wattage and distance for a 12 gauge wire? I have an electric sauna that will be about 80 feet of wire from the panel. The specifics of the sauna are : 120 Volt/1960… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
Is it a no-no to combine three #4 wires, a #4 ground wire
Is it a no-no to combine three #4 wires, a #4 ground wire and two #4 208 volt positive wires in the same conduit for a total of five positive wires and one ground? One would serve a three-phase 208 v … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
I actually have 2 questions a detached working shop. I plan
I actually have 2 questions for wiring a detached wood working shop. I plan to have 10 outlets. 1 for a small fridge and window a/c, 1 for a 2nd dust collector and 1 for a air filter. Rest for various… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
I want to do an underground branch feeder to individual 50a20/240
I want to do an underground branch feeder to individual 50a20/240 1ph pedastel sites for rv's. what is an acceptable direct buried cable for this application. Each one will be fed from a circuit break… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
On a commercial remodel, it's a music venue. I've got a 200 main panel and need
On a commercial remodel, it's a music venue. I've got a 200 main panel and need sub panels in 2 different locations. Is it allowable by code to have 2 sub panels? One is running a stage, the other is … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
Need 50 amp circuit for a hot tub at 125 feet. Manufacturer calls for 230 volt, single pha
Need 50 amp circuit for a hot tub at 125 feet. Manufacturer calls for 230 volt, single phase, 50 amp circuit. The circuit will be run AT GRADE from a sub-panel to a GFCI sub-panel at the hot tub. I'm … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
I want to run a spa that's probably a little over 200' from
I want to run a spa that's probably a little over 200' from the main panel. The previous spa owner had a 50 amp breaker on it, so I was considering using 6/3 + ground to provide power. The first 90' o… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
i obtained a older range that doesnt have the ampacity listed
i obtained a older range that doesn't have the ampacity listed on it and it had a three prong plug....thinking i was good, i changed the plug out to a four prong (my outlet is) 50 amp. i have since fo… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
I am adding a sub panel for a new pool. The new sub panel is
I am adding a sub panel for a new pool. The new sub panel is 3 feet from the main panel. I have a 60 amp breaker in the main panel feeding two 30 amp (230 volt) circuits in the sub panel. I have the b… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
The definition of a first floor, as it applies to nonmetallic-sheathed
The definition of a first floor, as it applies to nonmetallic-sheathed cable, is the level where _______ percent or more of the outside wall area is at or above finish grade. A. 25 B. 50 C. 75 D. 100 … read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
I want to install a kiln for my wife for her pottery. The instruction
I want to install a kiln for my wife for her pottery. The instruction manual states to make sure you ground the kiln. The kiln requires 240 volt single phase power @ 60 amps. I plan on running 2 - #6 … read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
A 6 kW, single phase electric shower is to be supplied by a
A 6 kW, single phase electric shower is to be supplied by a 2-core, copper, pvc insulated and sheathed cable with integral cpc, surface clipped. The run length is 20 m and the average ambient temperat… read more
Kevin
Kevin
Owner
High School or GED
258 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x