What wire size do I need for a 800A 480V service. I want to…

What wire size do...

What wire size do I need for a 800A 480V service

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

I want to replace the my main feed wire from my disconnect to my breaker panel

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

We would be going between 400 and 550 feet. I also want to run a 400A service in the same underground trench.

Show More
Show Less
Ask Your Own Electrical Question
Answered in 3 minutes by:
3/22/2018
George Smith
George Smith, Master Electrician
Category: Electrical
Satisfied Customers: 428
Experience: Superintendent at Electrical Solutions and Data
Verified

Thanks for counting on us to help with your electrical issue. My name is ***** ***** I look forward to helping you! Let me review your question!

Please ignore a request for a phone call that is not from me ! It is computer generated !

Unless you want to talk ?

Ask Your Own Electrical Question
Customer reply replied 30 days ago
No that is fine. I believe we can get it figured out online. Thank you!

Are you using direct burial or are you using conduit! Copper or aluminum wire?

Ask Your Own Electrical Question
Customer reply replied 30 days ago
No I want to put it in conduit. What do you think I should use? Isn't copper more conductive but aluminum is much cheaper?

Yes aluminium is cheaper! Your local codes may require copper!

Ask Your Own Electrical Question

Your voltage drop is important also! How critical is the 480 v?

Ask Your Own Electrical Question
Customer reply replied 30 days ago
Ok, I will have to check into that. What wire size do you recommend for each service? I'm not sure what my voltage drop would be. The 480V is important because I'm replacing a current system and everything is wired for 480V.

400 kcmil aluminum 4 conductors per phase will give you 472v at 500 ft for the 800 amp.

Ask Your Own Electrical Question
Customer reply replied 30 days ago
Id prefer to keep it at no more than two conductors per phase if that's possible?

600 kcmil aluminum 1 conductor per phase will give you 470v at 500 ft for the 400 amp service.

Ask Your Own Electrical Question

The 800 amp service isn't going to be done with 2 conductors!

Ask Your Own Electrical Question
Customer reply replied 30 days ago
What about using copper? Could I use 3 conductors per phase if I use copper?

600 kcmil copper with 3 conductors will give you 476v at 500 ft.

Ask Your Own Electrical Question
Customer reply replied 30 days ago
Ok thank you! How deep do you think I should bury it? Would you have any suggestions as to where to get the best price on wire?

Your depth depends on where your located and what will be over the trench ie: driveway , parking lot, walkway , grass ?

Ask Your Own Electrical Question

Hope I was of help today!

Please give me a 5 star rating before you sign off today!

Thanks !

George

Ask Your Own Electrical Question
Customer reply replied 30 days ago
Most of it will be under a truck driveway. I will definitely give you a 5 star rating! Thank you!

I'm in Chicago I would bury it at least 36". If there is a driveway over it it should be concrete encased!

Ask Your Own Electrical Question
Customer reply replied 30 days ago
Ok thank you! God bless!

Ok thanks!

The concrete may have to be dyed red also !

George Smith
George Smith, Master Electrician
Category: Electrical
Satisfied Customers: 428
Experience: Superintendent at Electrical Solutions and Data
Verified
George Smith and 87 other Electrical Specialists are ready to help you
Ask your own question now
Customer reply replied 30 days ago
Thanks for your help today! And by the way, my name's Kurt.

Thanks for the positive rating !

Please feel free to ask for me personally if you have any more question !

Thanks !

George

Ask Your Own Electrical Question
Customer reply replied 30 days ago
Ok thank you! I just might do that!
Was this answer helpful?
Ask George Smith Your Own Question
George Smith
George Smith
George Smith, Master Electrician
Category: Electrical
Satisfied Customers: 428
428 Satisfied Customers
Experience: Superintendent at Electrical Solutions and Data

George Smith is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I live in a mobile home with aluminum wires. We just
I live in a mobile home with aluminum wires. We just switched over to smart meter service. Would this affect the current running through my trailer? why because I use to be able to run a portable heat… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Underground conduit cover" First time. Depth of conduit.
depth of conduit. table 300.5 measures from the top of conduit to top of finish surface and the inspector measures from top of the conduit to the bottom of the concrete slab. wish is correct?… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
When using a metal conduit body such as an LB, or capped L
When using a metal conduit body such as an LB, or capped L at an enclosure does that fitting need to be supported other than with the nipple into the enclosure? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
What are the construction requirements for a new conduit
What are the construction requirements for a new conduit installation to an existing building? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
What type of wire does PG&E require to be buried in conduit?
what type of wire does PG&E require to be buried in conduit? The Distance would be close to 400' Will a single wire be able to go that distance or will I need a secondary? How many wires will be in th… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Is it permissible to run romex wire through conduit indoors
Is it permissible to run romex wire through conduit indoors and in a dry location? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have aluminum wiring & need a new water heater. Can I get
I have aluminum wiring & need a new water heater. Can I get one installs without … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Have 3 cdr awg 2 and 1 cdr awg 4 aluminum wire for a 100 amp
have 3 cdr awg 2 and 1 cdr awg 4 aluminum wire for a 100 amp sub panel. Is this wiring sufficient. distance is less than 2 feet from the main.… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
My house is older and has aluminum wiring. I'm having some
My house is older and has aluminum wiring. I'm having some difficulty getting a new light fixture to light. It's a problem that I have not experienced here before.… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Can I use a steel conduit lockout on pvc male adaptor into
Can I use a steel conduit lockout on pvc male adaptor into utility box on end of my pvc conduit?… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Can I add a 90 elbow to the main conduit so that I can raise
can I add a 90 elbow to the main conduit so that I can raise that conduit the conduit is running vertical and i need some height under the conduit … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
When I purchased my home, it had aluminum wiring in it. So
When I purchased my home, it had aluminum wiring in it. So we had the copalum crimping treatment done to the whole house. Now we want to add a few more outlets & lights and I wonder if we need the sam… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I am trying to hook up my garage with 2/0 aluminum wire to a
I am trying to hook up my garage with 2/0 aluminum wire to a 200 amp box in the garage. The wire of course has 3 wires one bare and the other 2 not. What do I do with the bare wire hook it up to the n… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have a dedicated 10 amp romex line in conduit, going to a
I have a dedicated 10 amp romex line in conduit, going to a direct wired garbage disposer under my kitchen sink. I want to connect this line up to a single gang outlet box to make exchanging the dispo… read more
Sam I
Sam I
Electrician
B.S.
559 satisfied customers
Underground power line going to water well. Aluminum wire.
Underground power line going to water well. Aluminum wire. 120 ft distance. . 240 volts across two terminals of breaker. only 150 volts at pump. checked individual. approx 130 volts from neutral to on… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
How much to install 100' of electrical line in a conduit if
how much to install 100' of electrical line in a conduit if the trench is already dug. Include the cost of wiring and adding a 50 Amp Circuit Breaker … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
What size wire is needed to run underground in conduit to a
What size wire is needed to run underground in conduit to a garage about 60 feet from the main connection at the power pole? This would be connected to a subpanel in the garage. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
A 1972 home has aluminum wiring. In addition to installing
A 1972 home has aluminum wiring. In addition to installing AlumiConn connectors at all lights, switches, outlets, etc....do the range, ac and water heater outlets need to be completely rewired so the … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x