1st I'm speaking about a mobile home. Out side is a 200 amp…

Hello 1st I'm speaking...

Hello 1st I'm speaking about a mobile home. Out side is a 200 amp panel and meter. It then leaves that panel running underground 8 to 10 feet to another 200 amp panel inside the trailor. I get 240v coming in and 240v leaving that panel but when it reaches the inside panel only one of the 2 leads is getting 120v the other drops to about 32v. This is aluminum wire feeding the indoor panel

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

So how is that the same wire coming out of the service panel has proper voltage but by the time that same wire reaches the 2nd panel the voltage has disappeared?

Contractor's Assistant: Do you plan on doing the work yourself?

Just since yesterday. I thought at 1st the main inside was bad so I replaced it. It worked for a few hours and then started with the same problem. Yes I do all of my own work. I am añ industrial journeyman have been for 20 years plus

Contractor's Assistant: Anything else we should know to help you best?

If water has entered the underground pipe the wire runs through cause such an issue

Contractor's Assistant: How long has this been going on? And how severe is the problem?

It's weird if that describes severe and my sister who lives there with her 6 MN old at the moment has no heat or air because I don't have 220 inside

Show More
Show Less
Ask Your Own Electrical Question
Answered in 5 minutes by:
3/18/2018
Sam I
Sam I, Electrician
Category: Electrical
Satisfied Customers: 578
Experience: Maintenance Electrician, Electrical Contractor, Locomotive Electrician
Verified

Hello, that sounds a lot like a bad neutral. Does the voltage fluctuate when you turn on various appliances? Try something like a hair dryer on different circuits so you can get each leg to have that load and test voltage at each leg when the test load is turned on

Ask Your Own Electrical Question

IF it doesn't fluctuate then it may be the phase wire that is low voltage is broken or partially broken in the conduit underground. Aluminum wire will corrode into powder in water or underground in earth when the insulation is nicked but it will still conduct electricity somewhat even in that state

Ask Your Own Electrical Question
Customer reply replied 1 month ago
That not really the issue. Picture main service has 240 coming in and before the wire enters the pipe running Underground it also has 240 volts but when it reaches the other panel one leg has 110 volts but the other leg does not it's not it's not going out without 110v one leg is not coming in. Its loosing voltage somewhere between the main panel outside and the indoor panel while running underground
Customer reply replied 1 month ago
If that pipe has filled with water could that be the cause

Yes, I read that above. That means your problem is either the connection to the inside panel or it is a bad wire between the outside panel and the inside panel.

Ask Your Own Electrical Question
Customer reply replied 1 month ago
What do u mean by the connection at the inside panel

If voltage goes up and down with different loads in the house then it is a bad neutral. If it doesn't then it is probably a bad hot leg. The water in the conduit doesn't matter. All conduit outdoors and underground is filled with water. What matters is if the insulation has failed and the aluminum has blown apart or is in the process

Ask Your Own Electrical Question

A loos connection could cause those readings. It depends on where your test point is. Are you putting the meter on the wire itself or the lugs or main buss bars?

Ask Your Own Electrical Question
Customer reply replied 1 month ago
I'm not at the panel right now bUT can be within the hour. Can I continue this conversation then if I need to I may just do the call thing
Customer reply replied 1 month ago
I've done both

ok I will be on for another couple hours

Ask Your Own Electrical Question
Customer reply replied 1 month ago
Ok that I didn't know. So I need to look for a lot of resistance in checking the continuity of that wire
Customer reply replied 1 month ago
If I do that how do I get back to this from the site

Yes, if you can check resistance on the main wires between the inside and outside panel you can sometimes tell that way. Sometimes you need a megger

Ask Your Own Electrical Question
Customer reply replied 1 month ago
What the heck is a megger

You can bookmark the page or you should be able to sign in to an account and look at a list of questions that you have and select this one

Ask Your Own Electrical Question
Customer reply replied 1 month ago
Ok

Megohmeter. It sends High DC voltage on the lines to check insulation resistance.

Ask Your Own Electrical Question
Customer reply replied 1 month ago
Ok wow. Never heard of one of them. I'll look into that

you can do the test I suggested first without a megger. Just turn off all the loads in the house except some lights and a couple outlet circuits leave the lights on and plug the hair dryer in and turn on full blast. Check voltage at the indoor panel main wires during the test. DO it again with the dryer on another circuit that is on the other hot leg.

Ask Your Own Electrical Question
Customer reply replied 1 month ago
Ok. I'll do that. Thank you. I know this wI'll sound stupid it's something that I should know but I question myself. When checking continuity with power off should I be getting continuity between the main leads and the neutral leads

no. There should be no continuity between any of the main wires at each panel. You would have to put a jumper wire, let's say a jumper between neutral and hot leg L1. Then you would go to the outside panel and test those wires there between hot leg L1 and neutral. If you get a high resistance then one of those wires is the problem. Put the jumper in different spots (L1 to L2 and L2 to N) to check the others

Ask Your Own Electrical Question
Customer reply replied 1 month ago
Oh there at this point will not be any more charges to my card right. Just the $16 as of now

That's correct. If you want a phone call later that's an extra $24

Ask Your Own Electrical Question
Customer reply replied 1 month ago
I thought not but the inside panel I am getting continue between l1 and l2 to the nuetral
Customer reply replied 1 month ago
some where in the pipe the leads r touching. Or could it be coming from upstream

make sure there is nothing (no circuit tapped off the main lines at both panels

Ask Your Own Electrical Question

If your breakers are off it wouldn't be up the line

Ask Your Own Electrical Question
Customer reply replied 1 month ago
Thank you. In the outside pale there r only two other breaker one feeds the a/c condensor the other well I've never checked
Customer reply replied 1 month ago
Thanks for all the help. I think I can take it from here. Thanks for the help

ok, let me know it goes or if you need any more help. Also if you do figure it out, please come back and give me a rating from 3 to 5 stars so I can get credit for answering with Just Answer

Ask Your Own Electrical Question
Customer reply replied 1 month ago
I'll do that now. Thanks again. I'll give you top ratings

ok thanks

Sam I
Sam I, Electrician
Category: Electrical
Satisfied Customers: 578
Experience: Maintenance Electrician, Electrical Contractor, Locomotive Electrician
Verified
Sam I and 87 other Electrical Specialists are ready to help you
Ask your own question now
Was this answer helpful?
Ask Sam I Your Own Question
Sam I
Sam I
Sam I, Electrician
Category: Electrical
Satisfied Customers: 578
578 Satisfied Customers
Experience: Maintenance Electrician, Electrical Contractor, Locomotive Electrician

Sam I is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I live in a mobile home with aluminum wires. We just
I live in a mobile home with aluminum wires. We just switched over to smart meter service. Would this affect the current running through my trailer? why because I use to be able to run a portable heat… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Underground conduit cover" First time. Depth of conduit.
depth of conduit. table 300.5 measures from the top of conduit to top of finish surface and the inspector measures from top of the conduit to the bottom of the concrete slab. wish is correct?… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I'm building a detached shop and need to get conduit in the
I'm building a detached shop and need to get conduit in the ground for the shop electrical panel. I have a 200amp main panel in the house that is about 50 ft away from where the shop panel will be. … read more
Sam I
Sam I
Electrician
578 satisfied customers
I have low voltage (12V) halogen system in my kitchen. Can I
I have low voltage (12V) halogen system in my kitchen. Can I combine it with a low voltage LED strip lighting system on the same stepdown as my halogen system? … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
How nice, I am looking for old GE low voltage switches and
I am looking for old GE low voltage switches and relays I would also like to know if a light is stuck on if I should remove switch entirely to avoid burning relay … read more
George Smith
George Smith
Vocational, Technical or Trade School
430 satisfied customers
What are the construction requirements for a new conduit
What are the construction requirements for a new conduit installation to an existing building? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Is it permissible to run romex wire through conduit indoors
Is it permissible to run romex wire through conduit indoors and in a dry location? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have aluminum wiring & need a new water heater. Can I get
I have aluminum wiring & need a new water heater. Can I get one installs without … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have Lightolier 120v track with R702WH low-voltage heads
I have Lightolier 120v track with R702WH low-voltage heads with MR16 halogens. I want to change the halogens to MR16 leds. Do any dimmers work and, if so, which? … read more
George Smith
George Smith
Vocational, Technical or Trade School
430 satisfied customers
I have a low voltage transformer in my garage which has 4
I have a low voltage transformer in my garage which has 4 lines coming out of it and out of the house to power landscape lights, etc... we have two main path lights that are connected to this transfor… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
My outdoor post light has low voltage. It did work and then
My outdoor post light has low voltage. It did work and then stopped working, I changed out three bulbs and they will not come on. I put an led bulb in the lamp and get a weak glow. The incodesent bulb… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My house is older and has aluminum wiring. I'm having some
My house is older and has aluminum wiring. I'm having some difficulty getting a new light fixture to light. It's a problem that I have not experienced here before.… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
If you run 110volts through a low voltage high bay lite on
If you run 110volts through a low voltage high bay lite on accident will it fry the built in driver. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
When I purchased my home, it had aluminum wiring in it. So
When I purchased my home, it had aluminum wiring in it. So we had the copalum crimping treatment done to the whole house. Now we want to add a few more outlets & lights and I wonder if we need the sam… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
There is a low voltage lighting circuit in my flat. Can I
There is a low voltage lighting circuit in my flat. Can I buy standard fittings and have them converted to plug into the LV circuit?… read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
I am trying to hook up my garage with 2/0 aluminum wire to a
I am trying to hook up my garage with 2/0 aluminum wire to a 200 amp box in the garage. The wire of course has 3 wires one bare and the other 2 not. What do I do with the bare wire hook it up to the n… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Can you splice in outdoor string lights to a low voltage
Can you splice in outdoor string lights to a low voltage landscape system? … read more
Sam I
Sam I
Electrician
578 satisfied customers
I have a kitchen with 8 low voltage (50W) recessed lights
I have a kitchen with 8 low voltage (50W) recessed lights around the perimeter ceiling. They have always burned out quickly, and all have been out for a long time now. Got tired of replacing them ever… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x