What would suddenly cause a 110 outlet to have a hot ground…

What would suddenly cause...

What would suddenly cause a 110 outlet to have a hot ground reverse

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Just within a couple hours

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Show More
Show Less
Ask Your Own Electrical Question
Answered in 5 minutes by:
3/17/2018
David Bowden
David Bowden, Electrician
Category: Electrical
Satisfied Customers: 1,202
Experience: Owner at Floridaco
Verified

Hello and welcome to Just Answer… My name is ***** ***** allow me a few moments while I do some research, my recommendation will appear shortly.

Ask Your Own Electrical Question
Customer reply replied 4 months ago
ok

Thank usually comes from an open or weak neutral. In AC wiring there is no "polarity reverse" since AC changes cycles 60 times a second.

Ask Your Own Electrical Question

If you have a 3 prong electrical tester with indicator lights, usually that will tell you want is not correct on the outlet. You can get these for a couple of dollars at your home improvement centers.

Ask Your Own Electrical Question
Customer reply replied 4 months ago
what would cause the open neutral
Customer reply replied 4 months ago
I have one that's what showed me whats going on with the circuit
Customer reply replied 4 months ago
it also rained her recently

usually it is a weak wire or bad connection, either at the outlet or coming into it from another location.

Ask Your Own Electrical Question
Customer reply replied 4 months ago
ok thanks

It is common on older homes and those using aluminum wires instead of copper.

Ask Your Own Electrical Question
Customer reply replied 4 months ago
ok its a 40n year old double wide trailoes with general electric breakers
Customer reply replied 4 months ago
thank you for your info gives five stars

Don't think the breakers are an issue, on way to help eliminate and isolate these type of problems is to pigtail the wires in the box and only have 2 wires on the outlets. This helps keep the circuit solid and then any issues at the plug are usually with the outlet.

Ask Your Own Electrical Question

You are most welcome...

One of the goals here at Just Answer, is to provide each customer with the best experience possible and for the experts to earn a 5 Star Rating based on their responses, recommendations, and professionalism, when answering questions. If I have achieved that goal for this question, please take a few moments to rate my service and select the 5 Stars before logging out.

It has been my pleasure providing an answer for you today, however if additional service is needed, please use the reply box to let me know and I will respond back once I have the requested information.

Enjoy the rest of your day,

Dave

David Bowden
David Bowden, Electrician
Category: Electrical
Satisfied Customers: 1,202
Experience: Owner at Floridaco
Verified
David Bowden and 87 other Electrical Specialists are ready to help you
Ask your own question now

Thank you very much for the positive rating, I sincerely ***** ***** If you need further assistance or help with another question, just let me know.

Best,

Dave

Ask Your Own Electrical Question

I just received notice of the added bonus, thank you very much it is greatly appreciated.

Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask David Bowden Your Own Question
David Bowden
David Bowden
David Bowden, Electrician
Category: Electrical
Satisfied Customers: 1,202
1,202 Satisfied Customers
Experience: Owner at Floridaco

David Bowden is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,196 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,345 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
All my outlets read correct with my plug tester. As soon as
Hello Mike,all my outlets read correct with my plug tester. As soon as I plug in an appliance, lamp, etc. the tester reads hot/grd. reverse. I've re-wired all outlets and get 110 with my volt meter. W… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,345 satisfied customers
I have a 15-amp GFCI outlet that failed (I discovered this
I have a 15-amp GFCI outlet that failed (I discovered this when it did not charge my cell phone battery). It did not trip until I pressed the "test" button, but then would not reset. There is another … read more
Alex
Alex
Owner
Bachelor\u0027s Degree
1,783 satisfied customers
have a 110v problem in a mobile home if I test the outlets(
have a 110v problem in a mobile home if I test the outlets( multiple outlets) with the black and neutral I read 104 v if I test the black and bare ground I get 110 v the breaker going to these outlets… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,345 satisfied customers
I am having a problem with one of my household electrical circuits.
I am having a problem with one of my household electrical circuits. I have been doing a kitchen remodel and all circuits were working perfectly until last night. Now I have very peculiar symptoms that… read more
TAKPOWER
TAKPOWER
Non Restricted Licensed Electrician
High School or GED
131 satisfied customers
i have a 110 outlet that reads across the neutral and hot is
i have a 110 outlet that reads across the neutral and hot is 110 but between the ground and the hot i read about 55 volts on the whole line for that room. One outlet in the lead end of the string does… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
I have a 3/4 HP single phase motor made in china with 6 leads
I have a 3/4 HP single phase motor made in china with 6 leads for 110 or 220 hook up. I want to run it on 110. The diagram shows T1, T3, T8 go to line 1. The T2, T4 and T6 go to line 2. I understand I… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
I FIPPED THE SWITCH FOR THE CELING LIGHT/FAN COMBO TO GO ON
I FIPPED THE SWITCH FOR THE CELING LIGHT/FAN COMBO TO GO ON LAST NIGHT. THE LIGHT BLINKED AND WENT OFF, AS DID ALL THE OTHER LIGHTS AND OUTLETS ON THE CIRCUIT. WENT TO THE BOX TO RESET THE CIRCUIT BRE… read more
Joseph
Joseph
743 satisfied customers
I live in an apartment complex and I have a question about
I live in an apartment complex and I have a question about how/if power consumption from other tenants in my buidling affects my electricy. My apartment complex has 10 units. Each unit has their own m… read more
Kevin
Kevin
Owner
High School or GED
258 satisfied customers
Good evening My house is around 22 years old. I bought it
Good evening My house is around 22 years old. I bought it 6 years ago everything was working fine (electricity) I have made a few room renovation and ran 1 line by room and sometime 2 lines when neede… read more
Rich
Rich
Master Electrician
Vocational, Technical or Trade Scho
1,117 satisfied customers
i live in an old house and the outlets are the basic hot neutral
i live in an old house and the outlets are the basic hot neutral set. now the problem is that only in my bedroom i plug in any three prong device and the outlet goes from open ground to hot neutral re… read more
Rich
Rich
Master Electrician
Vocational, Technical or Trade Scho
1,117 satisfied customers
Have 110volts at plug, when I plug anything in it does not
Have 110volts at plug, when I plug anything in it does not work. will not turn on a light on that circut. Was working fine until I pluged in a drill. did not pop the breaker. Help?… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
If you wire a GFCI outlet and do not have a ground wire will
If you wire a GFCI outlet and do not have a ground wire will it work properly or will it just work as a regular electrical outlet? Also, if you have a tester and instead of getting two yellow lights y… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
I have several outlets that suddenly stopped working. They
I have several outlets that suddenly stopped working. They are either located outside or in bathrooms. I suspect a problem with the ground fault, but that outlet works and has not been tripped. Any su… read more
Mike
Mike
Master Electrician
Working on MBA
1,426 satisfied customers
Hi, I just had 3 outlets go dead and with a tester, I got
Hi, I just had 3 outlets go dead and with a tester, I got a hot/ground reversed. I shut the power off and discovered where the the reverse is happening. The hot(black) and the ground(bare) are NOW wor… read more
Glenn
Glenn
Maintenance, Technician
Associate Degree
1,612 satisfied customers
on my camper i plugged into a 30 amp ground fault breaker outlet
on my camper i plugged into a 30 amp ground fault breaker outlet that tripped fairly quick only thing plugged in was the refridge. and mt a/c unit would not come on at all. as soon as i tried to turn … read more
InspectorL
InspectorL
Associate Degree
32 satisfied customers
i am replacing a single phase 110 electric moteo on my above
i am replacing a single phase 110 electric moteo on my above ground pool because the motor stopped working and when you touched it it would shock you. I ordered a new motor and installed it like the o… read more
Paul
Paul
Owner
Vocational, Technical or Trade Scho
1 satisfied customers
I have a 15 amp circuit that runs thru a standard duplex ...
I have a 15 amp circuit that runs thru a standard duplex outlet (tests OK), from this outlet it feeds a ceiling fan (operates OK) and continues to a room with multiple duplex receptacles and som light… read more
Joseph
Joseph
743 satisfied customers
When I test the outlet with a voltage tester, it reads ...
When I test the outlet with a voltage tester, it reads zero. But when I put one of the leads in the ground hole, it reads 110. What causes that?… read more
Brian
Brian
Architect
Bachelor\u0027s Degree
2,905 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x