I would like to install a sub-panel in my garage there is no…

I would like to...

I would like to install a sub-panel in my garage there is no outside panel just the meter straight into the house with the breaker box rated at 150 amps. The sub-panel is rated at 100 amps and has three double pole slots. I need to run a dryer (30 amp ?) circuit a small welder (240v) draws about 15 amps and an air compressor (240v) draws 20 amps . The run would be about 50 feet and doubt all would be running at once. could I run this on a 60 amp breaker with #4 wire

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

I just bought the house and would like to add the circuit

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Not sure what it might be

Show More
Show Less
Ask Your Own Electrical Question
Answered in 10 minutes by:
3/16/2018
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,212
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

Please be patient as it takes time to type and provide links. Also note that the website may be sending you a telephone offer, the offer is not originating from me.

1) If the loads will not be running simultaneously, a 60 amp sub-panel feeder circuit will be sufficient.

2) A 60 amp circuit @ 240 volts on a 50 foot run only requires 6 AWG copper conductors which will result in a voltage drop of 1.2% which is code compliant. If installing 4 AWG copper conductors, the voltage drop will be .8% (point 8%) which is also code compliant.

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks.................Kevin:)

Ask Your Own Electrical Question
Customer reply replied 1 month ago
Thanks Kevin, one additional question please does the box need to be bonded? or does that only happen at the main breaker panel.

1) Bonding only occurs at the main service disconnect and never at a downstream sub-panel.

2) The sub-panel feeder circuit requires 4 conductors..........ie..... 2 hots, 1 neutral and 1 equipment grounding conductor.

3) At the sub-panel, DO NOT install the green main bonding screw or a main bonding jumper strap at the neutral bus bar. The neutral must always be isolated from the panel metal enclosure. Only white neutrals will land on the sub-panel neutral bus bar but not any grounds.

4) The sub-panel will require a separate equipment ground bar to only land ground wires.

Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,212
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified
Kevin and 87 other Electrical Specialists are ready to help you
Ask your own question now
Customer reply replied 1 month ago
That what I thought thanks for the verification.

No problem, glad to assist.

I agree with your verification:)

Thank you for the positive service rating............much appreciated!

If you have any other questions, just let me know.

Take care and have a great day............Thanks again............Kevin:)

Ask Your Own Electrical Question
Was this answer helpful?
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,212
4,212 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,212 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I'd like to wire a welder outlet for a 250 V welder. It
I'd like to wire a welder outlet for a 250 V welder. It calls for a 250 V 50 amp GFIC power supply. I'd be using a 250 V 50 amp GFIC breaker ansd 6 gauge wire running about 50 ft through metal conduit… read more
David Bowden
David Bowden
Owner
764 satisfied customers
Iine in I have 3 phase 240v service, I have a welder
Iine in I have 3 phase 240v service, I have a welder requiring single phase 240 volt service..my question is which legs of the 3 phase works the best for this service L1 L2 or ?? … read more
Kevin
Kevin
Licensed Electrical Contractor
4,212 satisfied customers
Looking to step up 208v to 480v for my Lincoln electric
Looking to step up 208v to 480v for my Lincoln electric welder that's a 460v/585v machine what kva transformer should I be looking for I was told s 15kva anything It should have specific ?… read more
Kevin
Kevin
Licensed Electrical Contractor
4,212 satisfied customers
I have a ac 1- 220v mini welder with a two prong plug. How
I have a ac 1- 220v mini welder with a two prong plug. How would i wire this to plug into my house … read more
Terry Peterman
Terry Peterman
The Internet Electrician
Vocational, Technical or Trade School
19 satisfied customers
I was given a new arc welder for an early Christmas gift. I
I was given a new arc welder for an early Christmas gift. I would like to know what specifically do I need to connect this up to my shop without causing major problems. (I.E. size of outlets, wire gau… read more
George Smith
George Smith
Vocational, Technical or Trade School
428 satisfied customers
I just purchased a Hobart 210 welder that runs on both 115
I just purchased a Hobart 210 welder that runs on both 115 and 230v. I set up a 30 amp circuit single phase using 10 gauge wire. The welder runs fine when plugged into my 20 amp 115 volt circuit but o… read more
Sam I
Sam I
Electrician
B.S.
569 satisfied customers
I have a 240 volt arc welder with three wires,, black and, i
I have a 240 volt arc welder with three wires, white, black and green, i want to hook it up to my generatorL14-30 4 prong plug. to get 220 do I use a jumper cable in the plug from the black wire on on… read more
Kevin
Kevin
Licensed Electrical Contractor
4,212 satisfied customers
I have a Lincoln 180 dual welder that I would like to
I have a Lincoln 180 dual welder that I would like to connect to a 10-30 R that's already wired in my garage.The welder requires 20 amps at 230V.Can I make an extension cord with a 10-30/50 P at one e… read more
Leamon Rollo
Leamon Rollo
Vocational, Technical or Trade School
19 satisfied customers
I have a question about a 49 to 70 amp small stick welder,
hi,i have a question about a 49 to 70 amp small stick welder, my book says the effective input amps is 8.5 and the maximum input amps is 25.8 but it says to use a 20 amp breaker also,now it says it is… read more
Sam I
Sam I
Electrician
B.S.
569 satisfied customers
I have a Hobart 187 MIG Welder that I want to get wired.
I have a Hobart 187 MIG Welder that I want to get wired. What size wire should be used? It takes a 50v plug at 230v. … read more
WCohn
WCohn
Journeyman Plumber
Journeyman License
1,514 satisfied customers
I just bought an AC welder and it did not have the
I just bought an AC welder and it did not have the electrical plug. The power cord has three wires -- blue, brown, green. I am thinking the green is the ground. Does it matter which of the two remaini… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have a 220v welder with std 3 wire 6-50 NEMA male, and
I have a 220v welder with std 3 wire 6-50 NEMA male, and need to change power cord to use a 4 prong RV-type twist plug. What to do with the spare wire connected to the welder? Thanks … read more
George Smith
George Smith
Vocational, Technical or Trade School
428 satisfied customers
What would happen if a welder pulls 55 amps or 60... on a
What would happen if a welder pulls 55 amps or 60... on a nema 6-50 r receptacle?Will it be ok?… read more
Kevin
Kevin
Licensed Electrical Contractor
4,212 satisfied customers
I have a 250 amp welder wired for 120v plug in, where should
I have a 250 amp welder wired for 120v plug in, where should I plug it into? Washer and dryer outlet?… read more
George Smith
George Smith
Vocational, Technical or Trade School
428 satisfied customers
Match welder circuit install... Outlet is going to be 520
Miller match welder circuit install... Outlet is going to be 520 feet away from main feeder panel...My thoughts.... 50amp double pull breaker 60 -75°c termination #2 awg THHN copper.Will this work? Tr… read more
Kevin
Kevin
Licensed Electrical Contractor
4,212 satisfied customers
Had a 220v welder in the garage catch fire, I immediately
Had a 220v welder in the garage catch fire, I immediately shut the breakers off in the garage when this happened but than noticed my lights dimming when using any power. Shortly after the power in the… read more
Kevin
Kevin
Licensed Electrical Contractor
4,212 satisfied customers
I have a welder that has a NEMA 6-30P MALE plug. I have a
I have a clark welder that has a NEMA 6-30P MALE plug. I have a gasoline generator that has a NEMA L14-30R receptacle. Is there a way to use this generator to power my welder?… read more
Kevin
Kevin
Licensed Electrical Contractor
4,212 satisfied customers
I have a 25 amp rated D.C. Inverter stick welder. We had an
I have a 25 amp rated D.C. Inverter stick welder. We had an addition added onto the house so I had the electrician put a receptical on that fit the welder. The only problem is the switch on the fuse b… read more
Steve
Steve
Chief Engineer
9 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x