I would like to install a sub-panel in my garage there is no…

I would like to...

I would like to install a sub-panel in my garage there is no outside panel just the meter straight into the house with the breaker box rated at 150 amps. The sub-panel is rated at 100 amps and has three double pole slots. I need to run a dryer (30 amp ?) circuit a small welder (240v) draws about 15 amps and an air compressor (240v) draws 20 amps . The run would be about 50 feet and doubt all would be running at once. could I run this on a 60 amp breaker with #4 wire

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

I just bought the house and would like to add the circuit

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Not sure what it might be

Show More
Show Less
Ask Your Own Electrical Question
Answered in 10 minutes by:
3/16/2018
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,422
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

Please be patient as it takes time to type and provide links. Also note that the website may be sending you a telephone offer, the offer is not originating from me.

1) If the loads will not be running simultaneously, a 60 amp sub-panel feeder circuit will be sufficient.

2) A 60 amp circuit @ 240 volts on a 50 foot run only requires 6 AWG copper conductors which will result in a voltage drop of 1.2% which is code compliant. If installing 4 AWG copper conductors, the voltage drop will be .8% (point 8%) which is also code compliant.

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks.................Kevin:)

Ask Your Own Electrical Question
Customer reply replied 4 months ago
Thanks Kevin, one additional question please does the box need to be bonded? or does that only happen at the main breaker panel.

1) Bonding only occurs at the main service disconnect and never at a downstream sub-panel.

2) The sub-panel feeder circuit requires 4 conductors..........ie..... 2 hots, 1 neutral and 1 equipment grounding conductor.

3) At the sub-panel, DO NOT install the green main bonding screw or a main bonding jumper strap at the neutral bus bar. The neutral must always be isolated from the panel metal enclosure. Only white neutrals will land on the sub-panel neutral bus bar but not any grounds.

4) The sub-panel will require a separate equipment ground bar to only land ground wires.

Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,422
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified
Kevin and 87 other Electrical Specialists are ready to help you
Ask your own question now
Customer reply replied 4 months ago
That what I thought thanks for the verification.

No problem, glad to assist.

I agree with your verification:)

Thank you for the positive service rating............much appreciated!

If you have any other questions, just let me know.

Take care and have a great day............Thanks again............Kevin:)

Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,422
4,422 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,196 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,422 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I have installed a 240v Profusion heater in my garage. I
Hello. I have installed a 240v Profusion heater in my garage. I have a 45amp breaker with 8awg wire. The heater will not come on. There is a toggle switch on the back for using either an and external … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,422 satisfied customers
I would like to install one to two high amp/voltage outlets
I would like to install one to two high amp/voltage outlets in my detached garage to accommodate high-wattage space heaters or window units. I believe the outlets will be 220-240v and need 30 to 40 am… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
I want to put in a 50AMP welding outlet in my garage but my
I want to put in a 50AMP welding outlet in my garage but my current panel is full. I'm wondering if I can put in another small sub panel with breaker for the welder? … read more
Sam I
Sam I
Electrician
B.S.
821 satisfied customers
I would like to know the max size of a sub panel I can put
I would like to know the max size of a sub panel I can put in my detached garage. My house has a 200 amp panel.… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,422 satisfied customers
I need to run a 220 connection for a welder in my garage.
Hello - I need to run a 220 connection for a welder in my garage. The welder is rated for 200 amps 24 volts 25% duty cycle. On the plate for the unit it shows U1 230V 1max 27A 1eff 14.7A. The machine … read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
Can you tap a lug panel as a sub-panel off of a main lug
can you tap a lug panel as a sub-panel off of a main lug panel which has been tapped off of a main breaker panel?… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,422 satisfied customers
We just bought a house with a sundance spa. The main
We just bought a house with a sundance spa. The main electrical panel has 50 amps going to the dedicated circuit breaker which has 60 amp circuit breaker. When I question how can we have 50 amps feedi… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
Hi Jason, I'm wanting to put in a sub panel. Ultimate goal is to wire in a phase co
Hi Jason, I'm wanting to put in a sub panel. Ultimate goal is to wire in a phase converter so I can run a machine with a 2HP motor, heavy start load. It is 3 phase, 240v. I have a 5HP American Rotary … read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
California Household electrical project. My electricity
California Household electrical project. My electricity comes in on the west side of my house and my garage is about 70 feet east of the main panel. I know my 120 Air compressor draws too much power b… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
HI I have a 100 amp service in our house and want to put a
HI I have a 100 amp service in our house and want to put a sub panel in the garage for my workshop. I have a 220V table saw, 2 hp dust collection system, plus 7.5 amp compressor, plus lights and other… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
i want to install a sub panel in the garage of a house with
i want to install a sub panel in the garage of a house with only 120 v circuits. I will have 2 200amp outdoor panels with all the 240v circuits. can you give me the calculation and the breaker size I … read more
Phil
Phil
Consultant to Engrs, Govt & Contractors
Degree, Mech Engr Technology
9,698 satisfied customers
I have an existing 150 amp main service in my house. I would
I have an existing 150 amp main service in my house. I would like to run a 100 amp subpanel to my garage. Would it be acceptable to do this given the main service is only rated for 150 amps? Should I … read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
would like to install 220volt service to a garage with no current
would like to install 220volt service to a garage with no current service, electrician quotes 200 amp panle with 2awg wire to 2 50amp breakers and 3 20amp breakers for lighting and plugs. question is … read more
Sir Sparks
Sir Sparks
Owner
State & UK Certified Master electri
2,519 satisfied customers
Hi, I am installing a hot tub at my house and would like to
Hi, I am installing a hot tub at my house and would like to pull the service wiring for it from a main lug only 125 amp sub panel that is fed with a 60 amp 240v circuit (#6 copper, about 30 feet from … read more
electrifier
electrifier
Master Electrician
Bachelor's Degree
1,458 satisfied customers
I bought a welder for my garage and I need to know what size
I bought a welder for my garage and I need to know what size and type breakers I need I have a breaker box in the garage that is fed from the house. There is a 40 amp breaker in the main breaker box i… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
Running a seperate 220 line from dryer to garage (approx. 40
Running a seperate 220 line from dryer to garage (approx. 40 feet) for a Lincoln Electric Precision TIG 225 amp welder. I run a gas dryer and have no need for the existing three prong outlet. I have a… read more
Paul
Paul
Owner
Vocational, Technical or Trade Scho
799 satisfied customers
Hey guys,good morning.I ran 165 foot of 8/3 UF fom my house
Hey guys,good morning.I ran 165 foot of 8/3 UF fom my house main panel to garage.In the house panel.I installed a 30 amp double breaker,with 2 leg mounts.Both the black and red legs attached to them o… read more
Mike
Mike
Master Electrician
Working on MBA
1,426 satisfied customers
I have a 50 amp subpanel in my garage that is powered by the
I have a 50 amp subpanel in my garage that is powered by the Main Service Panel in the house (a 200 amp panel). I have a small pole barn in the back yard in which I need no more than a single 20 amp b… read more
Mike
Mike
Master Electrician
Working on MBA
1,426 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.