If I change a main panel and meter on a house but the main…

If I change a main...
If I change a main panel and meter on a house but the main utility feeders are too short is there a code violation to splice them either in the meter area or in a separate junction box?
Show More
Show Less
Ask Your Own Electrical Question
Answered in 3 minutes by:
3/15/2018
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,419
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

Please be patient as it takes time to type and provide links. Also note that the website may be sending you a telephone offer, the offer is not originating from me.

1) Is the service overhead or underground?

Ask Your Own Electrical Question
Customer reply replied 4 months ago
Underground

Thanks for confirming.

1) There should be no need to extend the underground service conductors as long as the meter enclosure is within the same distance as the original enclosure.

2) You will also need to contact the local utility. Most utilities own the underground service lateral conductors and they would be responsible if a splice is required. If the conductors are customer premise owned, splicing would require approval from the local electrical inspector.

Ask Your Own Electrical Question
Customer reply replied 4 months ago
OK thank you. So it sounds like there would not be a code violation if the feeders need to be extended a few inch because the new meter location is higher than the old meter location. However it sounds like you're telling me each utility provider may have a different policy about it.

1) Most underground service lateral cables are owned by the utility and they would be responsible to make an underground splice. If utility owned, you do not want to make the splice yourself since the only party that can kill power to the service lateral is by the utility pulling the fuse at the transformer. You need to confirm as to the owner of the service lateral cable.

2) Within the National Electrical Code, splices for the service lateral are allowed and are code compliant. NEC Article 300.5(E)

3) If the splice cannot be made underground, I doubt that the utility or the local electrical inspector would approve of an actual splice within the meter socket area. A splice would be code compliant if made within the riser portion of the meter can pedestal.

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks.................Kevin:)

Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,419
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified
Kevin and 87 other Electrical Specialists are ready to help you
Ask your own question now

Thank you for the positive service rating............much appreciated!

If you have any other questions, just let me know.

Take care and have a great day............Thanks again............Kevin:)

Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,419
4,419 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,196 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,419 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I'm installing a car charger in a condo garage. The unit is
Hi Kevin... I'm installing a car charger in a condo garage. The unit is on the 4th floor. So I want to run the wire directly from the disconnect at the meter instead of from the panel on the 4th floor… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
I have installed a 240v Profusion heater in my garage. I
Hello. I have installed a 240v Profusion heater in my garage. I have a 45amp breaker with 8awg wire. The heater will not come on. There is a toggle switch on the back for using either an and external … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
This house has a 200amp panel, the service entrance cable
This house has a 200amp panel, the service entrance cable comes from underground to the meter. The homeowner asked me if he could install a junction box in the SEC between the meter and the house pane… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
We are adding an addition onto our home and need to buy the
We are adding an addition onto our home and need to buy the right wire for outlets, lights, etc. and also wire for a dryer to be installed in the area. Is it 12-2 for the wiring and 10-3 for the dryer… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
A barn is located 400' from house service. Ran aerial 2 #4
A barn is located 400' from house service. Ran aerial 2 #4 al wires with messenger to a made up panel with a 2 pole disconnect switch with 20A fuses .Tapped a 50A 2 pole breaker at service. Drove 2 6f… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
I need to put 100 amp sub panel on other side of house there
I need to put 100 amp sub panel on other side of house there is a lot of obstacles on outside of house can I run it through attic… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
1- Does NEC prohibit the following? 2- What are all the
1- Does NEC prohibit the following? 2- What are all the consequences of following the following setup? Run one #10 Hot, Neutral and Ground from 120/240v main panel (from 1-pole 30A breaker) to a junct… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
I need advice on if this can be done costs and anything you
I need advice on if this can be done costs and anything you can add. I need a breaker box moved about 35 feet from current location to further to the end of the house?… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
Just bought a new square d home line 200 amp 30 spaces 60 circuits
just bought a new square d home line 200 amp 30 spaces 60 circuits plug on neutral ready load center my question is do i need to install ground buss directly to the metal of the panel and separate my … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
Hi, we put up a new pole barn. service company is upgrading
Hi, we put up a new pole barn. service company is upgrading 100 amp service to 200 amp at meter base.I have existing 1/0 al 3-wire feeding 100 amp in my house ,can a seperate 1/0 al 3-wire be used to … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,419 satisfied customers
Hello. Im replacing an old meter base with a new that the
Hello. I'm replacing an old meter base with a new that the electric company has provided. The new box is about five feet away from the old one so I know that I'll need to run new wire in conduit to th… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
I have an outdoor standard ground level path light figure,
I have an outdoor standard ground level path light figure, now want to eliminate this fixture and extend wiring to a lamp post using old locational as terminal box . What is best way to waterproof thi… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
Hi Here is my problem. I dug into the main wire to the
Hi Here is my problem. I dug into the main wire to the house and want to split it to my pole barn. the wiring will look like this. Transformer to meter socket mounted on shed. Meter socket to house th… read more
Machinc
Machinc
Retired
1,010 satisfied customers
Hello, Im currently renovating a basement suite. I am roughing
Hello, I'm currently renovating a basement suite. I am roughing in all new electrical wire for the suite. I want to add a second service panel on a second/separate power meter. I'm curious how an elec… read more
Phil
Phil
Consultant to Engrs, Govt & Contractors
Degree, Mech Engr Technology
3,671 satisfied customers
I have two circuits (two wires) into one breaker now. The
I have two circuits (two wires) into one breaker now. The inspector wants only one. One of the wires is too short to run outside the panel box to create a junction in a separate box. Can I use an insu… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
Can you run two sets of feeders from two different meter/mains
Can you run two sets of feeders from two different meter/mains in the same conduit and then split them into two sererate sub panels in two sererate suites… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
can we put a new service meter and transfer the wire from old
can we put a new service meter and transfer the wire from old panel box thought a juntion box to a new panel box in a different location… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
on a residence i will be changing the main service panel
on a residence i will be changing the main service panel the feeder wires are too short from the meter to the main breaker can i splice the feeder wires inside my new panel… read more
Paul
Paul
Owner
Vocational, Technical or Trade Scho
51 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x