I have a British-made industrial oven with electric heater…

I have a British-made industrial...
I have a British-made industrial oven with electric heater elements. According to the operator's manual, the 3-wire cord should be hooked up to: Live (230V), Neutral, and Ground. Since the unit is made in the UK, their 230V system is a bit different from ours. As I understand it, the US system has +120V, neutral, and -120V with the difference between the +120V and -120V equalling 240V and neutral not used unless it's to power 120V accessories which my industrial oven does not have. I would like to hook up this industrial oven in my garage to a dedicated electric drier circuit (old house, only a 3 wire system with a neutral but no ground). It seems to me that trying to hook up my oven to this power source could be a problem. The 3rd prong is a neutral so I can't hook my ground wire to it, correct? And if I hook up the neutral wire from the oven to the neutral wire of the drier circuit and the live wire to one of the the live wires of the drier circuit, then I'll only be getting 120V. My question is, can I hook up the live wire from the oven to one of the live wires of the drier circuit, hook up the neutral wire from the oven to the other live wire of the drier circuit (to give me 240V), and hook a jumper wire from the ground wire of the oven to the grounded box of an adjacent 120V grounded outlet?
Show More
Show Less
Ask Your Own Electrical Question
Answered in 4 minutes by:
3/12/2018
George Smith
George Smith, Master Electrician
Category: Electrical
Satisfied Customers: 442
Experience: Superintendent at Electrical Solutions and Data
Verified
Hi this is George let me look at your question!
Ask Your Own Electrical Question

I would think you're right! Without seeing the wiring on the heat elements ! They are rated for 230v so it's not that big of a difference! Do you know the actual voltage in the garage?

Ask Your Own Electrical Question
Customer reply replied 4 months ago
No, I don't know the actual voltage in the garage. I realize that the heating elements may not quite reach design temperature if my voltage is lower than spec'd, but it shouldn't hurt anything, right?You mention that you would think I'm right 'without seeing the wiring on the heat elements'. That implies that perhaps, depending on how they're wired, that maybe I could be wrong. How could the heating elements be wired differently? Is there a danger to me from a safety standpoint? How could I find out how the heating elements are wired? There is no detail about their wiring in the manual other than how to hook them up. Would taking the oven apart to see how the elements are wired give us the answer? What would I be looking for?

Can you send me a pic of the wiring and the heat elements?

Ask Your Own Electrical Question

They shouldn't be wired differently but I can't guess! There should be a wire on each end of the elements or banks of element!

Ask Your Own Electrical Question

However they are wired or connected to each other there should be a wire on each side or on each set!

Ask Your Own Electrical Question

I just want you to make sure ! You may have to reconfigure neutrals because you're using some as hots now! I'm more concerned about the neutrals!

George Smith
George Smith, Master Electrician
Category: Electrical
Satisfied Customers: 442
Experience: Superintendent at Electrical Solutions and Data
Verified
George Smith and 87 other Electrical Specialists are ready to help you
Ask your own question now
Customer reply replied 4 months ago
Okay, I'm going out to the garage to see how hard it is to gain access to the wiring. Back in a bit!
Phone call session started

Thanks for the positive rating !

Please feel free to ask for me personally if you have any more question !

Thanks !

George

Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask George Smith Your Own Question
George Smith
George Smith
George Smith, Master Electrician
Category: Electrical
Satisfied Customers: 442
442 Satisfied Customers
Experience: Superintendent at Electrical Solutions and Data

George Smith is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,196 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,345 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I want to know if it is possible to get 240v from two 120v
I want to know if it is possible to get 240v from two 120v pins from a push and twist plug from a US generator ... so that It can be used to power a British 240v wet dry vacuum … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
What's the difference between running 3 wire to outlets
What's the difference between running 3 wire to outlets versus 2 wires. The outlets will be bonded to junction box, conduit, and chassis regardless of 3rd wire and chassis will be bonded to the third … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
The power company here in the Philippines will be supplying
The power company here in the Philippines will be supplying two insulated wires at 220V for our house service. Can I use one wire as a ground or neutral for bonding and grounding and a single pole bre… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
My question is about wiring for a hot tub. In the specifications
My question is about wiring for a hot tub. In the specifications of the hot tub it is written: 110V plugs into a standard outlet or 230V conversion. What does it mean "230V conversion"?… read more
Steve
Steve
Chief Engineer
9 satisfied customers
I have a 4 wire 230V circuit for my hot tub. At the local panel,
I have a 4 wire 230V circuit for my hot tub. At the local panel, near the hot tub I have incoming 230V phase to phase and 120V phase to neutral. When the circuit breaker is installed the load side of … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
I am trying to hook up a tanning bed using the existing 220
I am trying to hook up a tanning bed using the existing 220 line in the house. But am kinda confused, the wires from tanning bed are green white and black, The wires in the 220 line are red white blac… read more
Steve
Steve
Chief Engineer
9 satisfied customers
I am putting in a dedicated 20 amp line to a Sauna, with a
I am putting in a dedicated 20 amp line to a Sauna, with a gfci receptical. I have strung a 2/12 cable directly to the service box, connecting to a 20 amp double circuit breaker. Red wire to one side … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
i have 3 ph 208 v machine...i need to hard wire it to test
i have 3 ph 208 v machine...i need to hard wire it to test it....is there a difference between 208v and 240v....on my 3 ph i have 3 hots and a ground...120v each hot… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
I am running a curcuit from a panel to a 240v outlet over a
I am running a curcuit from a panel to a 240v outlet over a 200 foot distance. Do I size each of the two hot wires for 120v? I ran both through the wire size calculator and 240 says I need 6 awg bt 12… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
Good Day Everyone, The convention of home electrical wiring
Good Day Everyone, The convention of home electrical wiring of let's say the US standards is three wires, one is hot (live), one is Neutral, and the other one is the ground. Which is actually the same… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
Electronic Ballast cause hot to hot voltage and frequency go
Electronic Ballast cause hot to hot voltage and frequency go up, why? HI Expert, Recently I am installing(NNN) NNN-NNNN MH lights with 120-240v electronic ballast in a medical herb greenhouse. During … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
I have a 240 volt electrical stovetop being repolaced with
I have a 240 volt electrical stovetop being repolaced with a gas stovetop. This new top needs a 120 plug to power the igniters. How do I lower the voltage coming in to that electrical box?… read more
Jerry
Jerry
Plumber
High School or GED
1,456 satisfied customers
i have a european appliance that i would like to use in the
i have a european appliance that i would like to use in the united states, it is a water still with two 1500 watt heaters for a total of 3000 watts, it operates on 220/240v, 50/60hz, and it has a g ty… read more
Craig
Craig
Electrical Director
Electrical Automation Technician
2,133 satisfied customers
Im looking at a building with an electrical system that is
I'm looking at a building with an electrical system that is 240v Delta w/ mid-tap ground. Phase B to ground is 208v. I've selected variable speed drives and transformers based on 230v 3 phase power. T… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
i need what to do. my stove had two hots and a ground now the
i need what to do. my stove had two hots and a ground now the new doulbe oven has two hot and a common ans a ground what do i need to do… read more
Mike
Mike
Master Electrician
Working on MBA
1,426 satisfied customers
I have a new air compresssor listed as 230 volts. I have
I have a new air compresssor listed as 230 volts. I have only the standard 110 volt two circuit (household) service. The wire from the compresspor is marked "neutral" , "Hot" and ground. I have conclu… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
can you take one hot conductor off of a 240v double pole breaker
can you take one hot conductor off of a 240v double pole breaker and use as a 120v. The neutral dedicated to the 120v receptacles only. Sharing bare ground on both circuits, 120v and 240v.… read more
Mike
Mike
Master Electrician
Working on MBA
1,426 satisfied customers
How to determine which wires are which voltage on a multi-tap
How to determine which wires are which voltage on a multi-tap ballast? I have some Cooper MHXB-400-MT low bay light fixtures that were previously wired for 120V. I'm moving them to a different shop an… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x