In New York State, the building's 1st floor is commercial space, 2nd floor are residential rental apartments. there are 3 meters in basement control the 2nd floor apartment but now vacant, hooked on fuse box. Contractor installed 2 new 200-amp service panels on 2nd floor, will use 4/0-4/0-4/0-2/0 Aluminum SER Service Entrance Cable to connect to basement meter #1 #2. Also install 1 new 100-amp service panels on 2nd floor, will use 2-2-2-4 Aluminum SER Service Entrance Cable connect to basement #3. Can he simply replace 3 fuse boxes below 3 meters? By what?
Show More
Show Less
Ask Your Own Electrical Question
Answered in 23 minutes by:
3/7/2018
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,220
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

Please be patient as it takes time to type and provide links. Also note that the website may be sending you a telephone offer, the offer is not originating from me.

1) Fuse type panelboards can always be replaced by a panelboard with circuit breakers. Fuse's and circuit breakers are both forms of OCPD's (over current protection devices).

2) Panelboards are sold in a variety of maximum amperage, circuit breaker slots and main lug or main breaker type.

Ask Your Own Electrical Question

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks.................Kevin:)

Ask Your Own Electrical Question
Customer reply replied 1 month ago
what does "main lug" mean?
Customer reply replied 1 month ago
Under 3 meters for 2nd floor, should put one 200-amp breaker on panel #1 (200-amp), then 200-amp breaker on panel #2 (200-amp), then 100-amp breaker on panel #3 (100-amp). I am trying to find smallest size panel as possible

1) Circuit breaker panelboards are sold in two different versions...........ie......... either a main lug type or a main breaker type.

2) Main lug types do not have a built-in main disconnect breaker and only have main lugs where the feeder conductors terminate. Main lug panels of course will have individual branch circuit breakers.

3) A main breaker panelboard is just that. It contains a main breaker that is built into the panel to allow as a means of disconnect.

Ask Your Own Electrical Question

1) Panels are sold in a variety of amperage ratings.........ie........ 30, 60, 100, 125, 150, 200 amps and even higher. I recommend a local electrical supply store as Home Depot and Lowe's often carry limited panelboard amperages and quantity of breaker slots. Electrical supply stores carry all types of panelboards that will be applicable for many applications.

2) The panel amperage is based on the feeder conductor size and the service amps originating into the meter socket.

Ask Your Own Electrical Question
Customer reply replied 1 month ago
Under 3 meters for 2nd floor, should put one 200-amp breaker on panel #1 (200-amp), then 200-amp breaker on panel #2 (200-amp), then 100-amp breaker on panel #3 (100-amp). I am trying to find smallest size panel as possible because I have two 200-amp panels and one 100-amp panel on 2nd floor.

1) Sounds like you want to install a main disconnect switch? If so, main disconnect switches are sold as the fusible type and are available at any local electrical supply store. 100 and 200 amp models are widely available.

Ask Your Own Electrical Question

1) Combination meter sockets with a built-in main breaker are also available. Square-D and Milbank are the industry leaders for these types of main disconnects. Instead of a fuse, these versions have a built-in main disconnect circuit breaker.

Ask Your Own Electrical Question
Customer reply replied 1 month ago
3 main disconnect switches. Two 200-amps, one 100-amps under those 3 meters in the photo, right?

1) Yes, those are fusible disconnect switches in the pictures

Ask Your Own Electrical Question
Customer reply replied 1 month ago
can I simply change them to two 200-amp and one 100-amp fuses? save lot of work

1) That depends upon the incoming service amps to each meter and the service entrance conductor sizes. You need to confirm the amperage. Look at the fusible disco switches. The main cartridge fuses will be labeled with the amperage.

Ask Your Own Electrical Question

1) Looks like a 60 amp service which is common for apartments. The main cartridge fuses are also 60 amps.

Ask Your Own Electrical Question
Customer reply replied 1 month ago
my 2nd floor has two 200-amp panels and one 100-amp panels. How shall I upgrade these basement main disconnect switches so I can connect SER cable from 2nd floor panels to them?

1) The panels below the fuses are a combination of a main disconnect and branch circuits. The cartridge fuses are the main disconnect. The individual yellow fuses look like branch circuits. Are the glass fuses serving the individual branch circuits within one apartment?

2) Does each apartment contain a smaller sub-panel or you installed either a 200 or 100 am panel in each each apartment?

Ask Your Own Electrical Question
Customer reply replied 1 month ago
1) These 3 meters are been vacant for 3 years. I was connecting 2nd floor outlets before. Now my contractor installed brand new two 200-amp panels and one 100-amp panel on 2nd floor with all brand new wiring. I am wondering if any way those SER cables from 2nd floor new panels connect to 3 meters in the photos, without much cost?
2) On 2nd floor, I have two 200-amp panel and one 100-amp panel for each apartment.
Customer reply replied 1 month ago
1) These 3 meters are been vacant for 3 years. *They* were connecting 2nd floor outlets before. Now my contractor installed brand new two 200-amp panels and one 100-amp panel on 2nd floor with all brand new wiring. I am wondering if any way those SER cables from 2nd floor new panels connect to 3 meters in the photos, without much cost?
2) On 2nd floor, I have two 200-amp panel and one 100-amp panel for each apartment.

Thanks for the replies.

1) Like I mentioned in my previous answer, the main cartridge fuses are 60 amps. A 60 amp service is very common for apartment units.

2) If you are looking to supply 100 or 200 amps to the new panels, then the service needs to be upgraded to 100 or 200 amps accordingly. The service/feeder conductors into the meters would also have to be upgraded to accommodate a 100 or 200 amp load.

3) If looking to retain the 60 amp service, the 100 or 200 amp main breaker in the new panels will only act as the means of disconnect and the 60 amp disco switch can remain in place. If an overload with 60 amp service, the 100 or 200 amp main breaker will not trip. The 60 amp cartridge fuses would blow on an overload condition.

4) The SER cables can either be confirmed to which panel they extend to by a toner or continuity tester. A voltage meter can also confirm by measuring voltage at the 100 and 200 amp panels and then disconnecting the cartridge fuses at each of the disco switches.

Ask Your Own Electrical Question

1) In addition, if upgrading to 100 or 200 amp service, you would require a new meter socket that is rated for 100 or 200 amps.

Ask Your Own Electrical Question

1) The original fuse boxes look like a combo main disconnect and branch circuits. I suspect the 25 amps yellow fuses are for the branch circuits. It is also a code violation to use 25 amp fuses on a 120 volt circuit. Fuses and/or breakers can only be 15 or 20 amp rated. I suspect the 25 amp fuses were installed to prevent blowing fuses on previously installed 15 or 20 amp fuses. If so, that is a code violation and can lead to a fire. The circuit is being overfused. You will need to confirm the wire sizes on each 25 amp glass fuse. If 14 AWG copper, max amp is 15. If 20 AWG copper, max amp is 20. Yet, I'm seeing 25 amp fuses?

Ask Your Own Electrical Question
Customer reply replied 1 month ago
there are still live electricity in those 3 meters. National Grid shut off powers in 3 black boxes under those 3 meters and put locks on 3 years ago. You wrote "If you are looking to supply 100 or 200 amps to the new panels, then the service needs to be upgraded to 100 or 200 amps accordingly. " How to do that?

1) Who reads the 3 meters? The local electrical utility or the property manger?

2) I suspect the exterior of the building contains the utility meter and the inside basement meter are customer premise meters in order to provide individual apartment billing, is that correct?

3) If looking to upgrade the service amps, then the building service supplied by the utility needs to be confirmed. The service entrance conductor sizes to the exterior and interior meters also need to be confirmed. If wanting to upgrade the individual apartment amps, then the meter sockets along with the service conductors and the main disconnect all need to be upgraded accordingly to accommodate a higher amperage.

Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,220
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified
Kevin and 87 other Electrical Specialists are ready to help you
Ask your own question now
Was this answer helpful?
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,220
4,220 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,220 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I want a single switch to transfer power between two outlets
I want a single switch to transfer power between two outlets so that only one is hot at any given moment. Like an A/B switch for a guitar or telephone line but for power to either one light or outlet.… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Need help with wiring a new combo switch/ gfci outlet with a
Need help with wiring a new combo switch/ gfci outlet with a separate light switch for vanity light. … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I live in a building. and the circuit breaker tripped for on
i live in a building. and the circuit breaker tripped for on side of the hall but the circuit breaker has a screw on one side not like a normal circuit breaker that you could just flip … read more
Sam I
Sam I
Electrician
B.S.
577 satisfied customers
I want to wire a new outlet I have an existing switch with
Hello, I want to wire a new outlet I have an existing switch with blue and black cables … read more
Sam I
Sam I
Electrician
B.S.
577 satisfied customers
I want to add two outlets and a light switch (with a
I want to add two outlets and a light switch (with a recessed light). What is the best way to wire them? … read more
George Smith
George Smith
Vocational, Technical or Trade School
430 satisfied customers
I have five receptacles connected to one circuit & breaker.
Hi! I have five receptacles connected to one circuit & breaker. I checked the voltage ... it correct. When I plug in a lamp into any one of the receptacles the lamp will not turn on. I also tested the… read more
Kevin
Kevin
Licensed Electrical Contractor
4,220 satisfied customers
I am trying to add an outlet and a switch for that outlet.
I am trying to add an outlet and a switch for that outlet. The power goes through to other areas. So basically I have power coming to a junction box, one of the wires coming out of the junction box goes to a light ( the old pull style). I wan to replace that old light with an outlet and have a switch for that outlet only. clear as mud right? LOL … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I'm trying to replace a light switch with a switch outlet
I'm trying to replace a light switch with a switch outlet combo. The old switch has 3 Romeo coming in. How do I wire up the new outlet/switch combo? … read more
George Smith
George Smith
Vocational, Technical or Trade School
430 satisfied customers
I need assistance upgrading a circuit breaker to a sub
I need assistance upgrading a circuit breaker to a sub panel. I have all the specs of everything just need to know if it will work. Have photos if needed. … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Our power dims but no circuit breakers trip. Is it a going
our power dims but no circuit breakers trip. Is it a going bad main breaker? … read more
Kevin
Kevin
Licensed Electrical Contractor
4,220 satisfied customers
Need to wire my food truck outlet on the outside of the
hello, need to wire my food truck outlet on the outside of the truck. I have a 30 amp breaker box... The outlet on the outside of the truck caught on fire because of the way he wired it lol - needless… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I checked all circuit breakers to see if any tripped. I
Hi, I checked all circuit breakers to see if any tripped. I reset all of them and checked voltage. They are all receiving power. So I changed the 2 outlets that went out on the side of one room. Still… read more
Kevin
Kevin
Licensed Electrical Contractor
4,220 satisfied customers
I have a problem with a circuit breaker tripping fairly
I have a problem with a circuit breaker tripping fairly regularly. I believe I have too many plugs on one circuit. How can I check to see if I have too many on one breaker. I have done a lot of wiring… read more
George Smith
George Smith
Vocational, Technical or Trade School
430 satisfied customers
My microwave flips a circuit breaker when I turn it on. It's
my microwave flips a circuit breaker when I turn it on. It's in the same location, same outlet, same everything. The outlet works with other things, like vacuum, elec light. The microwave works perfec… read more
Kevin
Kevin
Licensed Electrical Contractor
4,220 satisfied customers
Circuit breaker blew switch. Switch is not resetting. Just
Circuit breaker blew switch. Switch is not resetting. Just kinda dangles there, with no tension to either side. How can I fix this?… read more
Sam I
Sam I
Electrician
B.S.
577 satisfied customers
The circuit breaker hasn't popped but in living room non of
The circuit breaker hasn't popped but in living room non of the 4 outlets are working. Checked the 4 plugs for any signs of loose wires or spark marks. ? What's next? … read more
Kevin
Kevin
Licensed Electrical Contractor
4,220 satisfied customers
Wiring diagram for outlet on a switch the to a light on same
wiring diagram for outlet on a switch the to a light on same switch … read more
David Bowden
David Bowden
Owner
768 satisfied customers
Which wires go where? In replacing a switch and outlet in
Which wires go where? In replacing a switch and outlet in the bathroom I mistakenly didn't label the wires before I ran down to answer the door now I don't know where the three main lead wires into th… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x