In New York State, the building's 1st floor is commercial…

In New York State, the...
In New York State, the building's 1st floor is commercial space, 2nd floor are residential rental apartments. there are 3 meters in basement control the 2nd floor apartment but now vacant, hooked on fuse box. Contractor installed 2 new 200-amp service panels on 2nd floor, will use 4/0-4/0-4/0-2/0 Aluminum SER Service Entrance Cable to connect to basement meter #1 #2. Also install 1 new 100-amp service panels on 2nd floor, will use 2-2-2-4 Aluminum SER Service Entrance Cable connect to basement #3. Can he simply replace 3 fuse boxes below 3 meters? By what?
Show More
Show Less
Ask Your Own Electrical Question
Answered in 23 minutes by:
3/7/2018
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,461
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC General Class License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

Please be patient as it takes time to type and provide links. Also note that the website may be sending you a telephone offer, the offer is not originating from me.

1) Fuse type panelboards can always be replaced by a panelboard with circuit breakers. Fuse's and circuit breakers are both forms of OCPD's (over current protection devices).

2) Panelboards are sold in a variety of maximum amperage, circuit breaker slots and main lug or main breaker type.

Ask Your Own Electrical Question

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks.................Kevin:)

Ask Your Own Electrical Question
Customer reply replied 5 months ago
what does "main lug" mean?
Customer reply replied 5 months ago
Under 3 meters for 2nd floor, should put one 200-amp breaker on panel #1 (200-amp), then 200-amp breaker on panel #2 (200-amp), then 100-amp breaker on panel #3 (100-amp). I am trying to find smallest size panel as possible

1) Circuit breaker panelboards are sold in two different versions...........ie......... either a main lug type or a main breaker type.

2) Main lug types do not have a built-in main disconnect breaker and only have main lugs where the feeder conductors terminate. Main lug panels of course will have individual branch circuit breakers.

3) A main breaker panelboard is just that. It contains a main breaker that is built into the panel to allow as a means of disconnect.

Ask Your Own Electrical Question

1) Panels are sold in a variety of amperage ratings.........ie........ 30, 60, 100, 125, 150, 200 amps and even higher. I recommend a local electrical supply store as Home Depot and Lowe's often carry limited panelboard amperages and quantity of breaker slots. Electrical supply stores carry all types of panelboards that will be applicable for many applications.

2) The panel amperage is based on the feeder conductor size and the service amps originating into the meter socket.

Ask Your Own Electrical Question
Customer reply replied 5 months ago
Under 3 meters for 2nd floor, should put one 200-amp breaker on panel #1 (200-amp), then 200-amp breaker on panel #2 (200-amp), then 100-amp breaker on panel #3 (100-amp). I am trying to find smallest size panel as possible because I have two 200-amp panels and one 100-amp panel on 2nd floor.

1) Sounds like you want to install a main disconnect switch? If so, main disconnect switches are sold as the fusible type and are available at any local electrical supply store. 100 and 200 amp models are widely available.

Ask Your Own Electrical Question

1) Combination meter sockets with a built-in main breaker are also available. Square-D and Milbank are the industry leaders for these types of main disconnects. Instead of a fuse, these versions have a built-in main disconnect circuit breaker.

Ask Your Own Electrical Question
Customer reply replied 5 months ago
3 main disconnect switches. Two 200-amps, one 100-amps under those 3 meters in the photo, right?

1) Yes, those are fusible disconnect switches in the pictures

Ask Your Own Electrical Question
Customer reply replied 5 months ago
can I simply change them to two 200-amp and one 100-amp fuses? save lot of work

1) That depends upon the incoming service amps to each meter and the service entrance conductor sizes. You need to confirm the amperage. Look at the fusible disco switches. The main cartridge fuses will be labeled with the amperage.

Ask Your Own Electrical Question

1) Looks like a 60 amp service which is common for apartments. The main cartridge fuses are also 60 amps.

Ask Your Own Electrical Question
Customer reply replied 5 months ago
my 2nd floor has two 200-amp panels and one 100-amp panels. How shall I upgrade these basement main disconnect switches so I can connect SER cable from 2nd floor panels to them?

1) The panels below the fuses are a combination of a main disconnect and branch circuits. The cartridge fuses are the main disconnect. The individual yellow fuses look like branch circuits. Are the glass fuses serving the individual branch circuits within one apartment?

2) Does each apartment contain a smaller sub-panel or you installed either a 200 or 100 am panel in each each apartment?

Ask Your Own Electrical Question
Customer reply replied 5 months ago
1) These 3 meters are been vacant for 3 years. I was connecting 2nd floor outlets before. Now my contractor installed brand new two 200-amp panels and one 100-amp panel on 2nd floor with all brand new wiring. I am wondering if any way those SER cables from 2nd floor new panels connect to 3 meters in the photos, without much cost?
2) On 2nd floor, I have two 200-amp panel and one 100-amp panel for each apartment.
Customer reply replied 5 months ago
1) These 3 meters are been vacant for 3 years. *They* were connecting 2nd floor outlets before. Now my contractor installed brand new two 200-amp panels and one 100-amp panel on 2nd floor with all brand new wiring. I am wondering if any way those SER cables from 2nd floor new panels connect to 3 meters in the photos, without much cost?
2) On 2nd floor, I have two 200-amp panel and one 100-amp panel for each apartment.

Thanks for the replies.

1) Like I mentioned in my previous answer, the main cartridge fuses are 60 amps. A 60 amp service is very common for apartment units.

2) If you are looking to supply 100 or 200 amps to the new panels, then the service needs to be upgraded to 100 or 200 amps accordingly. The service/feeder conductors into the meters would also have to be upgraded to accommodate a 100 or 200 amp load.

3) If looking to retain the 60 amp service, the 100 or 200 amp main breaker in the new panels will only act as the means of disconnect and the 60 amp disco switch can remain in place. If an overload with 60 amp service, the 100 or 200 amp main breaker will not trip. The 60 amp cartridge fuses would blow on an overload condition.

4) The SER cables can either be confirmed to which panel they extend to by a toner or continuity tester. A voltage meter can also confirm by measuring voltage at the 100 and 200 amp panels and then disconnecting the cartridge fuses at each of the disco switches.

Ask Your Own Electrical Question

1) In addition, if upgrading to 100 or 200 amp service, you would require a new meter socket that is rated for 100 or 200 amps.

Ask Your Own Electrical Question

1) The original fuse boxes look like a combo main disconnect and branch circuits. I suspect the 25 amps yellow fuses are for the branch circuits. It is also a code violation to use 25 amp fuses on a 120 volt circuit. Fuses and/or breakers can only be 15 or 20 amp rated. I suspect the 25 amp fuses were installed to prevent blowing fuses on previously installed 15 or 20 amp fuses. If so, that is a code violation and can lead to a fire. The circuit is being overfused. You will need to confirm the wire sizes on each 25 amp glass fuse. If 14 AWG copper, max amp is 15. If 20 AWG copper, max amp is 20. Yet, I'm seeing 25 amp fuses?

Ask Your Own Electrical Question
Customer reply replied 5 months ago
there are still live electricity in those 3 meters. National Grid shut off powers in 3 black boxes under those 3 meters and put locks on 3 years ago. You wrote "If you are looking to supply 100 or 200 amps to the new panels, then the service needs to be upgraded to 100 or 200 amps accordingly. " How to do that?

1) Who reads the 3 meters? The local electrical utility or the property manger?

2) I suspect the exterior of the building contains the utility meter and the inside basement meter are customer premise meters in order to provide individual apartment billing, is that correct?

3) If looking to upgrade the service amps, then the building service supplied by the utility needs to be confirmed. The service entrance conductor sizes to the exterior and interior meters also need to be confirmed. If wanting to upgrade the individual apartment amps, then the meter sockets along with the service conductors and the main disconnect all need to be upgraded accordingly to accommodate a higher amperage.

Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,461
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC General Class License
Verified
Kevin and 87 other Electrical Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,461
4,461 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC General Class License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,290 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,461 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC General Class License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
In New York State, the building's 2nd floor are residential
In New York State, the building's 2nd floor are residential rental apartments. there are 3 meters in basement control the 2nd floor apartment but now vacant, hooked on fuse box. See photo "old 3 gang"… read more
George Smith
George Smith
Vocational, Technical or Trade School
450 satisfied customers
I've learned use 4/0-4/0-4/0-2/0 Aluminum SER Service
I've learned use 4/0-4/0-4/0-2/0 Aluminum SER Service Entrance Cable to connect between main panel and 200-amp subpanel; use 2-2-2-4 Aluminum SER Service Entrance Cable to connect between main panel a… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,461 satisfied customers
Convey power from the basement main service panel to the
Convey power from the basement main service panel to the sub-panel on 2nd floor, which cable shall I use? SER aluminum 2-2-2-4 ? or SER copper 2-2-2-4 ? or other?… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
In New York State, it is a 4-unit apartment building.
In New York State, it is a 4-unit apartment building. Apartment #3 and #4 are upstairs. Electrical meters and main shut off breakers in basement. We plan to make Apt #3 and #4 have own service panel i… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
I'm adding a new service to my garage. A second service for
I'm adding a new service to my garage. A second service for my garage. The service is overhead from the pole. I am in Minnesota. The purpose for the service is a very large welding machine. It require… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,461 satisfied customers
Thank you for your past answers---as it is a big help for
Thank you for your past answers---as it is a big help for the homeowner to understand the electricians calculations. If you answer soon I might not get back to you for several hours, since I am going … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
Service Entrance Cable marked as: (UL) AWG 4 AL TYPE USE-2
Service Entrance Cable marked as: (UL) AWG 4 AL TYPE USE-2 60 … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,461 satisfied customers
Hi, we put up a new pole barn. service company is upgrading
Hi, we put up a new pole barn. service company is upgrading 100 amp service to 200 amp at meter base.I have existing 1/0 al 3-wire feeding 100 amp in my house ,can a seperate 1/0 al 3-wire be used to … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,461 satisfied customers
I live in massachusetts with 2014 NEC. I have a Kohler auto
I live in massachusetts with 2014 NEC. I have a Kohler auto transfer switch and am 120 feet from ATS to AC disconnect switch 100 amp. Generator is 20 kw. DO I use #2-3 & #4 ground SER Aluminum Buildin… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
I have altered my original plan. Do you see any glaring errors?
I have altered my original plan. Do you see any glaring errors? Do you have any recommended changes? Does the underground conduit require any drain capability? Here is the new plan. My house has 100 a… read more
HotWired
HotWired
Industrial Electrician
Associate Degree
154 satisfied customers
I am installing a new service for a house in NH which will
I am installing a new service for a house in NH which will come with a 200 amp breaker panel. I have already installed a meter panel and 200 amp disconnect panel on my pole 100 feet away (specified by… read more
mrromex
mrromex
field supervisor
5 years of college courses
281 satisfied customers
Hi, Im Greg. I have a 200 amp 4 gang meter sokt. can w/breaker
Hi, I'm Greg. I have a 200 amp 4 gang meter sokt. can w/breaker discnct next to each meter. 2 stores and two apartments above the stores. 200 amp main breaker each store 100 amp main breaker each apt.… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
My house has 100 amp service. There is a 100 amp breaker in
My house has 100 amp service. There is a 100 amp breaker in the meter box at the last pole. The line runs overhead from the last pole to the house. Once the wire enters the house it runs 38 feet throu… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
Can I use a 2-2-2-4 aluminum ser entrance cable for 100 amp
Can I use a 2-2-2-4 aluminum ser entrance cable for 100 amp service in a commercial/residential building… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
I have a 400 amp dual lug meter base and two 200 amp QO breaker
I have a 400 amp dual lug meter base and two 200 amp QO breaker boxes they each have a 200 amp breaker how do I wire them in and what size and type of wire should be used… read more
electrifier
electrifier
Master Electrician
Bachelor's Degree
1,458 satisfied customers
Im just verifying. I have a single family house combined into
I'm just verifying. I have a single family house combined into Two Apartments. I told my Electrician, I want my Two apartments wired separately. Now my Apartments from outside have one SE cable feedin… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
i have a 200 amp ser cable feeding 5 meters. two are 100 amp
i have a 200 amp ser cable feeding 5 meters. two are 100 amp meters for each apartment. one meter is for my water heater on a 30 amp breaker box by iytself. and the other two 100 amp panels feed my ho… read more
electrifier
electrifier
Master Electrician
Bachelor's Degree
1,458 satisfied customers
i have a 100 amp breaker outside and i want to install a new
i have a 100 amp breaker outside and i want to install a new inside main box yo 200 amp service, i added an addition and i am switching over to all electric stove, hot water heater, etc.. what size br… read more
electrifier
electrifier
Master Electrician
Bachelor's Degree
1,458 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x