What size wire do...

What size wire do I need to run to a storage building that is 200 feet from my home electrical panel if I wish to put a 40 or 50 amp breaker at the storage building?

Contractor's Assistant: How old is the system in question? And have you consulted an electrician yet?

My home was built in 2002, but there will need to be new wire to the new storage building. I have not contracted with a electrician yet as I am trying to determine the wire cost to decide if this is something I want to move forward with.

Contractor's Assistant: Do you plan on doing the work yourself?

No.

Submitted: 3 months ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 15 minutes by:
12/28/2017
Electrician: Leamon Rollo, Electrician replied 3 months ago
Leamon Rollo
Leamon Rollo, Electrician
Category: Electrical
Satisfied Customers: 19
Experience: Owner at L & R Electric
Verified
Good afternoon, my name is ***** ***** I am going to try to assist you. Will you be putting the wire in pipe or direct bury?
Ask Your Own Electrical Question
Electrician: Leamon Rollo, Electrician replied 3 months ago
1 conductors per phase utilizing a #4 Copper conductor will limit the voltage drop to 2.40% or less when supplying 50.0 amps for 200 feet on a 240 volt system.
For Engineering Information Only:
70.0 Amps Rated ampacity of selected conductor
0.2957 Ohms Resistance (Ohms per 1000 feet)
0.048 Ohms Reactance (Ohms per 1000 feet)
7.199999999999999 volts maximum allowable voltage drop at 3%
5.741. Actual voltage drop loss at 2.40% for the circuit
0.9 Power Factor
This is 3 #4 copper & 1 # 8 green
Ask Your Own Electrical Question
Customer reply replied 3 months ago
Direct bury. It is in a rural area. I want a couple lights in the building (20 x 24) and three small wood working tools all 15 amp or less.
Customer reply replied 3 months ago
This will be a 110 system.
Customer reply replied 3 months ago
Could I get by with 40 amps. I will only be using one tool at a time?
Electrician: Leamon Rollo, Electrician replied 3 months ago
1 conductors per phase utilizing a #2 Aluminum conductor will limit the voltage drop to 2.45% or less when supplying 50.0 amps for 200 feet on a 240 volt system.
For Engineering Information Only:
75.0 Amps Rated ampacity of selected conductor
0.3042 Ohms Resistance (Ohms per 1000 feet)
0.045 Ohms Reactance (Ohms per 1000 feet)
7.199999999999999 volts maximum allowable voltage drop at 3%
5.868. Actual voltage drop loss at 2.45% for the circuit
0.9 Power FactorThis is 2-2-2-4 aluminum direct bury. It will be the least expensive. Both this and the copper will result in 50 Amp with little to no voltage drop.
Ask Your Own Electrical Question
Electrician: Leamon Rollo, Electrician replied 3 months ago
I can recalculate at 110 but if you use 240 volt which is 2 legs of 110 it will be smaller wire
Ask Your Own Electrical Question
Electrician: Leamon Rollo, Electrician replied 3 months ago
If it is calculated at 110 volts at 200 feet at 40 amps it will be 1/0-1/0-#4 which is 2 sizes bigger, harder to get under lugs and more expensive than the 240 volt method.
Ask Your Own Electrical Question
Electrician: Leamon Rollo, Electrician replied 3 months ago
Is there anything else I can help you with?
Ask Your Own Electrical Question
Customer reply replied 3 months ago
No. Thanks
Electrician: Leamon Rollo, Electrician replied 3 months ago
Thank you and please give me a rating if you’re happy with my service. Have a safe New Years.
Ask Your Own Electrical Question
Was this answer helpful?
Ask Leamon Rollo Your Own Question
Leamon Rollo
Leamon Rollo
Leamon Rollo, Electrician
Category: Electrical
Satisfied Customers: 19
19 Satisfied Customers
Experience: Owner at L & R Electric

Leamon Rollo is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I have old school electric box replaced 30 amp fuse now all
I have old school electric box replaced 30 amp fuse now all my plug ins are barely working a lamp will come on real dim … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I am remodeling a garage and removed the 2 4 bulb
I am remodeling a garage and removed the 2 4 bulb fluorescent lights and one single bulb ceiling light. Tried to reinstall them after hanging drywall and cant get any power to lights. … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Do you have to feed a neutral to a 480 volt transformer or
do you have to feed a neutral to a 480 volt transformer or does the transformer produce its own neutral … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
My pool booster pump is not working. The filter pump is
My pool booster pump is not working. The filter pump is working. Booster pump reads L1 to ground 120 L2 to ground 120 L1 to L!2 0. … read more
Sam I
Sam I
Electrician
B.S.
556 satisfied customers
I'm installing an oven that requires 20amp 240 service. The
I'm installing an oven that requires 20amp 240 service. The electrician re-wired a dedicated dishwasher 20 amp 120 breaker. (oven was backordered when he did the wiring). He took the old wire to dishw… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
What is better recessed lighting option for tray ceiling? 4
What is better recessed lighting option for tray ceiling? 4 6" in elevated part or 4" around the lower area? Tanks! Room is 12X18… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I want a single switch to transfer power between two outlets
I want a single switch to transfer power between two outlets so that only one is hot at any given moment. Like an A/B switch for a guitar or telephone line but for power to either one light or outlet.… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have a solar system setup and when I have the power hooked
I have a solar system setup and when I have the power hooked up the motors on my power tools are smoking am I supplying too much power? … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Replace wall dimmer switch. 1 month
replace wall dimmer switch JA: I'll do all I can to help. How long have you been dealing with this? Customer: 1 month JA: Do you plan on doing the work yourself? Customer: no JA: Anything else we shou… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
L am running a 100 amp subpanel from a 200 amp main panel.
l am running a 100 amp subpanel from a 200 amp main panel. The subpanel is about 100 feet away In the garage so will be buried underground. … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have 2 each Leviton 16400 switches controlling the same
I have 2 each Leviton 16400 switches controlling the same bank of outdoor lights, but neither one seems to work. The lights operate in the override position from the time clock so the lights do work. … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Do I need whole-house surge protection? I have an
Do I need whole-house surge protection? I have an airconditioner, furnace, TV, laptop computer, and that's about it. I live in Southern California (lightning very rare). … read more
Sam I
Sam I
Electrician
B.S.
556 satisfied customers
My house was wired 1983. Selling same. Fly by night
My house was wired 1983. Selling same. Fly by night inspector says have to replace panels because they are not current.. In code it states prior installation under past code is allowed to stay if not … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I had a power surge and my ceiling fan will not work with
i had a power surge and my ceiling fan will not work with the remote or manually pulling the chain … read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
1,196 satisfied customers
Have a 30 amp air conditioner break box. hooked up wire to
have a 30 amp air conditioner break box. hooked up white wire to one side, black to oppiste side. coming from breakere to A.C. pluged in the connect bar. no power to A.C. do not under stand how the fu… read more
George Smith
George Smith
Vocational, Technical or Trade School
427 satisfied customers
I have a single tandem 2x20amp breaker connected to 2 GFCI
I have a single tandem 2x20amp breaker connected to 2 GFCI outlets then 5 outlets down-stream of the BLACK wire and 4 downstream of the RED. Both circuits test good when connected individually. Howeve… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Electrical outlet has power to it, used tester to verify
electrical outlet has power to it , used tester to verify that power is present, but when I put something into the outlet it will not run … read more
Sam I
Sam I
Electrician
B.S.
556 satisfied customers
I have a Dayton model 5K459B dual voltage motor that I need
I have a Dayton model 5K459B dual voltage motor that I need to wire for 120 volt operation. The data label is damaged and I can not read the color coded wire connections. … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x