Customer Question
Just purchased property and...

Just purchased property and found that the 120V circuit for lighting and receptacle outlet has a neutral that's connected to the equipment ground. shed has 2 wire w/ground feeder protected by 20 circuit breaker. need to resolve.

Contractor's Assistant: How old is the system in question? And have you consulted an electrician yet?

The two wire feeder is 240Vac for the well pump motor and controller, previous owner not having a neutral used the ground and L1 for 120v can we use a transformer to resolve issue? 240 to 120V ac step down encapsulated transformer or would it be better to trench a new conductor cable for the 120vac? 5 years old

Contractor's Assistant: Do you plan on doing the work yourself?

Yes or use electrician if needed

Contractor's Assistant: Anything else we should know to help you best?

That's it, can we use a transformer or not for this application

Submitted: 8 months ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 3 minutes by:
12/5/2017
Electrician: George Smith, Master Electrician replied 8 months ago
George Smith
George Smith, Master Electrician
Category: Electrical
Satisfied Customers: 451
Experience: Superintendent at Electrical Solutions and Data
Verified

Thanks for counting on us to help with your electrical issue. My name is ***** ***** I look forward to helping you! Let me review your question!

Ask Your Own Electrical Question
Customer reply replied 8 months ago
motor load = 7 amps (primary side) of transformer.
lighting and receptacle load on secondary side is 100 Watt light bulb and intermittent use 1500 W space heater at receptacle.
feeder supplying shed is 2 conductor w/grnd direct underground burial cable. (no neutral). But it's been illegally wired to produce 120 by using equipment ground.
Electrician: George Smith, Master Electrician replied 8 months ago

Is there a tap for a neutral and ground!

If not a neutral should be brought in !

Ask Your Own Electrical Question
Customer reply replied 8 months ago
guess question here is, would it be easier solution to use a transformer or run an additional 120V 2 wire w/gnd cable to supply the 120V. think transformer is easiest cheapest fix but when I use code NEC 2014, looks like i have to use different ocp lower than rated circuit breakers which means I'd have to fuse both sides of xformer, is this correct? and if so maybe it's easier to run another 120v line instead.
Electrician: George Smith, Master Electrician replied 8 months ago

Yes and you need a ground also!

Ask Your Own Electrical Question
Customer reply replied 8 months ago
Hey George, thank you for the info. No, no neutral, neutral tap, it's a general purpose encapsulated 2 kVA xformer 240/120.
Electrician: George Smith, Master Electrician replied 8 months ago
that is a separate ground rod!
Ask Your Own Electrical Question
Customer reply replied 8 months ago
would you recommend finding a xformer w/ neutral tap or just running a new conductor to supply the 120v?
Electrician: George Smith, Master Electrician replied 8 months ago
I would do the xformer!
Ask Your Own Electrical Question
Electrician: George Smith, Master Electrician replied 8 months ago
Is your feeder direct burial?
Ask Your Own Electrical Question
Customer reply replied 8 months ago
me too but i'm having trouble finding a center tap, or neutral tap.
even if found, wouldn't i then have to 1. resize primary ocp and provide ocp for secondary?
Customer reply replied 8 months ago
direct burial cable #10AWG 2 conductor w/gnd
Electrician: George Smith, Master Electrician replied 8 months ago
You look at Grainger
Ask Your Own Electrical Question
Customer reply replied 8 months ago
about 110' from main service panel where ocp for feeder is located, so were looking into options other than digging another trench
Customer reply replied 8 months ago
checking now...
Customer reply replied 8 months ago
no, can't find center tap single phase transformer on grainger for 1.5-2kVA
Customer reply replied 8 months ago
No 1 phase transformers have neutral taps
Electrician: George Smith, Master Electrician replied 8 months ago
Guess it's teaching! How about Square D?
Ask Your Own Electrical Question
Electrician: George Smith, Master Electrician replied 8 months ago
Where you locstef?
Ask Your Own Electrical Question
Customer reply replied 8 months ago
Plenty of 240/120 transformers, but not finding any with neutral taps, only 3 phase has
Electrician: George Smith, Master Electrician replied 8 months ago
Do you have an electrical supply near by?
Ask Your Own Electrical Question
Electrician: George Smith, Master Electrician replied 8 months ago
If you trench I would put the feeder on pipe
Ask Your Own Electrical Question
Customer reply replied 8 months ago
zero help. so been looking online
Customer reply replied 8 months ago
here's the transformer i need to use: https://www.automationdirect.com/adc/Shopping/Catalog/Power_Products_(Electrical)/Power_Transformers/1-Phase_Encapsulated_Transformers_(NEMA_Rated)/480x240_VAC_to_240X120_VAC/C1F1C5LES
Customer reply replied 8 months ago
but there's no neutral, but it produces the 120V we need for lighting and receptacle.
Customer reply replied 8 months ago
where in nec does it state neutral requirements for xformer? i've looked in article 250 but not finding it.
found where to size the ocp for xformer less than 600 volts from table 450.3(b)
Customer reply replied 8 months ago
450, not 250, sorry typo
Electrician: George Smith, Master Electrician replied 8 months ago
I don't have my code book with me right now I'LL looking a little later and get back too you I'm at the eye doctor right now?
Ask Your Own Electrical Question
Electrician: George Smith, Master Electrician replied 8 months ago
Look in 240 and 450
Ask Your Own Electrical Question
Electrician: George Smith, Master Electrician replied 8 months ago

Did you find it ?

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 8 months ago
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,474
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC General Class License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) You don't need a transformer to resolve the problem. Just install a new 4 wire sub-panel feeder circuit comprised of 2 hots, 1 neutral and 1 equipment grounding conductor from the main panel out to the shed. Install a sub-panel at the shed with the respective branch circuit breakers.

2) Transformers are used used to step up or step down voltage.

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 8 months ago

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) You don't need a transformer to resolve the problem. Just install a new 4 wire sub-panel feeder circuit comprised of 2 hots, 1 neutral and 1 equipment grounding conductor from the main panel out to the shed. Install a sub-panel at the shed with the respective branch circuit breakers.

2) Transformers are used to step up or step down voltage.

Ask Your Own Electrical Question
Customer reply replied 8 months ago
that was my first option but sine trenching a new line and cable is costly and big job due to distance (~ 120' ). we thought of using a transformer to avoid having to do this.
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,474
4,474 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC General Class License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,290 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,474 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC General Class License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
Second opinion] I have a shed I am turning into an office. I
Second opinion] I have a shed I am turning into an office. I plan on putting a window unit in it and other wiring for office equipment. i.e. computer, printer, coffee pot, microfridge, fax machine. My… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,474 satisfied customers
Can I run a single pole 30 amp breaker from the utility
Can I run a single pole 30 amp breaker from the utility service with 10 gauge wire to a small shed into a small serice panel? … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,474 satisfied customers
I'm trying to hook up a 70 -2 amp breaker box. I will be
I'm trying to hook up a 70 -2 amp breaker box. I will be installing 4 15 amp breakers in the 2 slots. The feed wire is coming from a 30 amp breaker from the main box. The wire was for a 220 outlet ori… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,474 satisfied customers
I've got two cable runs I want to install. The first is a 72
I've got two cable runs I want to install. The first is a 72 foot run from my service panel to a sub-panel inside my detached workshop. I need 85 AMPs at the workshop with one outlet being 240V, 50 am… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,474 satisfied customers
Question about installing a 40 AMP - three circuit subpanel
Question about installing a 40 AMP - three circuit subpanel in my shed a few feet from my house.… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,474 satisfied customers
I wish to run about 75 feet of #4 awg thhn from my home to
I wish to run about 75 feet of #4 awg thhn from my home to my workshop. I have a large quantity of #14 awg thhn. Assume that six runs of the #14 would have the same current carrying capability as one … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,474 satisfied customers
I have a 50 amp main in my park model camper. I want to wire
I have a 50 amp main in my park model camper. I want to wire a storage shed. The shed will have a washer and dryer, some wall plugs and lighting. Can I install a subpanel with a 50 amp breaker to the … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,474 satisfied customers
I am putting power in a shed about 45 feet from feeder panel.in
I am putting power in a shed about 45 feet from feeder panel.in the shed i will have a 100 amp 2 circuit panel. What i need to know is the wire size and the size of the circuit breaker in the feeder p… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,474 satisfied customers
I have a 100 amp sub panel 103 ft away to a detached garage.
I have a 100 amp sub panel 103 ft away to a detached garage. I have 2 inch pvc conduit buried 24 inch deep. What size conductors, hot's neutral and ground, do I need to run?… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,474 satisfied customers
Installed 40AMP breaker , ran 10/2 w/grd to Shed, installed
Installed 40AMP breaker for Shed, ran 10/2 w/grd to Shed, installed 70AMP Sub Panel w/2 positions for 4 circuits, added Grd. Bar, connected to 10' grd. rod, installed 20 AMP GFI outlet and 5 other 20A… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,474 satisfied customers
I want to do an underground branch feeder to individual 50a20/240
I want to do an underground branch feeder to individual 50a20/240 1ph pedastel sites for rv's. what is an acceptable direct buried cable for this application. Each one will be fed from a circuit break… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,474 satisfied customers
1)I am installing sub panel in shed, running wires over head
1)I am installing sub panel in shed, running wires over head from garage to shed in liquid tite conduit. Can I use NM-B inside the liquid tite conduit if NOT underground? 2) I am using a blue wire for… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,474 satisfied customers
I am running a 100A sub panel to my garage. It is a separate
I am running a 100A sub panel to my garage. It is a separate building. Should I use #3/3 service wire and drive a separate gnd stake, or run a #3/3 SCR Cable.… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,474 satisfied customers
How to wire a 480v 3phase transformer to 240/120v panel with
How to wire a 480v 3phase transformer to 240/120v panel with neutral. It has H1,H2,H3 lugs on the high side and x1,x2,x3,x4 on low side. x4 is a mid tap. it is a MIDWEST 30KVA 9T83W3842… read more
Dr. Fix-It
Dr. Fix-It
Technical Lead
1,671 satisfied customers
Hello Mike... I have a fused disconnect (the old glass screw-in
Hello Mike... I have a fused disconnect (the old glass screw-in type) in my well house (220 submersible pump) and recently found that its badly rusted and needs replacing. I have a 2 fold question, 1.… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
I have a barn that is about 240 feet from my house and would
I have a barn that is about 240 feet from my house and would like to have power out there. There is a 50 amp breaker in the main panel of my house that used to be for a hot tub as far as I can tell. I… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,474 satisfied customers
I have a Homeline 70A 2-space load center. I am planning to
I have a Homeline 70A 2-space load center. I am planning to install 2 15 amp 110v circuit breakers to feed outlets in my basement. The wire I am using to feed this load center from my main has 3 wires… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,474 satisfied customers
Mike, problem is its a long way with lots of concrete and
Mike, problem is it's a long way with lots of concrete and asphalt in and skid road in between so laying in new line isn't really an option… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.