Just purchased property and found that the 120V circuit for lighting and receptacle outlet has a neutral that's connected to the equipment ground. shed has 2 wire w/ground feeder protected by 20 circuit breaker. need to resolve.

Contractor's Assistant: How old is the system in question? And have you consulted an electrician yet?

The two wire feeder is 240Vac for the well pump motor and controller, previous owner not having a neutral used the ground and L1 for 120v can we use a transformer to resolve issue? 240 to 120V ac step down encapsulated transformer or would it be better to trench a new conductor cable for the 120vac? 5 years old

Contractor's Assistant: Do you plan on doing the work yourself?

Yes or use electrician if needed

Contractor's Assistant: Anything else we should know to help you best?

That's it, can we use a transformer or not for this application

Submitted: 6 months ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 3 minutes by:
12/5/2017
Electrician: George Smith, Master Electrician replied 6 months ago
George Smith
George Smith, Master Electrician
Category: Electrical
Satisfied Customers: 438
Experience: Superintendent at Electrical Solutions and Data
Verified

Thanks for counting on us to help with your electrical issue. My name is ***** ***** I look forward to helping you! Let me review your question!

Ask Your Own Electrical Question
Customer reply replied 6 months ago
motor load = 7 amps (primary side) of transformer.
lighting and receptacle load on secondary side is 100 Watt light bulb and intermittent use 1500 W space heater at receptacle.
feeder supplying shed is 2 conductor w/grnd direct underground burial cable. (no neutral). But it's been illegally wired to produce 120 by using equipment ground.
Electrician: George Smith, Master Electrician replied 6 months ago

Is there a tap for a neutral and ground!

If not a neutral should be brought in !

Ask Your Own Electrical Question
Customer reply replied 6 months ago
guess question here is, would it be easier solution to use a transformer or run an additional 120V 2 wire w/gnd cable to supply the 120V. think transformer is easiest cheapest fix but when I use code NEC 2014, looks like i have to use different ocp lower than rated circuit breakers which means I'd have to fuse both sides of xformer, is this correct? and if so maybe it's easier to run another 120v line instead.
Electrician: George Smith, Master Electrician replied 6 months ago

Yes and you need a ground also!

Ask Your Own Electrical Question
Customer reply replied 6 months ago
Hey George, thank you for the info. No, no neutral, neutral tap, it's a general purpose encapsulated 2 kVA xformer 240/120.
Electrician: George Smith, Master Electrician replied 6 months ago
that is a separate ground rod!
Ask Your Own Electrical Question
Customer reply replied 6 months ago
would you recommend finding a xformer w/ neutral tap or just running a new conductor to supply the 120v?
Electrician: George Smith, Master Electrician replied 6 months ago
I would do the xformer!
Ask Your Own Electrical Question
Electrician: George Smith, Master Electrician replied 6 months ago
Is your feeder direct burial?
Ask Your Own Electrical Question
Customer reply replied 6 months ago
me too but i'm having trouble finding a center tap, or neutral tap.
even if found, wouldn't i then have to 1. resize primary ocp and provide ocp for secondary?
Customer reply replied 6 months ago
direct burial cable #10AWG 2 conductor w/gnd
Electrician: George Smith, Master Electrician replied 6 months ago
You look at Grainger
Ask Your Own Electrical Question
Customer reply replied 6 months ago
about 110' from main service panel where ocp for feeder is located, so were looking into options other than digging another trench
Customer reply replied 6 months ago
checking now...
Customer reply replied 6 months ago
no, can't find center tap single phase transformer on grainger for 1.5-2kVA
Customer reply replied 6 months ago
No 1 phase transformers have neutral taps
Electrician: George Smith, Master Electrician replied 6 months ago
Guess it's teaching! How about Square D?
Ask Your Own Electrical Question
Electrician: George Smith, Master Electrician replied 6 months ago
Where you locstef?
Ask Your Own Electrical Question
Customer reply replied 6 months ago
Plenty of 240/120 transformers, but not finding any with neutral taps, only 3 phase has
Electrician: George Smith, Master Electrician replied 6 months ago
Do you have an electrical supply near by?
Ask Your Own Electrical Question
Electrician: George Smith, Master Electrician replied 6 months ago
If you trench I would put the feeder on pipe
Ask Your Own Electrical Question
Customer reply replied 6 months ago
zero help. so been looking online
Customer reply replied 6 months ago
here's the transformer i need to use: https://www.automationdirect.com/adc/Shopping/Catalog/Power_Products_(Electrical)/Power_Transformers/1-Phase_Encapsulated_Transformers_(NEMA_Rated)/480x240_VAC_to_240X120_VAC/C1F1C5LES
Customer reply replied 6 months ago
but there's no neutral, but it produces the 120V we need for lighting and receptacle.
Customer reply replied 6 months ago
where in nec does it state neutral requirements for xformer? i've looked in article 250 but not finding it.
found where to size the ocp for xformer less than 600 volts from table 450.3(b)
Customer reply replied 6 months ago
450, not 250, sorry typo
Electrician: George Smith, Master Electrician replied 6 months ago
I don't have my code book with me right now I'LL looking a little later and get back too you I'm at the eye doctor right now?
Ask Your Own Electrical Question
Electrician: George Smith, Master Electrician replied 6 months ago
Look in 240 and 450
Ask Your Own Electrical Question
Electrician: George Smith, Master Electrician replied 6 months ago

Did you find it ?

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 6 months ago
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,354
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) You don't need a transformer to resolve the problem. Just install a new 4 wire sub-panel feeder circuit comprised of 2 hots, 1 neutral and 1 equipment grounding conductor from the main panel out to the shed. Install a sub-panel at the shed with the respective branch circuit breakers.

2) Transformers are used used to step up or step down voltage.

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 6 months ago

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) You don't need a transformer to resolve the problem. Just install a new 4 wire sub-panel feeder circuit comprised of 2 hots, 1 neutral and 1 equipment grounding conductor from the main panel out to the shed. Install a sub-panel at the shed with the respective branch circuit breakers.

2) Transformers are used to step up or step down voltage.

Ask Your Own Electrical Question
Customer reply replied 6 months ago
that was my first option but sine trenching a new line and cable is costly and big job due to distance (~ 120' ). we thought of using a transformer to avoid having to do this.
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,354
4,354 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,354 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I recently had a tankless water heater installed. The new
I recently had a tankless water heater installed. The new GFCI outlet the plumbers installed has tripped several times in the month since the install. What can I check to see what is causing it? I tho… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
I have a 110v hot tub with a circuit breaker built-in to the
I have a 110v hot tub with a circuit breaker built-in to the plug. Have been running it off an outdoor GFCI plug. Worked fine for a few months but now trips the 15amp circuit breaker in main panel. Do… read more
John D.
John D.
Master Electrician
1 satisfied customers
I have a circuit breaker that keeps tripping about once a
I have a circuit breaker that keeps tripping about once a day. It runs my garage outlets and my backyard. I have an air compressor and power strip for my woodworking tools as well as our solar system … read more
Kevin
Kevin
Licensed Electrical Contractor
4,354 satisfied customers
I have a breaker that wont stay on in my circuit breaker
I have a breaker that wont stay on in my circuit breaker panel. it is a Bryant type brd bd 20-20 cj-ac swd breaker. I would like to know how to replace it with a new one. reading other peoples questio… read more
David Bowden
David Bowden
Owner
987 satisfied customers
We have to replace allready my circuit breakers box and we
We have to replace allready my circuit breakers box and we instal de regular breakers but the inspector said we need to replace the breaker for type arc fault circuit interrupter it is true or no it i… read more
Sam I
Sam I
Electrician
B.S.
740 satisfied customers
The circuit breaker for our 4 year old microwave keeps
The circuit breaker for our 4 year old microwave keeps tripping, particularly if we use microwave consecutively, like to heat water, then reheat food, etc. We replaced circuit breaker and same thing is happening with new. It's almost like circuit can't handle multiple directions. What do you make of it? … read more
Sam I
Sam I
Electrician
B.S.
740 satisfied customers
Circuit breaker not thrown loss of power to section of
Circuit breaker not thrown loss of power to section of basement. It was off overnight tried it this morning there was power plugged in item and power off again … read more
Sam I
Sam I
Electrician
B.S.
740 satisfied customers
My new pump is tripping my circuit breaker, New and no, Yes,
I'm getting 120v both wires to the pump and it's a 115 Hayward super pump… read more
Sam I
Sam I
Electrician
B.S.
740 satisfied customers
Is it kosher to use two 120Volt circuit breakers to create a
Is it kosher to use two 120Volt circuit breakers to create a 240Volt circuit in a house panel?… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have a cutler hammer quad circuit breaker that dosen't
i have a cutler hammer quad circuit breaker that dosen't work on the outside 20 amp. breaker it is 20-30-30-20 … read more
Sam I
Sam I
Electrician
B.S.
740 satisfied customers
I live in a building. and the circuit breaker tripped for on
i live in a building. and the circuit breaker tripped for on side of the hall but the circuit breaker has a screw on one side not like a normal circuit breaker that you could just flip … read more
Sam I
Sam I
Electrician
B.S.
740 satisfied customers
I have five receptacles connected to one circuit & breaker.
Hi! I have five receptacles connected to one circuit & breaker. I checked the voltage ... it correct. When I plug in a lamp into any one of the receptacles the lamp will not turn on. I also tested the… read more
Kevin
Kevin
Licensed Electrical Contractor
4,354 satisfied customers
I need assistance upgrading a circuit breaker to a sub
I need assistance upgrading a circuit breaker to a sub panel. I have all the specs of everything just need to know if it will work. Have photos if needed. … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Our power dims but no circuit breakers trip. Is it a going
our power dims but no circuit breakers trip. Is it a going bad main breaker? … read more
Kevin
Kevin
Licensed Electrical Contractor
4,354 satisfied customers
I checked all circuit breakers to see if any tripped. I
Hi, I checked all circuit breakers to see if any tripped. I reset all of them and checked voltage. They are all receiving power. So I changed the 2 outlets that went out on the side of one room. Still… read more
Kevin
Kevin
Licensed Electrical Contractor
4,354 satisfied customers
I have a problem with a circuit breaker tripping fairly
I have a problem with a circuit breaker tripping fairly regularly. I believe I have too many plugs on one circuit. How can I check to see if I have too many on one breaker. I have done a lot of wiring… read more
George Smith
George Smith
Master Electrician
438 satisfied customers
Circuit breaker blew switch. Switch is not resetting. Just
Circuit breaker blew switch. Switch is not resetting. Just kinda dangles there, with no tension to either side. How can I fix this?… read more
Sam I
Sam I
Electrician
B.S.
740 satisfied customers
The circuit breaker hasn't popped but in living room non of
The circuit breaker hasn't popped but in living room non of the 4 outlets are working. Checked the 4 plugs for any signs of loose wires or spark marks. ? What's next? … read more
Kevin
Kevin
Licensed Electrical Contractor
4,354 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.