Huge bang and what looked like an arc flash. Lights went out…

Customer Question
Huge bang and what...

Huge bang and what looked like an arc flash. Lights went out but CB didn't trip. Sparky came in today, checked both RCDs and a visual but found nothing. What could he issue be? Very concerning.

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Happened last night

Contractor's Assistant: Do you plan on doing the work yourself?

?

Contractor's Assistant: Anything else we should know to help you best?

Bang came from the switchboard

Submitted: 6 months ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 8 minutes by:
11/23/2017
Electrician: Mike G., Master Electrician replied 6 months ago
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,243
Experience: Proven Professional 49 years Experience
Verified

Hi, I'm Mike and I'll be assisting you. Please stand by while I review your question.

Ask Your Own Electrical Question
Electrician: Mike G., Master Electrician replied 6 months ago

The bang is an indication of a short circuit. Either your breaker failed to trip or the short was ahead on the incoming line. The flash would leave a visual mark directing as to where to look. In some cases the arc will cause wires to move and break the path of the short. If the service feeder is in metal voduit the fault could be on the conductors in the conduit due to an insulation failure. Might want to get a more experienced electrician to look at it. I advise not to dismiss it.

Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Mike G. Your Own Question
Mike G.
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,243
8,243 Satisfied Customers
Experience: Proven Professional 49 years Experience

Mike G. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,243 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
What size copper wire do I need for a 100 amp service to a
What size copper wire do I need for a 100 amp service to a manufactured home on a run of 250 feet. ( Range, water heater, a/c & furnace, no dryer) Forgot to add will be in underground conduit 2"… read more
Jason
Jason
Service Technician
Associate Degree
3,942 satisfied customers
Can fiber optic cable be run in the same underground PVC conduit
Can fiber optic cable be run in the same underground PVC conduit as 120VAC?… read more
Mike
Mike
Master Electrician
Working on MBA
1,426 satisfied customers
I want to run a subpanel to my workshop 220 feet away from
I want to run a subpanel to my workshop 220 feet away from the main panel and want to be able to pull 50 amps maximum. I plan to run the wire in schedule 40 PVC conduit buried at least 18". I understa… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
The wiring to my new electric range consists of 2 insulated
The wiring to my new electric range consists of 2 insulated wires and one bare ground wire. Is this adequate and safe?… read more
Sam I
Sam I
Electrician
B.S.
740 satisfied customers
IN 2" CONDUIT WITH 10 10 CAT 6 CABLES IN SIDE ALONG THE WAY
IM PUTTING IN 2" CONDUIT WITH 10 10 CAT 6 CABLES IN SIDE ALONG THE WAY THESE 10 CABLE BRANCH OFF TO A BUILDING WHAT TYPE OF IN GROUND HAND PULL BOXES DO I NEED TO HAVE AT THESE AREAS WHERE THE 2 CABLE… read more
David Bowden
David Bowden
Owner
987 satisfied customers
CAN I RUN 1 MAIN 2" CONDUIT WITH A 2", PVC Pipe, Wye
CAN I RUN 1 MAIN 2" CONDUIT WITH A 2", PVC Pipe, Wye Schedule 80, Slip TO BRANCH A LINE OFF TO ANOTHER BUILDING ALONG THE PATH WAY SO I HAVE 4 BUILDING AND I WANT TO RUN CAT 6 TO THEM FROM ANOTHER BUI… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
1. According to the NEC, conduit seals are required within
1. According to the NEC, conduit seals are required within _______ inches from a pressurized enclosure when the conduit is not pressurized in Class I, Division 1 protection systems. A. 24 B. 30 C. 12 … read more
Chris Miller
Chris Miller
Social Worker
Master\u0027s Degree
101 satisfied customers
Underground conduit cover" First time. Depth of conduit.
depth of conduit. table 300.5 measures from the top of conduit to top of finish surface and the inspector measures from top of the conduit to the bottom of the concrete slab. wish is correct?… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I'm building a detached shop and need to get conduit in the
I'm building a detached shop and need to get conduit in the ground for the shop electrical panel. I have a 200amp main panel in the house that is about 50 ft away from where the shop panel will be. … read more
Sam I
Sam I
Electrician
B.S.
740 satisfied customers
When using a metal conduit body such as an LB, or capped L
When using a metal conduit body such as an LB, or capped L at an enclosure does that fitting need to be supported other than with the nipple into the enclosure? … read more
Mike G.
Mike G.
Master Electrician
8,243 satisfied customers
What are the construction requirements for a new conduit
What are the construction requirements for a new conduit installation to an existing building? … read more
Mike G.
Mike G.
Master Electrician
8,243 satisfied customers
What type of wire does PG&E require to be buried in conduit?
what type of wire does PG&E require to be buried in conduit? The Distance would be close to 400' Will a single wire be able to go that distance or will I need a secondary? How many wires will be in th… read more
Mike G.
Mike G.
Master Electrician
8,243 satisfied customers
Is it permissible to run romex wire through conduit indoors
Is it permissible to run romex wire through conduit indoors and in a dry location? … read more
Mike G.
Mike G.
Master Electrician
8,243 satisfied customers
Can I use a steel conduit lockout on pvc male adaptor into
Can I use a steel conduit lockout on pvc male adaptor into utility box on end of my pvc conduit?… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Can I add a 90 elbow to the main conduit so that I can raise
can I add a 90 elbow to the main conduit so that I can raise that conduit the conduit is running vertical and i need some height under the conduit … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have a dedicated 10 amp romex line in conduit, going to a
I have a dedicated 10 amp romex line in conduit, going to a direct wired garbage disposer under my kitchen sink. I want to connect this line up to a single gang outlet box to make exchanging the dispo… read more
Sam I
Sam I
Electrician
B.S.
740 satisfied customers
How much to install 100' of electrical line in a conduit if
how much to install 100' of electrical line in a conduit if the trench is already dug. Include the cost of wiring and adding a 50 Amp Circuit Breaker … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
the grounding wedge you show will bond the conduit to a box.
the grounding wedge you show will bond the conduit to a box. i am leaving a 2" sleeve in free air to hit a ground bar. this fitting does not bond the 500 kcmil to the sleeve… read more
Mike G.
Mike G.
Master Electrician
8,243 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x