I have had a power loss to everything this 15 amp circuit breaker is lined up to. A few outlets and a couple lights. Curcuit breaker never tripped. Swapped out with another 15 and still nothing. What I thought was a bad breaker worked in place of the swapped one.
Submitted: 8 months ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 6 minutes by:
11/18/2017
Electrician: Kevin, Licensed Electrical Contractor replied 8 months ago
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,416
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) Do you have a 2 wire lead AC voltage tester (a contact type) or a multimeter to check voltages?

2) Have you tried to temporarily "roll" the hot wire from the dead circuit to another known working 15 amp breaker in the panel to see if the trouble follows or goes away?

Ask Your Own Electrical Question
Customer reply replied 8 months ago
Haven’t tried any of these. Battery dead in multimeter. Breaker is fine. Works in the place of another.
Electrician: Kevin, Licensed Electrical Contractor replied 8 months ago

1) OK, get a replacement battery for the meter and measure voltage at a dead receptacle as shown in the diagram below and let me know the 3 voltage measurements:

2) Any chance that there is a GFCI device on the circuit which may have tripped?

Ask Your Own Electrical Question
Customer reply replied 8 months ago
Won’t be able to do anything until 4am. No GFCI as the only outlets affected are in the living room of home.
Electrician: Kevin, Licensed Electrical Contractor replied 8 months ago

OK, get a battery for the meter and we can continue. Just reply back to me at the same question like you have been doing and we can take it from there.

Thanks...........Kevin

Ask Your Own Electrical Question
Customer reply replied 8 months ago
Have multitester and voltage detector
Customer reply replied 8 months ago
No voltage but no continuity either. Reading around 90 when set to 200 ohms. Voltage detector picking up something on each outlet though.
Electrician: Kevin, Licensed Electrical Contractor replied 8 months ago

1) Continuity testing is not required. I need to know the 3 voltage measurements on a dead receptacle. Refer to the diagram I sent last night.

Ask Your Own Electrical Question
Customer reply replied 8 months ago
I get nothing from any outlet going to breaker which is why I tried a continuity test after.
Electrician: Kevin, Licensed Electrical Contractor replied 8 months ago

1) I assume that the breaker hot wire to the neutral bus bar in the panel is measuring 120 volts, correct? If so, then the problem is an open hot conductor downstream of the panel.

Back out all devices on the circuit and look for any backstab wired insert connections as these are always prone to come loose and cause a failure. Device wires should always terminate to the side screws and never back-stab inserted. See diagram shown below:

Ask Your Own Electrical Question
Customer reply replied 8 months ago
One of the first things I did was replace all outlets including ones with the backstab. I also have 120v coming off breaker
Electrician: Kevin, Licensed Electrical Contractor replied 8 months ago

OK, since the breaker is good, the problem is an open hot wire downstream of the panel. Double check all splices/terminations at the devices.

Ask Your Own Electrical Question
Customer reply replied 8 months ago
Everything looked fine when replacing all outlets to breaker. I’ll have to check light fixtures and maybe even crawl space under house but I’ll have to do that tomorrow morning. 7 day work 12 hour day schedule gives me almost no time.
Electrician: Kevin, Licensed Electrical Contractor replied 8 months ago

1) Yes I understand. All depends upon how the circuit was originally routed. Circuit could have been routed thru other known working boxes that contained slices. Yes, the hot wire could also have originated from any box on the circuit such as lighting or junction boxes or switch boxes.

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 8 months ago

1) Yes I understand. All depends upon how the circuit was originally routed. Circuit could have been routed thru other known working boxes that contained splices. Yes, the hot wire could also have originated from any box on the circuit such as lighting or junction boxes or switch boxes.

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 8 months ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks.................Kevin:)

Ask Your Own Electrical Question
Customer reply replied 8 months ago
It probably won’t be until our thanksgiving break I’ll even have another chance to look things over again but other than that I didn’t find any loose wires. Just need to check wire running under house.
Electrician: Kevin, Licensed Electrical Contractor replied 8 months ago

OK, very good.

Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,416
4,416 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,196 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,416 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
2 bathrooms in a condo. 1 dedicated GFI breaker serves a 110
2 bathrooms in a condo. 1 dedicated GFI breaker serves a 110 outlet in each bathroom. No other connections on the line that we can find. Nothing plugged into the outlets. On the backside of one a new … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
I have lost power in a room to the wall outlets. (There are
I have lost power in a room to the wall outlets. (There are two). I am pushing a lot of power through them, especially a room air conditioner which might be overloading the wall outlet. I know which b… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
I had 2 outdoor outlets added a few years ago. I asked for
I had 2 outdoor outlets added a few years ago. I asked for 2 dedicated 30 amp lines with outlets that would accept a conventional plug. One breaker no longer resets. The other trips on a frequent basi… read more
Rick
Rick
Owner
High School or GED
467 satisfied customers
My basement lights and outlets are on one 15 amp circuit breaker.
My basement lights and outlets are on one 15 amp circuit breaker. I was in the basebasement about a half hour earlier and I had lights and power. I went down into the basement to turn on the lights an… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
Mike, Im new lighting and outlet circuits in my home and eliminating
Mike, I'm new lighting and outlet circuits in my home and eliminating an old fuse box. I'm experienced with residential electrical work but not with AFCI issues. I put in 2 Siemens AFCI breakers for t… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
My house has two power circuits with 15 power points on each
My house has two power circuits with 15 power points on each circuit with one safety switch covering both, On the good circuit I can use any appliance without tripping the safety switch. on the other … read more
Charles
Charles
Owner
FCC Communication License
738 satisfied customers
I installed a GFI in a bathroom that is linked to a 2nd bathroom
I installed a GFI in a bathroom that is linked to a 2nd bathroom so both outlets should be controlled by the one GFI. When I test the down stream outlet using my tester, it trips the GFI but also trip… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
I was using a curling iron that had a patch of bare wire where
I was using a curling iron that had a patch of bare wire where insulated cord was melted off. This patch came into contact with my metal sink faucet and sparks flew. I checked the breaker which was no… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
Hi, I just repalced all of my outlets and switches in the
Hi, I just repalced all of my outlets and switches in the house to the new DECROA style and now every few hours the power in the living room goes out. The breaker is not tripped and there is no GFCI o… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
I have a 2 pole 20amp breaker for the kitchen. One pole(switch)
I have a 2 pole 20amp breaker for the kitchen. One pole(switch) is dedicated only for the refrigerator. The other pole (switch) is for the outlets in the kitchen. Starting yesterday when just using on… read more
electrifier
electrifier
Master Electrician
Bachelor's Degree
1,458 satisfied customers
I have two bedrooms on one electric line. last week we plugged
I have two bedrooms on one electric line. last week we plugged in an iron and curling iron and it shorted the line. the circuit breaker never flipped, and one bedroom remained powered. this week I sta… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
my breaker tripped last night and when I try to reset it it
my breaker tripped last night and when I try to reset it it keeps tripping. I have switched breakers and still the same. I have checked outlets for obvious signs of a problem but no luck. What can I d… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
A couple of years ago, I had my old house 100% rewired. I
A couple of years ago, I had my old house 100% rewired. I am dismayed, though, that when I plug an iron into the TV room outlet, or the bedroom outlet, to have the ceiling lights dims. Shouldn't a cir… read more
Sir Sparks
Sir Sparks
Owner
State & UK Certified Master electri
2,519 satisfied customers
I just bought an Infrared Sauna The requirement was 120v but
I just bought an Infrared Sauna The requirement was 120v but the circuit keeps throwing about 10 minutes into heat up. I am not sure what the problem could be. There is nothing else drawing on the lin… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
i have a 20 amp line that feeds 2 bath recpts. station A on
i have a 20 amp line that feeds 2 bath recpts. station A on the line is 20 amp GFCI. Whenever a hair dryer is used in A, it will run for a couple of min. & then trip the breaker. Any ideas?… read more
Glenn
Glenn
Maintenance, Technician
Associate Degree
1,612 satisfied customers
My electrical service (200 amp) was out for 18 hours ...
My electrical service (200 amp) was out for 18 hours and when it came back on, one of the circuits still had no power. I know what breaker is in that circuit and I have tried to reset it a number of t… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
i turned the light on in bathroom this morning and the light
i turned the light on in bathroom this morning and the light blew. i later noticed that a part of my house had no power. i checked my circuit breaker and all the curcuits were still in the on position… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
I have a circuit breaker with a 15 & a 20 amp switch. the 15
I have a circuit breaker with a 15 & a 20 amp switch. the 15 trips. two ceiling fans are not working a a couple of outlets. I have removed the fans from the circuit (open) and one outlet, but the circ… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x