I have an EcoSmart Eco 27 tankless water heater that runs…

Customer Question
I have an EcoSmart Eco...
I have an EcoSmart Eco 27 tankless water heater that runs off 3 double-pole 40A breakers. The 40A breakers are on a subpanel that’s fed by a double-pole 125A breaker on my main panel. About a week ago, the 125A breaker began to trip when we ran hot water. I’ve ordered a new double-pole 125A breaker and will install it when it arrives. However, both yesterday and today, other separate single-pole breakers have tripped under minimal use on those circuits (yesterday it was two breakers, today it was four). Besides the possibility that all of these breakers need replacing at the same time, what could be the issue? BACKGROUND: As far as I know, this electrical panel is 30 years old. It is labeled as a GE Load Center Type 1 Indoor Enclosure TM2420WF Mod 8.
Submitted: 8 months ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 5 minutes by:
11/12/2017
Electrician: WCohn, Construction Worker replied 8 months ago
WCohn
WCohn, Construction Worker
Category: Electrical
Satisfied Customers: 1,709
Experience: Been in contruction 18+years
Verified

Hello, my name is ***** ***** I look forward to helping you!

Ask Your Own Electrical Question
Electrician: WCohn, Construction Worker replied 8 months ago

My first guess is one of the elements in the water heater is blown and grounding out

Ask Your Own Electrical Question
Customer reply replied 8 months ago
I should have stated...I’ve already troubleshooted the water heater with the help of an EcoSmart technician over the phone with my multimeter. That problem was narrowed down to the 125A breaker. However, now, I’m considering there may be something wrong with the electrical panel itself, since I have other breakers tripping now under low use on those circuits. AND, this has never happened before in the three years we’ve lived here. But, all of a sudden, in the last week, we’ve had problems on 5 different circuits (1 double-pole 125A and 4 single-pole 15A).
Electrician: WCohn, Construction Worker replied 8 months ago

I would look for some wiring grounding out in the panel or on the bus connections. You may need an electrician to safely troubleshoot this.

Ask Your Own Electrical Question
Electrician: George Smith, Master Electrician replied 8 months ago
George Smith
George Smith, Master Electrician
Category: Electrical
Satisfied Customers: 444
Experience: Superintendent at Electrical Solutions and Data
Verified
Hi this George can I help you?
Ask Your Own Electrical Question
Electrician: George Smith, Master Electrician replied 8 months ago
Do you have a amp probe
Ask Your Own Electrical Question
Electrician: George Smith, Master Electrician replied 8 months ago
After 30 years most of your breakers could be tripping at lower rating than manufacturer specs!
Ask Your Own Electrical Question
Customer reply replied 8 months ago
I have this multimeter, so I think so: Klein MM100 (http://www.kleintools.com/catalog/discontinued-products/manual-ranging-multimeter)
Customer reply replied 8 months ago
That may be so, but for that many to start tripping in the same week?
Electrician: George Smith, Master Electrician replied 8 months ago
Are you capable of testing them?
Ask Your Own Electrical Question
Electrician: George Smith, Master Electrician replied 8 months ago
I'm trying look for your tester?
Does it have a clamp on amp probe
Ask Your Own Electrical Question
Customer reply replied 8 months ago
With some instruction, I can. However, I’m not at home right now, so it will have to be in a couple hours.
Customer reply replied 8 months ago
It’s the only one I see at the link I provided above.
Electrician: George Smith, Master Electrician replied 8 months ago
Ask Your Own Electrical Question
Electrician: George Smith, Master Electrician replied 8 months ago

Is this in a commercial building?

Ask Your Own Electrical Question
Customer reply replied 8 months ago
No, just my house.
Electrician: George Smith, Master Electrician replied 8 months ago

You have 3 phase in your house?

Ask Your Own Electrical Question
Electrician: George Smith, Master Electrician replied 8 months ago

sorry I misread your post !!

Ask Your Own Electrical Question
Electrician: George Smith, Master Electrician replied 8 months ago

I would try replacing a few of the breakers that are tripping first?

Inspect the panel and see if you can see anything obvious.

If that don't work an electrician needs to inspect your your panel .

Ask Your Own Electrical Question
Electrician: George Smith, Master Electrician replied 8 months ago

FYI breakers don't last forever !

Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask George Smith Your Own Question
George Smith
George Smith
George Smith, Master Electrician
Category: Electrical
Satisfied Customers: 444
444 Satisfied Customers
Experience: Superintendent at Electrical Solutions and Data

George Smith is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,196 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,345 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
Need help sizing a generator. A few days. I already have a
I already have a generator and subpanel, but looking to upgrade… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
I need to run a 100 AMP sub panel to an attached garage from
I need to run a 100 AMP sub panel to an attached garage from my 200 AMP main Panel. Trying to figure correct gauge for the wire to feed the box. Also please note I have a 200 AMP breaker at the meter … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,345 satisfied customers
I'm installing a subpanel in my basement to feed my finished basement, planning to us
I'm installing a subpanel in my basement to feed my finished basement, planning to use an EATON 125A main lug panel and I'm trying to determine the breaker size and wire size needed to connect to my m… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
I want to install a 125A sub panel for my new Tank less water
I want to install a 125A sub panel for my new Tank less water heater. What breaker do I need in the main breaker box and what size wire. Specs 2 double pole 40 amp breakers to run Heater at Unit runs … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
Hello, I've installed a Ecosmart 27 tankless water heater. http://www.ecosmartu
Hello, I've installed a Ecosmart 27 tankless water heater. http://www.ecosmartus.com/products/electric-tankless/eco-24-eco-27.aspx It required 3 x 40amp circuits. I used #8 wire. When it kicks in (wit… read more
Rick
Rick
Owner
High School or GED
467 satisfied customers
Have a old converted stone barn with two apartments fed by
Have a old converted stone barn with two apartments fed by a 1950's service upgrade overtop two existing circut panels. Newer 24 circuit panels infront of old ones. First panel has main circuit and a … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
I am purchasing a 240 volt water heater and do not have any
I am purchasing a 240 volt water heater and do not have any room left in my small panel for a double pole breaker. Would it be possible for me to pick up hots from two separate 120 volt receptacles an… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
i am running a 220 volt line to a hot tub. Im running it off
i am running a 220 volt line to a hot tub. I'm running it off a subpanel in my work shop. I am installing a service disconnect/gfci between the subpanel and the hot tub. I do not how the subpanel is g… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
I have a barn with a subpanel it it. At the main panel there
I have a barn with a subpanel it it. At the main panel there only 2 unidentified breakers left. They are not ganged and operate separately. The wiring appears to come from a cable the appears to leave… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
My Load Center / Mani Breaker Box has the space for a main
My Load Center / Mani Breaker Box has the space for a "main breaker", but it doesn't have one! How can I add a main breaker to my GE Load Center Flush Type TL2015F ? How do I know what is the amperage… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
I have just wired my garage for lights and outlets and installed
I have just wired my garage for lights and outlets and installed a 100 amp breaker box to work from! Three junction boxes have been placed between the new breaker box and the outlets, lights, and wher… read more
Mike
Mike
Master Electrician
Working on MBA
1,426 satisfied customers
I have an Old Square D QO N-20-412 Main Service Panel. On
I have an Old Square D QO N-20-412 Main Service Panel. On the inside it states: 125a Mains. Inside the panel on are (4) dual Pole Breakers, (2) top Left, (2) top right. Top Left is a 60amp and has two… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
I need three additional circuits and breakers - two 15 amp
I need three additional circuits and breakers - two 15 amp and 20 amp. I thought there were extra cb slots in an expansion power panel that was installed during last major renovations as there were kn… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
I am running power to a subpanel for my detached garage. I
I am running power to a subpanel for my detached garage. I will need about 40 amps. Will a tandem breaker be able to supply enough power for my garage?… read more
Mike
Mike
Master Electrician
Working on MBA
1,426 satisfied customers
Trouble shooting a Sport Court lighting problem. Customer has
Trouble shooting a Sport Court lighting problem. Customer has 7 lights standards with 1 - 1,000wt metal halide bulb in each. There is 1 small subpanel with a double 30a breaker in it. There are 4 - #1… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
I have installed a sub panel for a swim spa and a outdoor kitchen
I have installed a sub panel for a swim spa and a outdoor kitchen I used a 60amp gfi breaker at the main panel to power up sub panel, the sub panel has 3 -15amp 2 pole 240 breakers 1 for each pump and… read more
Rich
Rich
Master Electrician
Vocational, Technical or Trade Scho
1,117 satisfied customers
Have a 12-2 breaker box that I am just installing in a workshop
Have a 12-2 breaker box that I am just installing in a workshop to establish initial power to building. Cannot figure out where the ground wire goes in the breaker box, when I start the interior wirin… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
we ran a 220v feed to our electric oven, rated at 40 amps.
we ran a 220v feed to our electric oven, rated at 40 amps. 6/3 bx cable was used and terminated at a 3 prong outlet behind the stove. Question, at the service panel, we had to take a feed off of 2 sep… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x