I plugged in a coin operated washing machine that the coin…

Customer Question
I plugged in a...

I plugged in a coin operated washing machine that the coin box had been removed and as soon as I did I lost all power except one light. What could of happened

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

3 or 4 days. I've tested all connection in breaker box and says I got power but I got nothing

Contractor's Assistant: Do you plan on doing the work yourself?

Of course unless it's something I can can't handle

Contractor's Assistant: Anything else we should know to help you best?

Not that I can think of

Submitted: 10 months ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 2 minutes by:
10/7/2017
Electrician: Kevin, Licensed Electrical Contractor replied 10 months ago
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,474
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC General Class License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) Is the receptacle a 120 volt receptacle? If so, have you tried plugging in a lamp or a portable radio into the receptacle to confirm if it has power?

2) Do you have a 2 wire lead AC voltage tester (a contact type) or a multimeter to check voltage at the receptacle?

Ask Your Own Electrical Question
Customer reply replied 10 months ago
It's not just one plug in its my whole house almost. A few plug ins work but thats it. I had a battary charger plugged in when it happened. Yes I have a voltage meter
Electrician: Kevin, Licensed Electrical Contractor replied 10 months ago

OK, thanks for confirming.

1) You will need to remove the door from the electrical panel. Set your meter to the AC voltage setting @ 300 volts and measure across the 2 hot phases at the main circuit breaker. Can you measure approx 240 volts?

2) Next step is to leave the main breaker in the ON position and reset the meter setting to the 200 volt range. Place 1 meter probe to the neutral bus bar (where the white neutral wires are terminated) and the 2nd meter probe to 1 of the hot phases at the main breaker. Can you measure approx 120 volts? Next is to move the meter lead over to the other hot wire phase on the main breaker and measure for approx 120 volts.

Let me know the results and we can continue..........Thanks..........Kevin

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 10 months ago

1) What were the voltage measurements?

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 10 months ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks.................Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 10 months ago

Any other questions?

Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,474
4,474 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC General Class License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,290 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,474 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC General Class License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I do power line work but I'm baffled at what happened the
I do power line work but I'm baffled at what happened the other day at my Father and laws house. He has a 2 story house fed by a overhead transformer that has 4/0 aluminum going to breaker box At hous… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
I planned on replacing my ceiling fan and began by mapping
I planned on replacing my ceiling fan and began by mapping my circuit breaker to turn off the correct room. Surprisingly, NONE of the breakers turned my ceiling fan off. So, I opted to flip my main br… read more
ProGrade
ProGrade
Electrical Contractor
564 satisfied customers
I just moved into a rental with brand new seemingly not
I just moved into a rental with brand new seemingly not professionally installed wiring. Beyond a few items of concern, my main question is about the wiring to the washer/dryer. After being ran for ab… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
I have installed a fan/heater in my bathroom. Actually replacing
I have installed a fan/heater in my bathroom. Actually replacing like for like. There are 4 switches for this fan. Heater, Vent, light, and night light. All switches test out to 120 volts down stream … read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
Some but not all of the circuits in my home have lost power
Some but not all of the circuits in my home have lost power a few times without tripping the breaker. I reset all of the breakers anyway, (in case they were tripped even though they didn't appear to b… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
On my cerciut box the breaker that controls some sockets and
hi! on my cerciut box the breaker that controls some sockets and lights works from the box,the junctions in the basment but i keep getting nothing at the switches and one gives a reading of 240 when i… read more
mrromex
mrromex
field supervisor
5 years of college courses
281 satisfied customers
Heres a really weird one. I live in a 40 year old double
Here's a really weird one. I live in a 40 year old double wide mobile home. It still has the old aluminum wiring, but I've corrected connections when necessary using IDEAL NOALOX Anti-Oxidant compound… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
Need help resetting a tricky breaker. Please read details.
I'm having trouble resetting the breaker switch, something that I have easily done in the past at other residences with no trouble. It is only one part of the house that has lost power. Here are the d… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
My condo lost power in all areas except the refrigerator, I
My condo lost power in all areas except the refrigerator, I turned off all breakers waited for about 10 or 15 minutes and reset the breakers. The power came back on and stayed on. Two days later the s… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
Okay... so have three kids at home. Left for about an hour
Okay... so have three kids at home. Left for about an hour (grandpa and uncle were home with kids). Came back and found electric in basement part way off. Refrigerator, ice maker and oven all off. Tri… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
The second floor of my townhouse has no electricity, checked
The second floor of my townhouse has no electricity, checked the breakers and they are on, turned them on and off and still nothing. A couple of the breakers have a test button, tried them but nothing… read more
Alex
Alex
Owner
Bachelor\u0027s Degree
1,783 satisfied customers
Why does only a few of my outlets work and not others Eclictricity
Why does only a few of my outlets work and not others? Eclictricity went off but no breaker triped, replaced a bedroomsbreaker and it just got worse, nothing on bathroom, and all… read more
Mike
Mike
Master Electrician
Working on MBA
1,426 satisfied customers
Im trying to install a new light above my bar. My condo has
I'm trying to install a new light above my bar. My condo has a switch already wired, that is live (I only know this because I just electrocuted myself taking it out). Inside the box are 4 white wires … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
ive just aquired a vertical sun bed with 20 tubes... it has
ive just aquired a vertical sun bed with 20 tubes... it has 2 normal 3 pin plugs which both operate 10 tubes each.... but after about 4 mins it trips the main electrics out on my fuse box.... is there… read more
Sir Sparks
Sir Sparks
Owner
State & UK Certified Master electri
2,519 satisfied customers
I have a circuit showing 120v on the multimeter tested at the
I have a circuit showing 120v on the multimeter tested at the outlets but no appliances will operate. It was operating fine until just recently.… read more
electrifier
electrifier
Master Electrician
Bachelor's Degree
1,458 satisfied customers
One of my outside plugs got wet. Now the upstairs lights and
One of my outside plugs got wet. Now the upstairs lights and outlets in the master bathroom and the outlets in the 2nd bathroom. The 2nd bathroom lights didn't come on at first, but eventually did. I'… read more
Alex
Alex
Owner
Bachelor\u0027s Degree
1,783 satisfied customers
I have an LG dryer that has been working fine and is only 3
I have an LG dryer that has been working fine and is only 3 months old. It's electrical, 4-prong outlet, dual circuit breaker, 240v. All of a sudden, it's now not working. When I open the door, the li… read more
Sir Sparks
Sir Sparks
Owner
State & UK Certified Master electri
2,519 satisfied customers
Came home and some of my lights and outlets are not working
Came home and some of my lights and outlets are not working (kitchen/bath/laundry). At the breaker box I saw nothing tripped but these areas have gfci breakers. I tried to test them by pushing in the … read more
Sir Sparks
Sir Sparks
Owner
State & UK Certified Master electri
2,519 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.