Wiring 240 garage heater with 10/3 wire and double pole

wiring 240 garage heater...

wiring 240 garage heater with 10/3 wire and double pole 30anp breacker

Contractor's Assistant: How old is the system in question? And have you consulted an electrician yet?

Brand new and he is due in but the wires in heater are tagged 1234

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

It's a dimplex euh-b unit

Show More
Show Less
Ask Your Own Electrical Question
Answered in 2 minutes by:
9/22/2017
ProGrade
ProGrade, Certified Electrical Contractor
Category: Electrical
Satisfied Customers: 565
Experience: 28+ years exp. - installation, troubleshooting, & repair of commercial, & residential electrical systems.
Verified

Welcome.

Is there a wiring diagram on the unit?

If so could you share a picture of it with me?

Thank you

Ask Your Own Electrical Question

...and thanks for becoming a member

Ask Your Own Electrical Question
Customer reply replied 5 months ago
there is on the inside panel of the unit and not sure how to send it to you

Thanks, ***** ***** take a picture on your phone in this chat box use the paperclip icon to attach the picture and send it

Ask Your Own Electrical Question

From what I can find on the Dimplex website it appears that your line conductors should connect two terminals labeled L1 and L2 with the bare ground wire connect him to the Ground Terminal

Ask Your Own Electrical Question
Customer reply replied 5 months ago
1 and 2 are red and black with 3and4 to nuetrral and ground to case?

Normally a 240 unit would not require the white/neutral.

...not sure unless I can see the wiring diagram or find it online.

Do you see any additional model number information?

Ask Your Own Electrical Question

...and do you see a kW Rating on the unit?

Ask Your Own Electrical Question

Thank you...looking at the pictures...

Ask Your Own Electrical Question

Very good, that is the same diagram that I found online and note it says online 3 that it is optional. Line 3 would only be used on a 3-phase circuit so in your case nothing connects to L3

I verified, use black & white wires, one to L1 terminal & one to L2 terminal (it does not matter which goes where, they are interchangeable on single-phase power) then bare to ground screw.

Note: your circuit, a #10 on a 30A Breaker is only good for a unit rated not more than 5.5 kW.

Ask Your Own Electrical Question
Customer reply replied 5 months ago
peak on this unit is4kw so should be good and so I only needed 10-2 instead of 10-3 is what I am hearing?

That is correct. If you have 10/3, use the black & red for L1 & L2 bare for ground and cap off the white.

Yes, for 4kW you are good.

ProGrade
ProGrade, Certified Electrical Contractor
Category: Electrical
Satisfied Customers: 565
Experience: 28+ years exp. - installation, troubleshooting, & repair of commercial, & residential electrical systems.
Verified
ProGrade and 87 other Electrical Specialists are ready to help you
Ask your own question now
Customer reply replied 5 months ago
Thank you so much

You are welcome, glad to be of assistance, that's what we do.

You can save me (Prograde) as your favorite expert for this category and ask for me next time you have an electrical question.

Please rate my service before leaving the site.

I will leave the question open in case something else comes up while you are working on this.

Ask Your Own Electrical Question

Thank you very much for the excellent rating. I appreciate it.

Good luck with your project.

Ask Your Own Electrical Question
Was this answer helpful?
Ask ProGrade Your Own Question
ProGrade
ProGrade
ProGrade, Certified Electrical Contractor
Category: Electrical
Satisfied Customers: 565
565 Satisfied Customers
Experience: 28+ years exp. - installation, troubleshooting, & repair of commercial, & residential electrical systems.

ProGrade is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I'm having difficulty reconnecting four wires - red,,
Hi Michael, I'm having difficulty reconnecting four wires - red, white, yellow, blue - to my Sears Model 746 doorbell. I have both front and rear doorbell buttons. The circuit board shows screw-connec… read more
George Smith
George Smith
Vocational, Technical or Trade School
365 satisfied customers
Having an issue with wiring on an older home. A wire is
Having an issue with wiring on an older home. A wire is hanging from a Gas line and when the aluminum dryer vent touched that pipe it sparked … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Need to wire my food truck outlet on the outside of the
hello, need to wire my food truck outlet on the outside of the truck. I have a 30 amp breaker box... The outlet on the outside of the truck caught on fire because of the way he wired it lol - needless… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Wires from double pole breaker:red,,black and blue. Wires
Wires from double pole breaker:red,white,black and blue. Wires from hot water heater black and red only. How to I connect ? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I'm wiring a. Im wiring the control circuits for a Fire Pump
Im wiring the control circuits for a Fire Pump ,, methods for a raceway include LFMC.. is there a Lendth restriction on this LFMC … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have a 3 wire kitchen light fixture and a 2 wire
i have a 3 wire kitchen light fixture and a 2 wire electrical box. I know i need to connect the white with white and the black with black but do i need to connect the green wire from the light fixture… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have three black wires and three wires I don't remember
I have three black wires and three white wires I don't remember how the light switch was wired so far I have capped all three white wires and I found my hot wire but now the outlet next to the light s… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I'm trying to wire up a dimmer...I have 2 black wires in the
I'm trying to wire up a dimmer...I have 2 black wires in the box, a green ground and 2 white wires...how do I connect the dimmer? … read more
George Smith
George Smith
Vocational, Technical or Trade School
365 satisfied customers
I have 3 wires and 3 black wires, and I'm trying to hang a
I have 3 white wires and 3 black wires, and I'm trying to hang a kitchen light I can't seem to get it to work. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have 2 black wires, 2 capped together wires., and two
I have 2 black wires, 2 capped together white wires., and two copper wires that are tied together but not plugged into anything. We are trying to wire a motion sensor that has 1 black, 1 red, and 1 ye… read more
George Smith
George Smith
Vocational, Technical or Trade School
365 satisfied customers
I have a purple wire, a yellow, wire and grey wire and need
I have a purple wire, a yellow, wire and grey wire and need help installing a fan … read more
Sam I
Sam I
Electrician
B.S.
482 satisfied customers
I need to wire a 2 speed fan ( red, white, and black wire)
I need to wire a 2 speed fan ( red, white, and black wire) to a 6 pin carling or rocker switch that is ON-OFF-ONI want one side of the on to go to the low and the other to the high switch..Can send pi… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Fan with light kit white wire, blue wire and black wire. Try
Fan with light kit white wire, blue wire and black wire. Try to connect to three way switch wires to ceiling box are white, red and black. … read more
Sam I
Sam I
Electrician
B.S.
482 satisfied customers
Need to wire a 240 volt single phase 3 wire motor. Just
the motor has 2 connections for the hot wire and also has a common… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have 3 black wires and 3 wires and 1 coming out of
I have 3 black wires and 3 white wires and 1 white coming out of electrical outlet, how t … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have a sauna that is wired with 240 two wire for load (red
I have a sauna that is wired with 240 two wire for load (red and black) and a ground -- the neutral line (white) is not used -- currently it is not on a GFI and I would like to put it on a GFI - I wou… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
TROUBLE WIRING A LEVITON 6683. I HAVE ONE HOT WIRE BLACK/
I AM HAVING TROUBLE WIRING A LEVITON 6683. I HAVE ONE HOT WIRE BLACK/ WHITE /GROUND. I AM TRYING TO WIRE 2 /6683 SWITCHES OFF THIS WIRE TO GO TO DIFFERENT LIGHTS … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Had broken wire from outside breaker. changed wire to
had broken wire from outside breaker. changed wire to copper. 60 amp breaker trips when power is turned back on. disconnect wire on 60 amp wire and still have voltage in disconnected wire … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x