I have a junction box with Al wiring. One Black One Red and…

I have a junction box...
I have a junction box with Al wiring. One Black One Red and a stranded bare common. It used to have a drop in stove. I wish to change over to a new slide in stove with a 3 prong plug. Can I put a flush mount outlet here without a separate ground, using the bare aluminum common as ground?
Show More
Show Less
Ask Your Own Electrical Question
Answered in 6 minutes by:
9/14/2017
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,349
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) How many amps doe the new stove require?

2) What is the conductor size of the Aluminum wires in AWG?

3) Is the existing aluminum wiring a cable or wired with metal conduit or other?

Ask Your Own Electrical Question
Customer reply replied 9 months ago
New stove is standard amperage for oven stove. It is obviously 220V. The wires are 6guage AL. The previous stove was built in, originally from the 1970's, and had a wire to the junction box on the wall, that was in conduit and had a separate ground, neutral and two hots.
Customer reply replied 9 months ago
Dont want to rewire the junction box to include a separate ground but rather put in a stove flush mount outlet, using the 3 wires in the box, if possible.

Thanks for the replies.

1) There is no standard amperage on any stove. Amp ratings can range anywhere from 20 to 50 amps. I need to know the required amps for the new stove. Look at the specs or the nameplate label for the rating or provide me with the wattage rating on the new stove? 6 AWG aluminum is rated for a maximum of 40 amps.

2) I'm confused on the existing wiring. You originally mention you only have 1 black, 1 red and 1 stranded bare. Now you mention the wiring was installed in conduit and you have 4 separate wires.

Which is it? 3 or 4 wires? And are the house wire installed in metal conduit all the way from the panel to the wall box?

Ask Your Own Electrical Question
Customer reply replied 9 months ago
40 amp stove. The junction box has 3AL wires. The whip going to the stove was in conduit and had 4. Now want to just plug brand new stove in wall with plug it comes with. How to wire?
Customer reply replied 9 months ago
No conduit to panel, just outside of wall.

Thanks for confirming.

1) Since you only have 3 conductors, you will need a 40 amp double pole breaker and a NEMA rated 10-50R 3 prong receptacle. They don't manufacture a 40 amp receptacle. Code allows you to increase to the next higher receptacle size using 50 amps.

2) You will also require a 50 amp rated 3 prong NEMA rated 10-50P cord. At the rear of the stove, bond the cord neutral conductor to the stove green ground screw located on the stove frame and to the middle neutral terminal screw. Install either the metal bonding strap or an 8 AWG copper jumper wire from the stove neutral terminal screw to the stove green ground screw.

See attached diagrams:

Ask Your Own Electrical Question
Customer reply replied 9 months ago
Are u there

Yes I am. What is your question?

Ask Your Own Electrical Question
Customer reply replied 9 months ago
read above

I can only see your original reply and then I replied back with an answer. If you replied back to me, I don't see anything.

Ask Your Own Electrical Question
Customer reply replied 9 months ago
Can you hear me now? my apologies

I see that you opted me out. I have also opted out of the question. Perhaps another expert can better assist you.

Your question will be placed back to the expert pool and another expert will most likely pick up your question.

No need to reply back to me.

Ask Your Own Electrical Question
Customer reply replied 9 months ago
Didnt opt out. My apologies, cant see answer.
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,239
Experience: Proven Professional 49 years Experience
Verified

Hi, I'm Mike G and I'll be assisting you. You should install a 3 wire 50A receptacle with a 3 wire cord set to the unit. The connections in the range are as follows.

  1. Red and black to the outside terminations on the block.
  2. White wire to the center termination with a jumper to the frame for a ground

The diagram Kevin gave you will show the above.

The receptacle will have the bvlack and red to the outside terminations and the bare ground to the center.

Ask Your Own Electrical Question

Let me know if that helped.

Ask Your Own Electrical Question
Customer reply replied 9 months ago
Is this ground good enough on the frame of the stove? What if there is a large liquid spill on the frame. Will I need a better ground than the bare common wire? Does it need to be grounded to the panel?

An existing 3 wire circuit is allowed to remain by code. The bare wire is a neutral and a ground. At the range a bonfing jumper is all that is needed. The size can be a #10 copper wire or you may find a jumper in the range when you wire it.

Ask Your Own Electrical Question
Customer reply replied 9 months ago
Thank You Very Much Mike G and Kevin as well.

Anytime, you're welcome.

Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,239
Experience: Proven Professional 49 years Experience
Verified
Mike G. and 87 other Electrical Specialists are ready to help you
Ask your own question now
Was this answer helpful?
Ask Mike G. Your Own Question
Mike G.
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,239
8,239 Satisfied Customers
Experience: Proven Professional 49 years Experience

Mike G. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,239 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,349 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I had to remove the wire from the plug from one junction box
I had to remove the wire from the plug from one junction box to another but forgot to take a picture of it before I unwired it. I did however label what 3 wires were connected together with some paint… read more
Mike G.
Mike G.
Master Electrician
8,239 satisfied customers
I'm trying to branch 120v off of a 220 junction box outside
I'm trying to branch 120v off of a 220 junction box outside that serves my ac unit. Shouldn't I be able to pull 120 off of one of the hot legs? I'm trying to wire a temp rv box but I'm getting 220 off… read more
Kevin
Kevin
Licensed Electrical Contractor
4,349 satisfied customers
How do I trace a dead wiring circuit in my house? The outlet
How do I trace a dead wiring circuit in my house? The outlet has gone dead and there is no power to the outlet, but the breaker did not trip. … read more
Kevin
Kevin
Licensed Electrical Contractor
4,349 satisfied customers
I live in a mobile home with aluminum wires. We just
I live in a mobile home with aluminum wires. We just switched over to smart meter service. Would this affect the current running through my trailer? why because I use to be able to run a portable heat… read more
Mike G.
Mike G.
Master Electrician
8,239 satisfied customers
Underground conduit cover" First time. Depth of conduit.
depth of conduit. table 300.5 measures from the top of conduit to top of finish surface and the inspector measures from top of the conduit to the bottom of the concrete slab. wish is correct?… read more
Kevin
Kevin
Licensed Electrical Contractor
4,349 satisfied customers
I'm building a detached shop and need to get conduit in the
I'm building a detached shop and need to get conduit in the ground for the shop electrical panel. I have a 200amp main panel in the house that is about 50 ft away from where the shop panel will be. … read more
Sam I
Sam I
Electrician
B.S.
730 satisfied customers
What type of wire does PG&E require to be buried in conduit?
what type of wire does PG&E require to be buried in conduit? The Distance would be close to 400' Will a single wire be able to go that distance or will I need a secondary? How many wires will be in th… read more
Mike G.
Mike G.
Master Electrician
8,239 satisfied customers
Need to wire my food truck outlet on the outside of the
hello, need to wire my food truck outlet on the outside of the truck. I have a 30 amp breaker box... The outlet on the outside of the truck caught on fire because of the way he wired it lol - needless… read more
Mike G.
Mike G.
Master Electrician
8,239 satisfied customers
Is it permissible to run romex wire through conduit indoors
Is it permissible to run romex wire through conduit indoors and in a dry location? … read more
Mike G.
Mike G.
Master Electrician
8,239 satisfied customers
I have aluminum wiring & need a new water heater. Can I get
I have aluminum wiring & need a new water heater. Can I get one installs without … read more
Kevin
Kevin
Licensed Electrical Contractor
4,349 satisfied customers
I havea line into junction box and 14-3goingout to switch
I havea line into junction box and 14-3goingout to switch and also wire goingout to light . all grounds are connected. when I connect hot wire to black in the 14-3 ,tester shows about 5 volts in both … read more
Kevin
Kevin
Licensed Electrical Contractor
4,349 satisfied customers
I am looking for installation instructions for junction box
I am looking for installation instructions for junction box # BH614R … read more
Sam I
Sam I
Electrician
B.S.
730 satisfied customers
My house is older and has aluminum wiring. I'm having some
My house is older and has aluminum wiring. I'm having some difficulty getting a new light fixture to light. It's a problem that I have not experienced here before.… read more
Kevin
Kevin
Licensed Electrical Contractor
4,349 satisfied customers
IF YOU SPLISE A WIRE DO YOU INSTALL A JUNCTION BOX. JUST NOW
IF YOU SPLISE A WIRE DO YOU INSTALL A JUNCTION BOX … read more
Mike G.
Mike G.
Master Electrician
8,239 satisfied customers
Mounting of junction box in wet location...outside...how
Mounting of junction box in wet location...outside...how high off of the ground does the weatherproof box need to be mounted. Is there a code requirement?… read more
Mike G.
Mike G.
Master Electrician
8,239 satisfied customers
I would like to convert a wall outlet to a junction box so I
I would like to convert a wall outlet to a junction box so I can add power to the room behind the current wall outlet....I have already removed the wall plate and can see that there are currently 2 wi… read more
Mike G.
Mike G.
Master Electrician
8,239 satisfied customers
When I purchased my home, it had aluminum wiring in it. So
When I purchased my home, it had aluminum wiring in it. So we had the copalum crimping treatment done to the whole house. Now we want to add a few more outlets & lights and I wonder if we need the sam… read more
Mike G.
Mike G.
Master Electrician
8,239 satisfied customers
I need help to Hard wire a nanny cam inside the junction box
I need help to Hard wire a nanny cam inside the junction box of a wall outlet. My problem is that the nanny camera camera only has 2 wires (black and white). On the other hand, the wall outlet has 5, … read more
Sam I
Sam I
Electrician
B.S.
730 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x