Electrical

Electrical Questions? Ask an Electrician Online.

Ask an Expert,
Get an Answer ASAP!

Electrical
This answer was rated:

I have a 220V pool pump connected to a receptacle(L520RCCV3…

I have a 220V...

I have a 220V pool pump connected to a receptacle(L520RCCV3 twist lock) that supports 220V. I want to put a switch right above the receptacle using 1/2" SCH 40 conduit. The wires coming to the receptacle from the breaker panel are white, black and green. I know the black goes to the brass screw on the receptacle, the white to the silver screw and the green ground wire to the green screw. How do I connect the on/off switch to the receptacle? I have 12 gauge Romex cable to hook up the switch.

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Just started the project.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes.

Contractor's Assistant: Anything else we should know to help you best?

I have a Hubbell Taymac weather cover for the receptacle and a Hubbell Taymac plastic toggle cover for the switch.

Show More
Show Less
Ask Your Own Electrical Question
Answered in 5 minutes by:
9/14/2017
ProGrade
ProGrade, Certified Electrical Contractor
Category: Electrical
Satisfied Customers: 565
Experience: 28+ years exp. - installation, troubleshooting, & repair of commercial, & residential electrical systems.
Verified

Welcome.

Remove the black from the outlet, lengthen it by adding black wire with a wire nut to reach one side of your switch (it does not matter which terminal on the switch this wire connects to).

With another length of black wire, connect it to the other terminal on your switch then connect the other end of this wire to the terminal on your outlet that you removed the black wire from.

Add a ground wire to the switch and test that it works.

Let me know if you have any questions.

Ask Your Own Electrical Question
Customer reply replied 5 months ago
Ok, I wired as instructed, but before I test it, I have a question about the ground wire on the switch. Where does the other end of the ground get connected? To the green ground on the receptacle?

Yes, connect the ground wire to the switch to the ground in the outlet.

Simplest method is the disconnect the ground from the outlet add a 6-inch pigtail and the wire going up to the switch to the existing ground all under one wire nut. So, you would have three ground wires under one wire nut - the ground coming in the 6 in pigtail that you will then connect the other end of to the outlet and the wire going up to the switch.

Please let me know if you have any other questions thank you

ProGrade
ProGrade, Certified Electrical Contractor
Category: Electrical
Satisfied Customers: 565
Experience: 28+ years exp. - installation, troubleshooting, & repair of commercial, & residential electrical systems.
Verified
ProGrade and 87 other Electrical Specialists are ready to help you
Ask your own question now
Was this answer helpful?
Ask ProGrade Your Own Question
ProGrade
ProGrade
ProGrade, Certified Electrical Contractor
Category: Electrical
Satisfied Customers: 565
565 Satisfied Customers
Experience: 28+ years exp. - installation, troubleshooting, & repair of commercial, & residential electrical systems.

ProGrade is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I'm trying to replace a light switch with a switch outlet
I'm trying to replace a light switch with a switch outlet combo. The old switch has 3 Romeo coming in. How do I wire up the new outlet/switch combo? … read more
George Smith
George Smith
Vocational, Technical or Trade School
365 satisfied customers
When using a metal conduit body such as an LB, or capped L
When using a metal conduit body such as an LB, or capped L at an enclosure does that fitting need to be supported other than with the nipple into the enclosure? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
What are the construction requirements for a new conduit
What are the construction requirements for a new conduit installation to an existing building? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
What type of wire does PG&E require to be buried in conduit?
what type of wire does PG&E require to be buried in conduit? The Distance would be close to 400' Will a single wire be able to go that distance or will I need a secondary? How many wires will be in th… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Can i place an outlet beyound a gfi outlet by connecting to
can i place an outlet beyound a gfi outlet by connecting to the gfi?? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Is it permissible to run romex wire through conduit indoors
Is it permissible to run romex wire through conduit indoors and in a dry location? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have a half hot outlet and want to make both outlets hot.
I have a half hot outlet and want to make both outlets hot. I have two black wires going into the top outlet, which is always hot, and two red wires going into the bottom outlet, which is hot when the… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Have one room 2nd floor. 4 wall outlets and a light switch
Have one room 2nd floor. 4 wall outlets and a light switch in closet. Quit working. Utilizing a shop vac, drywall sander in 2 different outlets. Just quit. Breakers not blown. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I am trying to add a power outlet to wall. The light switch
I am trying to add a power outlet to wall. The light switch above it has 2 wires(black and white) and ground. I was told to run black wire from outlet to switch and leave black wire attached the switc… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have a half switched outlet that need to be changed. I
i have a half switched outlet that need to be changed. I understand that i should break the tab between the two brass screws to separate the red and the black wires but do i need to break the tab on t… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Can I use a steel conduit lockout on pvc male adaptor into
Can I use a steel conduit lockout on pvc male adaptor into utility box on end of my pvc conduit?… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Gfci outlet was fried which caused the upstairs outlets in
Ok... so gfci outlet was fried which caused the upstairs outlets in the bathrooms not to work... pulled the old gfci switch, put a new one in, had the white wires on the neutral side and black on the … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Wiring diagram for outlet on a switch the to a light on same
wiring diagram for outlet on a switch the to a light on same switch … read more
David Bowden
David Bowden
Owner
593 satisfied customers
Which wires go where? In replacing a switch and outlet in
Which wires go where? In replacing a switch and outlet in the bathroom I mistakenly didn't label the wires before I ran down to answer the door now I don't know where the three main lead wires into th… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I need to wire a switch and 2 outlets in same box) without
I need to wire a switch and 2 outlets in same box) without the switch controlling the outlets. The switch is for a ceiling light. Thanks. … read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
1,093 satisfied customers
I have a Leviton T5225 combination switch/outlet and I want
I have a Leviton T5225 combination switch/outlet and I want to wire it so the switch controls the outlet. There is a break-off tab connecting the two black screws. There is another dual outlet in the … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have a question related to electrical outlet combo switch,
i have a question related to electrical outlet combo switch … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have several outlets that seem to be in the same "switch"
hello there... I have several outlets that seem to be in the same "switch" in my panel. as it happens it is the bathroom, part of the kitchen, my bedroom, my children's bedroom and a hallway next to b… read more
Sam I
Sam I
Electrician
B.S.
482 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.