Have 480v disconnect fed by a 3 pole 30amp breaker. How do I step down to two separate 120V CIRUITS?

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Today

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Submitted: 11 months ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 13 minutes by:
7/30/2017
Electrician: David Bowden, Electrician replied 11 months ago
David Bowden
David Bowden, Electrician
Category: Electrical
Satisfied Customers: 1,190
Experience: Owner at Floridaco
Verified

Hello… my name is ***** ***** I am very knowledgeable in this subject to help answer your question, would you like my expert advice today?

Ask Your Own Electrical Question
Electrician: David Bowden, Electrician replied 11 months ago

As a qualified expert, I am only able to offer you some basic and specific advice via this email/text, which may or may not have been sufficient enough to answer your question right now to your satisfaction.

Therefore, I think it would be very beneficial for you if we can discuss this further in depth over the phone, that way we can save a lot of time by not having to type and wait for a response. If you agree, please initiate and request a phone call.

Ask Your Own Electrical Question
Customer reply replied 11 months ago
Dem can I get a phone csll
Customer reply replied 11 months ago
Call
Electrician: David Bowden, Electrician replied 11 months ago

yes you would need to request this from your end

Ask Your Own Electrical Question
Electrician: ProGrade, Certified Electrical Contractor replied 11 months ago
ProGrade
ProGrade, Certified Electrical Contractor
Category: Electrical
Satisfied Customers: 565
Experience: 28+ years exp. - installation, troubleshooting, & repair of commercial, & residential electrical systems.
Verified

Mr/Mrs Customer:

I disagree with the other "expert".

To get 120V circuits from an existing 480V supply, a step-down transformer is required.

If you will give me some more info, I can determine the size of the transformer...

What size 120V circuits do you need?

What size wire is at the 480V disconnect or what size breaker feeds the disconnect?

Let me know and we can continue.

Thank you

Ask Your Own Electrical Question
Electrician: ProGrade, Certified Electrical Contractor replied 11 months ago

The other guy opted out but with the info I requested above, I can help.

Thanks

Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask ProGrade Your Own Question
ProGrade
ProGrade
ProGrade, Certified Electrical Contractor
Category: Electrical
Satisfied Customers: 565
565 Satisfied Customers
Experience: 28+ years exp. - installation, troubleshooting, & repair of commercial, & residential electrical systems.

ProGrade is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,196 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,345 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I need to install two EPO buttons for one 480v circuit and
I need to install two EPO buttons for one 480v circuit and two 208 circuits all 3 breakers have 120v coils … read more
George Smith
George Smith
Vocational, Technical or Trade School
444 satisfied customers
I have two 400 kW gensets connected through a synchorization
Hello. I have two 400 kW gensets connected through a synchorization panel. Am generating 480V/60hz - 3phase power. … read more
Sam I
Sam I
Electrician
B.S.
821 satisfied customers
30amp circuit needs to be split into two 15amp circuits,
30amp circuit needs to be split into two 15amp circuits … read more
Sam I
Sam I
Electrician
B.S.
821 satisfied customers
I have a simlar question about a started G snswered on.
i have a simlar question about a started Mike G snswered on … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
I have a situation where 480V, 400A 3 phase feed is
I have a situation where 480V, 400A 3 phase feed is connected to the primary of an 330kVA isolation transformer and the secondary of an isolation transformer is connected to 400amp cables. It also has… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
Trying to figure out why my 30amp Seimens breaker keeps
trying to figure out why my 30amp Seimens breaker keeps tripping on my sun panel in the garage.… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
I need to go from 120V three phase to 480V three phase for
I need to go from 120V three phase to 480V three phase for a motor - the electrician hooked it up to 120V not 480V. How would this be done?… read more
Steve
Steve
Chief Engineer
9 satisfied customers
Hello, we just purchased a machine that requires 230 VAC +10%
Hello, we just purchased a machine that requires 230 VAC +10% -0% 3 phase with the electrical diagrams calling for 15 amps. Our building is supplied with 480 VAC 3 phase delta, with a transformer to s… read more
Steve
Steve
Chief Engineer
9 satisfied customers
I have a brand new dryer just bought it I have 2 single 20amp
I have a brand new dryer just bought it I have 2 single 20amp breaker it dryies for 5min and keeps triping I tested volts both have 120v manual said separate 30amp circuit can I use 2 single 30amp to … read more
seanecter
seanecter
27 satisfied customers
I have 4 wires coming from my sub-panel green white black and
I have 4 wires coming from my sub-panel green white black and red. the black and red are connected to the hot side of a 20 amp split breaker. how di I connect a series of outlets to this 4 wire cable?… read more
Steve
Steve
Chief Engineer
9 satisfied customers
im trying to power a 30 amp 110 volt ac travel trailer from
im trying to power a 30 amp 110 volt ac travel trailer from my electric welder 220 outlet in the wall of my house, the welder electric panel is 2- 30 amp 110 breakers, can i turn one of these off, and… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
For a 75kva transformer, 480 step down to a 240/120v, how would
For a 75kva transformer, 480 step down to a 240/120v, how would I size the primary and secondary conductors.… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
I have 480 volt 3 phase power that I need to connect to a portable
I have 480 volt 3 phase power that I need to connect to a portable building. I need a 200 amp 3 phase fusable disconnect on the exterior of the building. From there I plan to enter a 480 volt 3 plase … read more
Sir Sparks
Sir Sparks
Owner
State & UK Certified Master electri
2,519 satisfied customers
I have installed a 220v subpanel in my attic. using a 40amp
I have installed a 220v subpanel in my attic. using a 40amp double pole breaker, 8-3 wire and attaching the hot wires (red and black) to either side of the terminals in the sub panel, neutral and grou… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
Can a 6-3 w/ground ufb run for a shed 125 feet away?
Can I run 6-3 w/ground UFB for a shed 125 ft. away and what size sub-panel can I expect or do I need to go with #4 thhn? I'm looking at running 4 overhead shop lights and 4 receptacles at a work bench… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
I want to add electric service to 3 sheds using the two spaces
I want to add electric service to 3 sheds using the two spaces left on my 200 amp house panel. I want to use the no.10 awg wire I have on hand. I have 3-wire and 2-wire no. 10 awg wire. I would like t… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
I am buying a steam shower that has a 120 (singles pole) 27
I am buying a steam shower that has a 120 (singles pole) 27 amps need. I looked online for a wire gage calculator because i was afraid that since the electrical line was going to be at about 100 feet … read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
Can I run 240V on #8AWG to a sub-panel 250 feet away and then
Can I run 240V on #8AWG to a sub-panel 250 feet away and then use a step down transformer to supply 120V at the sub-panel?… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x