What size wire is needed to run underground in conduit to a

Customer Question
garage about 60 feet from...
What size wire is needed to run underground in conduit to a garage about 60 feet from the main connection at the power pole? This would be connected to a subpanel in the garage.
JA: I'll do all I can to help. How long have you been dealing with this?
Customer: no specified time
JA: Do you plan on doing the work yourself?
Customer: yes. running the wire, but nt connecting it.
JA: Anything else we should know to help you best?
Customer: not that I know
Submitted: 5 months ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 6 minutes by:
7/7/2017
Electrician: Kevin, Licensed Electrical Contractor replied 5 months ago
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 3,848
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) How many amps will the sub-panel feeder circuit be?

Ask Your Own Electrical Question
Customer reply replied 5 months ago
100
Electrician: Kevin, Licensed Electrical Contractor replied 5 months ago

Stand by for a few minutes while I calculate the voltage drop. I will be back shortly.

Thanks..............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 5 months ago

1) The National Electrical Code recommends the voltage drop be not greater than 3%.

2) A 100 amp feeder at 240 volts requires 4 AWG copper resulting in a voltage drop of 1.5% or a loss of 3.6 volts. Therefore 4 AWG copper will be code compliant.

3) If using aluminum conductors, 2 AWG aluminum will be required resulting in voltage drop of 1.4% or a loss of 3.3 volts. Therefore, 2 AWG aluminum is also code compliant.

4) A sub-panel feeder circuit needs to be a 4 wire circuit comprised of 4 conductors.....ie...... 2 hots, 1 neutral and 1 equipment ground. If installing Rigid or Intermediate metal conduit as the underground, a ground wire is not required since the metal underground conduit will act as the equipment ground.

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 5 months ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks.................Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 5 months ago

Any other questions?

Ask Your Own Electrical Question
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 3,848
3,848 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,425 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,780 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,848 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
Can I use a steel conduit lockout on pvc male adaptor into
Can I use a steel conduit lockout on pvc male adaptor into utility box on end of my pvc conduit?… read more
Kevin
Kevin
Licensed Electrical Contractor
3,848 satisfied customers
The Master Electrician Grounding between meter base and main
This is for Mike the Master Electrician Grounding between meter base and main circuit panel via metal conduit requires grounding pipe as well as neutral / and panel bonds. If using PVC, no need to gro… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,780 satisfied customers
Can I add a 90 elbow to the main conduit so that I can raise
can I add a 90 elbow to the main conduit so that I can raise that conduit the conduit is running vertical and i need some height under the conduit … read more
Kevin
Kevin
Licensed Electrical Contractor
3,848 satisfied customers
I have a dedicated 10 amp romex line in conduit, going to a
I have a dedicated 10 amp romex line in conduit, going to a direct wired garbage disposer under my kitchen sink. I want to connect this line up to a single gang outlet box to make exchanging the dispo… read more
Sam I
Sam I
Electrician
B.S.
439 satisfied customers
I am running 3 circuits inside of pvc conduit. 220v 30a
I am running 3 circuits inside of pvc conduit.220v 30a water heater 220v 15a ac 120v 20a receptaclecan I use 1 shared 10awg ground wire for all circuits?… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,780 satisfied customers
Need help determining wire size, wire type, and conduit size
Need help determining wire size, wire type, and conduit size for 200amp panel with a 200 amp subpanel. Here is a list of my questions: http://mnjustin.com/diagram.jpg… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,780 satisfied customers
How much to install 100' of electrical line in a conduit if
how much to install 100' of electrical line in a conduit if the trench is already dug. Include the cost of wiring and adding a 50 Amp Circuit Breaker … read more
Kevin
Kevin
Licensed Electrical Contractor
3,848 satisfied customers
What size wire is needed to run underground in conduit to a
What size wire is needed to run underground in conduit to a garage about 60 feet from the main connection at the power pole? This would be connected to a subpanel in the garage. … read more
Kevin
Kevin
Licensed Electrical Contractor
3,848 satisfied customers
Do you need to remove existing conduit and or conductors if
Do you need to remove existing conduit and or conductors if they are being abandoned and not being used? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,780 satisfied customers
Can I use the conduit that leads into the panel box by
Can I use the conduit that leads into the panel box by adding a second pair of wires to be connected to another circuit breaker? Easier to do than setting up another separate conduit attachment? I kno… read more
Kevin
Kevin
Licensed Electrical Contractor
3,848 satisfied customers
Can we use 2" BX armor conduit thru an attic instead of emt
can we use 2" BX armor conduit thru an attic instead of emt conduit for 1/0 gauge svc lines? 15' in length … read more
George Smith
George Smith
Vocational, Technical or Trade School
286 satisfied customers
I need to install about 200 ft of conduits on a warehouse
Hi Kevin... I need to install about 200 ft of conduits on a warehouse ceiling. The conduit needs to be suspended about 3 feet from the roof because of the large beams. Currently there are two rows of … read more
Kevin
Kevin
Licensed Electrical Contractor
3,848 satisfied customers
What minimum trade size IMC Intermediate Metal Conduit is
What minimum trade size IMC Intermediate Metal Conduit is required for qty 35(6AWG type THHN wires)? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,780 satisfied customers
Can you run electrical conduit in same trench as water
Can you run electrical conduit in same trench as water lines? … read more
ProGrade
ProGrade
Electrical Contractor
564 satisfied customers
My question involves a 1" conduit 20' with 7 pairs of #14
my question involves a 1" conduit 20' with 7 pairs of #14 sis/xhhw rated Insulted (14 conductors) terminated at 120 v shunt trip units 7 breakers to fire alarm relays. … read more
Steve
Steve
Chief Engineer
9 satisfied customers
I have a quad outlet in metal conduit that I want to put a
I have a quad outlet in metal conduit that I want to put a plug on so I can plug it in to a wall outlet. It has a green wire, yellow wire and white wire. Can you tell me which goes to which on the plu… read more
Kevin
Kevin
Licensed Electrical Contractor
3,848 satisfied customers
I have a black, and wire in mtl. conduit. It appears that
I have a black, white and green wire in mtl. conduit. It appears that the green wire is the hot wire. Do I hook this to the side of the plug with the brass screws. Which wire is likely to be the groun… read more
Kevin
Kevin
Licensed Electrical Contractor
3,848 satisfied customers
The house inside conduit has 5 red black and a bare copper,
the house inside conduit has 5 red black white green and a bare copper, I know to connect the colors together. what is the common wire and I think it gets wired to the bare ground but not for sure. I … read more
Kevin
Kevin
Licensed Electrical Contractor
3,848 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.