Needing to put subpanel in my shed, 100 amp service with a

needing to put subpanel in...
needing to put subpanel in my shed
JA: I'll do all I can to help. How long have you been dealing with this?
Customer: 100 amp service with a 120ft run is what im needing wireing info for. what size would work best for me in aluminum. 2/2/2?
JA: Do you plan on doing the work yourself?
Customer: yes
JA: Anything else we should know to help you best?
Customer: nope
Show More
Show Less
Ask Your Own Electrical Question
Answered in 2 minutes by:
11/21/2016
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 3,792
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) What type of loads, how many circuits and voltage is required in the shed?

Ask Your Own Electrical Question

1) Are you looking to install a 100 amp feeder circuit to the shed or how many amps?

Ask Your Own Electrical Question
Customer reply replied 12 months ago
ill be using wood working tools and air compressor. possibly a 120 volt welder. not sure how many circuits ill be running but i have a 20 slot box which I highly doubt ill ever use all of. basically lights and receptables for normal use.
Customer reply replied 12 months ago
100 amp yes

OK, standby for a few minutes as I need to calculate the voltage drop.

Ask Your Own Electrical Question

1) The National Electrical Code recommends that the voltage drop be limited to a max of 3%. Using 2 AWG aluminum is the minimum size for a 100 amp sub-panel feeder circuit and results in a 2.7% VD on a 240 volt/100 amp feeder at a 120 foot run. Therefore, the 2 AWG aluminum is code compliant.

2) The feeder circuit needs to be a 4 wire circuit comprised of 2 hots, 1 neutral and 1 equipment grounding conductor. The ground wire can be sized as 6 AWG aluminum.

3) The shed will require a quantity of two 8 foot ground rods spaced a minimum of 6 feet apart. 8 AWG copper will be required for the grounding electrode conductor.

4) At the sub-panel, do not install the main bonding screw or main bonding jumper. The neutral must remain isolated from the panel metal enclosure.

Ask Your Own Electrical Question

1) The sub-panel will require a separate equipment ground bar to land all grounding conductors. Only white neutrals will land on the panel neutral bus bar. If greater than 6 circuits at the sub, a main breaker panel is required.

Ask Your Own Electrical Question

Any other questions?

Ask Your Own Electrical Question

1) One more item......ie.........the 8 AWG ground wire from the ground rods to the sub-panel needs to be protected in 1/2" conduit. All 120 volt shed receptacles need to be GFCI protected.

Ask Your Own Electrical Question

Hope this helps………If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks..................Kevin:)

Ask Your Own Electrical Question
Customer reply replied 12 months ago
Great info. Thanks. Highly recommend

No problem, glad to assist:)

Thanks.............Kevin:)

Ask Your Own Electrical Question

Hope this helps………If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks..................Kevin:)

Ask Your Own Electrical Question

Any other questions?

Ask Your Own Electrical Question
Customer reply replied 11 months ago
Thank you Kevin for your help. I'll be doing the electrical tomorrow so if anything comes up I'll let you know.

Just curious, why the negative rating? I provided you with all correct code answers to your questions or did I miss something here?

Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 3,792
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified
Kevin and 87 other Electrical Specialists are ready to help you
Ask your own question now
Customer reply replied 11 months ago
No you did great. I'm not sure why it is giving negative feedback. I've went back to my email 3 times and clicked the 5 star option and it keeps telling me I'm sorry your not satisfied. I'll keep trying because I really do appreciate everything.

Thank you for the positive service rating............much appreciated!

If you have any other questions, just let me know.

Take care and have a great weekend.............Thanks again............Kevin:)

Ask Your Own Electrical Question
Customer reply replied 11 months ago
You too thanks

Thank you for the bonus.....that was not necessary, but is very much appreciated:)

Take care and Thanks again:

Happy Holidays...........Kevin:)

Ask Your Own Electrical Question
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 3,792
3,792 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,425 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,940 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,603 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,792 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
Can I add a 90 elbow to the main conduit so that I can raise
can I add a 90 elbow to the main conduit so that I can raise that conduit the conduit is running vertical and i need some height under the conduit … read more
Kevin
Kevin
Licensed Electrical Contractor
3,792 satisfied customers
I have a 240 volt arc welder with three wires,, black and, i
I have a 240 volt arc welder with three wires, white, black and green, i want to hook it up to my generatorL14-30 4 prong plug. to get 220 do I use a jumper cable in the plug from the black wire on on… read more
Kevin
Kevin
Licensed Electrical Contractor
3,792 satisfied customers
I have a dedicated 10 amp romex line in conduit, going to a
I have a dedicated 10 amp romex line in conduit, going to a direct wired garbage disposer under my kitchen sink. I want to connect this line up to a single gang outlet box to make exchanging the dispo… read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
I have a Lincoln 180 dual welder that I would like to
I have a Lincoln 180 dual welder that I would like to connect to a 10-30 R that's already wired in my garage.The welder requires 20 amps at 230V.Can I make an extension cord with a 10-30/50 P at one e… read more
Leamon Rollo
Leamon Rollo
Vocational, Technical or Trade School
13 satisfied customers
I have a question about a 49 to 70 amp small stick welder,
hi,i have a question about a 49 to 70 amp small stick welder, my book says the effective input amps is 8.5 and the maximum input amps is 25.8 but it says to use a 20 amp breaker also,now it says it is… read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
I am running 3 circuits inside of pvc conduit. 220v 30a
I am running 3 circuits inside of pvc conduit.220v 30a water heater 220v 15a ac 120v 20a receptaclecan I use 1 shared 10awg ground wire for all circuits?… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Need help determining wire size, wire type, and conduit size
Need help determining wire size, wire type, and conduit size for 200amp panel with a 200 amp subpanel. Here is a list of my questions: http://mnjustin.com/diagram.jpg… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
How much to install 100' of electrical line in a conduit if
how much to install 100' of electrical line in a conduit if the trench is already dug. Include the cost of wiring and adding a 50 Amp Circuit Breaker … read more
Kevin
Kevin
Licensed Electrical Contractor
3,792 satisfied customers
What size wire is needed to run underground in conduit to a
What size wire is needed to run underground in conduit to a garage about 60 feet from the main connection at the power pole? This would be connected to a subpanel in the garage. … read more
Kevin
Kevin
Licensed Electrical Contractor
3,792 satisfied customers
I have a Hobart 187 MIG Welder that I want to get wired.
I have a Hobart 187 MIG Welder that I want to get wired. What size wire should be used? It takes a 50v plug at 230v. … read more
WCohn
WCohn
Journeyman Plumber
Journeyman License
1,195 satisfied customers
I just bought an AC welder and it did not have the
I just bought an AC welder and it did not have the electrical plug. The power cord has three wires -- blue, brown, green. I am thinking the green is the ground. Does it matter which of the two remaini… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Do you need to remove existing conduit and or conductors if
Do you need to remove existing conduit and or conductors if they are being abandoned and not being used? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I have a 220v welder with std 3 wire 6-50 NEMA male, and
I have a 220v welder with std 3 wire 6-50 NEMA male, and need to change power cord to use a 4 prong RV-type twist plug. What to do with the spare wire connected to the welder? Thanks … read more
George Smith
George Smith
Vocational, Technical or Trade School
273 satisfied customers
Can I use the conduit that leads into the panel box by
Can I use the conduit that leads into the panel box by adding a second pair of wires to be connected to another circuit breaker? Easier to do than setting up another separate conduit attachment? I kno… read more
Kevin
Kevin
Licensed Electrical Contractor
3,792 satisfied customers
What would happen if a welder pulls 55 amps or 60... on a
What would happen if a welder pulls 55 amps or 60... on a nema 6-50 r receptacle?Will it be ok?… read more
Kevin
Kevin
Licensed Electrical Contractor
3,792 satisfied customers
I have a 250 amp welder wired for 120v plug in, where should
I have a 250 amp welder wired for 120v plug in, where should I plug it into? Washer and dryer outlet?… read more
George Smith
George Smith
Vocational, Technical or Trade School
273 satisfied customers
Match welder circuit install... Outlet is going to be 520
Miller match welder circuit install... Outlet is going to be 520 feet away from main feeder panel...My thoughts.... 50amp double pull breaker 60 -75°c termination #2 awg THHN copper.Will this work? Tr… read more
Kevin
Kevin
Licensed Electrical Contractor
3,792 satisfied customers
Had a 220v welder in the garage catch fire, I immediately
Had a 220v welder in the garage catch fire, I immediately shut the breakers off in the garage when this happened but than noticed my lights dimming when using any power. Shortly after the power in the… read more
Kevin
Kevin
Licensed Electrical Contractor
3,792 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x