Kevin> I am curious, I need to run a 200 amp 3 phase

Customer Question
Hi Kevin> I...
Hi Kevin> I am curious, I need to run a 200 amp 3 phase subpanel off of a 400 amp main service entrance. I am running about 120 feet away and am curious what size wire to use?
JA: I'll do all I can to help. How long have you been dealing with this?
Customer: about 3 hours
JA: Do you plan on doing the work yourself?
Customer: yes
JA: Anything else we should know to help you best?
Customer: not that I am aware.
Submitted: 1 year ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Customer reply replied 1 year ago
I plan to run 3 environmental chambers and 3 circulator pumps. EC's run on 50Amp 3 phase and circulators run on 30Amp 3 phase. Will 200amp sub panel be sufficient?
Answered in 20 minutes by:
10/18/2016
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 3,792
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) I will need to know the 3-phase supply voltage in order to perform the voltage drop calculation.

Please provide me with the supply voltage? 208 or 240 or 480 three-phase voltage?

2) Will all 3 chambers and pumps be running simultaneously?

3) What is the FLA (Full Load Amps) rating of each chamber and pump?

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Hi Kevin,Thanks for your help. I can answer two but if you could tell me how to get #3 I would appreciate it.1. It is 480v 3 phase2. It is possible that they could all be running at the same time3. How would I find this?Thanks
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

Thank you for the replies.

1) Electrical equipment such as chambers and pumps will have a nameplate rating located somewhere on the equipment. On the nameplate label, the FLA should be shown.

2) A 200 amp sub-panel will require either 2/0 AWG copper or 4/0 AWG Aluminum conductors. The National Electrical Code recommends that the voltage drop be limited to a maximum of 3%.

Using a 480V 3-phase @ 200 amps and at a 120 foot run with 2/0 AWG copper conductors results in a point eight % (.8%) VD or a loss of 3.9 volts. Therefore, 2/0 AWG Copper is code compliant.

Using a 480V 3-phase @ 200 amps and at a 120 foot run with 4/0 AWG Aluminum conductors results in a point seven % (.7%) VD or a loss of 3.5 volts. Therefore, 4/0 AWG aluminum is also code compliant.

3) The equipment grounding conductor needs to be sized as either 6 AWG Copper or 4 AWG aluminum.

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

1) A 200 amp sub-panel feeder is going to be an issue if all the equipment will be running simultaneously and will create an overload on the 200 amp 3 pole feeder breaker.

2) The pumps contain an electric motor and I assume the chambers also contain some type of motor or compressor. On any electric motor, the "in-rush" current upon motor start-up must be accounted for. For a few seconds, there is a higher amount of current upon the motor start-up. The NEC requires that the branch circuits be sized at a minimum of 125% of the motor FLA rating in order to accommodate the "in-rush" current.

3) Totaling the three chambers @ 50 amps each and the 3 pumps @ 30 amps each results in a minimum of 150 amps + 90 amps = 240 amps.

Multiply 240 amps by 1.25 = 300 amps.

This is assuming that the FLA ratings are 50 and 30 amps. If the FLA ratings are higher, then obviously the amperage will increase.

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks...............Kevin:)

Ask Your Own Electrical Question
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 3,792
3,792 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,425 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,940 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,603 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,792 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I have a davit with a Leeson motor C6C17NC66A and a Salzer
I have a davit with a Leeson motor C6C17NC66A and a Salzer rotary switch. Someone yanked out the pigtail for incoming power and I can't find where to reconnect the black, white, and green. Any ideas? … read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
Need to wire a 240 volt single phase 3 wire motor. Just
the motor has 2 connections for the hot wire and also has a common… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Doerr motor LR22132. The HP is listed as "SPCL". an you tell
doerr motor LR22132. The HP is listed as "SPCL". an you tell me what the real HP is? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Trying to exchange lighting fixtures in Motor home. Just
trying to exchange lighting fixtures in Motor home … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I have a 1 hp doerr motor. Can it be reversed. About a hour.
I have a 1 hp doerr motor. Can it be reversed JA: I'll do all I can to help. How long have you been dealing with this? Customer: About a hour JA: Do you plan on doing the work yourself? Customer: Yes … read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
Looking for Magnetek Universal Electric motor, ser.27ZA,
looking for Magnetek Universal Electric motor, ser.27ZA, 53930P Mod. DA 39142 115 60 950RPM 1BHP, or replacement … read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
When I turn on anything with a motor (washer, dryer,
When I turn on anything with a motor (washer, dryer, refrigerator) the voltage on one phase jumps to about 160v while the other drops to about 80v. I could not isolate it to a breaker.… read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
The motor runs but there is no electrical power, About a
Sometimes the power comes back or for a while and then stops. its almost like there was a loose connection. i checked all the connections and power cord.… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
My 220 power source has 3 wires, orange, and. The motor has
My 220 power source has 3 wires, orange, white and gray. The motor has 4 wires black white brown and brown with white lines. what do I connect … read more
Leamon Rollo
Leamon Rollo
Vocational, Technical or Trade School
13 satisfied customers
I am wiring in a new motor for my whole house fan to two
I am wiring in a new motor for my whole house fan to two existing two wire Romex to make the two speed fan switch work. I just need to know where to connect the three fan wires to the four Romex wires… read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
Can a 415volt three phase Induction motor be converted to
Hi Can a 415volt three phase Induction motor be converted to run on battery power. Spec 36 amp, 50 Hz 18.5 Kw, 4 pole. Cheers Phil. … read more
Kevin
Kevin
Licensed Electrical Contractor
3,792 satisfied customers
Motor is on and turning but bladers are not. Just started
Motor is on and turning but bladers are not JA: I'll do all I can to help. How long have you been dealing with this? Customer: Just started JA: Do you plan on doing the work yourself? Customer: YES JA… read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
I installed a rescue condenser fan motor ( 5 wire) and I
I installed a rescue condenser fan motor ( 5 wire) and I need help with the high speed and low speed wiring … read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
Bonding a Pool motor: The original bonding screw attachment
Bonding a Pool motor:The original bonding screw attachment to the motor snapped off at the head. The body of the screw is still in the casing of the motor. I tried to use an "easy out" to remove the s… read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
I just bought an electric trolling motor that says the
I just bought an electric trolling motor that says the intake is 24 volts. So can I use a 12v car battery? Or do I need a 24v battery?… read more
ProGrade
ProGrade
Electrical Contractor
564 satisfied customers
My timer is hook to my pool motor, and the motor loses
My timer is hook to my pool motor, and the motor loses power. Is this lack of electrical connections. It's trigger my main switch off couple of times. … read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
I am trying to wire a Switch to a motor. Switch is a
I am trying to wire a Switch to a motor. Switch is a magnetic 3hp single phase 18-26 amp to a single phase 3hp 220 v motor there are four wires from the motor blue, brown, black and green/yellow… read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
Second opinion] I need to wire a motor to 240v. The motor
Second opinion] I need to wire a motor to 240v. The motor has a white wire coming from the motor, and a black wire also. My panel box can produce 240v but on two 120v legs. What do I need to get 240v … read more
Jason
Jason
Service Technician
Associate Degree
3,940 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x