can i install a gfci breaker box when i have only three wires coming from the main panel two hots and a ground?
Submitted: 1 year ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Customer reply replied 1 year ago
no netural wire from main panel to hot tub
Answered in 23 minutes by:
9/9/2016
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 3,791
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) Yes, it is called a double pole GFCI disconnect circuit breaker.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
How do i wire the gfci woth no netural from main panel
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

1) Install a double pole GFCI breaker at the main panel or at a sub-panel. A GFCI double pole breaker requires a neutral bus bar connection for the white neutral pigtail. Otherwise, the GFCI breaker will not work.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Ok im install the sub panel with the gfci breaker but were to i get the netural wire from ,can not be ran from main panel?
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

1) If the hot tub is exterior, then the disco box feeder circuit requires 2 hots, 1 neutral and 1 equipment ground. Won't work without a neutral wire from the feeder circuit.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
exterior tub so im screwed then?
Customer reply replied 1 year ago
Can i make the ground wire from the feeder circuit the neturalwire?
And put a ground wire on the disco box?
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

1) If the feeder conductors from the main panel to the exterior disco panel were installed using a raceway (conduit), it may be possible to add the required neutral conductor.

2) No, a bare copper ground wire is only allowed to act as an equipment ground and never allowed to act as a neutral. Code violation:)

Refer to the diagram shown below for a hot tub disco switch connection:

Ask Your Own Electrical Question
Customer reply replied 1 year ago
I believe its a just a wire not bare
Can it be done that way then?
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

1) Another option, is to install a double pole exterior rated NEMA 3R weatherproof disconnect switch for the outside and install a double pole GFCI breaker in the house panel.

2) The 3rd wire can only be used as a neutral if it is white, grey or black (re-identified as a white neutral). However, the hot tub will not contain an equipment ground. Hot tub disco's require a 4 wire circuit or at a minimum, a 2 wire circuit for the 240 volt connection and the 3rd wire to be used as an equipment ground if a double pole disco switch is used.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
But i will still not have a neutral wire at the dsco box?
Customer reply replied 1 year ago
Thats a throw swicth?
Customer reply replied 1 year ago
Thats what they use for air conditioners
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

1) If the feeder circuit was installed in metal conduit, then the metal conduit will act as the equipment ground. If the feeder was installed in PVC gray electrical conmduit, then a separate equipment ground wire is required.

2) Hot tubs are either a combo of 120/240 or 240 volts only. Your model only requires 240 volts. Therefore, a neutral is not required for the tub connection. Look at the diagram I sent you. However, a double pole GFCI breaker requires a neutral connection for the white curly pigtail to a neutral bus bar. Your feeder circuit does not contain a neutral, therefore, you either need to install a neutral for the feeder or install a new 4 wire circuit or install a doublee pole disconnect switch at the exterior. No other choices on the matter in order to be code compliant.

3) Yes, it is called a NEMA rated 3R double pole disco switch. The disco switch must be rated for the same amps as the double pole breaker.

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

1) If the feeder circuit was installed in metal conduit, then the metal conduit will act as the equipment ground. If the feeder was installed in PVC gray electrical conmduit, then a separate equipment ground wire is required.

2) Hot tubs are either a combo of 120/240 or 240 volts only. Your model only requires 240 volts. Therefore, a neutral is not required for the tub connection. Look at the diagram I sent you. However, a double pole GFCI breaker requires a neutral connection for the white curly pigtail to a neutral bus bar. Your feeder circuit does not contain a neutral, therefore, you either need to install a neutral for the feeder or install a new 4 wire circuit or install a double pole disconnect switch at the exterior. No other choices on the matter in order to be code compliant.

3) Yes, it is called a NEMA rated 3R double pole disco switch. The disco switch must be rated for the same amps as the double pole breaker.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
if i install the gfci breaker in the main box and a quick disconnect at the outside then im gf i protected?
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

1) The hot tub must have a means of disconnect nearby. Either install a:

A) GFCI disco switch installed at the exterior using a 4 wire feeder circuit

or

B) A GFCI breaker installed in the main or sub-panel and and exterior disco switch. One of these is required to meet code.

2) Yes that is correct. If installing a double pole GFCI breaker at the main panel and an exterior rated NEMA 3R double pole disco switch, the hot tub will still be GFCI protected from the breaker installed at the panel. Totally code compliant and GFCI protected:)

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks...........Kevin:)

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Thank you very much for your help
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

No problem, glad to assist.

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks...........Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks..............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks...............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks...............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks...............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks...............Kevin:)

Ask Your Own Electrical Question
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 3,791
3,791 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,425 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,940 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,603 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,791 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I have 2 dedicated circuits in my circuit breaker box that
I have 2 dedicated circuits in my circuit breaker box that are 240V, they each have 2 hot wires going to them. The circuit is terminated to an individual plug (L6-20R) for each circuit. The device I'm… read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
I have 415 amps worth of branch circuit breakers. what size
I have 415 amps worth of branch circuit breakers. what size service do i need for my house? is 200 sufficient … read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
I'm trying to move a circuit breaker box in a place I'd like
I'm trying to move a circuit breaker box in a place I'd like to put a bathroom. Knowing it isn't code to have one in a bathroom, is a junction box ok? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
How do I determine the correct size circuit breaker panel
How do I determine the correct size circuit breaker panel for an stand alone workshop. I don't suspect I would draw more than 20 amps at any given time, but do I need a box assumes everything is turne… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
What is the function that makes a circuit breaker different
what is the function that makes a circuit breaker different from a switch so that it is able to break fault current … read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
Was wondering which circuit breaker I should look into
Hello, was wondering which circuit breaker I should look into replacing. As it stands my Dryer flips the circuit breaker for the upstairs bedrooms. Should I look into replacing the circuit breaker for… read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
My circuit breaker was buzzing, so I pushed the test button.
Hello. My circuit breaker was buzzing, so I pushed the test button. This switched all the sockets off in my house but left all the lights on. When I flipped the breaker switch back, al the sockets cam… read more
Sam I
Sam I
Electrician
B.S.
363 satisfied customers
My circuit breaker is tripped and will not reset. I've
My circuit breaker is tripped and will not reset. I've checked wiring to outlets looks okay. At the electrical panel there is no power to breaker itself. I check other breakers and the have power. Any… read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
947 satisfied customers
I just need to know what circuit breaker to buy for my
I just need to know what circuit breaker to buy for my mitsubishi mini split that is a 50A 2 pole that provides earth leakage protection … read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
Honda EU7000is has 30 amp line with circuit breaker with
Honda EU7000is has 30 amp line with circuit breaker with each line up to 22.6 amps. Questions is 32 amp draw too large and will trip circuit breaker and can circuit breaker be upgraded to 40 amp to al… read more
Sam I
Sam I
Electrician
B.S.
363 satisfied customers
I have a question about ITE circuit breakers, First call,
I have an ITE electrical panel #FEQ 28MBB. I need compatible circuit breakers… read more
Sam I
Sam I
Electrician
B.S.
363 satisfied customers
I have a zinsco circuit breaker panel. The main line circuit
I have a zinsco circuit breaker panel. The main line circuit breaker is a 125 amp Zinsco 2pole breaker.My question is can I safely replace 125 amp breaker with a 100 amp 2 pole breaker? Main lineRegar… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I have a well pump wired into a 240v/20a circuit breaker. C/
I have a well pump wired into a 240v/20a circuit breaker. C/B has white wire, black wire, ground wire. Pressure switch on well pump has same...black, white. ground. Output from pressure switch to pump… read more
ProGrade
ProGrade
Electrical Contractor
564 satisfied customers
I've checked ALL circuit breaker with a voltage meter. They
I've checked ALL circuit breaker with a voltage meter. They are good, but I still don't have power in both bathrooms. Not in the outlets or ceiling lights. Can you help. … read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
The circuit breaker tripped controlling all the electricity
The circuit breaker tripped controlling all the electricity in my son's bedroom. This circuit also controls the recessed lighting in the dining room. The only way I can reset the circuit breaker is if… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
How much to install 100' of electrical line in a conduit if
how much to install 100' of electrical line in a conduit if the trench is already dug. Include the cost of wiring and adding a 50 Amp Circuit Breaker … read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
I currently live in apartment with a circuit breaker that
I currently live in apartment with a circuit breaker that has 100 amps total. I would like to know to upgrade to 200 amps if it only requires switching the breaker box only or you have to bring anothe… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
What is the standard circuit breaker for an wall oven and
Greetings, What is the standard circuit breaker for an wall oven and for a dual fuel range? Aren't they typically 40A? The installation instruction I am looking at for a Kenmore Elite wall oven (3.4kW… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x