I have a commercial property that has three phase power. It

Customer Question
has three sets of breaker...
I have a commercial property that has three phase power. It has three sets of breaker panels. Two of the panels are full and the 3rd has open spaces. I want to install two new circuits for receptacles for a computer server room. I ran two sets of 12ga wire for two separate 20 amp circuits. I'm using 20amp rated receptacles and two separate 20 amp breakers. I'm wiring the breakers in the panel just as I have done in the past for a single phase panel. When I plug in a three-prong receptacle tester, it indicates that it is wired correctly. However, when I plug in a UPS to the receptacle, the UPS is indicating a site wiring fault. When I turned on the UPS, it fried it. Need help to understand what I am doing wrong. I'm happy to send pictures.
Submitted: 1 year ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 22 minutes by:
8/24/2016
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago
ProGrade
ProGrade, Certified Electrical Contractor
Category: Electrical
Satisfied Customers: 565
Experience: 28+ years exp. - installation, troubleshooting, & repair of commercial, & residential electrical systems.
Verified

Hi J, welcome to justanswer.com

Sorry to hear about your dilemna.

The receptacle tester did what it was designed to do unfortunately it could not tell you that you were dealing with a high leg on that phase. A multimeter would have been a big help.

What it sounds like you are up against is a 3-phase delta high leg. One phase of the 3-phases will read 190 to 210 volts to ground. It is the high leg and 120 volt equipment cannot be supplied from this phase of the panel.

With the UPS damaged, it will have to be replaced. There are some options available for the replacement. You could purchase a ups that runs on 230 volt single phase. Another option, if you have enough electrical capacity would be to add a sub feed panel off of one of your existing panels to give you more spaces for 120 volt equipment.

Please let me know if you have any additional questions or need more direction.

Thank you

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Hi, thanks for your quick response. I understand about 80% of what you are saying. It's my own knowledge limitations. I'm good at following directions, but I don't have electrical expertise. So your comments about the phase leg, etc is a bit over my head. Here's my knowledge of three phase... I understand that the breakers are not all on the same line bus, there is some pattern where each breaker is actually connected to either the A, B, or C line in. I know there is some benefit for motors and high power consuming equipment to draw power from multiple lines, but that is over my head and does not affect my current need to install a few simple receptacles.My assumption (which appears to be wrong) was that if I install a single 20 amp breaker in any single slot in the panel, that it was no different from a single phase installation. I thought because the three line buses are separate, that any one breaker installation was essentially the same as single phase. Again, I concede that this appears to be an incorrect assumption.That said, it's sounds like I need to measure the voltage and get back to you. I think my preference would be to understand how to connect a single phase subpanel to make this easier in the future. However, I have no problem purchasing a more advanced UPS. Also, in case it factors in to the decisions, the second 20 amp circuit was to be for a portable A/C unit.Thanks,
Jason
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

You are welcome Jason. Please check the voltage and let me know.

There are 3-phase systems that do have 120 volts to ground no matter which phase, that is a 120/208Y. Your delta high leg system is not one of these.

If the new breakers you installed were side by side, they are on different phases, one of them on the high leg, one of them not.

I can send separate insgructions to install a sub panel if you want. I will send a quote for the details separately.

If you did not want to pursue this option you could still install a 240 volt UPS. It would be powered from a double pole breaker off of any two phases.

Let me know what you find when you check voltage and what else I can do to help, thanks

Ask Your Own Electrical Question
Customer reply replied 1 year ago
I found my meter and I checked the voltage today. The two 20 amp breakers that I installed are both on the left side of the panel and are in slots 5th and 6th from the top. So if I assume that all breakers on the left side are the odd numbers and the right side are even numbers, these would be breakers #7 and #9. Breaker #7 measured 234 volts and breaker #9 measured 124.5 volts. Does this mean breaker #9 at 124.5 volts should work for a standard 120v receptacle or is even that extra voltage too much? I'm pricing the higher volt UPS in case that is the best course of action. If that should be the best choice can I just install a 30amp breaker and receptacle for position #7 or must there be a dual pole breaker between the high and low voltage slots? Also the wiring to the receptacle is 12ga copper, am I going to need to swap it with 10ga? The run is about 20 feet.
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

You verified that you have a high leg. Yes the number nine breaker is good for any circuit that needs 120 volts. The number 7 breaker cannot be used 4 230 volts. Equipment requiring 240 volts has to be fed from a double pole breaker.

The 12 gauge copper is good for a 16 amp load. If the load exceeds 16 amp you would need number 10 wire on a 30 amp breaker which would be good for up to 24 amps.

Let me know if you need anything else thank you

Ask Your Own Electrical Question
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

Hi Jason, I did not hear from you again so I was just checking in to see if you need any additional assistance thank you

Ask Your Own Electrical Question
Ask ProGrade Your Own Question
ProGrade
ProGrade
ProGrade, Certified Electrical Contractor
Category: Electrical
Satisfied Customers: 565
565 Satisfied Customers
Experience: 28+ years exp. - installation, troubleshooting, & repair of commercial, & residential electrical systems.

ProGrade is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I have a low voltage transformer in my garage which has 4
I have a low voltage transformer in my garage which has 4 lines coming out of it and out of the house to power landscape lights, etc... we have two main path lights that are connected to this transfor… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have a GE electric motor rebuilt with five black wires
I have a GE electric motor rebuilt with five black wires coming out with the following numbers 1 2 3 & 4&5 tighed together model # is 5KC49WG1181A HP 1 1/2 RPM 1725 HZ 60 PH 1 Code J ER 56A SF 1.0. A … read more
Sam I
Sam I
Electrician
B.S.
474 satisfied customers
My outdoor post light has low voltage. It did work and then
My outdoor post light has low voltage. It did work and then stopped working, I changed out three bulbs and they will not come on. I put an led bulb in the lamp and get a weak glow. The incodesent bulb… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a woodworking tool wired for 220v at 19.6A. The motor
I have a woodworking tool wired for 220v at 19.6A. The motor starter overload relaykeeps tripping once the tool is up to speed. The overload relay dial only goes from 10-16 which make me think the too… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I wired it up and ran motor without load no problem ... then
Mike,I wired it up and ran motor without load no problem ... then I put belt on compressor and started to run approx 1 minute into it — the motor started to smoke… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
If you run 110volts through a low voltage high bay lite on
If you run 110volts through a low voltage high bay lite on accident will it fry the built in driver. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I'm wiring a 230v compressor motor, and need to verify that
I'm wiring a 230v compressor motor, and need to verify that I have wires properly combined. I will provide motor information below. Thank youMake: Steveco Farm Duty Model: MS182C17FB2A Labeled Wires P… read more
George Smith
George Smith
Vocational, Technical or Trade School
322 satisfied customers
Trying to find a wiring diagram for a very old ge motor.
trying to find a wiring diagram for a very old ge motor … read more
Sam I
Sam I
Electrician
B.S.
474 satisfied customers
Need to wire a 240 volt single phase 3 wire motor. Just
the motor has 2 connections for the hot wire and also has a common… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
There is a low voltage lighting circuit in my flat. Can I
There is a low voltage lighting circuit in my flat. Can I buy standard fittings and have them converted to plug into the LV circuit?… read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
Can you splice in outdoor string lights to a low voltage
Can you splice in outdoor string lights to a low voltage landscape system? … read more
Sam I
Sam I
Electrician
B.S.
474 satisfied customers
I have a kitchen with 8 low voltage (50W) recessed lights
I have a kitchen with 8 low voltage (50W) recessed lights around the perimeter ceiling. They have always burned out quickly, and all have been out for a long time now. Got tired of replacing them ever… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have low voltage between black aqnd wires when i chech
hi i have low voltage between black aqnd white wires when i chech between black and ground i get 120 v whats happening? … read more
Sam I
Sam I
Electrician
B.S.
474 satisfied customers
My 220 power source has 3 wires, orange, and. The motor has
My 220 power source has 3 wires, orange, white and gray. The motor has 4 wires black white brown and brown with white lines. what do I connect … read more
Leamon Rollo
Leamon Rollo
Vocational, Technical or Trade School
18 satisfied customers
I am wiring in a new motor for my whole house fan to two
I am wiring in a new motor for my whole house fan to two existing two wire Romex to make the two speed fan switch work. I just need to know where to connect the three fan wires to the four Romex wires… read more
Sam I
Sam I
Electrician
B.S.
474 satisfied customers
Topic is low voltage landscape lighting. It appears that
Good Evening - Topic is low voltage landscape lighting. It appears that several lines do have power while other do not. For the lines that have no power, I have checked the following – • Light bulbs h… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have low voltage (12V) suspended track lighting. The old
I have low voltage (12V) suspended track lighting. The old transformer died. I got a replacement 120V step down to 12V with a 150 Watt max. I tested the load which measured 120V. After connecting the … read more
James I
James I
Pool Plant Operator
21 satisfied customers
I need to know if this timer is workable with a low voltage
I need to know if this timer is workable with a low voltage fireplace switch. There are 2 wires, as pictured, black and red. No ground.https://smile.amazon.com/Skytech-Fireplace-Control-Wireless-Mount… read more
George Smith
George Smith
Vocational, Technical or Trade School
322 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.