Electrical

Electrical Questions? Ask an Electrician Online.

Ask an Expert,
Get an Answer ASAP!

Electrical

I just moved into a rental with brand new seemingly not

Customer Question
professionally installed wiring. Beyond a...
I just moved into a rental with brand new seemingly not professionally installed wiring. Beyond a few items of concern, my main question is about the wiring to the washer/dryer. After being ran for about 25min for the very first time the washing machine displayed an error that the repairperson said indicated a faulty or possibly burned out motor. The washing machine plugs into the dryer in a stacked setup. The dryer is wired to a 4 prong outlet on a 30amp breaker that has only the dryer receptacle & a single 1 bulb light on it (as far as I can tell). The wire to the metal box is 12 gauge armored flexible conduit with no ground wire (just black/red hots and a white neutral). The ground wire from the receptaple is a pigtail screwed into the metal box. I tested the receptacle with a multimeter the wires are on the correct places. The hot to hot reads 208v. The hots to neutral each read 122v. The neutral to ground reads .004v. I've noticed other outlets/non transformer plugs seeming warm to the touch and I noticed one that looks to have been burned.
1. Is it likely that the wiring caused the damage to washing machine motor? Or is it just a fluke or manufacturer defect? In other words will the new one meet the same fate?
2. If the wiring is the issue how do I determine the cause? Is the cause undersized wire? If its undersized why didnt the breaker trip? Is something else wrong besides no ground, 12g wire?
3. Would installing GF protection help this issue?
Thank you
Submitted: 1 year ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 13 minutes by:
8/24/2016
Electrician: Mike G., Master Electrician replied 1 year ago
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 7,765
Experience: Proven Professional 48 years Experience
Verified

Hi, I'm Mike G and I'll be assisting you. The issues as I see from your description are as follows.

  1. The circuit should be #10 wire on a 30A 2 pole breaker
  2. The neutral and ground connect together by code exception for a pre-existing laundry circuit.
  3. Failure of a receptacle and plug is caused by loose jaws on the receptacle. Over time it arcs and the condition gets worst until you can see the burned connection.

Replace the receptacle, connect the ground to the box and the white wire. Installing a GFCI would be a good idea, but not required on a 240V circuit.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
I agree on point 1 and it IS on a 2 pole 30A breaker but undersized at 12g wire. My question is 1- could this be the reason the motor on the washing machine burned out and 2- will it happen again 3- whats the solution.
Customer reply replied 1 year ago
On points 2&3 seems like you missed the part when I said this is all brand new wiring & receptacle and appliance. Brand New. Never used. Not worn out.
Customer reply replied 1 year ago
Also wiring all over the house which again is BRAND NEW is warm to to the touch. Is this related to the other problem? How do I troubleshoot this problem when you can for sure rule out old worn out receptacles or miswired receptacles at least in terms of showing up correctly on a tester (hot neutral ground in correct places).
Electrician: Mike G., Master Electrician replied 1 year ago

I suggest opening the panel and testing each breaker to the neutral bar for 120V per breaker. Then turn off all the branch circuit breakers and test phase to phase on the incoming wire and then each phase to the neutral connection. While doing the tests look for any signs of arcing or discoloration by heat. Test the bus's phase to phase and each phase to neutral. Let me know the readings.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Ok I can try that tomorrow. But still curious could undersized wire cause a washing motor to burn up?
Customer reply replied 1 year ago
washing machine
Electrician: Mike G., Master Electrician replied 1 year ago

Loose connection arcing will produce low voltage which will fail a motor. The burnt outlet is the evidence.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
possibly a loose connection at the breaker? The burnt outlet I saw was 2 floors up on a different circuit.
Electrician: Mike G., Master Electrician replied 1 year ago

Very possible. Even new wiring can fail due to failure to tighten connections. Bad connection cause low voltage. Voltage drops, amperage increases. A 30A breaker would hold and not trip on a stackable washer dryer.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Would a bad connection show up in meter readings at the receptacle?
Electrician: Mike G., Master Electrician replied 1 year ago

It would if on the circuit ahead of the outlet. If it is the device having loose jaws, the burnt outlet is self evident. Just test the panel as instructed to eliminate a service connection or failing breaker or breaker connection. Come back with the results. You need to test not guess.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Ok. I'll write them to you tomorrow.
Customer reply replied 1 year ago
Thanks
Electrician: Mike G., Master Electrician replied 1 year ago

You're welcome.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Each breaker to neutral bar: 123v. Phase to phase off breakers: all were 123v with the exception of 1 half of the double pole 30A breaker in question which read 121. Also got 121 from adjacent 20A breakers. No signs of discoloration, burning, or loose connections. Bus to bus: 210v, Bus to neutral: 123v
Electrician: Mike G., Master Electrician replied 1 year ago

You gave me buss to buss 210V, what is lug to lug on the main breaker?

Ask Your Own Electrical Question
Customer reply replied 1 year ago
With further exploration I discovered the 30A dryer breaker is wired from the panel to a light switch junction box with 10g wire (no ground) then is spliced to 12g wire where it runs to a light fixture. There are 2 groups of 12g leaving the box but I cant be sure the line runs directly to the dryer outlet box without opening up the fixture.
Customer reply replied 1 year ago
Also 210v
Electrician: Mike G., Master Electrician replied 1 year ago

Somewhat lower than expected but having 123V phase to neutral is good. Everything considered the failure must have been at the device. To burn it was either a loose wire connection or a loose jaw on the device. Both would cause a low voltage that would affect the washer/dryer motor.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Well it was the device (and not the washing machine itself) is there a way to definitively isolate the receptacle device as the problem?
Customer reply replied 1 year ago
IF it was...
Electrician: Mike G., Master Electrician replied 1 year ago

The burnt device is the evidence of the cause.

Ask Your Own Electrical Question
Electrician: Mike G., Master Electrician replied 1 year ago

A short circuit in the appliance would have tripped the breaker before it burnt the device.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
The burnt outlet I mentioned before is not the dryer receptacle its just a random outlet on another floor that has nothing to do with this except that it gave me pause as to the quality of work done in the house.
Customer reply replied 1 year ago
The receptacle connected to the washer/dryer is brand new and at least from my eye undamaged and working properly.
Electrician: Mike G., Master Electrician replied 1 year ago

Sorry I forgot about that. No matter. The appliance may have had an issue that failed the motor. The readings at the panel were acceptable though low phase to phase. It should have been closer to 240V. Not explainable having g 123V at phase to neutral. If you look at the nameplate rating on the appliance you'll see it's operating voltage which I'm sure is more than 210V. Low voltage results in high amperage. High amperage will heat and fail electrical items.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Is there anything I can do to isolate the problem further?
Customer reply replied 1 year ago
If it was a fluke with the washing machine itself then fine I guess. But I dont want another $1000 wiring mistake in the form of another burned out machine.
Electrician: Mike G., Master Electrician replied 1 year ago

Retest at the panel. Phase to phase down in the lugs not on the lugs to see if there is a difference.

Ask Your Own Electrical Question
Electrician: Mike G., Master Electrician replied 1 year ago

Also test phase to phase on the 2 pole 30A breaker.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Still reading about 210 (it'll jump to 211 or 212 at first) for both phase to phase readings regardless of whether it tested on lugs or in them/on wire.
Electrician: Mike G., Master Electrician replied 1 year ago

I suggest calling the utility and having them test their distribution voltages. Having 210V is low. Did you look at the name plate on the appliance. I'm sure it requires a higher voltage. By code a combined voltage drop of 5℅ is the maximum.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Noticed signs of long term water and wetness around the pull box opened it see below:
Customer reply replied 1 year ago
Ok good to know. This is Brooklyn and everything is a million years old.
Electrician: Mike G., Master Electrician replied 1 year ago

The bug connection on the right looks to have possible issue from the picture. Is the tape melted?

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Washing machine says 208-240V ~60hz 12A
Electrician: Mike G., Master Electrician replied 1 year ago

Listed at a minimum of 208V, you're OK.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Ok.
Customer reply replied 1 year ago
Tape is not melted. Everything is cool/not warm.
Electrician: Mike G., Master Electrician replied 1 year ago

The only thing I can say is the burned outlet and the appliance motor failure were coincidental and not related. The voltage reading are OK within acceptable readings. The 210V is what an electrician would expect on a 3 phase phase to phase service. Single phase usually reads over 220V phase to phase.

There isn't any more I can add.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Should the washer/dryer be rewired with a 10g dedicated line before the new one goes in or is the current setup acceptable?
Customer reply replied 1 year ago
Is it possible that under load the voltage is dropping under 208?
Electrician: Mike G., Master Electrician replied 1 year ago

Fluctuation on the utility distribution may drop the voltage at certain times of day depending on area demands.

Ask Your Own Electrical Question
Ask Mike G. Your Own Question
Mike G.
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 7,765
7,765 Satisfied Customers
Experience: Proven Professional 48 years Experience

Mike G. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,425 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,940 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,765 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,715 satisfied customers

30 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
IF YOU SPLISE A WIRE DO YOU INSTALL A JUNCTION BOX. JUST NOW
IF YOU SPLISE A WIRE DO YOU INSTALL A JUNCTION BOX … read more
Mike G.
Mike G.
Master Electrician
7,765 satisfied customers
Mounting of junction box in wet location...outside...how
Mounting of junction box in wet location...outside...how high off of the ground does the weatherproof box need to be mounted. Is there a code requirement?… read more
Mike G.
Mike G.
Master Electrician
7,765 satisfied customers
I'm trying to move a circuit breaker box in a place I'd like
I'm trying to move a circuit breaker box in a place I'd like to put a bathroom. Knowing it isn't code to have one in a bathroom, is a junction box ok? … read more
Mike G.
Mike G.
Master Electrician
7,765 satisfied customers
I would like to convert a wall outlet to a junction box so I
I would like to convert a wall outlet to a junction box so I can add power to the room behind the current wall outlet....I have already removed the wall plate and can see that there are currently 2 wi… read more
Mike G.
Mike G.
Master Electrician
7,765 satisfied customers
Wiring diagram for outlet on a switch the to a light on same
wiring diagram for outlet on a switch the to a light on same switch … read more
David Bowden
David Bowden
Owner
330 satisfied customers
Which wires go where? In replacing a switch and outlet in
Which wires go where? In replacing a switch and outlet in the bathroom I mistakenly didn't label the wires before I ran down to answer the door now I don't know where the three main lead wires into th… read more
Mike G.
Mike G.
Master Electrician
7,765 satisfied customers
What is the function that makes a circuit breaker different
what is the function that makes a circuit breaker different from a switch so that it is able to break fault current … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
I need to wire a switch and 2 outlets in same box) without
I need to wire a switch and 2 outlets in same box) without the switch controlling the outlets. The switch is for a ceiling light. Thanks. … read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
953 satisfied customers
I need help to Hard wire a nanny cam inside the junction box
I need help to Hard wire a nanny cam inside the junction box of a wall outlet. My problem is that the nanny camera camera only has 2 wires (black and white). On the other hand, the wall outlet has 5, … read more
Sam I
Sam I
Electrician
B.S.
368 satisfied customers
Can you splice in outdoor string lights to a low voltage
Can you splice in outdoor string lights to a low voltage landscape system? … read more
Sam I
Sam I
Electrician
B.S.
368 satisfied customers
Can you put a junction box In a line going to and electric
can you put a junction box In a line going to and electric stove 40 amp size or does it have to be one continuous run … read more
Mike G.
Mike G.
Master Electrician
7,765 satisfied customers
I have a junction box with Al wiring. One Black One Red and
I have a junction box with Al wiring. One Black One Red and a stranded bare common. It used to have a drop in stove. I wish to change over to a new slide in stove with a 3 prong plug. Can I put a flus… read more
Mike G.
Mike G.
Master Electrician
7,765 satisfied customers
I have a well pump wired into a 240v/20a circuit breaker. C/
I have a well pump wired into a 240v/20a circuit breaker. C/B has white wire, black wire, ground wire. Pressure switch on well pump has same...black, white. ground. Output from pressure switch to pump… read more
ProGrade
ProGrade
Electrical Contractor
564 satisfied customers
I'm trying to locate a junction box on a 1988 cavco
I'm trying to locate a junction box on a 1988 cavco manufactured home … read more
ProGrade
ProGrade
Electrical Contractor
564 satisfied customers
What would be the reason to have an open junction box in the
what would be the reason to have an open junction box in the crawl space of a house? … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
I am trying to wire a Switch to a motor. Switch is a
I am trying to wire a Switch to a motor. Switch is a magnetic 3hp single phase 18-26 amp to a single phase 3hp 220 v motor there are four wires from the motor blue, brown, black and green/yellow… read more
Sam I
Sam I
Electrician
B.S.
368 satisfied customers
I am installing a 15 amp electrical outlet to a junction box
I am installing a 15 amp electrical outlet to a junction box that was not in use but is hot. When I removed the cover plate I discovered 3 black wires twisted and covered by a yellow plastic cover scr… read more
George Smith
George Smith
Vocational, Technical or Trade School
273 satisfied customers
Was just informed I might require a Hard Wire Junction box
Was just informed I might require a Hard Wire Junction box with installation of a water heater. Would like to know appx cost for this job and recommendations of electricians in my area … read more
Mike G.
Mike G.
Master Electrician
7,765 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x