When installing a 125amp subpanel panel can i feed it from a

100amp dp breaker ? Barely...
When installing a 125amp subpanel panel can i feed it from a 100amp dp breaker ? Barely gonna use 30amps.
Show More
Show Less
Ask Your Own Electrical Question
Answered in 2 minutes by:
8/17/2016
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 7,939
Experience: Proven Professional 49 years Experience
Verified

Hi, I'm Mike G and I'll be assisting you. Go ahead, no problem as long as the feeder is 100A.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Cool thx

Anytime, you're welcome. Don't forget to rate me.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Ok last but not least, how many 100amp dp breakers to sub panels can i run off a 200amp service panel?

What exactly are you trying to do?

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Tryin to figure out if i should run another sub or just add to the one I already have

If you have a 100A sub panel and need another there are other considerations.

How long is the existing feeder?

What size is it?

Is the feeder a 4 wire cable?

Is the new panel to be in the same building?

Just how many additional panels are you needing?

Ask Your Own Electrical Question
Customer reply replied 1 year ago
All in the same building. Feeder wire would be bout 5 feet. Panel will be next to the service panel and would be 2 wire.

The feed to the new sub panel needs to be 4 wire. 2 hots, 1 neutral and 1 ground. The wire size is 2,2,4&4 Aluminum. I suggest using a 100A lug kit instead of a breaker if this is off the existing sub panel. The main for one will serve both. You may not be able to use a 100A breaker, check the label on the existing panel.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Why not a 2 wire? Copper.
Customer reply replied 1 year ago
It's off the service panel not the sub

Off the main service panel you'll need a 2 pole 100A breaker in either the main panel or the sub panel being only 5 ft apart. You can use copper but you still need 4 wires per code.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
I know. I have all that already

Your follow up question was why not 2 wire. You need 4 wires not 2.

2 hots, 1 neutral and 1 ground.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
No. It's a #2 wire. The question was can i have 2 100amp breakers feeding subs off a 200amp service panel

Yes you may. The only limitation is if the label limits the size of any breaker.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
You mean the label on the service panel correct?
Customer reply replied 1 year ago
The max is 100a

That means you can install 100A breakers. Number possible is no concern.

Ask Your Own Electrical Question

You haven't rated my answer yet. Is there anything more required?

Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 7,939
Experience: Proven Professional 49 years Experience
Verified
Mike G. and 87 other Electrical Specialists are ready to help you
Ask your own question now
Ask Mike G. Your Own Question
Mike G.
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 7,939
7,939 Satisfied Customers
Experience: Proven Professional 49 years Experience

Mike G. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,939 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
My son bought a house and found that the electrical outlets
My son bought a house and found that the electrical outlets in the kitchen are not working. What could the problem be and what do u recommend? Thanks… read more
Mike G.
Mike G.
Master Electrician
7,939 satisfied customers
I have a double light switch in a bathroom. One controls the
I have a double light switch in a bathroom. One controls the overhead lights and the other operates the fan. The light switch component is dying. Can I replace this double with a single and how would … read more
George Smith
George Smith
Vocational, Technical or Trade School
315 satisfied customers
I am hearing some crackling sounds, intermittently, come
I am hearing some crackling sounds, intermittently, come form one of the electrical outlets in my kitchen. I replaced the outlet yesterday but still hear the sound. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I started hearing a buzzing sound from the ceiling of the
i started hearing a buzzing sound from the ceiling of the house. sounds electrical (also, it's at 50Hz, which I think is the UK mains AC frequency) … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
My ceiling light will not turn off by the switch anymore. so
hi my ceiling light will not turn off by the switch anymore. so I went and replaced the switch and it still stays on? … read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
1,044 satisfied customers
I am replacing a single pole switch with a Defiant digital
Hi. I am replacing a single pole switch with a Defiant digital timer. The current switch is wired with 2 black wires and a ground (no white neutral wire). do I just connect the 2 back wires? (one to L… read more
Mike G.
Mike G.
Master Electrician
7,939 satisfied customers
I have a dimplex smart baseboard heater. I connected it as a
Hi, my name is Don. I have a dimplex smart baseboard heater. I connected it as a 110 v off an outlet. I now realize it is a 240/220v. Can I disconnect the 12/2 wire off the outlet, run it to the circu… read more
Mike G.
Mike G.
Master Electrician
7,939 satisfied customers
I bought a ceiling light for my bedroom, but my ceiling I
I bought a ceiling light for my bedroom, but my ceiling I realized doesn't have a plug for a hanging light i wanted to see if theres a way to still install it, but use an extension cord against the wall down to a regular plug … read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
1,044 satisfied customers
I have these thermostats- all a little different in my home.
I have these thermostats- all a little different in my home. My biggest challenge is how to set them on manual only. I do not want them on time/ energy conservation or anything like that. I want to be… read more
George Smith
George Smith
Vocational, Technical or Trade School
315 satisfied customers
Installing a GFi receptacle in old where there is no ground
Installing a GFi receptacle in old where there is no ground wire. I can identify the hot wires on the line feed wires with a tester, but can identify the load wires since the are both dark. One looks … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have a mechanics question; please connect me to a
I have a mechanics question; please connect me to a mechanic! … read more
Leamon Rollo
Leamon Rollo
Vocational, Technical or Trade School
16 satisfied customers
I recently changed an outlet to a new one with usb
I recently changed an outlet to a new one with usb connection. The outlet had 2 black and 2 white. The new outlet only needed 1 and 1. I taped the remaining wires and now the lights don't work in the … read more
Mike G.
Mike G.
Master Electrician
7,939 satisfied customers
I have a vintage wadsworth 60 amp main fuse panel pull=out
I have a vintage wadsworth 60 amp main fuse panel pull=out fuse holder inside my breaker panel, I recently lost power in a couple of rooms in my house , I replaced all the buss 60, 30 & 20 amp fuses w… read more
Mike G.
Mike G.
Master Electrician
7,939 satisfied customers
I have an Intermatic Model ST01 wall switch timer. After 3
I have an Intermatic Model ST01 wall switch timer. After 3 months or so, it started clicking on and off. I got a new one and it is doing the same thing. I wired it exactly how it was wired initially a… read more
George Smith
George Smith
Vocational, Technical or Trade School
315 satisfied customers
Half the lights in the apartment I am renting go into a
half the lights in the apartment I am renting go into a pulsing mode once the switch is turned on for the fluorescent kitchen fixture that the landlord just installed. The breaker doesn't trip. None d… read more
Mike G.
Mike G.
Master Electrician
7,939 satisfied customers
My Craftmade TCS Fan/light control will not work. I've
My Craftmade TCS Fan/light control will not work. I've changed the batteries twice but it still will not work. What should the settings be on the ON Edge inside the remote? … read more
Leamon Rollo
Leamon Rollo
Vocational, Technical or Trade School
16 satisfied customers
I spilt water over an electric socket which had a lamp
I spilt water over an electric socket which had a lamp plugged in and switched on. I moped … read more
George Smith
George Smith
Vocational, Technical or Trade School
315 satisfied customers
Have a three phase delta grounded system. At the disconnect
have a three phase delta grounded system. At the disconnect with it turned off I read 275 to ground on all 3 phases but phase to phase read 3 volts..what do you think?… read more
Shane
Shane
Not Finished
0 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.