I am a retired carpenter/builder and recently removed a

Customer Question
countertop for a friend who...
I am a retired carpenter/builder and recently removed a countertop for a friend who is replacing same. There is a 4 burner cook top in the counter and a single built in oven in the wall. I am not an electrician but recognize issues with wiring. Here is what someone did. The 50 amp 3 conductor romex wire comes through a hole in the drywall, drapes in a 12"inch loop and enters a metal box Attached to stud behind drywall but mounted on surface of dry wall) romex secured with a proper clamp to box. The wires from the oven are in flex for only part of the run and then the insulated conductors exit the flex and pass directly into the box (no flex cable or proper clamp last 10 " or so. Also the flex from the stove top enters the box with no clamp. All leads were connected inside box red/red, black/black, white to bare copper conductor. I shut off breaker and removed cook top (to be replaced) oven to be re-connected. Is it acceptable to have both the stove top and single oven in 1 box and connected to the 3 wire supply as long as the leads are in flex and attached to the box with flex clamps. And is the romex ok coming through the drywall attached only to the box. I built and wired my own home but am reluctant to help my friend but he had what I consider to be some dangerous conditions. Thanks for any suggestions. And because of high season can't get anyone in to check it out. Thanks,
Bill d
Submitted: 1 year ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 13 minutes by:
8/6/2016
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 3,941
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) Based on your comments, there are few code violations as follows:

A) NM Romex needs to be protected and cannot be exposed. Either needs to be installed in a flexible metal conduit or EMT conduit, or better yet, just install individual conductors into a Flex metal conduit (Greenfield) and forget the Romex cable.

B) All cables and/or raceways entering or leaving a metal wall box need to have the proper clamps.

2) What you have in place is called a "tap connection" which is code compliant and a common installation. The wattage of the cooktop and oven determines the size of the double pole feeder breaker using a factor within the NEC. A 50 amp breaker is a very common size used in a tap connection. The cooktop and oven are basically sharing the same 50 amp circuit and this is code compliant.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Slightly confused about the romex nm, it is behind the wall (as most romex) and enters the cabinet space through a hole punched in the sheetrock then to the metal junction box. What is the easiest way to rotect the romex without running new conductors from the panel?
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

1) If the Romex is installed behind drywall, then it is protected and no corrective action required.

2) If the Romex enters into a storage cabinet area, I consider that as a code violation since the cabinet can be used for kitchen storage and it needs to be protected since it is exposed cable.

3) Where the Romex exits the drywall, install an accessible remodel type box with a blank metal cover that has a knockout and then extend the circuit into the cabinet area with Greenfield (flexible metal conduit). Secure the Greenfield with approved type of clamps.

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks.............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks.............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks...............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks.............Kevin:)

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Sorry for the delay, same question, can I slip steel flex over the exposed romex with an appropriate flex clamp where it enters the steel box or is it preferable to move the box over the romex where it enters the cabinet space through the sheetrock. Thanks.
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

1) The greenfield (flexible metal conduit) can be used as a sleeve to protect the Romex along with the appropriate flexible metal conduit clamp.

2) The greenfield will also require an anti-short bushing at each end to protect the Romex cable from abrasion on the ends of the FMC.

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks.............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks.............Kevin:)

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Last question about this circuit, the new stove top has 3 wires (red, black and bare) same as the supply. Obviously like wires together in the junction box, red/red, black/black, bare/bare. Assuming there should be a bare attached to the metal junction box to the other bare wires, feed and appliance.
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

1) Cooktops are either rated for a combo of 120 & 240 volts or only 240 volts. If only red and black wires and no white neutral wire, then the wires get spliced color to color.

2) All metal boxes are required to be grounded. The bare copper ground needs to terminate to a green ground screw on the back of the metal box.

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks.............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks...............Kevin:)

Ask Your Own Electrical Question
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 3,941
3,941 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,941 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I havea line into junction box and 14-3goingout to switch
I havea line into junction box and 14-3goingout to switch and also wire goingout to light . all grounds are connected. when I connect hot wire to black in the 14-3 ,tester shows about 5 volts in both … read more
Kevin
Kevin
Licensed Electrical Contractor
3,941 satisfied customers
I am looking for installation instructions for junction box
I am looking for installation instructions for junction box # BH614R … read more
Sam I
Sam I
Electrician
B.S.
472 satisfied customers
Half rou d junction box for a ceiling light fixture. There
Half rou d junction box for a ceiling light fixture. There is a water pipe nearby where i want the light to go … read more
George Smith
George Smith
Vocational, Technical or Trade School
314 satisfied customers
IF YOU SPLISE A WIRE DO YOU INSTALL A JUNCTION BOX. JUST NOW
IF YOU SPLISE A WIRE DO YOU INSTALL A JUNCTION BOX … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Mounting of junction box in wet location...outside...how
Mounting of junction box in wet location...outside...how high off of the ground does the weatherproof box need to be mounted. Is there a code requirement?… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I would like to convert a wall outlet to a junction box so I
I would like to convert a wall outlet to a junction box so I can add power to the room behind the current wall outlet....I have already removed the wall plate and can see that there are currently 2 wi… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I need help to Hard wire a nanny cam inside the junction box
I need help to Hard wire a nanny cam inside the junction box of a wall outlet. My problem is that the nanny camera camera only has 2 wires (black and white). On the other hand, the wall outlet has 5, … read more
Sam I
Sam I
Electrician
B.S.
472 satisfied customers
Can you put a junction box In a line going to and electric
can you put a junction box In a line going to and electric stove 40 amp size or does it have to be one continuous run … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have a junction box with Al wiring. One Black One Red and
I have a junction box with Al wiring. One Black One Red and a stranded bare common. It used to have a drop in stove. I wish to change over to a new slide in stove with a 3 prong plug. Can I put a flus… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Need help determining wire size, wire type, and conduit size
Need help determining wire size, wire type, and conduit size for 200amp panel with a 200 amp subpanel. Here is a list of my questions: http://mnjustin.com/diagram.jpg… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I'm trying to locate a junction box on a 1988 cavco
I'm trying to locate a junction box on a 1988 cavco manufactured home … read more
ProGrade
ProGrade
Electrical Contractor
564 satisfied customers
What size wire is needed to run underground in conduit to a
What size wire is needed to run underground in conduit to a garage about 60 feet from the main connection at the power pole? This would be connected to a subpanel in the garage. … read more
Kevin
Kevin
Licensed Electrical Contractor
3,941 satisfied customers
What would be the reason to have an open junction box in the
what would be the reason to have an open junction box in the crawl space of a house? … read more
Kevin
Kevin
Licensed Electrical Contractor
3,941 satisfied customers
6 wires in junction box. 2 2 black 2 copper. About 10
Hook up light, flip switch and it powers off entire living room… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
What is minimum size junction box for 200amp service line.
what is minimum size junction box for 200amp service line. … read more
Sam I
Sam I
Electrician
B.S.
472 satisfied customers
One junction box for pendant light has 1, 1 black and 1
One junction box for pendant light has 1 white, 1 black and 1 ground. The pendant light junction box has 2 whites, 2 blacks and one ground. What do I do differently with the box that has the two sets?… read more
Kevin
Kevin
Licensed Electrical Contractor
3,941 satisfied customers
Adding a receptacle to an existing junction box. The old
Adding a receptacle to an existing junction box. The old receptacle tests good but the new receptacle is showing an open hot/ ground. Getting continuity when I test the hot and ground wires. What's up… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Was just informed I might require a Hard Wire Junction box
Was just informed I might require a Hard Wire Junction box with installation of a water heater. Would like to know appx cost for this job and recommendations of electricians in my area … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x