I was away for 5 days and when I returned the AC was not

Customer Question
working. I checked the main...
I was away for 5 days and when I returned the AC was not working. I checked the main fuse panel and found that the ac breaker had switched to off. I switched it to on , the ac ran for 30 sec and then the breaker switched off again . I changed the capacitor, contactor and hard starter and 60 amp circuit breaker. I checked the compressor with a continuity meter and found continuity on all terminals. I just switched the power back on and all I got was a spark at the panel and the breaker switched off again.
Submitted: 1 year ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 4 minutes by:
8/5/2016
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago
ProGrade
ProGrade, Certified Electrical Contractor
Category: Electrical
Satisfied Customers: 565
Experience: 28+ years exp. - installation, troubleshooting, & repair of commercial, & residential electrical systems.
Verified

Hi Customer, welcome to justanswer.com

Checki g for continuity is good but with the symptoms you describe, you should check each terminal on the compressor and on the condensor fan to ground. If you find a problem on the compressor, obviously you will need an HVAC Tech on site. If you find a problem with the condensor fan, you can probably replace it wire for wire if you can find a motor that is an exact match.

Please let me know if you have any questions.

Thank you

Ask Your Own Electrical Question
Customer reply replied 1 year ago
I checked the compressor using a continuity meter and touching each of the terminals of of the compressor
Customer reply replied 1 year ago
Each time i looked for continuity between any two of the terminals i got a beep . How would I check the condensor fan
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

I understand that and it is a very good start but there is much more to testing the compressor then checking between the terminals.

1) you should disconnect the wire from each terminal and check each terminal to a good ground.

2) hopefully the wiring diagram is present and legible. If so, identify the common terminal the start terminal and the Run terminal.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Here is how I wired everything back
Compressor
Purple wire to Herm on capacitor
Red wire to contactor
black wire to contactorFan
Orange wire to "C" on capacitor
Brown wire to Fan on capacitor
Black wire to Black on contactorHard Start
Black to Herm on capacitor
Black to "c" on capacitorContactorRed side orange to "c" on capacitor
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

After identifying the compressor terminals check the resistance between each of the terminals and let me know what the reading is.

To check the fan get a reading from each power terminal on the fan to ground and let me know what that reading is.

For both of these tests you would use the ohmmeter sat on the R X 1 scale

Ask Your Own Electrical Question
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

If when testing the fan leads or the compressor terminals to ground you get a very low reading that device is defective and will need to be replaced

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Hello . I have a Radio shack digital multimeter . I set the meter of ohms On the compressor terminals I do not see any marks I had the following reading
Black 00.7, purple 01.9 and red 01.6 . I did not get any reading on each of the fan terminals
Customer reply replied 1 year ago
hello??
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

The readings on the compressor look good.

If the unit has a safety disconnect turn it off then turn your breaker on and see if it holds and let me know

Ask Your Own Electrical Question
Customer reply replied 1 year ago
i turned off the safety disconnect and turned back on the breaker and the air handler is blowing
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

Is this a package unit or a split system?

Reconnect the compressor wires and see if it trips or runs, thanks

Ask Your Own Electrical Question
Customer reply replied 1 year ago
maybe i mis wired something05 August 2016 05:06
Here is how I wired everything back
Compressor
Purple wire to Herm on capacitor
Red wire to contactor
black wire to contactorFan
Orange wire to "C" on capacitor
Brown wire to Fan on capacitor
Black wire to Black on contactorHard Start
Black to Herm on capacitor
Black to "c" on capacitorContactorRed side orange to "c" on capacitor
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

Perhaps you did mis-wire something. None of those colors mean anything without the wiring diagram from the unit are you able to find that and if so could you upload a picture

Ask Your Own Electrical Question
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

Thank you, I need the wiring diagram

Ask Your Own Electrical Question
Customer reply replied 1 year ago
I did not see your earlier note. This is a split unit, the air handler is inside and the compressor is outside . do you want me to turn the quick disconnect breaker on??
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

Yes, try it if you think you have the wiring right. That seems to be the only problem. Get the wiring right & it should run.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
when I turned on the quick disconnect breaker the main ac breaker switched off again
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

Something is wired wrong or shorted to ground. Sounds like it's a problem with the wiring but I cannot see enough in the picture. Can you send a picture of the area behind rhe contactor so I can see what those wires do.

Thanks

Ask Your Own Electrical Question
Customer reply replied 1 year ago
another
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

Got 'em, let me look at them & I will reply, thanks

Ask Your Own Electrical Question
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

Use Drawing 3 - Single-Phase wiring diagram.

Can you take a clear picture of the compressor terminals then enlarge it and look for markings on the terminals. If you can see the terminal identification check your connections against the wiring diagram. Black to C or Common Terminal, Purple to S or Start Terminal, & Red to R or Run Terminal.

And...does the hard start kit only have two wires? Can you send a picture of the wiring diagram o the hard start kit?

So far, I do not see anything mis-wired.

Thanks

Ask Your Own Electrical Question
Customer reply replied 1 year ago
images
Customer reply replied 1 year ago
I redid all the wiring according to the 1 phase diag. The only connection to clarify is the Start Capacitor. If I read it right is go to the com on capacitor and herm on capacitor
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

Thanks, look at the compressor, there is a Terminal marked "C", this is the common terminal, it gets the black wire. There is another Terminal marked "R", this is the run terminal, it gets the Red wire. The remaining terminal is the Start terminal and it gets the Purple wire.

Ask Your Own Electrical Question
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

After getting the compressor wiring correct, try running without the hard start kit...the capacitor in it could be shorted causing the problem.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
That is a new hard start kit , that i purchased today. I am still confused as to what would have caused the breaker to switch off while we were away??? I just turned the quick disconnect switch on and it threw the ac breaker
Customer reply replied 1 year ago
From the compressor I have the blk going to the left terminal on the contactor , the Purple going to the herm on the capacitor , and the red going to the right terminal on the contactor
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

That is what we are tryi g to find, so far, have eliminated the compressor per the readings from the ohmmeter. Not let's eliminate the hard start kit. Next, disconnect the wires from the compressor again, isolate them fromeach other & from ground, then see if breaker will hold & let me know. This will verify the ohmmeter readings.

Ask Your Own Electrical Question
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

If the breaker holds, reconnect the compressor wires, then remove the wires from the capacitor, remember where they go, isolate them from each other & from ground then try breaker.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
when i disconnected the hard start the breaker and turned on the quick disconnect the main breaker turned off, I concected it back and then disconnected the compressor , I heard a rumbling in the compresor for about 30 sec and then it went off but the breaker did not switch off
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

I would leave the new start capacitor off/disconnected for now.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
I made a mistake with the last test. I had disconnected one wire for the compressor and two from the fan. I reconnected the fan wires and disconnected the three wires for the compressor. When I turned on the quick disconnect breaker, with the hard start and fan connected the fan went on and the main breaker did not switch off.
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

Sounds like you have a bad compressor after all.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
When everythiing was disconnected from the capacitor , the red wire was still connected from the compressor to the contactor , I turned on the quick disconnect and the main ac breaker blew . Is it possible to just change the compressor??
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

Yes, should be able to just replace compressor

Ask Your Own Electrical Question
Customer reply replied 1 year ago
my system , per the info pale that I sent you used r22, is it possible to replace it with a r410 compressor??
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

Some systems can be converted, others are too expensive to convert. Your HVAC Tech can tell if yours is a candidate for conversion. It may be less expensive to make the change to a new unit which would also operate more efficiently and have a new warranty.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
thanks
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

You are very welcome.

Ask Your Own Electrical Question
Electrician: ProGrade, Certified Electrical Contractor replied 1 year ago

Please remember to rate my service, thank you

Ask Your Own Electrical Question
Ask ProGrade Your Own Question
ProGrade
ProGrade
ProGrade, Certified Electrical Contractor
Category: Electrical
Satisfied Customers: 565
565 Satisfied Customers
Experience: 28+ years exp. - installation, troubleshooting, & repair of commercial, & residential electrical systems.

ProGrade is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,425 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,780 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,828 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I'm wiring a 230v compressor motor, and need to verify that
I'm wiring a 230v compressor motor, and need to verify that I have wires properly combined. I will provide motor information below. Thank youMake: Steveco Farm Duty Model: MS182C17FB2A Labeled Wires P… read more
George Smith
George Smith
Vocational, Technical or Trade School
286 satisfied customers
Capacitor and switch unable to identify, no parts are
capacitor and switch unable to identify JA: I'll do all I can to help. How long have you been dealing with this? Customer: no parts are available locally JA: Do you plan on doing the work yourself? Cu… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,780 satisfied customers
I want to remove a double circuit breaker from electrical
i want to remove a double circuit breaker from electrical panel … read more
Sam I
Sam I
Electrician
B.S.
442 satisfied customers
I am trying to replace a five wire capacitor on a ceiling
i am trying to replace a five wire capacitor on a ceiling fan. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,828 satisfied customers
Can a General Electric type THQL-GCI hot tub circuit breaker
can a General Electric type THQL-GCI hot tub circuit breaker be tested with an ohm meter. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,828 satisfied customers
I have 2 dedicated circuits in my circuit breaker box that
I have 2 dedicated circuits in my circuit breaker box that are 240V, they each have 2 hot wires going to them. The circuit is terminated to an individual plug (L6-20R) for each circuit. The device I'm… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,828 satisfied customers
I'm trying to move a circuit breaker box in a place I'd like
I'm trying to move a circuit breaker box in a place I'd like to put a bathroom. Knowing it isn't code to have one in a bathroom, is a junction box ok? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,780 satisfied customers
Need to wire a 240 volt single phase 3 wire motor. Just
the motor has 2 connections for the hot wire and also has a common… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,780 satisfied customers
What is the function that makes a circuit breaker different
what is the function that makes a circuit breaker different from a switch so that it is able to break fault current … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,828 satisfied customers
Was wondering which circuit breaker I should look into
Hello, was wondering which circuit breaker I should look into replacing. As it stands my Dryer flips the circuit breaker for the upstairs bedrooms. Should I look into replacing the circuit breaker for… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,828 satisfied customers
My circuit breaker was buzzing, so I pushed the test button.
Hello. My circuit breaker was buzzing, so I pushed the test button. This switched all the sockets off in my house but left all the lights on. When I flipped the breaker switch back, al the sockets cam… read more
Sam I
Sam I
Electrician
B.S.
442 satisfied customers
My circuit breaker is tripped and will not reset. I've
My circuit breaker is tripped and will not reset. I've checked wiring to outlets looks okay. At the electrical panel there is no power to breaker itself. I check other breakers and the have power. Any… read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
996 satisfied customers
Honda EU7000is has 30 amp line with circuit breaker with
Honda EU7000is has 30 amp line with circuit breaker with each line up to 22.6 amps. Questions is 32 amp draw too large and will trip circuit breaker and can circuit breaker be upgraded to 40 amp to al… read more
Sam I
Sam I
Electrician
B.S.
442 satisfied customers
I have a well pump wired into a 240v/20a circuit breaker. C/
I have a well pump wired into a 240v/20a circuit breaker. C/B has white wire, black wire, ground wire. Pressure switch on well pump has same...black, white. ground. Output from pressure switch to pump… read more
ProGrade
ProGrade
Certified Electrical Contractor
565 satisfied customers
I've checked ALL circuit breaker with a voltage meter. They
I've checked ALL circuit breaker with a voltage meter. They are good, but I still don't have power in both bathrooms. Not in the outlets or ceiling lights. Can you help. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,828 satisfied customers
The circuit breaker tripped controlling all the electricity
The circuit breaker tripped controlling all the electricity in my son's bedroom. This circuit also controls the recessed lighting in the dining room. The only way I can reset the circuit breaker is if… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,780 satisfied customers
I am trying to wire a Switch to a motor. Switch is a
I am trying to wire a Switch to a motor. Switch is a magnetic 3hp single phase 18-26 amp to a single phase 3hp 220 v motor there are four wires from the motor blue, brown, black and green/yellow… read more
Sam I
Sam I
Electrician
B.S.
442 satisfied customers
What is the nec for wiring a control panel circuit breaker.
What is the nec for wiring a control panel circuit breaker. Can you feed the line into the bottom and have the load come out the top of the breaker… read more
George Smith
George Smith
Vocational, Technical or Trade School
286 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x