Hello,I have a Franklin QD control box wired into a breaker switch in a subpanel that has wires going up to my water tank to control a float switch and wires going down to my pump to shut it off when the float switch reaches its cutoff point. My question is; How do I use the power going down to the pump from the control box to wire in a second subpanel at the pump where I can put an extra outlet to use when the pump isnt running?
Submitted: 1 year ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 6 minutes by:
7/26/2016
Electrician: Mike G., Master Electrician replied 1 year ago
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 7,759
Experience: Proven Professional 48 years Experience
Verified

Hi, I'm Mike G and I'll be assisting you. To accomplish getting power for an always hot receptacle you'll need to pick up the circuit ahead of the control box and either run a seperate run to that receptacle or if the run to the pump outlet is in conduit, run the circuits together.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
You are saying I need to run new wire, seperate from what is in the control box? I have already achieved the first step, which was to have the pump powered from a new breaker switch next to the pump after the control box. Now I just want to be able to power another switch and outlet while the pump switch is off using the same power. That isnt possible?
Electrician: Mike G., Master Electrician replied 1 year ago

It's possible. All you need to do is extend the feed before the connection to the control terminations to the additional outlet.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Is that possible to splice the wires inside the control box to do that, or do I need an entirely new wire to the new outlet?
Electrician: Mike G., Master Electrician replied 1 year ago

Splice them at their entry into the control box

Ask Your Own Electrical Question
Customer reply replied 1 year ago
I just want to use the wires that are there, even if it means the entire subpanel box at the pump is being controlled by the float switch. This is just temporary, so for the mean time I can just make sure the tank is never full until I install a more permanent sub-box, which will require new wire buried in conduit coming from an entirely different main panel. What Im not understanding is how to change the way the power is flowing through the wires coming out of the control terminal that go to the pump. All of the wires in the conduit going to the pump are coming from the control terminal, so how can I splice the hot wires from the terminal with the feed before the connections without interfering with the control box outputs to the pump?
Customer reply replied 1 year ago
Ive already got power to the subpanel, my problem is that the other breaker to the new outlet only has power when the breaker to the pump is on. How do I wire it so that when the breaker to the pump is off, the new breaker will remain on?
Electrician: Mike G., Master Electrician replied 1 year ago

At the control box you have incoming feed and put going control wires. By splicing the incoming and running it along with the controlled wires will give you both outlets that you want.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Which requires new wire?
Customer reply replied 1 year ago
What do you mean by 'put going control wires'?
Electrician: Mike G., Master Electrician replied 1 year ago

Sorry, typo..... out going controlled wires.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
do I need new wire? Because my whole reasoning for doing this was to have temporary power while I work on setting up a whole new feed from a different source.
Customer reply replied 1 year ago
Or are you saying to just jump the terminal from incoming feed to the the outgoing wires? Therefore splicing the the main power from the switch back into one of the wires going down to the pump?
Customer reply replied 1 year ago
Hello? Still there?
Customer reply replied 1 year ago
Any chance you could answer my question? Can I just use the existing wires, or do I need to run an entirely new wire through the conduit that is spliced with the incoming feed to the control terminal, therefore bypassing the controlled wires?
Customer reply replied 1 year ago
Alright, if you cant answer my question I don't have all day to wait around for your response. You got 2 minutes.
Electrician: Mike G., Master Electrician replied 1 year ago

If you want to, yes you can. I thought you wanted an additional hot outlet. You can also put a double pole double through switch in the control box allowing for the single outlet to be auto it hot all the time.

Ask Your Own Electrical Question
Electrician: Mike G., Master Electrician replied 1 year ago

I can only reply to you when the message gets to me.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
in that case, why is it that when the breaker to the pump is off, there is no power to the secondary breaker for the new outlet? Did i wire it wrong, or does the control terminal require the pumps power to be engaged in order for full power to be present. Its confusing.
Electrician: Mike G., Master Electrician replied 1 year ago

You should have power to the control and from there to the pump. A splice on the power to bypass the control will give you power to the alternate. Now this can all be accomplished for use with a switch in the control box. It would allow the pump to be auto or manual.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
the control box is very small. About 4 inches by 6 inches and full of wires. Can I have the DPDT switch outside the box and wire the incoming feeds from breaker box to it and have doubled outgoing feeds to the control; one set going to control terminal and one set bypassing control terminal and reconnecting with a splice into outgoing from control terminal to breaker box at the pump. Then when I switch the DPDT to the spliced connection, I will get full power to the Breaker box at the pump and be able to use the secondary breaker to power an outlet without the pump breaker being switched on? I this correct or am i missing something?
Electrician: Mike G., Master Electrician replied 1 year ago

To have a working outlet at your second breaker box, an additional set of wires would be necessary if you want the second breaker idependant. I don't know why there is a second panel anyway.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
The Main panel is at my house, where the control box is hooked up, and the secondary panel is 500 ft below at the pump. I hooked up this panel so I could route the power that was originally going directly to the pump into the box instead and split the connection into two breaker switches, of which one is wired directly to the pump. So, why does the pump breaker have to be on, in order for the second breaker to have power? I don't get it. At this time I dont mind if the float switch at my tank is governing the power to the panel a the pump through the control terminal, I just want to be able to switch off the pump at the box next to the pump and use that power for a secondary outlet. Does that make sense?
Electrician: Mike G., Master Electrician replied 1 year ago

There in lies the problem. Installing the second breaker box and expecting to have an outlet live all the time when the feed down to the new breaker is controlled from the house is impossable. The feed is either hot or not depending on the control box and the float switch. You'll need a second circuit to accomplish what you intend.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
I think you are misunderstanding what I mean. The power from the control box, is going into a sub panel. In the sub panel is a breaker switch which is wired to the pump. There is also a breaker that is wired to an outlet. Im getting power to the pump through the breaker no problem. However, when that breaker to the pump is off, the secondary breaker will not power the outlet. So, why cant I simply capture the power in the sub-panel and route it to whichever breaker is on at the time. It seems stupidly simple.
Electrician: Mike G., Master Electrician replied 1 year ago

Float is at the house and determines when power is going to pump. Installing a panel with independant breakers to pump and another to an outlet. Can't have power without the float switch closed. You can only have the 2 outlets powered depending on the float switch.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
the float switch cuts power when the tank is full, so if the pump is not being powered, and the tank isn't full, there should be no interruption with the power flow to the secondary switch, right?
Customer reply replied 1 year ago
I suppose this is an odd topic, but I have to depart from the conversation for a bit. Could we pick it up another time? I feel like we are getting close to solving this problem.
Electrician: Mike G., Master Electrician replied 1 year ago

Come back when you can.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Gotta go. I will talk to you later Mike. Thanks for putting up with my strange electrical inquiries.
Electrician: Mike G., Master Electrician replied 1 year ago

Very good.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
hey mike, any chance you are around?
Electrician: Mike G., Master Electrician replied 1 year ago

I'm online.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
I thought about what you said and came up with the idea to splice the wires before entry, and tie them into DPDT switch that is connected to a set of wires that splice into the outgoing feed down to the new breaker box. My question is, how do I prevent the spliced connection from feeding back into the Control terminal? Do I need two switches? One at entry from main breaker to control box and one at exit from control box down to subpanel? That was the only way I could reason how to control the flow of current to completely bypass the controlbox and therefore send the positive/negative/ground feed from main breaker to power the secondary breaker in the panel by the pump.
Customer reply replied 1 year ago
I already attempted to completely bypass the control panel, but when I did, I could only get power to the secondary breaker for extra outlet and no longer to the new breaker switch for pump. Whereas before, I could only get power the pump breaker independently and then to the secondary breaker switch while the Pump switch was on.
Electrician: Mike G., Master Electrician replied 1 year ago

Let me ask exactly what you have with the float. The reason being that with a bladder tank and a pressure switch at tge pump the single feed would be able to power the sub panel. But there is another issue doing that, the sub panel needs a 4 wire feed and a driven ground rod.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Im not sure what you are asking? Could you rephrase your question? You want to know what type of float switch I have, and weather or not I have a ground rod at my sub-panel?
Electrician: Mike G., Master Electrician replied 1 year ago

It may be faster and better for us to speak via a phone. I'll send the offer.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Can you answer my question about using the switches to bypass the control box and pickup the connection without feedback into control box?
Customer reply replied 1 year ago
I already know that the pump will run the way it is wired into the sub-panel breaker from the connection through the control box, and so will the switch if the control-box is bypassed.
Customer reply replied 1 year ago
I just need to know if two DPDT switches will work to do the bypass?
Electrician: Mike G., Master Electrician replied 1 year ago

The use of switches and a panel is not workable. You have one controlled circuit and you want to impossibly modify it

I think we've come to the end. I'll opt out because we aren't getting anywhere. Good luck.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
I guess I will have to not rate you then.
Ask Mike G. Your Own Question
Mike G.
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 7,759
7,759 Satisfied Customers
Experience: Proven Professional 48 years Experience

Mike G. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,425 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,940 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,759 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,715 satisfied customers

30 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
Can I add a 90 elbow to the main conduit so that I can raise
can I add a 90 elbow to the main conduit so that I can raise that conduit the conduit is running vertical and i need some height under the conduit … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
Wiring diagram for outlet on a switch the to a light on same
wiring diagram for outlet on a switch the to a light on same switch … read more
David Bowden
David Bowden
Owner
320 satisfied customers
Which wires go where? In replacing a switch and outlet in
Which wires go where? In replacing a switch and outlet in the bathroom I mistakenly didn't label the wires before I ran down to answer the door now I don't know where the three main lead wires into th… read more
Mike G.
Mike G.
Master Electrician
7,759 satisfied customers
I have a legrand adorne outlet I took out the old outlet
Hi I have a legrand adorne outlet I took out the old outlet which had a red and black both on hot and a white on white. I put the red and black on hot - first I put the two hot wires in opposite sides… read more
Sam I
Sam I
Electrician
B.S.
363 satisfied customers
I need to wire a switch and 2 outlets in same box) without
I need to wire a switch and 2 outlets in same box) without the switch controlling the outlets. The switch is for a ceiling light. Thanks. … read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
947 satisfied customers
Question on wiring GFCI outlet... Late 80's...and no. Outlet
outlet is under the sink...bottom outlet goes to switch on the wall… read more
Sam I
Sam I
Electrician
B.S.
363 satisfied customers
I have a Leviton T5225 combination switch/outlet and I want
I have a Leviton T5225 combination switch/outlet and I want to wire it so the switch controls the outlet. There is a break-off tab connecting the two black screws. There is another dual outlet in the … read more
Mike G.
Mike G.
Master Electrician
7,759 satisfied customers
I have a question related to electrical outlet combo switch,
i have a question related to electrical outlet combo switch … read more
Mike G.
Mike G.
Master Electrician
7,759 satisfied customers
I have a dedicated 10 amp romex line in conduit, going to a
I have a dedicated 10 amp romex line in conduit, going to a direct wired garbage disposer under my kitchen sink. I want to connect this line up to a single gang outlet box to make exchanging the dispo… read more
Sam I
Sam I
Electrician
B.S.
363 satisfied customers
How do Locate a reset switch for a GFCI outlet. One day
how do Locate a reset switch for a GFCI outlet JA: I'll do all I can to help. How long have you been dealing with this? Customer: one day JA: Do you plan on doing the work yourself? Customer: yes JA: … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
I took down a half wall with an outlet. the outlet was
i took down a half wall with an outlet. the outlet was connected to a 3 way switch and now the light will not come on. what should i do … read more
Mike G.
Mike G.
Master Electrician
7,759 satisfied customers
I am running 3 circuits inside of pvc conduit. 220v 30a
I am running 3 circuits inside of pvc conduit.220v 30a water heater 220v 15a ac 120v 20a receptaclecan I use 1 shared 10awg ground wire for all circuits?… read more
Mike G.
Mike G.
Master Electrician
7,759 satisfied customers
I have several outlets that seem to be in the same "switch"
hello there... I have several outlets that seem to be in the same "switch" in my panel. as it happens it is the bathroom, part of the kitchen, my bedroom, my children's bedroom and a hallway next to b… read more
Sam I
Sam I
Electrician
B.S.
363 satisfied customers
How much to install 100' of electrical line in a conduit if
how much to install 100' of electrical line in a conduit if the trench is already dug. Include the cost of wiring and adding a 50 Amp Circuit Breaker … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
I have a combination switch/outlet that I would like to wire
I have a combination switch/outlet that I would like to wire into a box so that the switch operates the outlet. what would the wiring diagram look like? Thx … read more
Mike G.
Mike G.
Master Electrician
7,759 satisfied customers
What size wire is needed to run underground in conduit to a
What size wire is needed to run underground in conduit to a garage about 60 feet from the main connection at the power pole? This would be connected to a subpanel in the garage. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
Our garbage disposal is plugged into a switched outlet below
Our garbage disposal is plugged into a switched outlet below our kitchen sink. On the left side of the outlet you have two silver screws plus green ground. A white conductor is wired to bottom screw. … read more
Mike G.
Mike G.
Master Electrician
7,759 satisfied customers
I have a switched outlet (a switch that comes before the
I have a switched outlet (a switch that comes before the outlet and turns the power to the outlet on and off). I want to remove the switch and replace it with a blank, thus capping the wires in the bo… read more
Mike G.
Mike G.
Master Electrician
7,759 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x