I have a 220V feeding my well pump outside. There are 3

Customer Question
wires, hot, neutral and ground...
I have a 220V feeding my well pump outside. There are 3 wires, hot, neutral and ground. I would like to feed (2) 110V GFCI receptacles at the pool for the sand filter and pump. How do I do this?
Submitted: 1 year ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 12 minutes by:
7/14/2016
Electrician: Mike G., Master Electrician replied 1 year ago
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 7,773
Experience: Proven Professional 48 years Experience
Verified
Hi, I'm Mike G and I'll be assisting you. First thing is if you have a 220V feed, you don't have a neutral. It is 2 hots and a ground using the white wire as a hot. Next, pool equipment needs to be on its own circuit with a GFCI and an insulated ground wire. You need to run a new circuit with the wire size dependant on the length of the run.
Ask Your Own Electrical Question
Customer reply replied 1 year ago
Can I install a sub panel at the well and feed it by the wires I have out there and then install 20amp circuit breakers to feed the pool equipment?
Electrician: Mike G., Master Electrician replied 1 year ago

What size circuit do you have there?

What is the load for the well?

What are the number of wires on the existing feeder?

How are is the pool from the proposed panel?

Ask Your Own Electrical Question
Customer reply replied 1 year ago
I'm not sure about the well, I will have to check when I get home from work around 7pm, est. I'm located in North Carolina.
The well is fed from circuit breaker in the house.
The existing feeder has 3 wires, black, white and copper (ground) coming from the circuit breaker in the house to the well pump.
Pool is about 20 feet from the well house.
Pool information:
Sand Filter Pump – 3A, 288W, 120V, runs 8 hours a day
Chlorinator – 1.1A, 125W, 120V, runs 4 hours a day
Electrician: Mike G., Master Electrician replied 1 year ago

You are short 1 wire and the wire size is insufficiant for installing a sub panel. You need to run a new circuit or feeder.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
I don't have any more circuits available in the house panel.
How do I add the extra wire?
Electrician: Mike G., Master Electrician replied 1 year ago

You don't understand me. The size of the wire to the well was no doubt sized for Tyne well only. It not only being to small it is short 1 wire. Both make it advisable to run a new feeder if you want a sub panel or you can only run a new circuit for the pool. From the way you asked the question, I assume that you don't know the other requirements for a pool wiring. Equipotential bonding and distances for outlets and disconnects. Pool wiring has to be right all the time. Any thing missed will expose you to a shock hazard.

Ask Your Own Electrical Question
Ask Mike G. Your Own Question
Mike G.
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 7,773
7,773 Satisfied Customers
Experience: Proven Professional 48 years Experience

Mike G. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,425 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,940 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,773 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,715 satisfied customers

30 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
Can a General Electric type THQL-GCI hot tub circuit breaker
can a General Electric type THQL-GCI hot tub circuit breaker be tested with an ohm meter. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
I have 2 dedicated circuits in my circuit breaker box that
I have 2 dedicated circuits in my circuit breaker box that are 240V, they each have 2 hot wires going to them. The circuit is terminated to an individual plug (L6-20R) for each circuit. The device I'm… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
I have 415 amps worth of branch circuit breakers. what size
I have 415 amps worth of branch circuit breakers. what size service do i need for my house? is 200 sufficient … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
I'm trying to move a circuit breaker box in a place I'd like
I'm trying to move a circuit breaker box in a place I'd like to put a bathroom. Knowing it isn't code to have one in a bathroom, is a junction box ok? … read more
Mike G.
Mike G.
Master Electrician
7,773 satisfied customers
How do I determine the correct size circuit breaker panel
How do I determine the correct size circuit breaker panel for an stand alone workshop. I don't suspect I would draw more than 20 amps at any given time, but do I need a box assumes everything is turne… read more
Mike G.
Mike G.
Master Electrician
7,773 satisfied customers
Wiring diagram for outlet on a switch the to a light on same
wiring diagram for outlet on a switch the to a light on same switch … read more
David Bowden
David Bowden
Owner
331 satisfied customers
Which wires go where? In replacing a switch and outlet in
Which wires go where? In replacing a switch and outlet in the bathroom I mistakenly didn't label the wires before I ran down to answer the door now I don't know where the three main lead wires into th… read more
Mike G.
Mike G.
Master Electrician
7,773 satisfied customers
What is the function that makes a circuit breaker different
what is the function that makes a circuit breaker different from a switch so that it is able to break fault current … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
Question on wiring GFCI outlet... Late 80's...and no. Outlet
outlet is under the sink...bottom outlet goes to switch on the wall… read more
Sam I
Sam I
Electrician
B.S.
374 satisfied customers
Was wondering which circuit breaker I should look into
Hello, was wondering which circuit breaker I should look into replacing. As it stands my Dryer flips the circuit breaker for the upstairs bedrooms. Should I look into replacing the circuit breaker for… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
My circuit breaker is tripped and will not reset. I've
My circuit breaker is tripped and will not reset. I've checked wiring to outlets looks okay. At the electrical panel there is no power to breaker itself. I check other breakers and the have power. Any… read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
955 satisfied customers
Honda EU7000is has 30 amp line with circuit breaker with
Honda EU7000is has 30 amp line with circuit breaker with each line up to 22.6 amps. Questions is 32 amp draw too large and will trip circuit breaker and can circuit breaker be upgraded to 40 amp to al… read more
Sam I
Sam I
Electrician
B.S.
374 satisfied customers
I have a well pump wired into a 240v/20a circuit breaker. C/
I have a well pump wired into a 240v/20a circuit breaker. C/B has white wire, black wire, ground wire. Pressure switch on well pump has same...black, white. ground. Output from pressure switch to pump… read more
ProGrade
ProGrade
Electrical Contractor
564 satisfied customers
Wiring a gfci outlet in kitchen (had old normal outlet) and
Wiring a gfci outlet in kitchen (had old normal outlet) and have disposal and over sink light in same box. Power comes into outlet. There are also 3 other lines leaving to other outlets in kitchen. Wa… read more
Mike G.
Mike G.
Master Electrician
7,773 satisfied customers
I've checked ALL circuit breaker with a voltage meter. They
I've checked ALL circuit breaker with a voltage meter. They are good, but I still don't have power in both bathrooms. Not in the outlets or ceiling lights. Can you help. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
The circuit breaker tripped controlling all the electricity
The circuit breaker tripped controlling all the electricity in my son's bedroom. This circuit also controls the recessed lighting in the dining room. The only way I can reset the circuit breaker is if… read more
Mike G.
Mike G.
Master Electrician
7,773 satisfied customers
What is the nec for wiring a control panel circuit breaker.
What is the nec for wiring a control panel circuit breaker. Can you feed the line into the bottom and have the load come out the top of the breaker… read more
George Smith
George Smith
Vocational, Technical or Trade School
274 satisfied customers
Why does a circuit breaker trip trip and not the GFI outlet
Why does a circuit breaker trip trip and not the GFI outlet in a bathroom. … read more
Jason
Jason
Service Technician
Associate Degree
3,940 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x