I purchased Heatworks, model 1X the manual can be found with

Customer Question
Hello, I purchased Heatworks, model 1X...
Hello,
I purchased Heatworks, model 1X the manual can be found with this link:
https://cdn.shopify.com/s/files/1/0739/2987/files/model_1x_installation_manual.pdf?8527896642717297634
It is suppose to connect to the water heaters power supply. The problem I am having:
The wires going into the water heater are 10 gauge red, black and white. In the connection box of the water heater the white wire sits uncapped. I don’t know if this was a mistake by the water heater installer?
On page 6 and 7 there are diagrams. It appears that a white wire and black wire are going into the model 1x. I wanted to verify I take a 2/10 romex and connect the black and white from the connection box in the water heater then connect it to the model 1x. Do I just leave the red wire alone in the water heater?
I will include a diagram that I took a picture of that was on the side of the model 1x.
Submitted: 1 year ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 8 minutes by:
7/13/2016
Electrician: JACUSTOMER-1eysp1u4-,
 replied 1 year ago
JACUSTOMER-1eysp1u4-
Category: Electrical
Satisfied Customers: 41
Experience: Journeyman Electrician, Lead Man (Sub-Foreman) at Romanoff Electric
Verified

Hello welcome to Just Answer/Pearl , my name is***** and I will try to answer your electrical question today!

I will take a closer look at the link you posted , but normal water heater elements run off of line voltage in your home , 240 volts and do not usually require a white neutral wire (the black wire and the red wire if measured with a voltage meter will read 120 volts to the white wire if it is connected to the neutral bar in your electrical panel. the white wire is the circuit grounded conductor, where bare copper / green wires are the safety/ earth grounding conductor. Black, reds , and whites carry the current in the circuit throughout your home.)

The first thing I will do is read your manual , but in the meantime make sure the nameplate/ sticker on your water heater says 120 or 240 volts, the black / white diagram you describe sounds like a 120 volt connection .

Ask Your Own Electrical Question
Electrician: JACUSTOMER-1eysp1u4-,
 replied 1 year ago

So this 1x water heater is a supplemental unit to your existing water heater like the manual describes ?

According to the diagram I saw the 1x will need 240 volts plus the white neutral, blacks and reds hooked together then each pair crimped with a tool and then the spade crimps are then tightened under the set screws for each line, where the neutral is similarly crimped with a pigtail to a neutral bar connection. One thing to check in your existing installation at your electrical panel, make sure the white wire in the romex that feeds the existing water heater, is connected to the neutral bar of your panel, whoever installed the old heater should have at least capped off the wire , to answer your original question.

Ask Your Own Electrical Question
Customer reply replied 1 year ago

according to the diagram I sent you I do not see where the reds get hooked together? it looks like black get hooked together, green ground gets hooked together and then the white is confusing. It shows white crimped to a red which as you said goes to the neutral bar. Although, it says power ln (L2) for the white wire coming in?

Can you help me understand this diagram?

Electrician: JACUSTOMER-1eysp1u4-,
 replied 1 year ago

Thank you very much for the color picture that very much changes things.

The middle connection / green wires are the grounding wires I referred to earlier, in most homes with romex cables they are the bare copper that will be needed to connect to the middle terminal.

As you are aware the real issue with the installation is the operating voltage of the 1x, can you find a sticker or tag on the new unit which states it's operating voltage. I will look at the manual again but it's always best to see what the actual 1x / unit requires voltage wise. L2 can be a neutral which means this is a 120 volt unit, but I believe it's probably 240V like most water heaters and the red wire will be L2, that's why knowing the voltage of the unit is so important to determine which wire goes to the L2 connection.

Ask Your Own Electrical Question
Electrician: JACUSTOMER-1eysp1u4-,
 replied 1 year ago

Okay , I'm beginning to understand this unit now, it has a split phase operation and an input rating of 110-250 volts , that would mean L2 is the red wire NOT the white wire in the 10-3 romex, it can be capped off and not used in this installation. I determined this by the specs at the back of the online manual.

Ask Your Own Electrical Question
Electrician: JACUSTOMER-1eysp1u4-,
 replied 1 year ago

This is literally a daisy chain operation, whichever leads are connected to the existing water heater will make a parallel stop in your new unit then continue on to the old unit, L1's are blacks, L2's are reds , and the ground goes to the middle terminal under the lug screws. L2 going to you old heater is being controlled/switched by the 1x , basically It will monitor your old heater and only use it if it needs it/ the demand of your home needs the full size heater. Literally does what it says: maximizing your hot water needs without using unneeded electricity.

Ask Your Own Electrical Question
Electrician: JACUSTOMER-1eysp1u4-,
 replied 1 year ago

Let me know if you have any further questions, this thread will remain open for some time. Thank you for using Just Answer/Pearl, please do not forget to rate me , and have a wonderful day !

Ask Your Own Electrical Question
Ask JACUSTOMER-1eysp1u4- Your Own Question
JACUSTOMER-1eysp1u4-
JACUSTOMER-1eysp1u4-
JACUSTOMER-1eysp1u4-
Category: Electrical
Satisfied Customers: 41
41 Satisfied Customers
Experience: Journeyman Electrician, Lead Man (Sub-Foreman) at Romanoff Electric

JACUSTOMER-1eysp1u4- is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,425 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,940 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,603 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,715 satisfied customers

30 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
MAZON Harbor Breeze 3 blade ceiling fan, w/remote, 44", Need
MAZON Harbor Breeze 3 blade ceiling fan , w/remote, 44", Need replacement BULB … read more
David Bowden
David Bowden
Owner
325 satisfied customers
I have a 22.5 cu in plastic box and want to put 2 14-3 and 2
I have a 22.5 cu in plastic box and want to put 2 14-3 and 2 14-2 wires plus a 3 way switch in, is this ok … read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
This is so weird... I turned on the light/fan in my bedroom,
This is so weird... I turned on the light/fan in my bedroom, the lightswitch sparked and the lights on the fan went out, but the fan still worked. My husband replaced the switch and the lights worked … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Im trying to install a decora smart dimmer switch. 2 hour. I
I wired it black to black white to white and the ground to the box… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I'm planning to supply power to 34 more sites on our rv
I'm planning to supply power to 34 more sites on our rv park. Supply 50 amp service to all. Covering 400 ft to 90 ft area approximately. Planning to build a power house at one end of the 400 ft rectan… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Is it code to have a three pole 20 amp breaker which
Is it code to have a three pole 20 amp breaker which supplies multiple receptacles on a commercial job? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
The ceiling fan leaks power into pull chains. I have
The ceiling fan leaks power into pull chains. I have disconnected the fan, put it on the table and used an old appliance cable. Reconnect all wires to fan and plug it in an outlet. I have the same pro… read more
George Smith
George Smith
Vocational, Technical or Trade School
273 satisfied customers
I am installing a GE Oven/Microwave combination, model#
I am installing a GE Oven/Microwave combination, model# ***** rated at 7.2kW @ 240V. I currently have a 30A breaker feeding 240V via 10/3 wiring. The GE spec calls for a 30A breaker @ 240V. Question i… read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
I'm installing a solar array and need to know the size wire
I'm installing a solar array and need to know the size wire to run from the 80 amp sub panel at solar array to the main breaker box / disconnect. The run is about 200 feet. I expect to install the wir… read more
Wayne Roberts
Wayne Roberts
Electrical Trade
82 satisfied customers
The Master Electrician Grounding between meter base and main
This is for Mike the Master Electrician Grounding between meter base and main circuit panel via metal conduit requires grounding pipe as well as neutral / and panel bonds. If using PVC, no need to gro… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Can a General Electric type THQL-GCI hot tub circuit breaker
can a General Electric type THQL-GCI hot tub circuit breaker be tested with an ohm meter. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
Can I obtain 5 feet of the high temp 18 gauge insulated wire
Can I obtain 5 feet of the high temp 18 gauge insulated wire from you to have a lamp repairman rewire 4 kitchen lamps I purchased from A Lightolier sales rep approx 40 years ago.At that time I was an … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I have 3 70 watt lamps in wired series and the last one will
I have 3 70 watt lamps in wired series and the last one will not light … read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
It's a 50 room motel shut down for zillions of violations.
It's a 50 room motel shut down for zillions of violations. Presently wired in Romex...some has mentioned that if occupied by more than 65 people ...I have to use my cable.… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I am installing three 30 amp 208volt receptacles, to be used
I am installing three 30 amp 208volt receptacles, to be used for Window Air Conditioners. I would like to do this with 1 run of 3/4" EMT, can I do this with #10 wire? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I have a and 1/2 hp that I want to use on a boat lift. 120
I have a smith and jones 1/2 hp that I want to use on a boat lift. 120 v. I need to be able to reverse the direction using the existing switch. Is the a simple explanation as to how this should be wir… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
You provided a 3-way lighting circuit for my steel building
Hello, you provided a 3-way lighting circuit for my steel building workshop that was very helpful.For some reason I am having a mental block on how to wire up a bathroom GFI outlet, light, fan and swi… read more
mrromex
mrromex
field supervisor
5 years of college courses
281 satisfied customers
I'm trying to install a Utilitech TM-097 wall timer to
Hi I'm trying to install a Utilitech TM-097 wall timer to control the lights outside my garage. The light switch box had two switches: one for lights inside garage and one for the outside lights. The … read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x