I have a square d main plug on neutral ready I plan on using as a subpanel. I know I need to isolate the neutral and ground. I believe I need to purchase ground bus bars separately. Is this correct? Will I still be able to use the afci's without the pigtail? Also, do I need to isolate the neutral from the case? If so, how? I don't see a bonding screw. As for the main ground wire. What size do I need? It's 100amp sub and has 2/0 feed. Does it connect to the main panel? If so, what's the point of isolating the neutral from ground in the sub?
Thanks,
Brian
Submitted: 2 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 8 minutes by:
3/1/2016
Electrician: ProGrade, Certified Electrical Contractor replied 2 years ago
ProGrade
ProGrade, Certified Electrical Contractor
Category: Electrical
Satisfied Customers: 565
Experience: 28+ years exp. - installation, troubleshooting, & repair of commercial, & residential electrical systems.
Verified

Hi Brian, welcome to justanswer.com

Allen sub-panels that have a neutral load have to be fed with 4-wires supply and neutral & ground isolated from each other at the sub-panel and neutral isolated from ground. This is a safety requirement. If sub is only fed with 3-wire ad the neutral developed a problem, all metal parts of the sub and all grounded metal from the sub would be hot.

Should be a #6 Copper

Ask Your Own Electrical Question
Customer reply replied 2 years ago
i understand it needs a 4 wire feed. My main question is more about the new subpanel that I'm installing. I'm moving the old sub to a different location so decided to use a new one. Since it's not by the main panel I purchased a main to use as a sub so I could cut off power at either location. Being that it's a plug on neutral panel I don't see where you can isolate the neutral and ground by removing a bonding strap or ground screw. Do I need to purchase the ground bus bars separately? The brand is a square d plug on neutral. It's a 200 amp panel but will be fed with a 100 amp breaker.
Electrician: ProGrade, Certified Electrical Contractor replied 2 years ago

The plug on neutral speaks to the type of breaker only. You would use Square D breakers designed for use in plug on neutral panels, they do not have a pigtail, this helps clean up some of the clutter in the panel.

The main neutral lug & neutral bus work the same as all panels. A bonding screw is required to bond the neutral, without it, the neutral is isolated. You will need to purchase separate ground bar (s) for the ground wires. Does that clarify your concerns? Thanks Ken

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Is there a screw that bonds the neutral to the case itself that needs to be removed? If the neutral is connected to the case, and I add ground bars, they won't be isolated. This plug on neutral ready box seems to be designed differently than the old style.
Electrician: ProGrade, Certified Electrical Contractor replied 2 years ago

Shouldn't be anything to remove, the default is that it is not bonded. You would need to add/install the bonding screw if this was being used as a main panel.

Brian, I checked with my Square D Distributor, if you need this panel bonded you have to add a bonding screw/jumper. If you will install the ground bar (s) and keep neutrals & grounds separated you will be goid. Thanks Ken

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Thanks Ken.....when I researched online a lot of people mentioned removing the bonding strap or screw to use as a subpanel. I didn't know if the panel I purchased was different being that it's a plug on neutral ready. Your answer was exactly what I was looking for. One more quick question. The old subpanel has a separate ground rod. With the new location of the new sub it would be easier to run a ground to the main. Can I attach that to the ground bar inside the main or does it have to have it's own ground rod as to keep it from being part of the neutral/ground circuit.
Electrician: ProGrade, Certified Electrical Contractor replied 2 years ago

Glad to help. If the new sub-panel is in the same building a separate ground rod is not required, if it serves a detached building such as a garage or shop, the ground wire and a separate ground rod is required.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Does the ground wire feed from the subpanel connect directly to the ground did or can it be connected inside the main panel.
Electrician: ProGrade, Certified Electrical Contractor replied 2 years ago

Into the main panel

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Sorry but one more quick question. I just installed two ground bars. Do I need to run a jumper between the two or is the case basically the jumper.Thanks for all the great help!
Electrician: ProGrade, Certified Electrical Contractor replied 2 years ago

No need for a jump right if at least two screws were used to mount them.

Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask ProGrade Your Own Question
ProGrade
ProGrade
ProGrade, Certified Electrical Contractor
Category: Electrical
Satisfied Customers: 565
565 Satisfied Customers
Experience: 28+ years exp. - installation, troubleshooting, & repair of commercial, & residential electrical systems.

ProGrade is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,290 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,414 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I have a new square D Schneider homeline with neutral load
I have a new square D Schneider homeline with neutral load center. I am trying to figure out how to wire the breakers. On other panels bare would go to one side of the bar, white to the other bar, and… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
Can you pigtail the ground and neutral wires in a service
Can you pigtail the ground and neutral wires in a service panel … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I just installed a sub panel into a basement for a buddy, he
I just installed a sub panel into a basement for a buddy, he has a 200amp main, installed a 60amp to feed the sub panel, ran 6ga. New box has 100amp disconnect, two 15amp arc fault for lights, 4 20amp… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
Need to ask a little later when I'm in the panel location.
Need to ask a little later when I'm in the panel location. I'll get back to you, thanks … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
Question about installing a 40 AMP - three circuit subpanel
Question about installing a 40 AMP - three circuit subpanel in my shed a few feet from my house.… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I bought a 70 AMP Homeline Circuit breaker load center
I bought a 70 AMP Homeline Circuit breaker load center (subpanel) that I need to install in my attic. I have one 40AMP 240V and one 30 AMP 240V circuits that I want to redirect to the sub panel. I bou… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
If PV system is installed on a remote building, with the
If PV system is installed on a remote building, with the inverter backfeeding an existing sub-panel fed by a 4-wire feeder (L1, L2, N, G), should the neutral and ground in the subpanel be bonded toget… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I need to run a 100 AMP sub panel to an attached garage from
I need to run a 100 AMP sub panel to an attached garage from my 200 AMP main Panel. Trying to figure correct gauge for the wire to feed the box. Also please note I have a 200 AMP breaker at the meter … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
Relocating the 150A main service from the back of the house
Relocating the 150A main service from the back of the house to the back of the garage, which is nearer the power pole. The new main panel is a 200A Square D. I have run 2" conduit through the garage a… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
i had a 100 amp breaker on panel #1 feeding a 60 amp in panel
i had a 100 amp breaker on panel #1 feeding a 60 amp in panel #2 which fed the 12 breakers upstairs and did not disconnect grounding screw in panel #2 never had an issue....I have a downstairs 100 amp… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
The square d sub I bought for this does not have a ground bar.
The square d sub I bought for this does not have a ground bar. Do I need to install one? I am going to run a 10awg ground to the sub. sounds better.… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I need a simple answer on whats the difference between the
I need a simple answer on what's the difference between the neutral conductor buss bar and the ground bus bar (residential)… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
I have an existing 100amp service with a pony panel that is
I have an existing 100amp service with a pony panel that is full. I have 200 amp service to the house. I want to upgrade panel to 200amp and add a 100amp subpannel to a basement apartment. Should i ju… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I want to add a 100amp sub-panel in an attached garage. I
I want to add a 100amp sub-panel in an attached garage. I have 200amp service in the house now. What wire size do I need? The distance from the service panel to the sub-panel is approx. 30ft.… read more
mrromex
mrromex
field supervisor
5 years of college courses
281 satisfied customers
Im trying to wire a subpanel to an addition to my house, which
I'm trying to wire a subpanel to an addition to my house, which is AFCI. In the panel there is a small grounding bar and a large grounding bar...the large one is connected to an AWG#2 wire that goes t… read more
Craig
Craig
Electrical Director
Electrical Automation Technician
2,133 satisfied customers
I have a sub panel with only one bus for neutral and ground.I
I have a sub panel with only one bus for neutral and ground.I learned that the ground and neutral need to be isolated.Can I use a ground rod to the bus insted?… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
I want to run electrical power to a storage building. I will
I want to run electrical power to a storage building. I will use small hand held tools and a small window unit ac unit in the building. I would like to have an overhead light and 3 electrical outlets.… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
I am replacing an old 125 amp sub panel (Challenger). Its
I am replacing an old 125 amp sub panel (Challenger). It's run off the main on a double pole 100amp breaker and SER cable. I bought a 125 amp Siemens subpanel, 3 wire Type 1 that can be used as a main… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x