Powering rv sites in a rv park expansion, load calculations…

Customer Question
Powering rv sites in...

Powering rv sites in a rv park expansion

Contractor's Assistant: Sometimes electrical issues that that you think will be really complicated end up being easy to fix. The Electrician I'm going to connect you with knows all the tricks and shortcuts. Tell me a bit more about what's going on so we can help you best.

Load calculations for medium size RV sites and extra-large rv sites

Contractor's Assistant: Is there anything else the Electrician should be aware of?

Yes

Contractor's Assistant: What else should I tell the Electrician?

The owner of the park is asking to power the medium-size sites with a nominal service of 100 Amp and an actual of 50 Amp (204 V/1 Ph), but for the large or extra-large sites he wants 100 Amp nominal and 100 Amp actual . When I read table 551.73 on NEC, I do not get these same recommendations. If I listen to the owner, the size of the service is considerably higher than if I calculate it with the NEC.

Submitted: 2 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 32 minutes by:
2/29/2016
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,293
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) I agree with you. Nowhere within Article 551 does it state that RV sites must have 100 amp feeders. The NEC only states 20 amp, 30 amp and 50 amp sites. 100 amp feeder sites would be considered as "optional" in my code interpretation.

2) Article 551.71 (Type Receptacles Provided) states that a percentage of the total sites must be a mixture of the various feeder amperages.

3) Table 551.73(A) Demand Factors would also be applicable when calculating the site feeder and service entrance conductors.

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks.................Kevin:)

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Hello Kevin:
So what is your recommendation for the extra-large sites. For the medium sites, I have: 5 straight runs of 17 sites, 1 straight run of 16 sites, and 1 straight run of 15 sites. For the large and extra-large sites, I have 1 straight run of 9 sites, 1 straight run of 16 sites, and 1 straight run of 21 sites.All sites have a power tower comprised of (1) 20-Amp 1-pole breaker, (1) 30-Amp 2-pole breaker, and (1) 50-Amp 2-pole breaker.For the medium sites, I can run a feeder from a 200 Amp breaker to feed a group of 4 sites, or a 250 Amp breaker for 5 sites.
What would you do with the large and extra large? 200 Amp for 2 sites?..F.
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

1) Yes, installing either a 200 amp or a 250 amp feeder will satisfy the 50 amp sites.

2) For the medium sites you will have no other choice but to 1st satisfy article 551.71 (percentage breakdown on receptacle types) and then apply the demand factors.

3) I would then apply article 551.73 (D) Feeder circuit capacity. and calculate the larger sites (100 amp) separately and then apply the demand factor table. Since the total number of large sites = 46, use a demand factor of 41% ------> (36 plus sites) as shown in table 551.73(A).

4) Then total the 2 load calculations from above and size the service based on these 2 load calc's. By separating the 2 load calc's and then totaling them, this will satisfy 551.73(D).

Your thoughts?

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

1) Since the RV park owner is requesting for 100% demand on each of the 100 amp sites, that's gonna be a large increase on the total park service, not to mention your individual feeder runs. I recommend to show the customer article 551.73 and explain that the probability of all sites being filled to capacity and all using 100 amps each and simultaneously is highly unlikely. Thus the reason why the NEC developed the demand table.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
The problem is that all the extra large sites run the heating during the night. If you read the fine print notes FPN on the bottom of 551.73(C). It says (I use NEC 2002) that he demand factor may be inadequate in extreme weather areas. When the park has no extra large vacancies, the breakers trip. I need give them more than the 41% that you mentioned above. But the question is how much. If you go back to my listing, each straight run has its own panel, or I can add one if they don't already have it. This means that the demand factor is for fewer than 36-plus units. Also, if you read 551.73(A), what does "supply facility" mean? a power supply tower unit next to each RV? If that is the case, what load should I assume for each one of these stations? 9600 VA? or is this load for the 50 Amp breaker only? the power supply tower station does not have only a 50 Amp breaker but also a 30 Amp and a 20 Amp. So what load is the actual basis of calculation.
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

Thanks for the replies.

1) Where the tower has more than 1 receptacle, the calculated load shall be calculated only for the highest receptacle. If a 50 amp breaker, then the 9600 VA value will be used. 9600 VA will the basis of calculation per 551.73(A).....ie.......last sentence in the 1st paragraph (highest rated receptacle).

2) Yes, the supply facility will be the tower (the plug-in pedestal) located next to each RV site.

3) I'm using the 2011 NEC and it also shows the FPN for extreme hot or cold temperatures. In consideration of the FPN and this being a case-by-case basis. I would ask the RV owner to quantify the average site capacity or future site capacity during the summer and winter months. Logically, I would start out by splitting the 36 sites by 50% down to 18 sites, thus increasing the demand factor from 41% to 47% as a minimum. This will provide an increase in amps. Once again, in cases such as this, I think obtaining an average capacity during the summer and winter months would be in order and appropriate to confirm from the park owner. So the $64K question for the owner is "will all 46 of the large sites be utilized all of the time" during summer and winter months? I doubt it:)

Keep in mind, you can only design the electrical distribution system based upon the NEC requirements as well as the estimated loads. How many RV rigs that stay in the park are going to have 240 volt electric hot water heaters, 240 volt electric dryers, 240 volt ranges, 240 volt heaters, etc. all running simultaneously? Far and few in between will have these amenities in my opinion. For example, even a 100 amp service on a 1700 sq feet house with electric appliances will only pull an average of high 80 or low 90 amps in most cases under average Full Load.

Ask Your Own Electrical Question
Was this answer helpful?
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,293
4,293 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,293 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
The wiring to my new electric range consists of 2 insulated
The wiring to my new electric range consists of 2 insulated wires and one bare ground wire. Is this adequate and safe?… read more
Sam I
Sam I
Electrician
B.S.
656 satisfied customers
Is getting AFCI breakers worth the extra cost? Also, how can
Hi, Is getting AFCI breakers worth the extra cost? Also, how can I connect them if there is limited space on the neutral bus? Could I connect several AFCI to a single bus slot? Thanks.… read more
Kevin
Kevin
Licensed Electrical Contractor
4,293 satisfied customers
Lomax electrical wire is disconnected from exterior light
Lomax electrical wire is disconnected from exterior light fixture up in a tree. Branch fell on it and broke it from fixture.What is the name of the instrument I saw an electrician use to determine if … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a four hole dryer socket in my wall but have a three
I have a four hole dryer socket in my wall but have a three socket dry how do i make the change … read more
Kevin
Kevin
Licensed Electrical Contractor
4,293 satisfied customers
I have a GH-A Bremas switch for a boat lift. the motor is a
I have a GH-A Bremas switch for a boat lift. the motor is a Westinghouse series EA81 3/4 hp code K. I have 5 wires from the switch, but the old switch just had 4 wires. i do not know how to wire the s… read more
Sam I
Sam I
Electrician
B.S.
656 satisfied customers
All basement and outlets in the kitchen have a power only if
Hi,All basement and outlets in the kitchen have a power only if switch on … read more
Kevin
Kevin
Licensed Electrical Contractor
4,293 satisfied customers
I have a couple baseboard heaters that I swapped out because
I have a couple baseboard heaters that I swapped out because the covers were missing. They were in fact working but thought it wasn't safe as they were missing covers. Anyways I swapped them out and n… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I live in a double wide home have electrical issues on one
i live in a double wide home have electrical issues on one side of the home and husband cannot figure it out and cannot afford electrician they are very expensive here … read more
Kevin
Kevin
Licensed Electrical Contractor
4,293 satisfied customers
I have a comercial facility in NYC about 15 years old that
I have a comercial facility in NYC about 15 years old that has fluorescent light fixtures hanging from chains wired with 12 awg wires without a casing, each wire has its own insulation but they are no… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Is it kosher to use two 120Volt circuit breakers to create a
Is it kosher to use two 120Volt circuit breakers to create a 240Volt circuit in a house panel?… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Installing mini split ac/heater 18k btu 208/230 volt single
installing mini split ac/heater 18k btu 208/230 volt single phase, do I use 20 or 30 amp breaker? … read more
Kevin
Kevin
Licensed Electrical Contractor
4,293 satisfied customers
Trying to figure out how to change a dedicated 240v circuit
trying to figure out how to change a dedicated 240v circuit line into 120v Not an expert so wont attempt it myself but read quite a bit about it … read more
Kevin
Kevin
Licensed Electrical Contractor
4,293 satisfied customers
Any step by step guide/video to install this door bell? l
any step by step guide/video to install this door bell? https://www.ebay.com/itm/Tmezon-Wireless-IP-7-Inch-Monitor-WIFI-Video-Intercom-Doorbell-Door-Phone-Bell/322562112758?hash=item4b1a333cf6%3Ag%3Am… read more
Sam I
Sam I
Electrician
B.S.
656 satisfied customers
How much would it typically cost to add grounders to the
How much would it typically cost to add grounders to the electrical outlets in my home. Right now, all of my outlets are just 2 prongs.… read more
canuck the pro
canuck the pro
253 satisfied customers
I'm replacing a T101-70 with A T104 = the 101 has 3
i'm replacing a T101-70 with A T104 = the 101 has 3 terminals with 3 white wires going on # 1 then 1 white and ! Black on 2 and then two Black on 3 withe 1 … read more
David Bowden
David Bowden
Owner
850 satisfied customers
Hooking up dryer says I need a 30 amp on each side that's a
Hooking up dryer says I need a 30 amp on each side that's a double breaker that say 30 and 30 right?… read more
Kevin
Kevin
Licensed Electrical Contractor
4,293 satisfied customers
My lamp would turn off and on if the plug was jostled. Now
My lamp would turn off and on if the plug was jostled. Now my beautiful lamp doesn't work at all. Can I fix it? Would a new plug work? If I'm unable to fix the problem, where do I go to get it fixed?… read more
Sam I
Sam I
Electrician
B.S.
656 satisfied customers
I have 2 lights wired in series with the power to the
I have 2 lights wired in series with the power to the switch. All blacks are connected in first box, as well as the whites. Same with second box. When switch is on there is power at second box, but th… read more
David Bowden
David Bowden
Owner
850 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x