I am adding a 100 amp subpanel next to my 200 amp main

Customer Question
I am adding a...

I am adding a 100 amp subpanel next to my 200 amp main panel. what size breaker and wire do I use from my main panel to the subpanel?

Contractor's Assistant: Thanks. Can you give me any more details about your issue?

I am installing an electric car charger 32 A. my plan is to add a subpanel and connect the car charger to the subpanel. to make room in the main panel I am routing the refrigerator and garage outlets to the subpanel.

Submitted: 2 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 32 minutes by:
2/28/2016
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,361
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello Mike and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) Based on the sub-panel loads that you want to connect, I recommend a minimum of a 70 amp double pole feeder breaker will be required. The 70 amp sub-panel feeder circuit will require a 4 wire circuit comprised of 2 hots, 1 neutral and 1 equipment ground. A quantity of (3) three 4 AWG copper wires (type THHN insulated) will be required for the 2 hots and 1 neutral. An 8 AWG copper can be used for the equipment grounding conductor.

2) If the existing 200 amp main panel can sustain a 100 amp feeder circuit, I recommend installing a 100 amp double pole breaker in the main panel as this will obviously take care of the 3 sub-panel loads as well as providing for some future circuits. If using a 100 amp feeder breaker, the 2 hots and 1 neutral will require 4 AWG Copper (type THHN insulated) and an 8 AWG Copper for the equipment ground wire.

3) If connecting the 200 amp main panel to the sub-panel by EMT metal conduit, then the equipment grounding conductor can be eliminated since the EMT metal conduit will act as the equipment grounding conductor.

4) Since the sub-panel will be installed directly next to the main panel, a main lug sub-panel can be installed.

5) At the sub-panel, DO NOT install the green main bonding screw or a main bonding jumper strap to the neutral bus bar. On any sub-panel, the neutral feeder must always be isolated from the sub-panel metal enclosure cabinet. By not installing the main bonding screw or jumper, this is how the neutral remains isolated.

6) At the sub-panel neutral bus bar, only white neutral conductors will land there. Never inter-mix bare copper or green insulated ground wires onto the neutral bus bar. The sub-panel will require a separately installed equipment grounding bar to land any equipment grounding conductors.

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks................Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks................Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks..............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks...............Kevin:)

Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,361
4,361 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,196 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,361 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
3 outlets stopped working at the same time. There were no
3 outlets stopped working at the same time. There were no tripped circuit breakers. So 3 outlets are not working … read more
David Bowden
David Bowden
Owner
1,015 satisfied customers
I'm splicing into an existing line for a dryer outlet. When
I'm splicing into an existing line for a dryer outlet. When I open the original outlet I find the electrician has run 10-3 to a 3-prong outlet. He has the neutral wire attached where I would expect th… read more
Sam I
Sam I
Electrician
B.S.
745 satisfied customers
Switched outlet downstream of a gfci outlet. is it proper to
switched outlet downstream of a gfci outlet. is it proper to have the line go into a gfci outlet first, then load to both a black and red wires in a 3 NM wire used in switched outlets downstream… read more
Sam I
Sam I
Electrician
B.S.
745 satisfied customers
Trying to replace an outlet and there is an unexpected pink
Trying to replace an outlet and there is an unexpected pink wire. Is this just another hot wire? New outlet has 4 hot insertion points and 2 white plus ground … read more
Sam I
Sam I
Electrician
B.S.
745 satisfied customers
I just bought an IBOT pool cleaner. Beside a GFI outlet near
I just bought an IBOT pool cleaner. Beside a GFI outlet near the pool, do I still have to ground it? … read more
Kevin
Kevin
Licensed Electrical Contractor
4,361 satisfied customers
Have a light switch that controls overhead light and outlet.
Have a light switch that controls overhead light and outlet.Present switch has 3 black wires to switch. Box has 3 white wires capped off together, also 2 ground wires capped together.Have already isol… read more
Sam I
Sam I
Electrician
B.S.
745 satisfied customers
IN 2" CONDUIT WITH 10 10 CAT 6 CABLES IN SIDE ALONG THE WAY
IM PUTTING IN 2" CONDUIT WITH 10 10 CAT 6 CABLES IN SIDE ALONG THE WAY THESE 10 CABLE BRANCH OFF TO A BUILDING WHAT TYPE OF IN GROUND HAND PULL BOXES DO I NEED TO HAVE AT THESE AREAS WHERE THE 2 CABLE… read more
David Bowden
David Bowden
Owner
1,015 satisfied customers
CAN I RUN 1 MAIN 2" CONDUIT WITH A 2", PVC Pipe, Wye
CAN I RUN 1 MAIN 2" CONDUIT WITH A 2", PVC Pipe, Wye Schedule 80, Slip TO BRANCH A LINE OFF TO ANOTHER BUILDING ALONG THE PATH WAY SO I HAVE 4 BUILDING AND I WANT TO RUN CAT 6 TO THEM FROM ANOTHER BUI… read more
Kevin
Kevin
Licensed Electrical Contractor
4,361 satisfied customers
1. According to the NEC, conduit seals are required within
1. According to the NEC, conduit seals are required within _______ inches from a pressurized enclosure when the conduit is not pressurized in Class I, Division 1 protection systems. A. 24 B. 30 C. 12 … read more
Chris Miller
Chris Miller
Social Worker
Master\u0027s Degree
101 satisfied customers
Installing an exterior outlet next to my back door...the
Installing an exterior outlet next to my back door...the line feed is from the load side of a gfci outlet in the same circuit so I'm using a regular receptacle in an exterior square box and feeding th… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
I swapped out an outlet like for like and the gfi outlet is
I swapped out an outlet like for like and the gfi outlet is tripped. It makes no sense to me. … read more
David Bowden
David Bowden
Owner
1,015 satisfied customers
Underground conduit cover" First time. Depth of conduit.
depth of conduit. table 300.5 measures from the top of conduit to top of finish surface and the inspector measures from top of the conduit to the bottom of the concrete slab. wish is correct?… read more
Kevin
Kevin
Licensed Electrical Contractor
4,361 satisfied customers
I'm building a detached shop and need to get conduit in the
I'm building a detached shop and need to get conduit in the ground for the shop electrical panel. I have a 200amp main panel in the house that is about 50 ft away from where the shop panel will be. … read more
Sam I
Sam I
Electrician
B.S.
745 satisfied customers
I am trying to add an outlet and a switch for that outlet.
I am trying to add an outlet and a switch for that outlet. The power goes through to other areas. So basically I have power coming to a junction box, one of the wires coming out of the junction box goes to a light ( the old pull style). I wan to replace that old light with an outlet and have a switch for that outlet only. clear as mud right? LOL … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
When using a metal conduit body such as an LB, or capped L
When using a metal conduit body such as an LB, or capped L at an enclosure does that fitting need to be supported other than with the nipple into the enclosure? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
What are the construction requirements for a new conduit
What are the construction requirements for a new conduit installation to an existing building? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
What type of wire does PG&E require to be buried in conduit?
what type of wire does PG&E require to be buried in conduit? The Distance would be close to 400' Will a single wire be able to go that distance or will I need a secondary? How many wires will be in th… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
Is it permissible to run romex wire through conduit indoors
Is it permissible to run romex wire through conduit indoors and in a dry location? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,196 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x