Customer Question
oven range install. 40amp...
oven range install. 40amp breaker. 8-3 wire. existing junction box has 10-3 wire inside aluminum flex to goes to the receptacle. Is the 10-3 ok?
Submitted: 2 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 5 minutes by:
2/21/2016
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,473
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC General Class License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) No, if the range requires a 40 amp breaker, the branch circuit conductors either need to be 8 AWG Copper or 6 AWG Aluminum. which are both rated for 40 amps.

2) 10 AWG copper is rated for 30 amps while 10 AWG Aluminum is rated for 20 amps.

3) Installing undersized conductors on a branch circuit is a code violation due to over fusing as well as a potential safety issue. Undersized wires can heat up and possibly become too hot and melt due to the electrical current in the circuit. A 40 amp range must have the correct contiguous conductors all the way thru to the wall receptacle and the cord must also be rated as 40 amp conductors. The wall receptacle must also have a NEMA rating of 50 amps as they don't manufacture a 40 amp receptacle.

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks...............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks...............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks...............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks.............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks...............Kevin:)

Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 4,473
4,473 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC General Class License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,290 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,473 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC General Class License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I have a junction box with Al wiring. One Black One Red and
I have a junction box with Al wiring. One Black One Red and a stranded bare common. It used to have a drop in stove. I wish to change over to a new slide in stove with a 3 prong plug. Can I put a flus… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
This is a general question on the grounding wire from the
Hi George, this is a general question on the grounding wire from the supply line for a 3 prong non-grounding 220V receptacle. Since the 3 prong receptacle is non grounding, with 2 hots and 1 neutral, … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,473 satisfied customers
Kenmore model 911.40499891 single oven need to know the
Kenmore model 911.40499891 single oven need to know the wattage for this model and size wire from unit to junction box and type… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
Trying to install a new oven and cooktop and just want to double
Trying to install a new oven and cooktop and just want to double check the connections before I go ahead.… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
Trying to run some new wiring for my built-in electric convection
Trying to run some new wiring for my built-in electric convection oven. Previously, it connected to an 8-3 with ground (the oven has black, red, white, and ground wires and is recommended for direct w… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
I am replacing an electric range (oven + cooktop). It plugs
I am replacing an electric range (oven + cooktop). It plugs into a 3-pronged, 220V receptacle. I want to replace it with a separate 4-wire electric cooktop and 4-wire electric oven that will be 6' awa… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
I have an old electric wall oven I want to replace with new
I have an old electric wall oven I want to replace with new one. My existing wiring: HOT, HOT, Ground. 240VAC 6Gauge wire, 40amp CBK. New oven has HOT, HOT, Neutral, Ground wiring. How do I adapt my o… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,473 satisfied customers
I bought a new electric kitchen range to replace my 18 yr old
I bought a new electric kitchen range to replace my 18 yr old one. The old range was hard wired and I had a question about hard wiring my new range. The installation instructions allow for my new rang… read more
Rick
Rick
Owner
High School or GED
467 satisfied customers
i am replacing a double oven that was installed about 30 years
i am replacing a double oven that was installed about 30 years ago. the house feed is 8/2 with ground and has a seperate bare ground wire run with it. Can I use the jacketed bare ground with the new o… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
can i change from hard wire into the junction box,by putting
can i change from hard wire into the junction box,by putting in the 4 wire range replacement cord and a 4 prong 50amp out let? here is my situation i am installing a new kenmore electric wall oven the… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
I am working on a old farm house; remodeling the kitchen.
I am working on a old farm house; remodeling the kitchen. I have the floor removed and I need to run a 6/3 cable from an existing receptacle (removing it and making the connection in a junction box) a… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
I would like to replace my electric range with an electric
I would like to replace my electric range with an electric cooktop and oven combination. My current range has 10.9kw and is connected with an 8 awg (3-wire? B, R, W and Grd) to a 40A breaker and the d… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
Im replacing a double-oven (electric) with a Microwave/Oven
I'm replacing a double-oven (electric) with a Microwave/Oven Combo AND a Warmer Oven. The old double-oven was on a junction box with 8/3 wiring. I have to make a new outlet for the Warming Oven. Can I… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
I am installing an outside flood light. The power source is
I am installing an outside flood light. The power source is an electrical receptor. I am making it into a junction box. It has two wires coming to it, about 10-3 wire and I need to connect to it to wi… read more
Rich
Rich
Master Electrician
Vocational, Technical or Trade Scho
1,117 satisfied customers
I purchased Whirlpool GBS307P Built-In Oven and a GJC3055R
I purchased Whirlpool GBS307P Built-In Oven and a GJC3055R Cooktop. I am trying to ready the counterspace required to install the Cooktop over the BuiltIn Oven. This pair of appliances is a Combinatio… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
I want to take a 240v 4 wire that was going to a oven no longer
I want to take a 240v 4 wire that was going to a oven no longer in use and want to set up a junction box and run a 10/2 30 amp wire for my RV outlet. I think I know but want to be sure that I will be … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
I have an outlet that is 250 volt and 50 amp. I want to power
I have an outlet that is 250 volt and 50 amp. I want to power device that needs protection at 240 volt and 40 amp. Can I plug into the outlet, run 6/2 45 feet to a new subpanel and install a 40 amp do… read more
Mike
Mike
Master Electrician
Working on MBA
1,426 satisfied customers
We are replacing double ovens with a Jenn-Air single oven.
We are replacing double ovens with a Jenn-Air single oven. The double ovens were connected from a 40 amp breaker with 8 gauge wire. The single Jenn-Air oven has 12 gauge wire. My question is, What amp… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.