The electrician ran 12-3 with a 50amp breaker to the garage sub panel and I feel that wasn't right so I want to re-do it, or at least verify it's not incorrect. He said he does 12-3 all the time. Here's the details and what I think is correct, and the type of boxes he installed in the house and in the garage:I'm running from a Square D 60-Circuit 30-Space 200-Amp Main Breaker Load Center inside the house to an outside garage, the run will be in 2" conduit to a Square D 12-Circuit 6-Space 100-Amp Main Lug Load Center in the garage, and the run will be approximately 25 feet. What size breaker do I need and what size wire? I have 6-3 ordered and 2" CARLON conduit with appropriate fittings and connectors. Additionally, do I need a grounding rod at the garage, or will it use the ground in the house panel?My gut instincts tell me my electrical is wrong when he put in 12-3 wire to that garage box and attached it to a 50 amp breaker...
Submitted: 2 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 3 hours by:
2/20/2016
Electrician: Jason, Service Technician replied 2 years ago
Jason
Jason, Service Technician
Category: Electrical
Satisfied Customers: 4,304
Experience: Over 20 years of experience in all types of installations, troubleshooting, and repairs.
Verified

Hello. Welcome to Just Answer.

Ask Your Own Electrical Question
Electrician: Jason, Service Technician replied 2 years ago

Your instincts are correct. His installation is very dangerous.

Ask Your Own Electrical Question
Electrician: Jason, Service Technician replied 2 years ago

12 gauge wire is not rated for 50 amps. It's not even rated for half that amperage. It's rated at 20 amps.

Ask Your Own Electrical Question
Electrician: Jason, Service Technician replied 2 years ago

Since you have ordered #6 wire, you can only connect it to a 60 amp breaker or smaller (assuming it's copper wire).

Ask Your Own Electrical Question
Electrician: Jason, Service Technician replied 2 years ago

You need 4 conductors between the two panels. If the enter distance between the panels will be piped in, you can easily add a ground wire, since you've ordered 6-3, especially in 2" conduit.

Ask Your Own Electrical Question
Electrician: Jason, Service Technician replied 2 years ago

If the garage is detached from the house, you need a ground rod at the sub panel.

Ask Your Own Electrical Question
Electrician: Jason, Service Technician replied 2 years ago

In the sub panel, ground wires and neutral wires are to be on separate bars, not mixed on the same bar(s).

Ask Your Own Electrical Question
Was this answer helpful?
Ask Jason Your Own Question
Jason
Jason
Jason, Service Technician
Category: Electrical
Satisfied Customers: 4,304
4,304 Satisfied Customers
Experience: Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Jason is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

4,304 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
1. If you were to mount a nonmetallic box to the front of a
1. If you were to mount a nonmetallic box to the front of a stud, what type of bracket should the box have? A. FP C. NP B. BP D. JP 2. In order to join a section of rigid conduit to a section of EMT, … read more
electrifier
electrifier
Master Electrician
Bachelor's Degree
1,458 satisfied customers
IN 2" CONDUIT WITH 10 10 CAT 6 CABLES IN SIDE ALONG THE WAY
IM PUTTING IN 2" CONDUIT WITH 10 10 CAT 6 CABLES IN SIDE ALONG THE WAY THESE 10 CABLE BRANCH OFF TO A BUILDING WHAT TYPE OF IN GROUND HAND PULL BOXES DO I NEED TO HAVE AT THESE AREAS WHERE THE 2 CABLE… read more
David Bowden
David Bowden
Owner
848 satisfied customers
CAN I RUN 1 MAIN 2" CONDUIT WITH A 2", PVC Pipe, Wye
CAN I RUN 1 MAIN 2" CONDUIT WITH A 2", PVC Pipe, Wye Schedule 80, Slip TO BRANCH A LINE OFF TO ANOTHER BUILDING ALONG THE PATH WAY SO I HAVE 4 BUILDING AND I WANT TO RUN CAT 6 TO THEM FROM ANOTHER BUI… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
1. According to the NEC, conduit seals are required within
1. According to the NEC, conduit seals are required within _______ inches from a pressurized enclosure when the conduit is not pressurized in Class I, Division 1 protection systems. A. 24 B. 30 C. 12 … read more
Chris Miller
Chris Miller
Social Worker
Master\u0027s Degree
100 satisfied customers
Underground conduit cover" First time. Depth of conduit.
depth of conduit. table 300.5 measures from the top of conduit to top of finish surface and the inspector measures from top of the conduit to the bottom of the concrete slab. wish is correct?… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I'm building a detached shop and need to get conduit in the
I'm building a detached shop and need to get conduit in the ground for the shop electrical panel. I have a 200amp main panel in the house that is about 50 ft away from where the shop panel will be. … read more
Sam I
Sam I
Electrician
B.S.
654 satisfied customers
When using a metal conduit body such as an LB, or capped L
When using a metal conduit body such as an LB, or capped L at an enclosure does that fitting need to be supported other than with the nipple into the enclosure? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
What are the construction requirements for a new conduit
What are the construction requirements for a new conduit installation to an existing building? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
What type of wire does PG&E require to be buried in conduit?
what type of wire does PG&E require to be buried in conduit? The Distance would be close to 400' Will a single wire be able to go that distance or will I need a secondary? How many wires will be in th… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Is it permissible to run romex wire through conduit indoors
Is it permissible to run romex wire through conduit indoors and in a dry location? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Can I use a steel conduit lockout on pvc male adaptor into
Can I use a steel conduit lockout on pvc male adaptor into utility box on end of my pvc conduit?… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Can I add a 90 elbow to the main conduit so that I can raise
can I add a 90 elbow to the main conduit so that I can raise that conduit the conduit is running vertical and i need some height under the conduit … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have a single phase 30 amp 120 volt standard connector on
I have a single phase 30 amp 120 volt standard connector on my RV. The hydro pedestal is 200 feet from my RV. I need a over the ground, extension cord Preferably at 100 feet lengths times two to make … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have a dedicated 10 amp romex line in conduit, going to a
I have a dedicated 10 amp romex line in conduit, going to a direct wired garbage disposer under my kitchen sink. I want to connect this line up to a single gang outlet box to make exchanging the dispo… read more
Sam I
Sam I
Electrician
B.S.
654 satisfied customers
DO YOU SELL 3 WIRE CONNECTORS FOR GENERATOR HOOK UPS OR CAN
DO YOU SELL 3 WIRE CONNECTORS FOR GENERATOR HOOK UPS OR CAN I DELETE THE 4TH WIRE AS MY HOUSE HOOK UP FOR THE GENERATOR ONLY TAKES 3 WIRE AND THE CABLE IS 4 WIRE. … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I am running 3 circuits inside of pvc conduit. 220v 30a
I am running 3 circuits inside of pvc conduit.220v 30a water heater 220v 15a ac 120v 20a receptaclecan I use 1 shared 10awg ground wire for all circuits?… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
How much to install 100' of electrical line in a conduit if
how much to install 100' of electrical line in a conduit if the trench is already dug. Include the cost of wiring and adding a 50 Amp Circuit Breaker … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
What size wire is needed to run underground in conduit to a
What size wire is needed to run underground in conduit to a garage about 60 feet from the main connection at the power pole? This would be connected to a subpanel in the garage. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x