I am working on a 240 volt infrared heater that is 3000 watts. It was installed by someone else that was not an Electrician. They used nm flexible conduit 12 guage wire from a two pole 20 amp breaker to the rheostat to the heater. The rheostat/control switch burned up wires got hot and the insulation failed. Should this circuit be on a 30 amp two pole breaker with 10 guage wire. I plan to re do this in EMT. Thanks Chris
Submitted: 2 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 3 minutes by:
2/12/2016
Electrician: Mike G., Master Electrician replied 2 years ago
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,248
Experience: Proven Professional 49 years Experience
Verified

Hi, I'm Mike G and I'll be assisting you. From your description and question I would check the rating of the switch. A spec grade 20A switch should have been used.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
OK it looks like the heater came with a 15A 240v rheostat. My brother in law got a new one and is still only a 15 amp. Why did they sell a 15 amp switch for a 3000 watt heater!?
Electrician: Mike G., Master Electrician replied 2 years ago

Why? Can only guess that they don't know what it should be.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
OK thanks for the help I should have checked the swich.
Electrician: Mike G., Master Electrician replied 2 years ago

Very good, you're welcome.

Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Mike G. Your Own Question
Mike G.
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,248
8,248 Satisfied Customers
Experience: Proven Professional 49 years Experience

Mike G. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,248 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I was changing switch without turning fuse off. Switch
I was changing switch without turning fuse off. Switch arched and now the switch and lights don't work … read more
Mike G.
Mike G.
Master Electrician
8,248 satisfied customers
I replaced a light switch for my closet now the switch turns
I replaced a light switch for my closet now the switch turns off the power to my bathroom livingroom and closet how do I fix it just for the closet… read more
David Bowden
David Bowden
Owner
990 satisfied customers
I'm replacing a switch with a new dimmer. The old switch has
Hi, I'm replacing a switch with a new dimmer. The old switch has a black wire on one side, which is capped and attached to another black wire that goes into the box. The other side has a red wire. It … read more
Sam I
Sam I
Electrician
B.S.
740 satisfied customers
The wiring to my new electric range consists of 2 insulated
The wiring to my new electric range consists of 2 insulated wires and one bare ground wire. Is this adequate and safe?… read more
Sam I
Sam I
Electrician
B.S.
740 satisfied customers
IN 2" CONDUIT WITH 10 10 CAT 6 CABLES IN SIDE ALONG THE WAY
IM PUTTING IN 2" CONDUIT WITH 10 10 CAT 6 CABLES IN SIDE ALONG THE WAY THESE 10 CABLE BRANCH OFF TO A BUILDING WHAT TYPE OF IN GROUND HAND PULL BOXES DO I NEED TO HAVE AT THESE AREAS WHERE THE 2 CABLE… read more
David Bowden
David Bowden
Owner
990 satisfied customers
CAN I RUN 1 MAIN 2" CONDUIT WITH A 2", PVC Pipe, Wye
CAN I RUN 1 MAIN 2" CONDUIT WITH A 2", PVC Pipe, Wye Schedule 80, Slip TO BRANCH A LINE OFF TO ANOTHER BUILDING ALONG THE PATH WAY SO I HAVE 4 BUILDING AND I WANT TO RUN CAT 6 TO THEM FROM ANOTHER BUI… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
1. According to the NEC, conduit seals are required within
1. According to the NEC, conduit seals are required within _______ inches from a pressurized enclosure when the conduit is not pressurized in Class I, Division 1 protection systems. A. 24 B. 30 C. 12 … read more
Chris Miller
Chris Miller
Social Worker
Master\u0027s Degree
101 satisfied customers
I am looking to replace a switch with smart switch. I have
I am looking to replace a switch with smart switch.I have two switches next to each other that power two sections of the room. I have photos of both of these switches.What would be the easiest way to … read more
Sam I
Sam I
Electrician
B.S.
740 satisfied customers
Underground conduit cover" First time. Depth of conduit.
depth of conduit. table 300.5 measures from the top of conduit to top of finish surface and the inspector measures from top of the conduit to the bottom of the concrete slab. wish is correct?… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I'm building a detached shop and need to get conduit in the
I'm building a detached shop and need to get conduit in the ground for the shop electrical panel. I have a 200amp main panel in the house that is about 50 ft away from where the shop panel will be. … read more
Sam I
Sam I
Electrician
B.S.
740 satisfied customers
I'm trying to replace a light switch with a switch outlet
I'm trying to replace a light switch with a switch outlet combo. The old switch has 3 Romeo coming in. How do I wire up the new outlet/switch combo? … read more
George Smith
George Smith
Vocational, Technical or Trade School
438 satisfied customers
When using a metal conduit body such as an LB, or capped L
When using a metal conduit body such as an LB, or capped L at an enclosure does that fitting need to be supported other than with the nipple into the enclosure? … read more
Mike G.
Mike G.
Master Electrician
8,248 satisfied customers
What are the construction requirements for a new conduit
What are the construction requirements for a new conduit installation to an existing building? … read more
Mike G.
Mike G.
Master Electrician
8,248 satisfied customers
I am attempting to wire a smart switch to replace the switch
I am attempting to wire a smart switch to replace the switch for the light in my dining room. The smart switch shows attachments for hot, neutral, ground and load, but in my box there are two neutral … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
What type of wire does PG&E require to be buried in conduit?
what type of wire does PG&E require to be buried in conduit? The Distance would be close to 400' Will a single wire be able to go that distance or will I need a secondary? How many wires will be in th… read more
Mike G.
Mike G.
Master Electrician
8,248 satisfied customers
Is it permissible to run romex wire through conduit indoors
Is it permissible to run romex wire through conduit indoors and in a dry location? … read more
Mike G.
Mike G.
Master Electrician
8,248 satisfied customers
Can I use a steel conduit lockout on pvc male adaptor into
Can I use a steel conduit lockout on pvc male adaptor into utility box on end of my pvc conduit?… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Can I add a 90 elbow to the main conduit so that I can raise
can I add a 90 elbow to the main conduit so that I can raise that conduit the conduit is running vertical and i need some height under the conduit … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x