The genset has a Honda GX620 engine. The alternator head is

Customer Question
a Mecc Alte MR2-200/2 brushless...
The genset has a Honda GX620 engine. The alternator head is a Mecc Alte MR2-200/2 brushless, 12KW surge, 10.2KW continuous. Engine speed checked at 3590-3620 RPM. Capacitors check good. I flashed both capacitors with 12 VDC while running, no output. Substituted two new capacitors, still no output. AC voltage at capacitor leads is 5.5 on one and 0.3 at the other. Replaced diodes on rotor, still no output. All output voltage checks were made at the terminal block before any circuit breakers.
Submitted: 1 year ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 4 days by:
2/16/2016
Electrician: Pete, Auto Service Technician replied 1 year ago
Pete
Pete, Auto Service Technician
Category: Electrical
Satisfied Customers: 29,540
Experience: Over 17 years diagnosing and repairing automobiles various makes and models with some training and certifications.
Verified

My name is ***** ***** I am a professional here at Just Answer. I noticed that your question had not received a response and thought I would see if you still need help with this.I apologize for the delay and I hope I can still assist you with this here.My info is somewhat limited on your model here but I had seen no one else has responded and would like to see if I can help here.If at any time you feel that I cannot help with this please let me know.

I see no one has replied with any info to this issue here on this generator.IN some cases this can be due to the info being difficult to obtain or the correct person that may have this info may not be online to help.You may have a wiring fault on the generator or shorted or damaged wiring leading to it causing this fault here.If you have not had the wiring inspected to see if any issues are found this should be done.If this was already done and found to be o.k. let me know so we can continue.

If more help is needed, use the reply tab to continue our conversation. If no further assistance is needed, kindly rate my service.You can rate at any time and we can continue to work on your question as this will not close out your question.Keep in mind in some cases it can be difficult to fully diagnose or help repair your vehicle without seeing it and I work on delivering the best possible answer from what I see to work with.

Thanks Pete

Ask Your Own Electrical Question
Customer reply replied 1 year ago
I removed the stator assembly for access to rotor. Visual inspection of rotor and stator windings didn't reveal any abnormalities. Resistance check of stator windings were within specs. Resistance check of Rotor windings were within specs. No shorts to ground were detected. It has two exciter windings. One exciter winding was within specs. The other exciter winding showed much higher resistance than specified and readings were inconsistent. Shouldn't it still produce output voltage on one side?
Electrician: Pete, Auto Service Technician replied 1 year ago

Unfortunately my info is limited on the testing for this model here.

I will open your question up for others here to see if someone else can assist further on this as there may be others here that may have more info on what to check or do with this issue.I hope you can get this resolved with ease.No need to reply to my last post here unless it is a last resort as it will keep your question locked to me and others will not be able to view it.If you feel you want to continue to work with me on this feel free to reply at any time but keep in mind in some cases it can be difficult to fully diagnose or help repair this without seeing your vehicle.

Thanks Pete

Ask Your Own Electrical Question
Customer reply replied 1 year ago
It's a generator not a vehicle so I don't understand what you are answering.
Customer reply replied 1 year ago
The question is fully explained we need someone that knows about generators that produce electrity so you can use it to turn on elecritic things like a tv or a refrigerator or anything that needs electricity. The generator starts it just doesn't put out voltage. The quiestion is very detailed and it needs to be answered by someone who knows gererators. Thank you pete but you should have given it to someone else sooner we have been waiting for an answer to several days and now my friend is discouraged and needs this generator to help him with building his house out in the woods were there is no eletricity and his last generator was stolen and this is all he can afford at this time so we would really appricate if someone could answer that knows about generators we really need the help. Thankyou.
Customer reply replied 1 year ago
Here is what I was told, it's just a general idea of might be a wiring issue of wome kind. Nothing about what to check next
or further test procedures. He thinks the just answer web site is a dead end. I sugested him to ask you so see if we can get an
answer if its at all posible. Thank you.
Customer reply replied 1 year ago
not wome I ment some kind.
Ask Pete Your Own Question
Pete
Pete
Pete, Auto Service Technician
Category: Electrical
Satisfied Customers: 29,540
29,540 Satisfied Customers
Experience: Over 17 years diagnosing and repairing automobiles various makes and models with some training and certifications.

Pete is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,425 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,940 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,603 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,715 satisfied customers

30 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
Can a General Electric type THQL-GCI hot tub circuit breaker
can a General Electric type THQL-GCI hot tub circuit breaker be tested with an ohm meter. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
I have 2 dedicated circuits in my circuit breaker box that
I have 2 dedicated circuits in my circuit breaker box that are 240V, they each have 2 hot wires going to them. The circuit is terminated to an individual plug (L6-20R) for each circuit. The device I'm… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
I have 415 amps worth of branch circuit breakers. what size
I have 415 amps worth of branch circuit breakers. what size service do i need for my house? is 200 sufficient … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
I'm trying to move a circuit breaker box in a place I'd like
I'm trying to move a circuit breaker box in a place I'd like to put a bathroom. Knowing it isn't code to have one in a bathroom, is a junction box ok? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
How do I determine the correct size circuit breaker panel
How do I determine the correct size circuit breaker panel for an stand alone workshop. I don't suspect I would draw more than 20 amps at any given time, but do I need a box assumes everything is turne… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
What is the function that makes a circuit breaker different
what is the function that makes a circuit breaker different from a switch so that it is able to break fault current … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
Was wondering which circuit breaker I should look into
Hello, was wondering which circuit breaker I should look into replacing. As it stands my Dryer flips the circuit breaker for the upstairs bedrooms. Should I look into replacing the circuit breaker for… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
My circuit breaker was buzzing, so I pushed the test button.
Hello. My circuit breaker was buzzing, so I pushed the test button. This switched all the sockets off in my house but left all the lights on. When I flipped the breaker switch back, al the sockets cam… read more
Sam I
Sam I
Electrician
B.S.
368 satisfied customers
My circuit breaker is tripped and will not reset. I've
My circuit breaker is tripped and will not reset. I've checked wiring to outlets looks okay. At the electrical panel there is no power to breaker itself. I check other breakers and the have power. Any… read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
953 satisfied customers
I just need to know what circuit breaker to buy for my
I just need to know what circuit breaker to buy for my mitsubishi mini split that is a 50A 2 pole that provides earth leakage protection … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
Honda EU7000is has 30 amp line with circuit breaker with
Honda EU7000is has 30 amp line with circuit breaker with each line up to 22.6 amps. Questions is 32 amp draw too large and will trip circuit breaker and can circuit breaker be upgraded to 40 amp to al… read more
Sam I
Sam I
Electrician
B.S.
368 satisfied customers
I have a question about ITE circuit breakers, First call,
I have an ITE electrical panel #FEQ 28MBB. I need compatible circuit breakers… read more
Sam I
Sam I
Electrician
B.S.
368 satisfied customers
I have a zinsco circuit breaker panel. The main line circuit
I have a zinsco circuit breaker panel. The main line circuit breaker is a 125 amp Zinsco 2pole breaker.My question is can I safely replace 125 amp breaker with a 100 amp 2 pole breaker? Main lineRegar… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I have a well pump wired into a 240v/20a circuit breaker. C/
I have a well pump wired into a 240v/20a circuit breaker. C/B has white wire, black wire, ground wire. Pressure switch on well pump has same...black, white. ground. Output from pressure switch to pump… read more
ProGrade
ProGrade
Electrical Contractor
564 satisfied customers
I've checked ALL circuit breaker with a voltage meter. They
I've checked ALL circuit breaker with a voltage meter. They are good, but I still don't have power in both bathrooms. Not in the outlets or ceiling lights. Can you help. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
The circuit breaker tripped controlling all the electricity
The circuit breaker tripped controlling all the electricity in my son's bedroom. This circuit also controls the recessed lighting in the dining room. The only way I can reset the circuit breaker is if… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I currently live in apartment with a circuit breaker that
I currently live in apartment with a circuit breaker that has 100 amps total. I would like to know to upgrade to 200 amps if it only requires switching the breaker box only or you have to bring anothe… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
What is the nec for wiring a control panel circuit breaker.
What is the nec for wiring a control panel circuit breaker. Can you feed the line into the bottom and have the load come out the top of the breaker… read more
George Smith
George Smith
Vocational, Technical or Trade School
273 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x