I just switched out a light switch in a room that had a

Customer Question
ceiling fan. One switch...
I just switched out a light switch in a room that had a ceiling fan. One switch controlled the light on the fan the other controlled the fan. I'm going to a standard light fixture with no fan but I have a dimmer switch. I can't get the light to turn off now that the power is back on
Submitted: 2 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 9 minutes by:
1/31/2016
Electrician: Mike G., Master Electrician replied 2 years ago
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,424
Experience: Proven Professional 49 years Experience
Verified

Hi, I'm Mike G nd I'll be assisting you. First thing, you should only have one wire under a screw. If more than one, connect the wired together with a short pigtail wire and connect it to the screw. Multiple wires under a screw will fail the connection and cause arcing which will make repairs more expensive. Yes, you may install a dimmer in place of the switch.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
How do I know which wires to pigtail and what wire goes under the screw?
Customer reply replied 2 years ago
When I didn't have the three wires under the screw, there was NO power to the room at all
Electrician: Mike G., Master Electrician replied 2 years ago

Connect all 3 wires together with a short pigtail wire in a wirenut. Connect the other end of the pigtail to the screw. You will continue to have power and it will not fail as having 3 wires under a screw.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Ok made the pigtail and got it connected. The light works but I can't control the light from the switch it just stays on still. Same issue just now with a pigtail
Electrician: Mike G., Master Electrician replied 2 years ago

OK, one of the 3 wires is to the light and needs to be on a switch with an additional pigtail to the same switch from the other wires.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
basically figure out what wire the light is and take that out of pigtail #1. Then take the end of pigtail #1 that is under the screw right now and combine that with wire for the light in pigtail #2 and then put that tail under the screw?
Electrician: Mike G., Master Electrician replied 2 years ago

That correct.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Ok I have to go and get some more wire I don't have enough for another pigtail. Thank you for your help. Hope this fixes the issue
Electrician: Mike G., Master Electrician replied 2 years ago

Very good, let me know how it went.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
What type of wire should I buy?
Electrician: Mike G., Master Electrician replied 2 years ago

#14/2 NM. Strip it and you'll have a single #14 to use.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Ok made the other pigtail and had the same issue with the light just staying on. I tried the grouping of the wires 3 different ways because of the 3 different black wires all had the same result
Electrician: Mike G., Master Electrician replied 2 years ago

With all the wires not connected, is the light off? If yes, with your tester from ground to each wire find the hot wire. Now touch that wire to the others to see which wire goes to the light. When found put it on the switch and then connect the remaining wires together with the pigtails to the switches.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
I don't have a tester, is there a way to do it without one?
Electrician: Mike G., Master Electrician replied 2 years ago

Not safely. You should have a tester available anytime you do anything electrical. You can pick up an inexpensive one at any home center for around$10.00. Get one, follow the instructions and let me know how it went.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Ok did it dangerously and found my live wire. Now my question is what wires do I put together? Should one of the pigtail ends be attached to the actual light switch?
Electrician: Mike G., Master Electrician replied 2 years ago

OK, touch it to the other wires one at a time to see which one is the light. Put that wire and a pigtail on a switch. Now connect all pigtails and remaining wires together in a wirenut.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
It just keeps the light on still. My switch is playing no role in this besides being connect by a pigtail. And the only reason the light is on is because the 2 wires are touching in a wirenut.
Wirenut #1 has live, light, and pigtail coming out to the switch and the and pigtail going to the third wire that has all my outlets on it which equals wirenut #2.
Electrician: Mike G., Master Electrician replied 2 years ago

The wire to the light should only be on the switch, not in the wurenut. The pigtail to the switch is where it gets power, depending on the switch position.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Thank you for your help, i couldn't get it figured out but you were a great help.
Electrician: Mike G., Master Electrician replied 2 years ago

Glad to help, you're welcome.

Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Mike G. Your Own Question
Mike G.
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,424
8,424 Satisfied Customers
Experience: Proven Professional 49 years Experience

Mike G. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,424 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,414 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I tried to hang a pendant light and the ground wire from the
I tried to hang a pendant light and the ground wire from the new fixture to the green screen burnt thru. I've now disconnected all the cables from the light but the other ceiling fan on potentially th… read more
Steven Parent
Steven Parent
Journeymen Electrician
Electrical Journeyman Certificate
69 satisfied customers
I upgraded a dining room light to a lighted ceiling fan, i
I upgraded a dining room light to a lighted ceiling fan, i did not realize that a switch loop was set up and when i installed the ceiling fan my dinning room light switches now control my kitchen ligh… read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
1,320 satisfied customers
I was installing new light and turned off the power. The
I was installing new light and turned off the power. The light is part of a arc circuit breaker. And no lights would turn back on, so I unhooked the light at the switch, and a bought and installed a n… read more
Steven Parent
Steven Parent
Journeymen Electrician
Electrical Journeyman Certificate
69 satisfied customers
I am putting up a new light/fan and dimmer switch and I am
I am putting up a new light/fan and dimmer switch and I am having a problem. Coming from the box in the ceiling there are three black wired together and then I have two whites together and then one wh… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
I installed a ceiling fan about a week ago with a light kit
I installed a ceiling fan about a week ago with a light kit that came with the fan. I also bought a remote control for the fan and light. I also had a switch that when I turned on the switch the remot… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
I've got a red wire from ceiling that I am trying to wire to
I've got a red wire from ceiling that I am trying to wire to my ceiling fan. On the ceiling fan I've got the blue, white, black and green. I wire everything and just cap off the red, but then it has a… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
I am replacing a ceiling fan. The existing ceiling box
I am replacing a ceiling fan. The existing ceiling box has two cables, one with black, white, red, bare copper which is the one that I think was used on the previous fan, and another with just black, … read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
Recently I purchased an RF meter (RF only, not low frequency
Recently I purchased an RF meter (RF only, not low frequency EMF) to check my wireless devices. Out of curiosity, I walked around the house with it, and was surprised to find rapidly fluctuating level… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I have an issue here I had a light in my kitchen and replaced
I have an issue here I had a light in my kitchen and replaced it with a fan/light kit. I have two switches one is a normal on/off style the other is a push on/off with dim feature. I now when I use th… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,424 satisfied customers
Hi - I have a light switch that controls a ceiling fan and
Hi - I have a light switch that controls a ceiling fan and light. The dinner for this fixture stopped working, I replaced the light switch with a new dimmer and it worked for two days, then the same t… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
I am replacing a ceiling ligght fan combo with track lighting.
I am replacing a ceiling ligght fan combo with track lighting. the new track lighting has a black white and ground. When I removed the fan there was a red black white and ground coming out of the ceil… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,424 satisfied customers
Have 2 ceiling fans that each have 2 switches, but current
Have 2 ceiling fans that each have 2 switches, but current set up has only switch working to turn on the fan and the light. I want to fix the wiring so that one switch operates the light and one the f… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,424 satisfied customers
i am wiring a ceiling fan and a dimmer switch from one powwer
i am wiring a ceiling fan and a dimmer switch from one powwer sorce. The problem is the fan is in series and the dimmer has a hot netral and ground. I wired the fan and dimmer incomig hots together an… read more
Sir Sparks
Sir Sparks
Owner
State & UK Certified Master electri
2,519 satisfied customers
I just wired my chandelier into the ceiling there use to be
I just wired my chandelier into the ceiling there use to be a ceiling fan there. We we turnrd back on the power it worked but, I can't get the light switch to turn it off.… read more
Sir Sparks
Sir Sparks
Owner
State & UK Certified Master electri
2,519 satisfied customers
I have just created a new room and am installing 4 recessed
I have just created a new room and am installing 4 recessed pot lights in the ceiling. My breaker panel is on the south wall of this room. I have a single pole dimmer switch installed beside the entra… read more
Mike
Mike
Master Electrician
Working on MBA
1,426 satisfied customers
I am trying to install a dimmer switch for my ceiling fan and
I am trying to install a dimmer switch for my ceiling fan and light. At the old light switch on the wall there are two sets of wires. Two blacks, two whites, and two grounds. Only one set of the white… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
Im trying to install a new fixture in my dining room. There
I'm trying to install a new fixture in my dining room. There is also recess lighting in the room on a three way with dimmers. the fixture i'm trying to install is on a single dimmer. I hooked up the l… read more
electrifier
electrifier
Master Electrician
Bachelor's Degree
1,458 satisfied customers
I have a Leviton Decor dimmer switch connected to an existing
I have a Leviton Decor dimmer switch connected to an existing kitchen light fixture which needs to be replaced ... there are two sets of wires in the ceiling fixture ... one with a black, white and gr… read more
Paul
Paul
Owner
Vocational, Technical or Trade Scho
51 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x