please verify via this cutsheet, figure J on the last page single phasehttps://www.platt.com/CutSheets/Actuant/AcmeBuck-Boost-Transformers.pdfwhat is my input?
what is my output?seems like H4 and X1 are my inputwire nut x2 and x3H4+H2 & H1+X4 are my outputs?is this correct?
Submitted: 2 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 8 minutes by:
1/19/2016
Electrician: ProGrade, Certified Electrical Contractor replied 2 years ago
ProGrade
ProGrade, Certified Electrical Contractor
Category: Electrical
Satisfied Customers: 565
Experience: 28+ years exp. - installation, troubleshooting, & repair of commercial, & residential electrical systems.
Verified

That is correct which puts both input & output on H4, et al. Let me know if you have any questions

Ask Your Own Electrical Question
Customer reply replied 2 years ago
this seems crazy to me, why does it take it through h2? thats how its draining the volts from that leg?
Electrician: ProGrade, Certified Electrical Contractor replied 2 years ago

Those are the characteristics of a buck-boost transformer. What are you trying to do, increase the voltage? From what to what?

Ask Your Own Electrical Question
Customer reply replied 2 years ago
i have the t137921chart says use fig J for 277, the closest to my 252v yes i have 252 coming inthen trying to step down to 208vwith ability to pull 30.3 amps max draw ever 20a continuous
Electrician: ProGrade, Certified Electrical Contractor replied 2 years ago

10-4, thanks, looking at the data, will return

Ask Your Own Electrical Question
Electrician: ProGrade, Certified Electrical Contractor replied 2 years ago

You are attempting to use a buck-boost transformer where a step-down transformer should be used instead. Does the load specifically require 208 Volts or will it run on 230?

If you have 252 volts, that is within specs for a 230 Volt system (230 x 1.10 = 253)

However, if this is on a 480/277 Volt System, you still need a step-down transformer, not a buck-boost.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
boy oh boy lol,i trust you on this for sure, and makes me nuts because I do, and acme tech support told me to use this, the place I got it from also called acme and was told the same thing, that they recommend i use this t137921 to 40a or t137922 to 70a.so i said send it.but before this, they sent me wrong one already, but it was a step down isolation, i wired it right, metered it out, 212v, hooked oven up and it ran perfect for about 2 minutes.once the max draw kicked in and it really started the warming cycle, pulling 30.3a max, it smoked like a rocket
1st one could only handly 8a LOL, when i told them 30.3a at start up.so 2nd try here with this different buck boost
sarcastic: i told them again 252v to 208v 30.3max 20 continiously
so they said use this one, and supposedly he was doing the math and discussing 3 or 4 different ones and reccomended this oneso now im nervous again, it better not blow any heating elements this platt will be buying them not me....do you know how to check the math on this buck boost? 252v in 208 or closest to it out need 30a max 20 continiouslydoesnt the cut sheet give us what is needed to calculate the exact drop in V and respective available A ...in your opionion, this will work right? even though maybe its not what you would have sold to someone? it gets the job done at least?
Customer reply replied 2 years ago
man i cant believe you left me hanging like this i needed this answer , in a few hours the acme tech support will be open but I used this to get the answers faster
Electrician: ProGrade, Certified Electrical Contractor replied 2 years ago

Because you are trying to use it in a manner that it is not intended or designed for, see above

Ask Your Own Electrical Question
Was this answer helpful?
Ask Mike Your Own Question
Mike
Mike
Mike, Master Electrician
Category: Electrical
Satisfied Customers: 1,426
1,426 Satisfied Customers
Experience: Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Mike is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
Im changing out a F16T12 magnetic ballast for a similar
Hi. Im changing out a F16T12 magnetic ballast for a similar electronic ballast. My problem is that the magnetic ballast had a red and blue wire coming out of one end, connecting to a red and blue wire… read more
Sam I
Sam I
Electrician
B.S.
651 satisfied customers
Have 480V 3 phase subpanel 3 hots 1 ground can you wire a
have 480V 3 phase subpanel 3 hots 1 ground can you wire a single phase 120 240 transformer just using ground wire for center tape for neutral 480V Panel is a subpanel … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I am replacing 3 breaker panels in an apartment house. I
I am replacing 3 breaker panels in an apartment house. I need to know the grounding requirements. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Hope all is well. I want to make a cable and next some
For Jason only. Hey Jason hope all is well. I want to make a cable and next some assistance. Basically I'd like to have a 100 feet 10/3 SOOW with one end using a 120/30 twist lock plug and on the othe… read more
Jason
Jason
Service Technician
Associate Degree
3,942 satisfied customers
I have two switches controlling two lights in my living room
I have two switches controlling two lights in my living room I want to use one of the switches to control a fan. I ran the fan over to one of the lights and need to figure out how to separate switches… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Have a range hood with no ground. What do i do with the
Have a range hood with no ground . What do i do with the ground from house wiring … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
My Motorhome has a power converter (see picture 1), the
My Motorhome has a power converter (see picture 1), the input power is 120v and 6 amps that give 720 Watts, the out put is12v and 40amps, that only give 480 Watts, can you explain it? Thanks… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Its our remote control fan and light. Model is fan-md
new battery we can not get the remote to work like turn off the fan … read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
1,236 satisfied customers
First time doing wiring. Please watch this short video on my
First time doing wiring. Please watch this short video on my rough in wiring. Do you see any code violations?https://www.youtube.com/watch?v=knHm6iEZqLc… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
My doorbell was working until I replaced the doorbell
My doorbell was working until I replaced the doorbell buttom … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Can I pigtail two ceiling fans together if they will always
Can I pigtail two ceiling fans together if they will always be at the same fan speed and light setting?my garage/shop will have two ceiling fans about 30 feet apart. I was wanting to do just one wall … read more
Sam I
Sam I
Electrician
B.S.
651 satisfied customers
2nd question on instaliing a light switch with motion
2nd question on instaliing a light switch with motion detection. a bx box has a few white,red,black wires tied together, no green. the switch has black,red,green and white. I tied the wiers from the s… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Can a 125 VAC, 60 Hz, 13 A, 1000 Watt remote control switch
can a 125 VAC, 60 Hz, 13 A, 1000 Watt remote control switch be used with a 120 VAC, 60 Hz 1580 Watt microwave … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Where does the red wire go that comes from the fan to the 3
Where does the red wire go that comes from the fan to the 3 speed fan switch. … read more
canuck the pro
canuck the pro
253 satisfied customers
I have a modified sainwave inverter. Out put is 220 volts
Ok here is my question I have a modified sainwave inverter . Out put is 220 volts with two 110 legs it has no neutral just a ground how do I get a neutral for my return voltage ? When I hook it to my … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Installing a light switch with motion sensor. Have only a
installing a light switch with motion sensor. Have only a black and white wire in BX in box. switch has white,red,black and green. can I do this with just 2 wires in box?… read more
David Bowden
David Bowden
Owner
843 satisfied customers
Does all outside wiring need to be in a solid aluminum
does all outside wiring need to be in a solid aluminum conduit or can it be flexile grey stuff? I want to run a line fro the basement out to a split unit condensor. also in nyc do I ahve to use BX or … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I tripped the breaker installing a ceiling fan and now the
I tripped the breaker installing a ceiling fan and now the power won't come back on. How do I fix it … read more
George Smith
George Smith
Vocational, Technical or Trade School
434 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x