Tankless hot water heater flickering the lights. Can you use an AC Capacitor on each leg of the 220 to eliminate the flicker? Specs of water heater: 220v 60amp, real pull of 51amps. On a scope you can see the water heater chopping the top off the sine wave on about every 5th or 6th high.
Submitted: 1 year ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 4 minutes by:
12/15/2015
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 3,791
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) Flickering lights is an indication of a loose wire connection, usually a hot wire. Since the H2O heater resides on a separate circuit than the lighting, this suggests a loose hot phase connection either at the meter socket or at the lugs of the main breaker. Lighting circuits are a separate circuit than the H2O heater. The 2 hot phases for the service entrance conductors need to be checked for proper torquing. Also double check the H2O branch circuit connections/terminations.

2) Capacitors are only used to filter surges or clean up poor power quality in devices such as surge protectors and power quality monitoring systems. A cap is not going to resolve the problem:)

3) On a properly wired 120 and/or 240 volt AC system, an oscilloscope should show a fairly clean sine wave.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
There are no loose connections, and the grounds are solid. Even installed a new ground for the meter base. Took the main wires out of the box cleaned them and put anti oxidizer goop on them. (yes the mains are aluminum) The power company replaced the transformer and meter. Sine wave at the meter still shows the tops of the waves getting cut off as the water heater reduces the load under low flow. If the water heater is under full load-no flicker.
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

Thanks for the replies.

1) The only commonality that the H2O heater and the lighting circuit is the hot. The H2O heater does not have a neutral, so that eliminates that possibility.

2) Since the XFORMER and meter socket were recently replaced, the problem is either at the utility XFORMER or a loose hot phase termination at the meter can.

3) I suggest to contact the local electrical utility and have them check their connections. They can also install a power quality monitor at the meter can to confirm the cause of the problem if within their transformer.

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

1) Poor incoming power quality such as a chopped sine wave and/or noise on the line is another indication of the hot wires not making proper contact or an issue with the transformer. The LOAD side lug connections at the meter can be temporarily removed and the utility can place a scope or power quality monitoring device on the LINE side of the meter to confirm if the problem is the utility.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Maybe i did not make that clear:
Utility installed in XFORMER just for me on a new pole. They ran all new wire from XFORMER to the meter base on house.
Utility says "we have done all we can do." They had monitor on the meter side for a week." Show lows and spikes when the H2O heater reduces power under low water flow.
Power coming from the XFORMER looks good.
Customer reply replied 1 year ago
new XFORMER just for me
Customer reply replied 1 year ago
At this point I am just trying to reduce the flicker. I switched to all LED lights, and that helped. but still makes you twitch when running hot water.
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

1) Well, utility companies have been known to make mistakes. Been down this road before:)

2) Your lighting system requires a neutral conductor for the 120 volt circuits, yet the H2O heater is a 240 volt circuit which does not require a neutral connection. Flickering lights indicate a loose hot wire and dimming lights indicate a loose neutral wire. Thus the only commonality between the lighting circuit and the H2O heater are the hots.

3) Since the H2O heater only requires 2 hots and the flickering stops when the H2O heater is under full load is due to the contacts expanding. When the H2O heater is not under full load, the contacts (terminations) contract. In any electrical circuit, amperage flow causes terminations to expand as the conductors heat up and a reduction in amps or no amps flowing cause the terminations to contract when cooling down.

4) In fact, the H2O heater technically does not even require a ground connection. The ground on the H2O heater is only for safety reasons. Electrically speaking, the H2O heater will work correctly with or without a ground. The neutral conductors are the grounded conductors and the hot wires are the ungrounded conductors. Therefore, I don't see how a potential grounding issue can be caused by the H2O heater which flickers the lighting circuit?

I will opt out of the question and place it back to the open board. Perhaps another expert here has a better idea than I do. No need to reply back to me. You will be notified once another electrician picks up the question.

Thanks.............Kevin:)

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Thank you
Electrician: Wayne Roberts, Electrical Technician replied 1 year ago
Wayne Roberts
Wayne Roberts, Electrical Technician
Category: Electrical
Satisfied Customers: 82
Experience: Electrican 6+ years
Verified

Do you have a 200 amp service?

Ask Your Own Electrical Question
Customer reply replied 1 year ago
sir
Electrician: Wayne Roberts, Electrical Technician replied 1 year ago

Look at the position of the breakers in the panel, the water heater should be closest to the main lugs and definitely before the lights.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
There are no lights on the side of the box, but there are other unused 220 breakers above it in the box.
Electrician: Wayne Roberts, Electrical Technician replied 1 year ago

Well, this seems to be a common issue. These tank-less water heaters have caused a lot of people similar headache. What gauge wire is coming out of the tank-less heater breaker? If the water heater is less that 75 ft away it can be #6 copper. Any more than 75ft #4 copper.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
It's about 4 feet, #6, The setup is a 60 amp breaker with #6 copper coming down to another switch box 4 feet away with a60 amp breaker in it. I can send pic if needed.
Electrician: Wayne Roberts, Electrical Technician replied 1 year ago

Everything you can provide in the way of information would be most appreciated. I was thinking voltage drop...but that is a very short distance and the wire # ***** within code. Are there sub panels? As in your main panel feed another 100 amp panel?

Ask Your Own Electrical Question
Electrician: Wayne Roberts, Electrical Technician replied 1 year ago

I would scour for any loose connections as well, if you can... remove the cover from the tank less and just kind-of probe its components looking for anything loose or amiss. But it doesn't hurt to double check everything.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
There are no sub panels fed from this main panel. There is a panel that is wired off the top of this panel.Pics coming
Electrician: Wayne Roberts, Electrical Technician replied 1 year ago

Are the lights controlled by the same panel as the tank less or are they in the panel on the right?

Ask Your Own Electrical Question
Electrician: Wayne Roberts, Electrical Technician replied 1 year ago

And, are the dimming lights plugged into a receptical?

Ask Your Own Electrical Question
Electrician: Wayne Roberts, Electrical Technician replied 1 year ago

If the offending lights are controlled by the right panel we then must determine how that panel is fed.

Ask Your Own Electrical Question
Customer reply replied 1 year ago
Well the lights that are flickering are on the left leg of box the H2O heater is on, and on the two breakers below the H2O heater.
The lights that are flickering are ceiling and wall mount lights, with incandescent bulbs and LED bulbs.
Customer reply replied 1 year ago
not noticed it on any of the lights on the right panel, but will check it right now.
Customer reply replied 1 year ago
It's there on the lights on the right panel but very faint.
Electrician: Wayne Roberts, Electrical Technician replied 1 year ago

Well, I can tell you whats happening and how to try and eliminate the problem. However, most people only get limited results. You have to rearrange the breakers in the panel to balance the load across both phases. This and putting the H2O heater breaker as close to the lugs as possible may eliminate or reduce the problem. Beyond this all i can say is you can upgrade service or supplement power with solar or wind. The heater is simply a power hog. As far as the sine wave goes, i'm not sure. That is very interesting. I can offer no more help to you so im opting out boss. Good luck, and be safe!

Ask Your Own Electrical Question
Customer reply replied 1 year ago
k, thanks
Customer reply replied 1 year ago
video of the lights on the far right panel.
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

One question that needs to be confirmed:

1) Did the lights flicker prior to the utility company replacing the transformer, the meter and the service entrance conductors to the meter can?

2) Is the tankless H2O heater a new installation or was this previously installed prior to the utility company work?

3) Can you temporarily shut OFF all of the branch circuit breakers in the home with the exception of the problem lighting circuit and the H2O heater breakers? Turn the H2O heater to Full Load and then to minimal load a few times. Do the lights still flicker with no other circuit breakers in the ON position?

Ask Your Own Electrical Question
Customer reply replied 1 year ago
1: Yes, oh my they flickered way worse than they do now.2: The H2O heater is was replacing a tank water heater (that had no flicker) Once the new tankless was installed, we had flicker so I sent that unit back and got a replacement. It did the same thing so I sent it back and got a totally different brand. (same results)3: Not sure i have tried this in this setup. I will do it and post shortly.
Customer reply replied 1 year ago
Okay, The lights on the same leg as the H2O heater still flicker.
It did seem to help the lights on the other legs, and other panel to not flicker as much. But alas, they still flickered.
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

OK, Thank you for confirming that.

1) Here is how your panels are configured:

The panel on the left is your main panel. The middle panel is a sub-panel that is being fed from the main panel. The smaller 70 amp panel connected to the H2O heater is also a sub-panel being fed from the main panel. Thus you have 2 separately installed sub-panels of which both are fed off of the main.

2) Can you provide me with a breakout of the quantity of lighting circuits that flicker in each panel?

How many in the main panel and how many in the middle sub-panel flicker?

Ask Your Own Electrical Question
Customer reply replied 1 year ago
I can try: It is a very very big house. 6100 sqf 7 bed 5 bath. Before I type all that up, I am going to try and balance the load on the legs. I will post tomorrow the results.
Electrician: Kevin, Licensed Electrical Contractor replied 1 year ago

1) Since you are familiar with what a hot leg is, are you comfortable in "rolling" 1 or 2 of the flickering lighting circuits over to other known working single pole breakers of the same amperage in the main panel or middle sub-panel?

We need to determine if the lighting flickering is being caused by one hot phase or both of the hot phases and if the flickering will follow or go away when "rolling" the lighting circuit or circuits over to the opposite phase.

Keep in mind that the lighting circuits only reside on (1) one hot leg, yet the H2O heater takes 2 hot legs. The $64K question is, does the flickering stop or does it follow when a lighting circuit is "rolled" from 1 hot phase to the other hot phase?

As you are probably already aware of, your main panel contains 2 hot phases which originate from the transformer and tandem thru the meter and onto the lugs on the main panel. The double pole feeder breakers to the other 2 sub-panels also contain the same 2 hot phases.

2) If you have a "clamp-on" amp meter and when the home is under Full Load (all possible electrical items in the ON position).......ie..........every light, TV, radio, microwave, dryer, washer, pumps, etc are all in the ON position. In other words, fire up every possible load in the home simultaneously. Then the clamp-on amp meter can quickly confirm if the 2 hot phases are close to being balanced. Both phases won't have identical amps under full load but should be somewhat close.

The amount of amps on the neutral service entrance conductor at the main panel will be the difference in amps of the 2 hot phase amp measurements..........ie........ Highest Hot phase (-) subtracted from the lower hot phase will = the total neutral current under Full Load.

3) There is no hierarchy as to the position/location of a double pole circuit breaker in any panel. The voltage (120VAC each side) is evenly distributed on both sides of the hot bus bar from the main breaker thru the hot bus bars and onto to a double pole breaker. What does matter is if the phase amps are close to being balanced when under full load.

Reply back to me when you have an opportunity and we can take it from there............Thanks...........Kevin:)

Ask Your Own Electrical Question
Ask Mike Your Own Question
Mike
Mike
Mike, Master Electrician
Category: Electrical
Satisfied Customers: 1,425
1,425 Satisfied Customers
Experience: Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Mike is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,425 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,940 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,603 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,791 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I have 2 dedicated circuits in my circuit breaker box that
I have 2 dedicated circuits in my circuit breaker box that are 240V, they each have 2 hot wires going to them. The circuit is terminated to an individual plug (L6-20R) for each circuit. The device I'm… read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
I have 415 amps worth of branch circuit breakers. what size
I have 415 amps worth of branch circuit breakers. what size service do i need for my house? is 200 sufficient … read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
I'm trying to move a circuit breaker box in a place I'd like
I'm trying to move a circuit breaker box in a place I'd like to put a bathroom. Knowing it isn't code to have one in a bathroom, is a junction box ok? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
How do I determine the correct size circuit breaker panel
How do I determine the correct size circuit breaker panel for an stand alone workshop. I don't suspect I would draw more than 20 amps at any given time, but do I need a box assumes everything is turne… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
What is the function that makes a circuit breaker different
what is the function that makes a circuit breaker different from a switch so that it is able to break fault current … read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
Was wondering which circuit breaker I should look into
Hello, was wondering which circuit breaker I should look into replacing. As it stands my Dryer flips the circuit breaker for the upstairs bedrooms. Should I look into replacing the circuit breaker for… read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
My circuit breaker was buzzing, so I pushed the test button.
Hello. My circuit breaker was buzzing, so I pushed the test button. This switched all the sockets off in my house but left all the lights on. When I flipped the breaker switch back, al the sockets cam… read more
Sam I
Sam I
Electrician
B.S.
364 satisfied customers
My circuit breaker is tripped and will not reset. I've
My circuit breaker is tripped and will not reset. I've checked wiring to outlets looks okay. At the electrical panel there is no power to breaker itself. I check other breakers and the have power. Any… read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
950 satisfied customers
I just need to know what circuit breaker to buy for my
I just need to know what circuit breaker to buy for my mitsubishi mini split that is a 50A 2 pole that provides earth leakage protection … read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
Honda EU7000is has 30 amp line with circuit breaker with
Honda EU7000is has 30 amp line with circuit breaker with each line up to 22.6 amps. Questions is 32 amp draw too large and will trip circuit breaker and can circuit breaker be upgraded to 40 amp to al… read more
Sam I
Sam I
Electrician
B.S.
364 satisfied customers
I have a question about ITE circuit breakers, First call,
I have an ITE electrical panel #FEQ 28MBB. I need compatible circuit breakers… read more
Sam I
Sam I
Electrician
B.S.
364 satisfied customers
I have a zinsco circuit breaker panel. The main line circuit
I have a zinsco circuit breaker panel. The main line circuit breaker is a 125 amp Zinsco 2pole breaker.My question is can I safely replace 125 amp breaker with a 100 amp 2 pole breaker? Main lineRegar… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I have a well pump wired into a 240v/20a circuit breaker. C/
I have a well pump wired into a 240v/20a circuit breaker. C/B has white wire, black wire, ground wire. Pressure switch on well pump has same...black, white. ground. Output from pressure switch to pump… read more
ProGrade
ProGrade
Electrical Contractor
564 satisfied customers
I've checked ALL circuit breaker with a voltage meter. They
I've checked ALL circuit breaker with a voltage meter. They are good, but I still don't have power in both bathrooms. Not in the outlets or ceiling lights. Can you help. … read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
The circuit breaker tripped controlling all the electricity
The circuit breaker tripped controlling all the electricity in my son's bedroom. This circuit also controls the recessed lighting in the dining room. The only way I can reset the circuit breaker is if… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
One of my circuit breakers tripped a few months ago. It
Hello. One of my circuit breakers tripped a few months ago. It would not turn back on. Tonight, the night before I have scheduled an electrician to come, I checked the breaker and I was able to flip i… read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
I currently live in apartment with a circuit breaker that
I currently live in apartment with a circuit breaker that has 100 amps total. I would like to know to upgrade to 200 amps if it only requires switching the breaker box only or you have to bring anothe… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
What is the standard circuit breaker for an wall oven and
Greetings, What is the standard circuit breaker for an wall oven and for a dual fuel range? Aren't they typically 40A? The installation instruction I am looking at for a Kenmore Elite wall oven (3.4kW… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x