My name is ***** ***** and... I am replacing a light fixture

Customer Question
Customer: My name is *****...
Customer: My name is ***** ***** and... I am replacing a light fixture in our garage... There are 12 fixtures on the circuit... In the box, there are 3 sets of 2 wire romex
JA: Thanks. Can you give me any more details about your issue?
Customer: i need to know how to wire the 3 romex cables back together
JA: OK got it. Last thing — JustAnswer charges a fee (generally around $18) to post your type of question to Electrical Experts (you only pay if satisfied). There are a couple customers ahead of you. Are you willing to wait a bit?
Customer: sure
JA: OK. Now I'm going to take you to a page to place a secure deposit with JustAnswer. Don't worry, this chat is saved. After that, we will finish helping you.
Submitted: 2 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Customer reply replied 2 years ago
The Romex cables all have black, white, and a copper ground wire. so at the lighting fixture, I need to use the black, white, and ground for the new fixture and connect the wires correctly to continue the string.
Customer reply replied 2 years ago
additionally, i was shocked by the white wires while the breaker was off. Could there me multiple circuits wired together?
Customer reply replied 2 years ago
i am sure the 3 black wires were wired together when I removed the light fixture.
Answered in 35 minutes by:
12/4/2015
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 3,939
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) Do you have an AC voltmeter available to confirm some voltage measurements?

2) You were most likely shocked as the circuit is configured as a shared neutral circuit.

3) You don't remember how the original light was spliced?

4) Have all of the wire splices been removed? Any groups of wires that are still original and wire nutted together?

Ask Your Own Electrical Question
Customer reply replied 2 years ago
I remember the 3 black wires were all nutted together. I had to remove the entire box and replace it (long story) I do have a volt meter. What is my next step?
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

1) Undo all of the splices on each wire color and spread each wire apart so they don't short. Turn the breaker ON. See if you can locate a constant 120 volt hot and white neutral in the box and label it as circuit feed using some white electrical tape and a Sharpie marker. Turn the wall switch ON/OFF to confirm if the hot wire is a constant hot or is a switched loop wire.

2) Measure each of the whites with the breaker in the ON position from white to bare copper ground. Do you measure any voltage on any of the whites?

3) How many of the whites were spliced together.

FYI.........next time before removing wire nut splices, you need to label the wires before removing everything.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
I am pretty sure that originally only 2 whites were spliced together. I won't be able to measure the volts on the whites until tomorrow. Will you be available to answer questions then?
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

No problem, I will be logged on the web site tomorrow, so just reply back to me on this same question and we can take it from there.

In the meantime, have a good evening and we'll catch up with you tomorrow..........Thanks.............Kevin:)

Ask Your Own Electrical Question
Customer reply replied 2 years ago
I just unspliced everything and there is no constant 120 volt.
Customer reply replied 2 years ago
The only way I measure any voltage is off of one white and a copper ground
Customer reply replied 2 years ago
I am pretty confident that that white wire was originally spliced into another white wire by itself
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

Thanks for the replies.

1) If measuring 120 volts on a white to ground, then that white wire is acting as a hot wire and is not a neutral wire.

Did the white wire have a piece of black electrical tape wrapped around it to re-identify it as a hot conductor?

Ask Your Own Electrical Question
Customer reply replied 2 years ago
No it was not marked. This is a parking garage with multiple lights that operate off a photo cell
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

1) Are the wires installed in EMT or Rigid Metal Conduit or was a flexible raceway or electrical cable installed?

Ask Your Own Electrical Question
Customer reply replied 2 years ago
They are romex with no conduit
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

That explains why one of the white wires is hot. Code allows the white Romex wire to act as a hot wire if necessary.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Ok so you have any ideas how I should re wire it?
Customer reply replied 2 years ago
Is it as simple as all 3 blacks and all 3 whites together?
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

1) No, one of the whites is being used as a hot wire. The other 2 whites are most likely neutrals. If splicing a white hot wire to a neutral wire, the breaker will trip due to a direct short circuit.

2) Label the white wire that is hot with some black electrical tape. Then splice the other 2 white wires together using a plastic wire nut.

3) The photo cell will contain a black, a red and a white wire. Can you confirm what wire color is spliced to the photo cell black wire? Possibly another black wire or a white wire?

Ask Your Own Electrical Question
Customer reply replied 2 years ago
There are no red wires.. All I have is 3 sets of romex each contains a black, white, and copper ground
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

The photo cell should contain a red wire. Not the Romex cables.

What is the wire color that the photo cell red is connected too?

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Again, there are no red wires
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

What are the wire colors on the photo cell? 2 blacks and 1 white?

Ask Your Own Electrical Question
Customer reply replied 2 years ago
I am working with only 3 sets of romex. There is NO red wire anywhere
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

You mentioned that you have a photo cell installed. I've never seen a photo cell that did not contain a red switched loop wire.

All photo cells contain 3 wires.....ie........a black, a red and a white. Somewhere you have a junction box where the 3 photo cell wires are spliced at. The red photo cell wire is the switched loop conductor that connects to the lights. Thus, a process of elimination to identify which of the light fixture box black wires is connected to the red photo cell wire. Thus the reason I was asking this.

I will opt out of the question and place it back to the open board. No need to reply back to me. You will be notified once another expert picks up the question. Thanks.

Ask Your Own Electrical Question
Electrician: AssuredElectrical, Master Electrician replied 2 years ago
AssuredElectrical
AssuredElectrical, Master Electrician
Category: Electrical
Satisfied Customers: 4,241
Experience: Contractor-42+ Years in the ElectricalTrade
Verified

Welcome. My name is ***** ***** would be glad to assist.

The very first thing you must do, is go directly to the photocell location, the inspect its wiring.

There is a red wire coming out of the photocell and you need to see what color wire is connected to that red.

see if it isnt connected to a white wire from a romex cable.

report findings and we can continue

Ask Your Own Electrical Question
Customer reply replied 2 years ago
I am pretty sure it is a black wire because I found 1 of the 3 black wires at the fixture to be hot when photocell is on. I will confirm at the photocell in a bit Thank You
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

Very good.

Although you previously posted that only a white were was hot and nothing else?

Ask Your Own Electrical Question
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

Ok.

I do not see a photo cell in the picture.

Where is it located and can you get a picture?

Ask Your Own Electrical Question
Customer reply replied 2 years ago
The photocell is located on the back of the building but the wires from it going to this junction box. Do you want me to see if there is a red wires spliced into a black wire at the photocell? I'll get you a picture in a couple of hours thanks for your help.
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

What needs to be done, is to identify the cable from the contactor junction box you posted a picture of, then identify which cable goes out to the lights.

Once you have identified the 2 cables, we can then determine how the fixtures were originally wired.

So, identify cable #1 from the photo cell to the junction box.

Identify cable from lights to the junction box

See how they are interconnected to each other and then we have the basic setup and can proceed.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Sounds complicated but doable. Since I have determined that one of the black wires is hot when photocell is activated and dead when it isn't, wouldn't that indicate that that particular is the feed from the photocell?
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

Ok, first, I do not think that the lights are actually connected to the photo cell.

12 lights are too many to have on the photocell as a load.

That is why you have the large junction box and those 2 contactors.

The photocell turns on the contactors and they turn on the lights.

So, you will find that the photocell cable connects to power and then to the contactors, the light cable will connect to the contactors.

So, it is looking to appear, that the blacks connect all together at the lights as do the whites

But, that is why we find the connections first and do not begin to make guesses.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
I can confirm that three black wires were wired together originally at the light fixture. I am going to look at the photocell now
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

Ok, thanks.

If the 3 blacks were all connected together, it is most likely the 3 whites should also go together. Not a 100%, but certainly 95% of the time.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
If one of the whites has constant power.. And one of the blacks has power activated by the photocell, wouldn't that be an issue down the line? Currently I have 2 of the whites spliced together (one is constant 120v) all 3 of the blacks, and one white not connected. I then have a light fixture connected with the black to blacks and white to copper ground. The issue I am faced with is the next light in the line will not light up but all other lights do..
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

Ok, since we have no idea of how someone performed the installation, we need to make a test.

First, a white should not show power and should certainly not connect to other whites, if it does, as that is a dangerous situation.

Remove the white you state has power from the connection to a 2nd white, then cap it off.

Then connect the 2 remaining whites together and see if that makes the next light work.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
I removed the constant hot white and capped it. Then connected the two remaining whites and same result. All lights come on with the photocell except for the next light past the fixture I replaced
Customer reply replied 2 years ago
I took the liberty to try all 3 of the whites together and i got the same result
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

Ok, do this.

Disconnect all the whites.

Find the white that is inside the same cable as the Black that has 120 volts when the photocell turns on the lights.

Connect that one white to the white wire on the fixture.

Leave the other 2 whites disconnected and not touching each other.

Then test.

If you get the same result, you have a problem with that other fixture and need to get inside to find the problem.

What type of fixture is it? Make and Model is helpful.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
I will do that tomorrow but I am testing the voltage on the fixture that isn't working so I eliminated the possibility of it being the fixture.
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

please elaborate.

you can go to the fixture that is not working and measdure between the white and black wire connection from the romex cables and get 120 volts?

how many cables?

Ask Your Own Electrical Question
Customer reply replied 2 years ago
There is only one romex black and white going into the non working fixture. I cannot measure any voltage on it. It was working before I started this project
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

ok, your connection at the other fixture is probably loose.

they need to be redone

Ask Your Own Electrical Question
Customer reply replied 2 years ago
I agree but with 3 sets of romex, I am still struggling with the configuration
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

ok,

ok, your connection at the other fixture is probably loose.

they need to be redone

.all blacks together and all whites together

Ask Your Own Electrical Question
Customer reply replied 2 years ago
I tried all blacks and all whites together and the next fixture in line still isn't working
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

Ok, by way of elimination, if the wires are connected well with good copper to copper contact, the next fixture is not wired from that fixture but from another location.

If the connections are not well made, which we see all the time from those not familiar with electrical, then anything downstream will not operate.

Since there are 3 whites and blacks, there is also something else connected.

So, disconnect the 2 whites and 2 blacks that are not the power and see what else is not operating.

Then by process of elimination, it may show that the first assumption is correct

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Ok I will do that but the power I am getting is from one black and then copper ground wire.
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

Oh, NO, that is not usable power

Must be a black and white or else the fixture will not work

Ask Your Own Electrical Question
Customer reply replied 2 years ago
The fixture is working from black and the white wire from the fixture is connected to the copper ground. Is that bad?
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

Oh my, that is extremely dangerous for shock hazard and fire hazards.

The ground must be disconnected from the whites immediately.

If there is no voltage showing between the black and white of the same cable, you will have to trace the cable and find the break point or run a new one.

Ground wires are for your safety only and if connected to a white anywhere can cause a dangerous loop of unprotected circuits.

It is illegal to use a ground wire for anything other than grounding!!

Ask Your Own Electrical Question
Ask AssuredElectrical Your Own Question
AssuredElectrical
AssuredElectrical
AssuredElectrical, Master Electrician
Category: Electrical
Satisfied Customers: 4,241
4,241 Satisfied Customers
Experience: Contractor-42+ Years in the ElectricalTrade

AssuredElectrical is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,939 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

4,241 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I havea line into junction box and 14-3goingout to switch
I havea line into junction box and 14-3goingout to switch and also wire goingout to light . all grounds are connected. when I connect hot wire to black in the 14-3 ,tester shows about 5 volts in both … read more
Kevin
Kevin
Licensed Electrical Contractor
3,939 satisfied customers
I am looking for installation instructions for junction box
I am looking for installation instructions for junction box # BH614R … read more
Sam I
Sam I
Electrician
B.S.
472 satisfied customers
I also purchased a photocell from Lowes. To run my LED
I also purchased a photocell from Lowes. To run my LED lights into a my soffit. I first wired a dimmer to the switch and it worked fine. I then ran a 14/3 wire from the attic to the photo cell - in th… read more
Sam I
Sam I
Electrician
B.S.
472 satisfied customers
Half rou d junction box for a ceiling light fixture. There
Half rou d junction box for a ceiling light fixture. There is a water pipe nearby where i want the light to go … read more
George Smith
George Smith
Vocational, Technical or Trade School
314 satisfied customers
IF YOU SPLISE A WIRE DO YOU INSTALL A JUNCTION BOX. JUST NOW
IF YOU SPLISE A WIRE DO YOU INSTALL A JUNCTION BOX … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Mounting of junction box in wet location...outside...how
Mounting of junction box in wet location...outside...how high off of the ground does the weatherproof box need to be mounted. Is there a code requirement?… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I would like to convert a wall outlet to a junction box so I
I would like to convert a wall outlet to a junction box so I can add power to the room behind the current wall outlet....I have already removed the wall plate and can see that there are currently 2 wi… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I need help to Hard wire a nanny cam inside the junction box
I need help to Hard wire a nanny cam inside the junction box of a wall outlet. My problem is that the nanny camera camera only has 2 wires (black and white). On the other hand, the wall outlet has 5, … read more
Sam I
Sam I
Electrician
B.S.
472 satisfied customers
Can you put a junction box In a line going to and electric
can you put a junction box In a line going to and electric stove 40 amp size or does it have to be one continuous run … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have a junction box with Al wiring. One Black One Red and
I have a junction box with Al wiring. One Black One Red and a stranded bare common. It used to have a drop in stove. I wish to change over to a new slide in stove with a 3 prong plug. Can I put a flus… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Need help determining wire size, wire type, and conduit size
Need help determining wire size, wire type, and conduit size for 200amp panel with a 200 amp subpanel. Here is a list of my questions: http://mnjustin.com/diagram.jpg… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I want to connect a photocell to a 4way switch. Not. A
Not long. A diagram like on the site would be nice … read more
Sam I
Sam I
Electrician
B.S.
472 satisfied customers
I want to add a light switch before a photocell that will be
I want to add a light switch before a photocell that will be controlling a light. I think this example is close but not sure … read more
Sam I
Sam I
Electrician
B.S.
472 satisfied customers
I'm trying to locate a junction box on a 1988 cavco
I'm trying to locate a junction box on a 1988 cavco manufactured home … read more
ProGrade
ProGrade
Electrical Contractor
564 satisfied customers
What would be the reason to have an open junction box in the
what would be the reason to have an open junction box in the crawl space of a house? … read more
Kevin
Kevin
Licensed Electrical Contractor
3,939 satisfied customers
What is minimum size junction box for 200amp service line.
what is minimum size junction box for 200amp service line. … read more
Sam I
Sam I
Electrician
B.S.
472 satisfied customers
Adding a receptacle to an existing junction box. The old
Adding a receptacle to an existing junction box. The old receptacle tests good but the new receptacle is showing an open hot/ ground. Getting continuity when I test the hot and ground wires. What's up… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Was just informed I might require a Hard Wire Junction box
Was just informed I might require a Hard Wire Junction box with installation of a water heater. Would like to know appx cost for this job and recommendations of electricians in my area … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x