I'm installing power on my new property. From the power drop

Customer Question
Hello- I'm installing power on my...
Hello-
I'm installing power on my new property. From the power drop at the pole I have a single phase 200 amp main panel and I'm running about 130 ft to my 200amp sub panel which is outdoors freestanding and not attached to a building.
Would I be correct in running (2) 3" conduit with (3) 4/0 aluminum wires in each conduit? Also, what size ground do I need in each?
From the sub panel I'm runnng 1 1/2" conduit 230 ft to the well/pump which is a deep well with a 1 1/2 hp pump on 220V. What size wire do I need to run for the 230ft? Would (3) #4 copper with a #10 copper ground be correct?
Thank you!
Submitted: 2 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 1 hour by:
11/16/2015
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 3,792
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) The sub-panel feeder circuit requires a 4 wire circuit comprised of 2 hots, 1 neutral and 1 equipment grounding conductor. Yes, 4/0 aluminum conductors are required and will result in a 1.8% voltage drop or a loss of 4.4 volts. National Electrical Code recommends the voltage drop be 3% or less. Therefore, the 4/0 aluminum is OK. If installing the feeder circuit in PVC conduit, the equipment grounding conductor needs to be sized as a minimum of 4 AWG aluminum.

2) All 4 sub-panel feeder conductors can fit inside (1) one 2" diameter gray electrical PVC Schedule 40 conduit. Although to make the wire pull easier, I recommend to increase the conduit to either 2 1/2" or 3" diameter. Bury the sub-panel feeder conduit run a minimum of 24" below final grade.

At the sub-panel, you will need a quantity of (2) two 8 foot ground rods spaced a minimum of 6 feet apart. The grounding electrode conductors at the rods needs to be sized as 4 AWG copper.

3) A 240 volt single phase motor that is 1 1/2 hp has a full load current of 10 amps. Due to the "in-rush" current, the minimum breaker size is sized at 125% of the FLA rating. Therefore, 1.25 x 10 amps = 12.5 amps. Round up to the next available trade size breaker and use a 15 amp double pole breaker for the well pump.

4) The 230 foot well pump run requires 8 AWG copper for the 2 hots and (1) one 10 AWG copper for the equipment grounding conductor. If using PVC conduit for the well pump, minimal diameter pipe is 1/2". In order to make the wire pull easier, I recommend to install 1" conduit. The voltage drop on 240 volts/15 amps on a 230 foot run results in 2.2% voltage drop or a loss of 5.2 volts which is code compliant and therefore OK.

5) Since the 200 amp sub-panel will be installed outdoors and exposed to the elements, it needs to be rated as a minimum of a NEMA 3R (waterproof type) panel. Install a 200 amp sub-panel that has a 200 amp main breaker and not a main lug type of panel.

6) All feeder and branch circuit conductors need to be rated as type "THW" for wet conditions.

7) Install a warning ribbon tape directly above the sub-panel feeder trench and the well pump trench. Bury the warning ribbon tape approximately 6" below final grade level on the entire conduit/trench run to provide a warning that anybody digging and/or trenching in the future that an electrical line exists directly below.

8) At the sub-panel, DO NOT install the green main bonding screw or a main bonding jumper strap. On all sub-panels, the neutral must remain isolated from the panel metal enclosure., By not installing the main bonding jumper is how the neutral remains isolated. At the sub-panel, you will need to install a separate equipment ground bar for the equipment grounding and grounding electrode conductors. DO NOT inter-mix white neutrals and grounds on the neutral bus bar. Neutrals only land on the neutral bus bar and grounds only land on the equipment ground bar in a sub-panel.

9) Identify both conduit runs by pounding either metal stakes in the ground and spray painting them with a red color and/or reference the conduit run dimensions from corners of the building and/or power pole structures and/or the property easement/boundary lines. Document both conduit runs with the appropriate dimensions for future reference and create an "as-built" drawing in the event future digging near these areas need to occur. Make a copy of the "as-builts" and tape them inside the respective electrical panels for future reference.

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks..............Kevin:)

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

If you have any additional questions, just let me know and I’ll be glad to answer them for you.

Otherwise, don’t forget to rate me before you log Off.

Thanks..............Kevin:)

Ask Your Own Electrical Question
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 3,792
3,792 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,425 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,940 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,603 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,792 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I have a davit with a Leeson motor C6C17NC66A and a Salzer
I have a davit with a Leeson motor C6C17NC66A and a Salzer rotary switch. Someone yanked out the pigtail for incoming power and I can't find where to reconnect the black, white, and green. Any ideas? … read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
Can I add a 90 elbow to the main conduit so that I can raise
can I add a 90 elbow to the main conduit so that I can raise that conduit the conduit is running vertical and i need some height under the conduit … read more
Kevin
Kevin
Licensed Electrical Contractor
3,792 satisfied customers
When I purchased my home, it had aluminum wiring in it. So
When I purchased my home, it had aluminum wiring in it. So we had the copalum crimping treatment done to the whole house. Now we want to add a few more outlets & lights and I wonder if we need the sam… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I am trying to hook up my garage with 2/0 aluminum wire to a
I am trying to hook up my garage with 2/0 aluminum wire to a 200 amp box in the garage. The wire of course has 3 wires one bare and the other 2 not. What do I do with the bare wire hook it up to the n… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
The motor runs but there is no electrical power, About a
Sometimes the power comes back or for a while and then stops. its almost like there was a loose connection. i checked all the connections and power cord.… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I have a dedicated 10 amp romex line in conduit, going to a
I have a dedicated 10 amp romex line in conduit, going to a direct wired garbage disposer under my kitchen sink. I want to connect this line up to a single gang outlet box to make exchanging the dispo… read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
I am running 3 circuits inside of pvc conduit. 220v 30a
I am running 3 circuits inside of pvc conduit.220v 30a water heater 220v 15a ac 120v 20a receptaclecan I use 1 shared 10awg ground wire for all circuits?… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Motor is on and turning but bladers are not. Just started
Motor is on and turning but bladers are not JA: I'll do all I can to help. How long have you been dealing with this? Customer: Just started JA: Do you plan on doing the work yourself? Customer: YES JA… read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
Need help determining wire size, wire type, and conduit size
Need help determining wire size, wire type, and conduit size for 200amp panel with a 200 amp subpanel. Here is a list of my questions: http://mnjustin.com/diagram.jpg… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Underground power line going to water well. Aluminum wire.
Underground power line going to water well. Aluminum wire. 120 ft distance. . 240 volts across two terminals of breaker. only 150 volts at pump. checked individual. approx 130 volts from neutral to on… read more
Kevin
Kevin
Licensed Electrical Contractor
3,792 satisfied customers
How much to install 100' of electrical line in a conduit if
how much to install 100' of electrical line in a conduit if the trench is already dug. Include the cost of wiring and adding a 50 Amp Circuit Breaker … read more
Kevin
Kevin
Licensed Electrical Contractor
3,792 satisfied customers
What size wire is needed to run underground in conduit to a
What size wire is needed to run underground in conduit to a garage about 60 feet from the main connection at the power pole? This would be connected to a subpanel in the garage. … read more
Kevin
Kevin
Licensed Electrical Contractor
3,792 satisfied customers
My timer is hook to my pool motor, and the motor loses
My timer is hook to my pool motor, and the motor loses power. Is this lack of electrical connections. It's trigger my main switch off couple of times. … read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
Do you need to remove existing conduit and or conductors if
Do you need to remove existing conduit and or conductors if they are being abandoned and not being used? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
A 1972 home has aluminum wiring. In addition to installing
A 1972 home has aluminum wiring. In addition to installing AlumiConn connectors at all lights, switches, outlets, etc....do the range, ac and water heater outlets need to be completely rewired so the … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Can I use the conduit that leads into the panel box by
Can I use the conduit that leads into the panel box by adding a second pair of wires to be connected to another circuit breaker? Easier to do than setting up another separate conduit attachment? I kno… read more
Kevin
Kevin
Licensed Electrical Contractor
3,792 satisfied customers
I need to install about 200 ft of conduits on a warehouse
Hi Kevin... I need to install about 200 ft of conduits on a warehouse ceiling. The conduit needs to be suspended about 3 feet from the roof because of the large beams. Currently there are two rows of … read more
Kevin
Kevin
Licensed Electrical Contractor
3,792 satisfied customers
I am running 4/0 4/0 4/0 2/0 aluminum wire through 3"pvc
i am running 4/0 4/0 4/0 2/0 aluminum wire through 3"pvc conduit 450' with know bends---can you give me some tips on how to pull this through … read more
ProGrade
ProGrade
Electrical Contractor
564 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.