Electrical

Electrical Questions? Ask an Electrician Online.

Ask an Expert,
Get an Answer ASAP!

Electrical

I would like to run power from the meter pole to my garage.

Customer Question
I have a 200A feed...
I would like to run power from the meter pole to my garage. I have a 200A feed from meter on pole to main panel in the house. I purchased a 200A disconnect that has feed through lugs, and can also handle upto 8 additional breakers. My plan is to run the
200A through the feed through lugs, than use a 80 amp breaker to feed the garage. I'm using use 2-2-2-4 AL wire from disconnect panel to panel in the garage. I'm a bit confused on how to do this. In the meter there are 2 lines (hot) 1 neutral, on the line
side, on the load side there are the 2 hots, and the neutral and ground is together, now wiring that in the disconnect is simple being it feeds straight through, how or where do my wires for the garage hook up to?
Submitted: 2 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 8 minutes by:
11/3/2015
Electrician: AssuredElectrical, Master Electrician replied 2 years ago
AssuredElectrical
AssuredElectrical, Master Electrician
Category: Electrical
Satisfied Customers: 4,241
Experience: Contractor-42+ Years in the ElectricalTrade
Verified

Welcome. My name is ***** ***** would be glad to assist.

Thanks for the details on the situation.

The key here, is that the neutral and ground will ONLY come in contact with each other at the Main location.

There after, the ground and neutral must be completely isolated from each other.

Also, in your situation, since the location at the garage is a separate structure, you are required to install grounding rods to add to the ground connection.

See the below diagram fro an example, which shows how sub panels are installed in detached buildings from the Main disconnect.

Let me know any questions,

Thanks

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Ok so does the panel in the house stay the same?
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

From the posting, the house panel is existing.

Anything existing does not change, only new installations are required to be in the newer requirements.

If the house is also a brand new installation, then it should be wired with 4 wires and connected the same as the garage.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
I don't bond the subpage correct?
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

No, the sub panel does not get the bonding screw through the neutral bar either.

Ground and neutral 100 % separated

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Does the neutral not carry current?
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

Dont why the question, but yes, it carries current just like a hot.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Than why in the drawing is the neutral and ground hooked in the same bar in the main disconnect.
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

Because the neutral grounds at the Main, that is required at the main only.

It is a 3 wire power at the main.

The main is where the ground starts, then it is separated and 4 wire from it to any other locations.

Required Neutral-to-Case Connections.
Service Disconnecting Means [250.24(B)]. Because electric utilities are not required to install an equipment grounding conductor, alternating-current services supplied from a grounded utility transformer shall have a grounded (neutral) conductor run from the electric utility transformer to each service disconnecting means. The grounded (neutral) conductor shall be bonded to each disconnecting means’ enclosure (neutral-to-case connection) by a screw or strap supplied by the equipment manufacturer [250.28]. Figures 37 and 38 250-24B 01.cdr 250-24B 02.cdr

Ask Your Own Electrical Question
Customer reply replied 2 years ago
My concern is the main panel now is in my basement, I install a main disconnect on the pole after the meter the panel in the basement becomes a sub panel correct?
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

Ok,

If there is no disconnect at the pole now, and the power runs from the meter to the house panel, then the house is the main now.

If you now install a new disconnect at the meter, the house becomes a sub panel, and it MUST have a 4 wire feeder tot he panel, the 3 wire feeder is obsolete.

I understood the situation as there was an existing disconnect and you were just changing it to a different type to feed thru

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Oh no sorry new install of the disconnect. So I have to rip up my old feeder wire from my house to the pole and install 4 wires? Can't I just install the disconnect as is, run 2 hots from the breaker in the disconnect to the garage, ground and bond the panel at the garage?
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

Well, wish I could say yes, but code dictates the rules and I have to provide the information accordingly through my state licensing and for the safety of the ground fault path.

Main only with the neutral to ground bond.

Not sure what 2 hots are doing for you with only 240 volts?

Would be best to come off the main panel at the house, but understand it may be further away in some applications.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
it's pretty far away from the house to garage. So what would happen if I used the feed through disconnect at the pole, hooking up the house as it is in the meter in the disconnect, than hooking up the garage in the disconnect box with the ground and neutral hooked together in the disconnect box, and keep the neutral and ground separate at the subpage in the garage?
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

You do not connect the ground to the neutral in junction boxes, never allowed at anytime.

You are creating a path for current on the ground, if the neutral ever is broken. Very dangerous.

That is a long run for this happen on also

Underground aluminum will fail at some point in time if not in conduit, repair these all the time.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
Ok can I run 2 hots and a neutral from the disconnect to the sub panel in the garage, ground and bond the panel in the garage?
Electrician: AssuredElectrical, Master Electrician replied 2 years ago

I am not sure of what you are asking, sorry. It sounds like you wish for me to provide something different than what I have done thus far.

I can give the direction of how it is supposed to be wired by the code for your safety and operation and that is all I am allowed to do.

I think it is posted unless something is unclear on the previous postings?

I cannot provide instruction for wiring that could be dangerous or against code.

I understand the dilemma, but please understand my responsibilities also.

What you wish to perform would not be permitted by the local jurisdiction, so if anything did take place, the insurance probably would not cover in the situation.

Ask Your Own Electrical Question
Ask AssuredElectrical Your Own Question
AssuredElectrical
AssuredElectrical
AssuredElectrical, Master Electrician
Category: Electrical
Satisfied Customers: 4,241
4,241 Satisfied Customers
Experience: Contractor-42+ Years in the ElectricalTrade

AssuredElectrical is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,425 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,940 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,603 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,715 satisfied customers

30 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

4,241 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
Half rou d junction box for a ceiling light fixture. There
Half rou d junction box for a ceiling light fixture. There is a water pipe nearby where i want the light to go … read more
George Smith
George Smith
Vocational, Technical or Trade School
274 satisfied customers
IF YOU SPLISE A WIRE DO YOU INSTALL A JUNCTION BOX. JUST NOW
IF YOU SPLISE A WIRE DO YOU INSTALL A JUNCTION BOX … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Mounting of junction box in wet location...outside...how
Mounting of junction box in wet location...outside...how high off of the ground does the weatherproof box need to be mounted. Is there a code requirement?… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I would like to convert a wall outlet to a junction box so I
I would like to convert a wall outlet to a junction box so I can add power to the room behind the current wall outlet....I have already removed the wall plate and can see that there are currently 2 wi… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I need help to Hard wire a nanny cam inside the junction box
I need help to Hard wire a nanny cam inside the junction box of a wall outlet. My problem is that the nanny camera camera only has 2 wires (black and white). On the other hand, the wall outlet has 5, … read more
Sam I
Sam I
Electrician
B.S.
374 satisfied customers
Can you put a junction box In a line going to and electric
can you put a junction box In a line going to and electric stove 40 amp size or does it have to be one continuous run … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I have a junction box with Al wiring. One Black One Red and
I have a junction box with Al wiring. One Black One Red and a stranded bare common. It used to have a drop in stove. I wish to change over to a new slide in stove with a 3 prong plug. Can I put a flus… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Need help determining wire size, wire type, and conduit size
Need help determining wire size, wire type, and conduit size for 200amp panel with a 200 amp subpanel. Here is a list of my questions: http://mnjustin.com/diagram.jpg… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I'm trying to locate a junction box on a 1988 cavco
I'm trying to locate a junction box on a 1988 cavco manufactured home … read more
ProGrade
ProGrade
Electrical Contractor
564 satisfied customers
What size wire is needed to run underground in conduit to a
What size wire is needed to run underground in conduit to a garage about 60 feet from the main connection at the power pole? This would be connected to a subpanel in the garage. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
What would be the reason to have an open junction box in the
what would be the reason to have an open junction box in the crawl space of a house? … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
6 wires in junction box. 2 2 black 2 copper. About 10
Hook up light, flip switch and it powers off entire living room… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
What is minimum size junction box for 200amp service line.
what is minimum size junction box for 200amp service line. … read more
Sam I
Sam I
Electrician
B.S.
374 satisfied customers
One junction box for pendant light has 1, 1 black and 1
One junction box for pendant light has 1 white, 1 black and 1 ground. The pendant light junction box has 2 whites, 2 blacks and one ground. What do I do differently with the box that has the two sets?… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
I am installing a 15 amp electrical outlet to a junction box
I am installing a 15 amp electrical outlet to a junction box that was not in use but is hot. When I removed the cover plate I discovered 3 black wires twisted and covered by a yellow plastic cover scr… read more
George Smith
George Smith
Vocational, Technical or Trade School
274 satisfied customers
Adding a receptacle to an existing junction box. The old
Adding a receptacle to an existing junction box. The old receptacle tests good but the new receptacle is showing an open hot/ ground. Getting continuity when I test the hot and ground wires. What's up… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Was just informed I might require a Hard Wire Junction box
Was just informed I might require a Hard Wire Junction box with installation of a water heater. Would like to know appx cost for this job and recommendations of electricians in my area … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
There is an old junction box outside that serves our pool
There is an old junction box outside that serves our pool light. It sticks up about 14 inches out of the ground. We would like it moved or put underground but the two electricians who have come by the… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question