I have a california home built in the 80's and it has gfci's

Customer Question
in the kitchen that work...
i have a california home built in the 80's and it has gfci's in the kitchen that work fine, upstairs in the 2 baths the inspector noted that 2 in 2 baths did not kick with the 3 light tester but do show wired correctly and i have visually checked for correct wiring line and load side... this problem i confusing me, i have tried everything, it must be a bootleg ground before the gfci and i cannot find it...
Submitted: 2 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 11 minutes by:
8/25/2015
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 3,793
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified

Hello and welcome to Just Answer. My name is ***** ***** I will be happy to assist you with your electrical question.

1) Bootleg grounds are only commonly found on older wiring systems such as Knob & Tube or older Romex cables that did not contain a ground wire or metal conduit. Since the home was built in the 80's, I assume that the branch circuits contain an equipment ground? Home was either wired with modern Romex cables or EMT metal conduit?

2) FYI........GFCI's do not require an equipment grounding conductor to function.

3) Do the 2 baths reside on one dedicated circuit or do they reside on a multi-wired branch circuit.....ie........ better known as a shared neutral circuit?

4) Are the bathrooms wired to a GFCI breaker or to a GFCI receptacle?

If wired to a GFCI receptacle, have you temporarily disconnected the LOAD side on each GFCI and then confirm that the GFCI trip button and reset button works correctly?

5) Are the bathrooms wired to any exterior and/or garage receptacles? If so, unplug any loads on the exterior and/or garage receptacles and re-test.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
its 3 wire romex
i know they dont require a ground done that before
shared neutral circuit i am pretty sure
the home owner had a gfi receptacle in the 1st and 2nd bath i dis connected at the first gfi and still cant get the first one to work he did not know he did not need more than 1 gfi on the circuit
i have unplugged everything i am right over the panel, unless there is something hidden in the walls between the panel and this bath i dont know
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

Thanks for the replies.

1) Are you saying the circuit is a shared neutral? Please confirm?

2) Have you performed a visual inspection inside the panel? If a shared neutral circuit, the Romex cable should contain 1 black, 1 red, 1 white and 1 bare copper all within the same cable. Also if a shared neutral, the breaker should be a double pole breaker or 2 single poles with a common trip handle.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
its a shared neutral that is the exact set up in the panel that you described, double pole breaker
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

OK, very good.

1) Since a shared neutral circuit, the neutral cannot be wired to the LOAD side of a GFCI receptacle. Nothing can connect to the GFCI LOAD side, as it will trip every time.

2) Have you confirmed that nothing is wired to the LOAD sides?

Shown in the diagram below is the only way a shared neutral circuit will work correctly using 2 separate GFCI receptacles.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
that is good to know but the first bath has nothing connected to the load. i have tried different gfi's on the first stop and disconnected everything else downstream..
Customer reply replied 2 years ago
the gfi is not kicking when you use the tester but the reset button works great shows wired correctly
Customer reply replied 2 years ago
this is a 15amp circuit its connected to 1 side of a dual 15 amp skinny breaker which can be switched off individually
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

OK, let's try this.

1) Perhaps the GFCI cube tester is not working correctly? If you have a voltmeter handy, you can intentionally test and trip a GFCI by inserting 1 meter probe to hot (short slot on GFCI) and the other probe to ground.

Ask Your Own Electrical Question
Customer reply replied 2 years ago
i have 2 and they work on the gfi's down in the kitchen
Customer reply replied 2 years ago
the inspectors did the same
Customer reply replied 2 years ago
i am not at the location now perhaps we can call it a night and try again tomorrow
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

OK, thanks for confirming. Just wanted to make sure the cube testers worked OK.

I will be logged on the web site tomorrow. Just reply back to me on this same question.

1) One item that I forgot to mention regarding GFCI 3 prong Cube testers as explained below:

Even though a GFCI receptacle does not require an equipment ground to work properly, a GFCI 3 prong cube tester requires an equipment ground in order to test and intentionally trip the GFCI receptacle. The GFCI cube tester works by connecting a 5 mA bleed resistor between the LINE and Ground. Therefore, I suspect that the GFCI's are unable to trip using the cube tester due to a faulty or open equipment ground within the branch circuit.

Hope this helps………If you have any additional questions, let me know and I’ll be glad to answer them for you.

Otherwise,don’t forget to rate me before you log Off.

The next timeyou have an electrical question, you can also request for me at: http://www.justanswer.com/home-improvement/expert-your-electrician ……….Thanks…………..Kevin!

Ask Your Own Electrical Question
Customer reply replied 2 years ago
hey Kevin, i have tried a few more things still not working, you say "equipment ground" does that mean, a load plugged into the circuit? or the internal bonded ground? im thinking of running a new circuit from the panel to the 1st bath or would that not work
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

1) An equipment ground is the bare copper ground wire inside a NM Romex cable that is terminated to the panel neutral bus bar or to a separate ground bar inside the panel. EMT and Rigid metal conduit also acts as an equipment ground since it is bonded to the panel metal enclosure. All branch circuits installed from the mid 1960's are required to have some form of an equipment ground, depending upon the wiring scheme that was installed.

2) You shouldn't require a new circuit. If the GFCI test and reset buttons both work and the GFCI can be tripped using the test button and reset, then the GFCI is working properly. I would not install a new circuit just because a GFCI 3 prong cube tester is unable to test and trip a GFCI receptacle. The GFCI test and reset buttons are what matters. I have a few of those GFCI testers somewhere in my tool assortment and I never use them as they often provide false indications. Whenever I test a GFCI or checking a circuit if it's hot or dead, I always use my Wiggy solenoid tester. A Wiggy tester or a multi-meter can easily confirm and check for proper voltage/polarity and can also intentionally trip a GFCI device to test it.

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

Refer to the link shown below on GFCI testers:

http://www.thecircuitdetective.com/outlet_tester_readings.htm

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

1) As I previously mentioned and the link also discusses the same, the GFCI cube testers are very sensitive to a good ground.

Ask Your Own Electrical Question
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago

If you have any additional questions, let me know and I’ll be glad to answer them for you.

Otherwise,don’t forget to rate me before you log Off.

Thanks....................Kevin!

Ask Your Own Electrical Question
Ask Kevin Your Own Question
Kevin
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 3,793
3,793 Satisfied Customers
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

Kevin is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,425 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,940 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,603 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,793 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
Can I add a 90 elbow to the main conduit so that I can raise
can I add a 90 elbow to the main conduit so that I can raise that conduit the conduit is running vertical and i need some height under the conduit … read more
Kevin
Kevin
Licensed Electrical Contractor
3,793 satisfied customers
Need to wire a 240 volt single phase 3 wire motor. Just
the motor has 2 connections for the hot wire and also has a common… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I have 3 black wires and 3 wires and 1 coming out of
I have 3 black wires and 3 white wires and 1 white coming out of electrical outlet, how t … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I have a sauna that is wired with 240 two wire for load (red
I have a sauna that is wired with 240 two wire for load (red and black) and a ground -- the neutral line (white) is not used -- currently it is not on a GFI and I would like to put it on a GFI - I wou… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
TROUBLE WIRING A LEVITON 6683. I HAVE ONE HOT WIRE BLACK/
I AM HAVING TROUBLE WIRING A LEVITON 6683. I HAVE ONE HOT WIRE BLACK/ WHITE /GROUND. I AM TRYING TO WIRE 2 /6683 SWITCHES OFF THIS WIRE TO GO TO DIFFERENT LIGHTS … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Wondering if I can run wires that are not mounted on studs
Wondering if I can run wires that are not mounted on studs in wall in the state of VA? … read more
Kevin
Kevin
Licensed Electrical Contractor
3,793 satisfied customers
Had broken wire from outside breaker. changed wire to
had broken wire from outside breaker. changed wire to copper. 60 amp breaker trips when power is turned back on. disconnect wire on 60 amp wire and still have voltage in disconnected wire … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
How do I wire a motion sensor with black and supply wires,
Hi! How do I wire a motion sensor with black and white supply wires, red (or pink) light wires and red, blue and brown sensor wires? Thanks. … read more
Sam I
Sam I
Electrician
B.S.
379 satisfied customers
I have a dedicated 10 amp romex line in conduit, going to a
I have a dedicated 10 amp romex line in conduit, going to a direct wired garbage disposer under my kitchen sink. I want to connect this line up to a single gang outlet box to make exchanging the dispo… read more
Sam I
Sam I
Electrician
B.S.
379 satisfied customers
I am running 3 circuits inside of pvc conduit. 220v 30a
I am running 3 circuits inside of pvc conduit.220v 30a water heater 220v 15a ac 120v 20a receptaclecan I use 1 shared 10awg ground wire for all circuits?… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Are the wires from the main box to a jump box sapose to be
are the wires from the main box to a jump box sapose to be in riggid conduet … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Wiring garage have 14-3 and 14-2 wire going to outlet and
Wiring garage have 14-3 and 14-2 wire going to outlet and there is no ground how would you hook these up to sub panel… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Need help determining wire size, wire type, and conduit size
Need help determining wire size, wire type, and conduit size for 200amp panel with a 200 amp subpanel. Here is a list of my questions: http://mnjustin.com/diagram.jpg… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
How much to install 100' of electrical line in a conduit if
how much to install 100' of electrical line in a conduit if the trench is already dug. Include the cost of wiring and adding a 50 Amp Circuit Breaker … read more
Kevin
Kevin
Licensed Electrical Contractor
3,793 satisfied customers
What size wire is needed to run underground in conduit to a
What size wire is needed to run underground in conduit to a garage about 60 feet from the main connection at the power pole? This would be connected to a subpanel in the garage. … read more
Kevin
Kevin
Licensed Electrical Contractor
3,793 satisfied customers
Do you need to remove existing conduit and or conductors if
Do you need to remove existing conduit and or conductors if they are being abandoned and not being used? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Can I use the conduit that leads into the panel box by
Can I use the conduit that leads into the panel box by adding a second pair of wires to be connected to another circuit breaker? Easier to do than setting up another separate conduit attachment? I kno… read more
Kevin
Kevin
Licensed Electrical Contractor
3,793 satisfied customers
I have a black, and wire in mtl. conduit. It appears that
I have a black, white and green wire in mtl. conduit. It appears that the green wire is the hot wire. Do I hook this to the side of the plug with the brass screws. Which wire is likely to be the groun… read more
Kevin
Kevin
Licensed Electrical Contractor
3,793 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x