Electrical

Electrical Questions? Ask an Electrician Online.

Ask an Expert,
Get an Answer ASAP!

Electrical

An inspection was done on our home by a potentioal buyer,

Customer Question
Hi, an inspection was done...
Hi, an inspection was done on our home by a potentioal buyer, their inspector reported that there was no bonding bushing at the service entarance wires. Our panel was replaced by an electrcian at the time we had our pool installed it is a 42 slot 200 amp Square D HOM panel, the panel is located in the garage wall exterior and goes directly to the Meter Can with a bushing installed where the service leads come thru into the panel., is the correct or am i or the inspector missing something?
Submitted: 2 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 15 minutes by:
7/25/2015
Electrician: Jason, Service Technician replied 2 years ago
Jason
Jason, Service Technician
Category: Electrical
Satisfied Customers: 4,290
Experience: Over 20 years of experience in all types of installations, troubleshooting, and repairs.
Verified
Hello. Welcome to Just Answer.
Ask Your Own Electrical Question
Electrician: Jason, Service Technician replied 2 years ago
Is there a metal pipe or metal nipple between the meter base and the panel?
Ask Your Own Electrical Question
Customer reply replied 2 years ago
Yes as far as I can tell is there a way to test this?
Electrician: Jason, Service Technician replied 2 years ago
The best approach is to replace the bushing that is there with a bonding bushing. This can be done by turning off all breakers in the panel, including the main. Then, the meter would need to be removed from the meter base. That will de-energize the wires going through the unapproved bushing.
At that point, those mains can be disconnected from the breaker and the neutral bar. The existing bushing can be taken off, and replaced with a bonding bushing.
If you can get me a photo of the inside of the panel, with the entry port for the main wires shown, I'll be able to tell why the inspector failed the existing bushing.
Ask Your Own Electrical Question
Customer reply replied 2 years ago
Jason, I did a further examination of my Breaker Panel and I remember that the individual that installed it had problems because he matched the thru bushing from the Meter Can which placed the Panel higher in the wall, I also used a multi-meter and checked the continuity thru the bushing to the inside front face of the Meter Can with the Bushing and the Ground Bonding Screw it zeroed out with full continuity present, the bushing is metal alng with the locking nuts, there are plastic nuts at both ends of the bushing threads to allow for a smooth entrance and exit for the two 2 Awg Load wires and the one 3 Awg Common comming from the Meter Can, this should be acceptable for a 200 amp Panel, is that correct?
Electrician: Jason, Service Technician replied 2 years ago
The wires you've described don't sound large enough for a 200 amp main breaker.
Also, did you find the bonding bushing in the meter can, or in the breaker panel?
It sounds like the inspector wants a bonding bushing in the panel itself. That would mean a metal bushing, with a grounding lug/screw, and the ground wire coming out of the pipe nipple, through the lug on the bushing, and then connecting to the ground bar.
It may be difficult to get him to approve anything else.
Ask Your Own Electrical Question
Ask Jason Your Own Question
Jason
Jason
Jason, Service Technician
Category: Electrical
Satisfied Customers: 4,290
4,290 Satisfied Customers
Experience: Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Jason is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

4,290 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
We have this same scenario, but every time we turn breaker
We have this same scenario, but every time we turn breaker back on, it blows the fuse... I'm wondering if the light switch is wired incorrectly...… read more
David Bowden
David Bowden
Owner
471 satisfied customers
Are you up for a challenge Pearl? Just today... Here goes...
Nope - Just say the word and I'll send you my question...… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
My power flickered for a bit and then went out. I have knob
my power flickered for a bit and then went out. I have knob and tube wiring. I went into the attic and looked for broken wires but saw nothing (?). i put the volt meter in the socket and had a little … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Have been trying to wire a ceiling fan to the wall switch. I
Have been trying to wire a ceiling fan to the wall switch. I ran a new line 14/2 from fan position to switch. found switch originally wired with white being hot . … read more
David Bowden
David Bowden
Owner
471 satisfied customers
Need GOULD Circuit Breaker Panel size 14WX42H. 1983. Just
just panel should not need electrician I am electric engineer myself … read more
George Smith
George Smith
Vocational, Technical or Trade School
322 satisfied customers
I disconnected my thermostat to replace it (without
I disconnected my thermostat to replace it (without labelling anything). The wires have MANY more colors than are referenced. Pink, grey, orange, brown... Now the system won't come on. Please help!… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Into outlet started making noise and then a little smoke
Into outlet started making noise and then a little smoke came out. There was a glade plug -in in the outlet and I removed it once I heard the noise … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
This question to be answered by NETHINGELECTRIC ONLY. I just
This question to be answered by NETHINGELECTRIC ONLY. I just replaced some old incandescent ceiling fixture light bulbs with some new LED bulbs. I'm having trouble with the dimmer switch though. Do I … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Is it easier to convert a 3-ph 440v machine to a 3-ph 220v
Is it easier to convert a 3-ph 440v machine to a 3-ph 220v or easier to convert a 3-ph 220v to a 3-ph 440 volt?… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have a dual outlet wall receptacle with two sets of wires
I have a dual outlet wall receptacle with two sets of wires attached to it. I want to split this receptacle so that one outlet is controlled by a switch and add another unswitched dual outlet "downstream." Is this possible and if so, how should it be wired? Thanks. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have a ProFusion 7500W garage heater, and when I hooked up
I have a ProFusion 7500W garage heater, and when I hooked up a 240 line voltage thermostat to it the heater kicks off well before the room reaches temperature. Is the thermostat faulty? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Hope all is well. happy New Years. I will be installing a 30
Hello Jason. Hope all is well. happy New Years. I will be installing a 30 amp breaker for a audio amplifier. My service panel doesn't have a ground. I'm planning on using a 10/3 cable. What should I d… read more
Jason
Jason
Service Technician
4,290 satisfied customers
I have a couple of questions. I'm replacing a hunter 27186
hello, I have a couple of questions. I'm replacing a hunter 27186 fan/light switch with a new Lutron fan/light switch model macl-lfqh. my question is the hunter controller black (hot) wire goes to the… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I NEED TO REPLACE AN" I NEED TO REPLACE AN 'ENOCEAN 20A
I NEED TO REPLACE AN 'ENOCEAN 20A RELAY CONTROLLER' BUT … read more
Sam I
Sam I
Electrician
B.S.
474 satisfied customers
I have a lev ThyssenKrupp elevator that the buttons on the
I have a lev ThyssenKrupp elevator that the buttons on the front do not light up. I have turned on and off the circuit breakers. I think the problem may be the battery pack. I think it is located on t… read more
George Smith
George Smith
Vocational, Technical or Trade School
322 satisfied customers
I am replacing light switch and have three black wires. On
I am replacing light switch and have three black wires. On the old one they 2 were wired through the back and one was attached to one of the screws(not the ground. I reattached using the screws but li… read more
George Smith
George Smith
Vocational, Technical or Trade School
322 satisfied customers
I have an old style Nema 6-15 socket and a Nema 10-50
I have an old style Nema 6-15 socket and a Nema 10-50 sockets not being used. Cannot rewire. Looking for some type of Step Down Transformer/Converter I can use with one of these to convert to standard… read more
George Smith
George Smith
Vocational, Technical or Trade School
322 satisfied customers
I have a legrand dimmer switch that i installed replacing a
I have a legrand dimmer switch that i installed replacing a single pole non dimmer switch. I only had two wires on the old switch and they were unmarked. The wire i assumed was hot was the one coming … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x