Customer Question
My generator has a 4...
My generator has a 4 prong 240v out let that I am trying to split down to 2 120v supplies. Each hot leg Wigs 117v when metered to the neutral. The problem is that when I use one leg the other leg spikes to 164v. Not sure why it would go out of ba***** *****ke that??
Submitted: 2 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 46 minutes by:
6/26/2015
Electrician: AssuredElectrical, Master Electrician replied 2 years ago
AssuredElectrical
AssuredElectrical, Master Electrician
Category: Electrical
Satisfied Customers: 4,241
Experience: Contractor-42+ Years in the ElectricalTrade
Verified
Welcome. My name is ***** ***** would be glad to assist.What type of load is on each of the phases?Tell me exactly how the items are wired on the cord that plugs into the generator receptacle.Let me know and we can continue,Thanks
Ask Your Own Electrical Question
Customer reply replied 2 years ago
Hi Tommy,
1) phase 15 amp A/C unit Old style hard start
2) phase 8 amp A/C with soft srartI fire up the soft start and it runs fine but the other leg spikes so I haven't tried to use it.
Wired Black hot, Red hot, White common, Green ground.I would have to take the cord cap apart to give you the Alpha characters but the two hot legs are on the sides, neutral at the top and dog leg ground on the bottom.
Electrician: AssuredElectrical, Master Electrician replied 2 years ago
Ok, thanks.Need the wiring so lets try it this way if we can.You have a cord with a male plug and plugged into the generator receptacle, correct?On the other end of the cord, you wire to what?Straight to the appliances?To receptacles?Or?How and where are you measuring?Everything is wired and ready, correct? Nothing disconnected, correct? Details and then we can move forward.
Ask Your Own Electrical Question
Customer reply replied 2 years ago
yes
1) Direct wiring to Hard Start A/C unit. About a 50' run.
2) Wired to cabin Panel. There are other outlets on this circuit but none are in use.(soft start)
Measuring with a Fluke meter.
Measuring 1) at the wire nut for the A/C unit (hard start)
Measuring 2) at the outlet that the A/C is plugged into.(soft start)
Everything wired and ready
Electrician: AssuredElectrical, Master Electrician replied 2 years ago
Ok, thanks.I believe all you have is an excitation situation.Since you have no load on the one phase, the windings are sitting in limbo, so to speak.The other phase needs excitation to begin to balance and produce some current.Take a simple lamp and plug into one of the receptacles. Even a high voltage is not going to do any damage to a standard household lamp.See if that doesn't begin the the excitation process within the generator.Turn on the lamp or even 2 if you have them before starting the AC unit on the other phase.You are trying to put the generator at a great imbalance to start with the AC unit.Always best to have a 220 volt AC unit to keep the phases balanced in current, which also keeps the voltage balanced
Ask Your Own Electrical Question
Customer reply replied 2 years ago
I will try as you have suggested but if that is the case, I will have to leave lamps burning all of the time because the A/C cycles on and off. At the very least I will have to add some other load to the direct wiring to the hard start A/C unit. This is a cabin in the middle of nowhere. I'm just trying to get the most out of the generator because the 120v side is only 20 amps and the 240v side is 30 amps.
Electrician: AssuredElectrical, Master Electrician replied 2 years ago
No, actually you need to do nothing if the test holds true.As soon as anything is started the voltage will drop on the other phase.It is not like it is going to be at the high level for any amount of time and then drop if its excitation.It will be in a 1/4 cycle is which equal to you blinking.It will not hurt a thing nor cause any issues.
Ask Your Own Electrical Question
Electrician: AssuredElectrical, Master Electrician replied 2 years ago
If it doesn't change is the problem. That will be a generator issue and needs work.
Ask Your Own Electrical Question
Electrician: AssuredElectrical, Master Electrician replied 2 years ago
One thing I just noticed on the write up."I'm just trying to get the most out of the generator because the 120v side is only 20 amps and the 240v side is 30 amps"I do not suggest having a phase imbalance of 30 amps on a generator.you are supposed to always balance as close as possible on them.That is why the receptacle is made to connect to a 120/240 volt panel and then distribute power, not for direct wiring.
Ask Your Own Electrical Question
Customer reply replied 2 years ago
I will give it a try but the Hard Start A/C is direct wired so I will try starting it first because I can add a load to the other leg.
Generator is new but who knows. Will get back to you. Thanks
Electrician: AssuredElectrical, Master Electrician replied 2 years ago
Ok, very good.Some AC units can pull 3-5 times normal at starting, so the generator must be large enough for the application.
Ask Your Own Electrical Question
Customer reply replied 2 years ago
Are you suggesting that I wire the 240 to my panel and then draw the power to both A/C units from there
Customer reply replied 2 years ago
I think I will dump the Hard Start and get a soft start just in case.
Electrician: AssuredElectrical, Master Electrician replied 2 years ago
With generators, i ti best to have a separate panel.You wire form the main panel to that panel, then from the generator to that panel.That becomes your emergency circuit panel. Only has the items for emergency useYou interlock the breakers, so only one power source at a time.Then you have a safe and viable installation.Your way is time consuming when you need the generator and takes time etc.I prefer quick and no work setupsYou can do it your way, just not suggested.
Ask Your Own Electrical Question
Customer reply replied 2 years ago
There is no main panel. It is a generator or nothing. I'm way out and stand alone.
Electrician: AssuredElectrical, Master Electrician replied 2 years ago
Ok, then just install a small panel with the circuit breakers you need.Then pre-wire the genny to it and be ready at a moments notice.this allows for later if you add any solar or another generator and have backup.Panel is best either way.
Ask Your Own Electrical Question
Customer reply replied 2 years ago
Got it. Will let you know the out come.
Electrician: AssuredElectrical, Master Electrician replied 2 years ago
Ok, thanks
Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask AssuredElectrical Your Own Question
AssuredElectrical
AssuredElectrical
AssuredElectrical, Master Electrician
Category: Electrical
Satisfied Customers: 4,241
4,241 Satisfied Customers
Experience: Contractor-42+ Years in the ElectricalTrade

AssuredElectrical is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

4,241 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I understand that multiple GFCIs (in series) is redundant
I understand that multiple GFCI's (in series) is redundant and therefore not necessary, however is it a "code violation"? I have two circuits that have 2 GFCI's in series. Of course my problem is that… read more
electrifier
electrifier
Master Electrician
Bachelor's Degree
1,458 satisfied customers
Both buttons on my GFI outlet are stuck and cannot be reset.
Both buttons on my GFI outlet are stuck and cannot be reset. All outlets on that circuit are dead. I reset the circuit breakers for all outlets and still no luck. Any ideas?… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
using a buck boost transformer can you plug in a 220 appliance
using a buck boost transformer can you plug in a 220 appliance into a 110 outlet… read more
electrifier
electrifier
Master Electrician
Bachelor's Degree
1,458 satisfied customers
I have a circuit breaker that keeps tripping about once a
I have a circuit breaker that keeps tripping about once a day. It runs my garage outlets and my backyard. I have an air compressor and power strip for my woodworking tools as well as our solar system … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have a breaker that wont stay on in my circuit breaker
I have a breaker that wont stay on in my circuit breaker panel. it is a Bryant type brd bd 20-20 cj-ac swd breaker. I would like to know how to replace it with a new one. reading other peoples questio… read more
David Bowden
David Bowden
Owner
987 satisfied customers
We have to replace allready my circuit breakers box and we
We have to replace allready my circuit breakers box and we instal de regular breakers but the inspector said we need to replace the breaker for type arc fault circuit interrupter it is true or no it i… read more
Sam I
Sam I
Electrician
B.S.
736 satisfied customers
The circuit breaker for our 4 year old microwave keeps
The circuit breaker for our 4 year old microwave keeps tripping, particularly if we use microwave consecutively, like to heat water, then reheat food, etc. We replaced circuit breaker and same thing is happening with new. It's almost like circuit can't handle multiple directions. What do you make of it? … read more
Sam I
Sam I
Electrician
B.S.
736 satisfied customers
Circuit breaker not thrown loss of power to section of
Circuit breaker not thrown loss of power to section of basement. It was off overnight tried it this morning there was power plugged in item and power off again … read more
Sam I
Sam I
Electrician
B.S.
736 satisfied customers
My new pump is tripping my circuit breaker, New and no, Yes,
I'm getting 120v both wires to the pump and it's a 115 Hayward super pump… read more
Sam I
Sam I
Electrician
B.S.
736 satisfied customers
Is it kosher to use two 120Volt circuit breakers to create a
Is it kosher to use two 120Volt circuit breakers to create a 240Volt circuit in a house panel?… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I live in a building. and the circuit breaker tripped for on
i live in a building. and the circuit breaker tripped for on side of the hall but the circuit breaker has a screw on one side not like a normal circuit breaker that you could just flip … read more
Sam I
Sam I
Electrician
B.S.
736 satisfied customers
I need assistance upgrading a circuit breaker to a sub
I need assistance upgrading a circuit breaker to a sub panel. I have all the specs of everything just need to know if it will work. Have photos if needed. … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I need to wire a 20A 250V Outlet. Ive got the power coming
I need to wire a 20A 250V Outlet. I've got the power coming from a 20A circuit breaker and the outlet the box has one hot (black) one neutral (white) , and one ground wire, but the 20a outlet wiring c… read more
Jason
Jason
Service Technician
Associate Degree
3,942 satisfied customers
I am wiring a 30 amp 120 volt circuit to power my RV. The distance
I am wiring a 30 amp 120 volt circuit to power my RV. The distance from the circuit breaker to the 30 amp outlet will be 70-80 feet. Do I need 10 or 8 guage wire? Do I need 10/2 or 10/3 or 8/2 or 8/3?… read more
Jason
Jason
Service Technician
Associate Degree
3,942 satisfied customers
I have a Coleman Powermate MAXA 5000ER generator Model PMO525202.
I have a Coleman Powermate MAXA 5000ER generator Model PMO525202. i would like to get a wiring diagram for the generator side of the unit it is equipped with both a 240 and 120 outlet two circuit brea… read more
Craig
Craig
Electrical Director
Electrical Automation Technician
2,133 satisfied customers
When the circuit breaker is off, there is a wee spark (you
When the circuit breaker is off, there is a wee spark (you can touch the two without a shock) between the ground wire and the white wire. Is this normal or does this mean that there is a cross-wire so… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have a really old fuse box with Buss Type W and Type S fuses.
I have a really old fuse box with Buss Type W and Type S fuses. The same Type W-20 fuse keeps blowing when I turn on the AC, can I put in a higher rated fuse instead like a Type S-30? Would that help?… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have partial loss of power in my house: no circuit breakers
I have partial loss of power in my house: no circuit breakers tripped. The lights appear dim and then fade away. Effected areas are scattered: Kitchen the oven (220) with dim light panel; two bedrooms… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x